I considered that, but it's tripping at night, so it's not a power output
issue. It does have #6 wire, so this could be done, but I don't think it's
related. It's a genuine CH240 breaker. We even replaced it once before.

At this point, I must have a fault or faults on the roof. Maybe a rodent
chewed through some wires. I'm going to wait for another fault and then go
pull the modules to check it out.



On Mon, Jun 1, 2020 at 11:00 AM jay <jay.pe...@gmail.com> wrote:

> Hi Jason,
>
> My curiosity is about both breakers tripping.
> I would suggest using a larger output breaker, I believe its a 40, put in
> a 50 as a test.  I would assume the wire size will still be protected by
> the 50.
>
> And I would also ask if the breakers are actual CH or clones?
>
> jay
>
> peltz power
>
> On Jun 1, 2020, at 7:23 AM, Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
> Well, that didn't resolve it. The main breaker and a branch circuit
> breaker tripped again a few days ago. It was the same branch this time.
>
> As my next diagnostic step I swapped two circuits (on which breaker they
> are landed). If history is a guide, it will work for about two weeks and
> then trip again.
>
> I'm dumbfounded. I really don't want to have to tear this whole system
> apart. At this point, if I have to remove all the modules, I feel that I
> need to replace all of the trunk cable which is an expensive proposition. I
> really don't know what else to do at this point.
>
> Jason
>
>
> On Mon, May 25, 2020, 10:43 AM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> I strongly suspect the CH240 combined breaker was compromised (we will
>> see). Since it happened that two different strings tripped, I doubt I have
>> two microinverters with internal faults. It has to be the combined breaker.
>> I was just surprised that branch circuit breakers were tripping
>> simultaneously with the combined output breaker.
>>
>> Of all the supply side connected systems I have installed, I have never
>> seen a combined output fusible disconnect fuse blow, but I have seen many
>> combined output breakers tripped. I was worried early on that I would be
>> replacing fuses constantly, but that has not been an issue whatsoever.
>>
>>
>>
>>
>>
>>
>> On Thu, May 21, 2020 at 11:15 AM <scot.a...@solarcentex.com> wrote:
>>
>>> Actually, we had a IQ7 string loaded up to its max panel size and max
>>> string length and in the spring on cool, clear day, it tripped the string’s
>>> associated breaker in the Enphase combiner.
>>>
>>>
>>>
>>> We reset but of course that breaker was impaired and it tripped again.
>>> We replaced and never had an issue going forward. We suspect the breaker
>>> was less than perfect from the start as we’ve add equally nice days since.
>>>
>>>
>>>
>>> This almost reminds me of loading up Outback FM80. It says 4,000 watts
>>> but in reality, 3,600 is the max when amps spike. I will be extra careful
>>> going forward on IQ7 string length when going to the max published…
>>>
>>>
>>>
>>> My story.
>>>
>>>
>>>
>>> Scot
>>>
>>>
>>>
>>> *From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> *On
>>> Behalf Of *Jason Szumlanski
>>> *Sent:* Thursday, May 21, 2020 8:57 AM
>>> *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
>>> *Subject:* [RE-wrenches] Enphase intermittent breaker trippjng
>>>
>>>
>>>
>>> I'm trying to resolve an intermittent frustrating problem with and
>>> Enphase IQ system. There are three AC Branch circuits of 9 microinverters
>>> each coming into an Enphase AC combiner.
>>>
>>>
>>>
>>> What has been happening is one of the BR220 branch circuit breakers and
>>> the combine CH240 breaker in the main backfed load center have been
>>> tripping simultaneously. It has happened about four times in the last 6
>>> months. It was always the same branch circuit breaker, so we kept
>>> investigating that string, checking the junction box, trunk cable, and cap,
>>> etc. Finally we swapped out the BR220 breaker.
>>>
>>>
>>>
>>> Fast forward 4 weeks, and we got another call. This time a different
>>> branch circuit breaker and the main breaker tripped simultaneously. We
>>> checked that branch circuit and could not find any fault. It seems unlikely
>>> that two branch circuit breakers would be faulty, so we have now switched
>>> out the CH240 main breaker in hopes that it is the culprit.
>>>
>>>
>>>
>>> I'm not totally confident in this resolution and I have my fingers
>>> crossed. If that doesn't work, does anyone have any suggestions on another
>>> diagnostic step? These intermittent problems are a major hassle. One
>>> thought I had was to switch to a supply side interconnection with a fusible
>>> disconnect. Maybe the intermittent fault would blow one of the two line
>>> fuses so at least I could narrow it down to which line the fault is on if
>>> there is in fact a fault.
>>>
>>>
>>>
>>> I have experienced two other tripping breaker issues with Enphase
>>> systems in the past. Neither of them were systems I installed. One turned
>>> out to be branch circuits that were not properly paired up and landed on
>>> different breakers. Another time we had an inverter with an internal fault
>>> which eventually"blew up" with a loud popping noise and smoke billowing out
>>> of it. That happened after resetting a trip breaker multiple times. This
>>> case seems to be unrelated to those issues. I'm perplexed.
>>>
>>>
>>>
>>> Jason Szumlanski
>>>
>>> Florida Solar Design Group
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/8c0096d709302b67472f73bf32acfd40845b7e4c?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=cea813884cd1776f>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> <https://mailtrack.io/trace/link/7f6e46baa53c0f088f6f5abc3faeb59b5b39edac?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=046124c43854e1c6>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/4ead2a999e321be27ee82b54537fca6114171f77?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=53ba99e19aec38ce>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/c05eb859e4e6f49d4ff50203fb3f688b154912ed?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4673099afce34622>
>>>
>>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/833b32db0cd9b4ac8404176f341a407a99fdbd9e?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e251c31629e87d66>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/71bb51b2728637d9ad93b24d683a193a72006019?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=38ee76e96b406bb9>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/8087ed9e2dd757e2954dced8db769542d582ca08?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=a25cf8271d2631a3>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/3a7d1829947402a13cf48b068d7a32bac6b949f9?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=025e09a842f8cce6>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/0dcb42e4595ea9843c350b74bb8c2700a8cf76a2?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=1ede486b5e2071b9>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/c8fed885f4d68840a28393cff58ea97019ff9897?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=9cbdc0024d590368>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/5ad9358e3c2ecbc8f2854c2d7b15b002312ebadb?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=d9df06b27b1a8494>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/b58440751026799b545dd915c9be157731498e57?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=249a8c1c6330f5f7>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org