Are the module pv connectors, the same brand as the pv connectors on the 
Enphase inverters?

 

Bryan Norkunas

br...@pv-cables.com

 

Description: Description: PV-Cables_Logo_Transparent_Bkgnd_140x140

PV-Cables Inc. 

989 Milton Ave Ste 1D

Ferndale CA 95536

(707) 923-3000 office

www.pv-cables.com <http://www.pv-cables.com/> 

 

 Description: Description: cid:image002.jpg@01CD22E8.974B6470 Please print only 
if necessary.

 

NOTE: This email message and any attachments are for the sole use of the 
intended recipient(s) and may contain confidential and/or privileged 
information. Any unauthorized review, use, disclosure or distribution is 
prohibited. If you are not the intended recipient, please contact the sender by 
replying to this email, and destroy all copies of the original message.

 

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Jason Szumlanski
Sent: Monday, June 1, 2020 7:24 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Enphase intermittent breaker trippjng

 

Well, that didn't resolve it. The main breaker and a branch circuit breaker 
tripped again a few days ago. It was the same branch this time. 

 

As my next diagnostic step I swapped two circuits (on which breaker they are 
landed). If history is a guide, it will work for about two weeks and then trip 
again.

 

I'm dumbfounded. I really don't want to have to tear this whole system apart. 
At this point, if I have to remove all the modules, I feel that I need to 
replace all of the trunk cable which is an expensive proposition. I really 
don't know what else to do at this point.

 

Jason

 

 

On Mon, May 25, 2020, 10:43 AM Jason Szumlanski 
<ja...@floridasolardesigngroup.com> wrote:

I strongly suspect the CH240 combined breaker was compromised (we will see). 
Since it happened that two different strings tripped, I doubt I have two 
microinverters with internal faults. It has to be the combined breaker. I was 
just surprised that branch circuit breakers were tripping simultaneously with 
the combined output breaker.

 

Of all the supply side connected systems I have installed, I have never seen a 
combined output fusible disconnect fuse blow, but I have seen many combined 
output breakers tripped. I was worried early on that I would be replacing fuses 
constantly, but that has not been an issue whatsoever.

 

 

                        
        

 

 

 

On Thu, May 21, 2020 at 11:15 AM <scot.a...@solarcentex.com> wrote:

Actually, we had a IQ7 string loaded up to its max panel size and max string 
length and in the spring on cool, clear day, it tripped the string’s associated 
breaker in the Enphase combiner.

 

We reset but of course that breaker was impaired and it tripped again. We 
replaced and never had an issue going forward. We suspect the breaker was less 
than perfect from the start as we’ve add equally nice days since.

 

This almost reminds me of loading up Outback FM80. It says 4,000 watts but in 
reality, 3,600 is the max when amps spike. I will be extra careful going 
forward on IQ7 string length when going to the max published…

 

My story.

 

Scot

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
Jason Szumlanski
Sent: Thursday, May 21, 2020 8:57 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Enphase intermittent breaker trippjng

 

I'm trying to resolve an intermittent frustrating problem with and Enphase IQ 
system. There are three AC Branch circuits of 9 microinverters each coming into 
an Enphase AC combiner. 

 

What has been happening is one of the BR220 branch circuit breakers and the 
combine CH240 breaker in the main backfed load center have been tripping 
simultaneously. It has happened about four times in the last 6 months. It was 
always the same branch circuit breaker, so we kept investigating that string, 
checking the junction box, trunk cable, and cap, etc. Finally we swapped out 
the BR220 breaker. 

 

Fast forward 4 weeks, and we got another call. This time a different branch 
circuit breaker and the main breaker tripped simultaneously. We checked that 
branch circuit and could not find any fault. It seems unlikely that two branch 
circuit breakers would be faulty, so we have now switched out the CH240 main 
breaker in hopes that it is the culprit.  

 

I'm not totally confident in this resolution and I have my fingers crossed. If 
that doesn't work, does anyone have any suggestions on another diagnostic step? 
These intermittent problems are a major hassle. One thought I had was to switch 
to a supply side interconnection with a fusible disconnect. Maybe the 
intermittent fault would blow one of the two line fuses so at least I could 
narrow it down to which line the fault is on if there is in fact a fault.

 

I have experienced two other tripping breaker issues with Enphase systems in 
the past. Neither of them were systems I installed. One turned out to be branch 
circuits that were not properly paired up and landed on different breakers. 
Another time we had an inverter with an internal fault which eventually"blew 
up" with a loud popping noise and smoke billowing out of it. That happened 
after resetting a trip breaker multiple times. This case seems to be unrelated 
to those issues. I'm perplexed. 

 

Jason Szumlanski

Florida Solar Design Group

 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
<https://mailtrack.io/trace/link/796b1796eb4c075a74298513a530f62e4a496cb2?notrack=1&url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c7dea131fd9cb45a>
 

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
<https://mailtrack.io/trace/link/c06e48af2da3d129a58c08ef2043bd2d8fcbef6f?notrack=1&url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=06899a19621f54d8>
 

List rules & etiquette:
www.re-wrenches.org/etiquette.htm 
<https://mailtrack.io/trace/link/215cb4d0fcfb04e4124aae9b2616249f1eef5542?notrack=1&url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8bc84049c81c183c>
 

Check out or update participant bios:
www.members.re-wrenches.org 
<https://mailtrack.io/trace/link/27c3e706e7f2b4836b1669b31c9454db7fee1b52?notrack=1&url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4a75a2d55681f39a>
 

Error! Filename not specified.

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to