The problem is the intermittent nature of the problem. It can take 2-weeks or more to trip again. The owner is not going to want to leave a string off for an indefinite period of time.
On Mon, Jun 1, 2020 at 11:00 AM Dave Angelini Offgrid Solar < offgridso...@sti.net> wrote: > Run the system without the branch that tripped. Sorry if I missed that you > have done this. I appreciate you reminding me why I keep all of the > electronics inside. I get tempted[image: Wink] > > > > *Dave Angelini Offgrid Solar > "we go where powerlines don't" > http://members.sti.net/offgridsolar/ > <https://mailtrack.io/trace/link/3184eed65ad0009b17f7a1eb448e78663d79c7d8?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&userId=1613865&signature=7eb043f982852f6d> > e-mail offgridso...@sti.net <offgridso...@sti.net> > text 209 813 0060* > > On Mon, 1 Jun 2020 10:23:35 -0400, Jason Szumlanski < > ja...@floridasolardesigngroup.com> wrote: > > Well, that didn't resolve it. The main breaker and a branch circuit > breaker tripped again a few days ago. It was the same branch this time. > > As my next diagnostic step I swapped two circuits (on which breaker they > are landed). If history is a guide, it will work for about two weeks and > then trip again. > > I'm dumbfounded. I really don't want to have to tear this whole system > apart. At this point, if I have to remove all the modules, I feel that I > need to replace all of the trunk cable which is an expensive proposition. I > really don't know what else to do at this point. > > Jason > > > On Mon, May 25, 2020, 10:43 AM Jason Szumlanski < > ja...@floridasolardesigngroup.com> wrote: > >> I strongly suspect the CH240 combined breaker was compromised (we will >> see). Since it happened that two different strings tripped, I doubt I have >> two microinverters with internal faults. It has to be the combined breaker. >> I was just surprised that branch circuit breakers were tripping >> simultaneously with the combined output breaker. >> >> Of all the supply side connected systems I have installed, I have never >> seen a combined output fusible disconnect fuse blow, but I have seen many >> combined output breakers tripped. I was worried early on that I would be >> replacing fuses constantly, but that has not been an issue whatsoever. >> >> >> >> >> >> On Thu, May 21, 2020 at 11:15 AM <scot.a...@solarcentex.com> wrote: >> >>> Actually, we had a IQ7 string loaded up to its max panel size and max >>> string length and in the spring on cool, clear day, it tripped the string's >>> associated breaker in the Enphase combiner. >>> >>> >>> >>> We reset but of course that breaker was impaired and it tripped again. >>> We replaced and never had an issue going forward. We suspect the breaker >>> was less than perfect from the start as we've add equally nice days since. >>> >>> >>> >>> This almost reminds me of loading up Outback FM80. It says 4,000 watts >>> but in reality, 3,600 is the max when amps spike. I will be extra careful >>> going forward on IQ7 string length when going to the max published... >>> >>> >>> >>> My story. >>> >>> >>> >>> Scot >>> >>> >>> >>> *From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> *On >>> Behalf Of *Jason Szumlanski >>> *Sent:* Thursday, May 21, 2020 8:57 AM >>> *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org> >>> *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng >>> >>> >>> >>> I'm trying to resolve an intermittent frustrating problem with and >>> Enphase IQ system. There are three AC Branch circuits of 9 microinverters >>> each coming into an Enphase AC combiner. >>> >>> >>> >>> What has been happening is one of the BR220 branch circuit breakers and >>> the combine CH240 breaker in the main backfed load center have been >>> tripping simultaneously. It has happened about four times in the last 6 >>> months. It was always the same branch circuit breaker, so we kept >>> investigating that string, checking the junction box, trunk cable, and cap, >>> etc. Finally we swapped out the BR220 breaker. >>> >>> >>> >>> Fast forward 4 weeks, and we got another call. This time a different >>> branch circuit breaker and the main breaker tripped simultaneously. We >>> checked that branch circuit and could not find any fault. It seems unlikely >>> that two branch circuit breakers would be faulty, so we have now switched >>> out the CH240 main breaker in hopes that it is the culprit. >>> >>> >>> >>> I'm not totally confident in this resolution and I have my fingers >>> crossed. If that doesn't work, does anyone have any suggestions on another >>> diagnostic step? These intermittent problems are a major hassle. One >>> thought I had was to switch to a supply side interconnection with a fusible >>> disconnect. Maybe the intermittent fault would blow one of the two line >>> fuses so at least I could narrow it down to which line the fault is on if >>> there is in fact a fault. >>> >>> >>> >>> I have experienced two other tripping breaker issues with Enphase >>> systems in the past. Neither of them were systems I installed. One turned >>> out to be branch circuits that were not properly paired up and landed on >>> different breakers. Another time we had an inverter with an internal fault >>> which eventually"blew up" with a loud popping noise and smoke billowing out >>> of it. That happened after resetting a trip breaker multiple times. This >>> case seems to be unrelated to those issues. I'm perplexed. >>> >>> >>> >>> Jason Szumlanski >>> >>> Florida Solar Design Group >>> >>> >>> >>> >>> _______________________________________________ >>> List sponsored by Redwood Alliance >>> >>> List Address: RE-wrenches@lists.re-wrenches.org >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> <https://mailtrack.io/trace/link/fe17c52b9a8d3bc08283b160a0f5a8119e164f80?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=9be98fc5b7d988f8> >>> >>> List-Archive: >>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >>> <https://mailtrack.io/trace/link/56e1e0ef112289d1a242c87c9a287bac904aa544?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=d4debec5a869742f> >>> >>> List rules & etiquette: >>> www.re-wrenches.org/etiquette.htm >>> <https://mailtrack.io/trace/link/8d2e543d7e9cacc05ab138f49e856b75d2e32eda?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=4222e664d0288417> >>> >>> Check out or update participant bios: >>> www.members.re-wrenches.org >>> <https://mailtrack.io/trace/link/fe890d63cd82ab67c5f01a708be999b95203b04e?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=af2d121248233133> >>> >> _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <https://mailtrack.io/trace/link/75f7db9b6b07fd612f2781111afc2b19f9cf63db?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=46a764246342ac65> > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > <https://mailtrack.io/trace/link/3450fa5b9216fb23b94d4c411f0c3c594574bdbd?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=6f92823e6621aa30> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > <https://mailtrack.io/trace/link/f6b6aba3ac134446a790b702da6f12cc4279d80c?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=2bcb0609252d15ae> > > Check out or update participant bios: > www.members.re-wrenches.org > <https://mailtrack.io/trace/link/4d8715a2def645f7f812021350e0b50fb3fd90cc?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=0d5a1db579515698> > >
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org