You can tighten up the graph to minutes, even seconds if you set it up to
do so
Jerry
On Mon, Jun 1, 2020, 10:01 AM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> I didn't think an eGauge would provide that granular of detail if there is
> a very brief intermittent issue. If I'm w
I didn't think an eGauge would provide that granular of detail if there is
a very brief intermittent issue. If I'm wrong about that it might be worth
a try.
What I really want to do is install a separate breaker in the main panel
for the Envoy so it doesn't lose power when the IQ Combiner main bre
Jason, Wrenches
Can you install a data logger, say an eguage so you can see spikes or a
frequency shift, surge, most anything.
Install two non connected breakers to isolate the line, just for testing
purposes and see if it's only one that pops.
Jerry
On Mon, Jun 1, 2020, 9:11 AM Jason Szumlanski
Hi All
I’m wondering if anyone can point me to information or has information about
the following
1. Can cad tel ( first solar) modules be recycled or are they toxic waste?
2. How much active material is there per module or maybe watt. It has to be
really small.
I’ve had someone ask me abo
I considered that, but it's tripping at night, so it's not a power output
issue. It does have #6 wire, so this could be done, but I don't think it's
related. It's a genuine CH240 breaker. We even replaced it once before.
At this point, I must have a fault or faults on the roof. Maybe a rodent
chew
The problem is the intermittent nature of the problem. It can take 2-weeks
or more to trip again. The owner is not going to want to leave a string off
for an indefinite period of time.
On Mon, Jun 1, 2020 at 11:00 AM Dave Angelini Offgrid Solar <
offgridso...@sti.net> wrote:
> Run the system wi
That was the second thing I checked after the j-box. They all appear to be
good. I replaced a questionable one, but the tripping continued. I have
seen end cap issues before, especially if the hang down and get wet.
There are no excess connectors with sealing caps, so it's not that, either.
On
It's not weather. It's at all times of the day and night, and I confirmed
that there is no correlation to rain or high winds. That was my first
suspicion.
On Mon, Jun 1, 2020 at 10:27 AM Ray wrote:
> Is it at all weather related? Rain, or high humidity? High
> temperatures? Do you have any
Jason
Can you check for heat? How close is the branch breaker to the main breaker?
Maybe the bus bar is loose or the breaker is loose or wire is loose somewhere
causing heat to trip the breaker.
Thank you,
Maverick
> On Jun 1, 2020, at 9:24 AM, Jason Szumlanski
> wrote:
>
>
> Well, tha
Hi Jason,
My curiosity is about both breakers tripping.
I would suggest using a larger output breaker, I believe its a 40, put in a 50
as a test. I would assume the wire size will still be protected by the 50.
And I would also ask if the breakers are actual CH or clones?
jay
peltz power
Run the system without the branch that tripped. Sorry if I missed that
you have done this. I appreciate you reminding me why I keep all of the
electronics inside. I get tempted
Dave Angelini Offgrid Solar
"we go
where powerlines don't"
http://members.sti.net/offgridsolar/ [1]
e-mail
offgridso.
Are the module pv connectors, the same brand as the pv connectors on the
Enphase inverters?
Bryan Norkunas
br...@pv-cables.com
Description: Description: PV-Cables_Logo_Transparent_Bkgnd_140x140
PV-Cables Inc.
989 Milton Ave Ste 1D
Ferndale CA 95536
(707) 923-3000 office
www.pv-cable
Hi Jason - I know I've mentioned this before, but were you able to verify
that the branch trunk cable end caps are properly installed? We've had a
few cases of intermittent breaker tripping where the end caps were not
installed, had fallen off, or not properly installed. A little moisture
leads to
Is it at all weather related? Rain, or high humidity? High
temperatures? Do you have any indication what time of day it trips off at?
Ray Walters
Remote Solar
303 505-8760
On 6/1/20 10:23 AM, Jason Szumlanski wrote:
Well, that didn't resolve it. The main breaker and a branch circuit
breaker
Well, that didn't resolve it. The main breaker and a branch circuit breaker
tripped again a few days ago. It was the same branch this time.
As my next diagnostic step I swapped two circuits (on which breaker they
are landed). If history is a guide, it will work for about two weeks and
then trip ag