It's not weather. It's at all times of the day and night, and I confirmed
that there is no correlation to rain or high winds. That was my first
suspicion.



On Mon, Jun 1, 2020 at 10:27 AM Ray <r...@solarray.com> wrote:

> Is it at all weather related?  Rain, or high humidity?  High
> temperatures?  Do you have any indication what time of day it trips off at?
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 6/1/20 10:23 AM, Jason Szumlanski wrote:
>
> Well, that didn't resolve it. The main breaker and a branch circuit
> breaker tripped again a few days ago. It was the same branch this time.
>
> As my next diagnostic step I swapped two circuits (on which breaker they
> are landed). If history is a guide, it will work for about two weeks and
> then trip again.
>
> I'm dumbfounded. I really don't want to have to tear this whole system
> apart. At this point, if I have to remove all the modules, I feel that I
> need to replace all of the trunk cable which is an expensive proposition. I
> really don't know what else to do at this point.
>
> Jason
>
>
> On Mon, May 25, 2020, 10:43 AM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> I strongly suspect the CH240 combined breaker was compromised (we will
>> see). Since it happened that two different strings tripped, I doubt I have
>> two microinverters with internal faults. It has to be the combined breaker.
>> I was just surprised that branch circuit breakers were tripping
>> simultaneously with the combined output breaker.
>>
>> Of all the supply side connected systems I have installed, I have never
>> seen a combined output fusible disconnect fuse blow, but I have seen many
>> combined output breakers tripped. I was worried early on that I would be
>> replacing fuses constantly, but that has not been an issue whatsoever.
>>
>>
>>
>>
>>
>>
>>
>> On Thu, May 21, 2020 at 11:15 AM <scot.a...@solarcentex.com> wrote:
>>
>>> Actually, we had a IQ7 string loaded up to its max panel size and max
>>> string length and in the spring on cool, clear day, it tripped the string’s
>>> associated breaker in the Enphase combiner.
>>>
>>>
>>>
>>> We reset but of course that breaker was impaired and it tripped again.
>>> We replaced and never had an issue going forward. We suspect the breaker
>>> was less than perfect from the start as we’ve add equally nice days since.
>>>
>>>
>>>
>>> This almost reminds me of loading up Outback FM80. It says 4,000 watts
>>> but in reality, 3,600 is the max when amps spike. I will be extra careful
>>> going forward on IQ7 string length when going to the max published…
>>>
>>>
>>>
>>> My story.
>>>
>>>
>>>
>>> Scot
>>>
>>>
>>>
>>> *From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> *On
>>> Behalf Of *Jason Szumlanski
>>> *Sent:* Thursday, May 21, 2020 8:57 AM
>>> *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
>>> *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng
>>>
>>>
>>>
>>> I'm trying to resolve an intermittent frustrating problem with and
>>> Enphase IQ system. There are three AC Branch circuits of 9 microinverters
>>> each coming into an Enphase AC combiner.
>>>
>>>
>>>
>>> What has been happening is one of the BR220 branch circuit breakers and
>>> the combine CH240 breaker in the main backfed load center have been
>>> tripping simultaneously. It has happened about four times in the last 6
>>> months. It was always the same branch circuit breaker, so we kept
>>> investigating that string, checking the junction box, trunk cable, and cap,
>>> etc. Finally we swapped out the BR220 breaker.
>>>
>>>
>>>
>>> Fast forward 4 weeks, and we got another call. This time a different
>>> branch circuit breaker and the main breaker tripped simultaneously. We
>>> checked that branch circuit and could not find any fault. It seems unlikely
>>> that two branch circuit breakers would be faulty, so we have now switched
>>> out the CH240 main breaker in hopes that it is the culprit.
>>>
>>>
>>>
>>> I'm not totally confident in this resolution and I have my fingers
>>> crossed. If that doesn't work, does anyone have any suggestions on another
>>> diagnostic step? These intermittent problems are a major hassle. One
>>> thought I had was to switch to a supply side interconnection with a fusible
>>> disconnect. Maybe the intermittent fault would blow one of the two line
>>> fuses so at least I could narrow it down to which line the fault is on if
>>> there is in fact a fault.
>>>
>>>
>>>
>>> I have experienced two other tripping breaker issues with Enphase
>>> systems in the past. Neither of them were systems I installed. One turned
>>> out to be branch circuits that were not properly paired up and landed on
>>> different breakers. Another time we had an inverter with an internal fault
>>> which eventually"blew up" with a loud popping noise and smoke billowing out
>>> of it. That happened after resetting a trip breaker multiple times. This
>>> case seems to be unrelated to those issues. I'm perplexed.
>>>
>>>
>>>
>>> Jason Szumlanski
>>>
>>> Florida Solar Design Group
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/fdc3b2ff41fb06d9fc639def42a495f3c136f3db?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=098ec45eb33f9b00>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> <https://mailtrack.io/trace/link/6bc50363ca2add2d415fb87b3cd23366d9e7d039?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=a337cd5107c087d0>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/75ef476cb6bde5c4268917fd9cc2e6db3770fcae?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=56066347dd7e5127>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/2665831d506b33b1248b1ac93f51a36e161ebdda?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=e07a34933e58e994>
>>>
>>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <https://mailtrack.io/trace/link/66018640dfb9cd7bbdd7ee9d01d95dc0d33549ef?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=0597a67facffbf38>
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> <https://mailtrack.io/trace/link/36249f76ae59219ded6c24b42c26030cc7f79f76?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=be80d3682a1c98bb>
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm 
> <https://mailtrack.io/trace/link/1a533dda41f4c49b5e99a6ee9e91e575fa518886?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f94a28b8d3a69cab>
>
> Check out or update participant bios:www.members.re-wrenches.org 
> <https://mailtrack.io/trace/link/21bf07b6c4bd0b07c7cd1accb625bb1970481392?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=7c9caaa93a1a66e1>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/5468f7a737fd7e45c58f1705a0a1ed0ccd347595?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=83b4369d9d971356>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/4c3b02bf6234d19fd2ca8148a484b40d8f963690?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=87433120c7b8d362>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/a6ec6f78624a6a5fadbfb0018bce4b8c17cb66a2?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=569ecbab7a50fc52>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/23e853250b78cd0ba3ee23f17fe87cc1c5adb638?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4ccb869a2bf020e0>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to