Re: [RE-wrenches] Outback inverter-generator question

2017-12-18 Thread Chris Mason
charged in just over an hr. and NO l did not
> > take
> > >> any losses into account but this was with D-8 DCFLA not sealed AGM's
> > >>
> > >> On Sat, Aug 12, 2017 at 2:32 PM, Ron Young  >
> > >> wrote:
> > >>> Have a client where I recently installed an Outback VFX3524 inverter
> in
> > >>> June. He’s using a Honda generator and has recently started having
> > issues.
> > >>> He has been complaining that the inverter seems to be running hot
> but I
> > >>> believe this is because he doesn’t have good ventilation around it.
> He
> > is
> > >>> probably also running high on the loads. He doesn’t have a Mate so
> > can’t
> > >>> identify the error. He is in a remote location and I am currently
> > unable to
> > >>> travel due to fire restrictions in my area (major BC wildfires).
> > >>>
> > >>> Here is his recent email:
> > >>> -Seems the inverter is recognizing the power in as an issue, and
> > throwing
> > >>> an error.
> > >>> -My existing 5000 Honda generator has been online with the unit since
> > you
> > >>> installed it.
> > >>> -The last few days, when there is very little load, or the unit goes
> to
> > >>> float, the generator goes into a high rpm.
> > >>> -My existing 5000 Honda crapped out on me this morning, and holds a
> low
> > >>> rpm, not putting out much power.  Will run a tool, but still won’t
> > hold a
> > >>> higher rpm.
> > >>> -I borrowed an identical 5000 Honda generator, and it seemed to be
> > doing
> > >>> fine for about 1.5 hours.
> > >>> -Now it’s doing the same thing as the other generator.  The inverter
> > >>> system throws an error, the generator is taken offline, and the
> > generator
> > >>> rpm go up.
> > >>> -If I manually manipulate the throttle not he generator lower, then
> the
> > >>> inverter re-engages.
> > >>>
> > >>> What the heck could this be?  I don’t want to fry the borrowed
> > generator,
> > >>> but we can’t systematically bypass the inverter, and the house
> > requires the
> > >>> power.
> > >>>
> > >>> Ron Young
> > >>> earthRight - Solareagle
> > >
> > > *Allan Sindelar*
> > > al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>  > al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>>
> > > NABCEP Certified PV Installation Professional
> > > New Mexico EE98J Journeyman Electrician
> > > Founder (Retired), Positive Energy, Inc.
> > > *505 780-2738 cell*
> > >
> > > ___
> > > List sponsored by Redwood Alliance
> > >
> > > List Address: RE-wrenches@lists.re-wrenches.org
> > >
> > > Change listserver email address & settings:
> > > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> > >
> > > List-Archive: http://www.mail-archive.com/
> re-wrenc...@lists.re-wrenches.
> > org/maillist.html
> > >
> > > List rules & etiquette:
> > > www.re-wrenches.org/etiquette.htm
> > >
> > > Check out or update participant bios:
> > > www.members.re-wrenches.org
> >
> > ___
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> > org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> >
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-09 Thread Chris Mason
If the unit is still under warranty, have any Generac dealer run through
the diagnostics. The testing flow suggests rotor or stator problems, and
there is a proscribed testing flow that needs to be performed. If it is
determined to be a warranty issue, it will be fixed for you at no cost.
If it is not under warranty, I would still have a dealer look at it. There
are a large number of possible issues and you are going to spend a lot of
time trying to find the problem. A Generac tech will likely find the
problem in a few minutes unless it is a serious problem, in which case you
were never going to find it.
I'm a Generac tech so I can speak from some experience that this is likely
not a simple issue.

On Mon, Jan 8, 2018 at 8:13 PM, David Palumbo  wrote:

> I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that
> starts quickly
> • but immediately shuts down with an “Under Voltage” shutdown alarm
> • I can clear shutdown alarm and restart with same result. I tried this a
> few times with same result. One of the start attempts included a back fire
> before shutting down.
> • Generator was recently run successfully for a few hours during a cold
> snap. Started after several attempts at -10 F.
> • According to the EcoGen manual this Under Voltage alarm is triggered “If
> the generator voltage falls below 85% of nominal for more than 15
> seconds”.  This definitely isn’t happening as the generator starts as usual
> but shuts down within one or two seconds.
> I will check for fouled spark plugs tomorrow. Anything else that might be
> the problem?
>
> David Palumbo
> Independent Power LLC
> Hyde Park, VT
> 802-371-8678 voice or text
>
> Sent from Mail for Windows 10
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] 1,000V combiners

2018-01-19 Thread Chris Mason
We are looking at Fronius Symo  24.0-3 480 for a 120KW rooftop project but
I am having problems identifying a 1,000V fused disco combiner for the six
strings. I'm looking for suggestions for suitable products.

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] automatic transfer switch

2018-01-19 Thread Chris Mason
I think Radians are redundant anyway, if you parallel the output they will
keep going when one fails. Also, the 8KW are two x 4KW modules, both can
function independently. I know this because we lost one at home and kept
going until a replacement arrived.

On Thu, Jan 11, 2018 at 7:03 PM, jay  wrote:

> HI all,
>
> I’m doing a project with 2 radians in a redundant configuration.
> Each one would go into a transfer switch to power the common load.
>
> I’m looking for a good, fast transfer switch.  30amp 120/240 is fine.
> And maybe a mechanical feature as well.
> Code isn’t an issue
> Will be off grid, remote mexico.
>
> There is the Iota of course, but was just looking for options.
>
> thx in advance,
>
> jay
>
> peltz power
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1,000V combiners

2018-01-23 Thread Chris Mason
The reason I need these inverters is we had two CL60 480V inverters with
bases, and they fell off the bases in the hurricane and filled with water.
They were good inverters but the bases were garbage and could not support
the inverters in high wind. Very disappointing as the arrays had only a
relatively small amount of damage.

I am planning on using the Symo 24 fused inputs directly, recabling to hard
wire the strings to the inverters. That's how we do all our European spec
systems, it's so much better to have all the strings present at the
inverter.

Thanks for your advice.

On Tue, Jan 23, 2018 at 11:40 AM, Connell Christopher <
connell.christop...@fronius.com> wrote:

> Hi Chris,
>
> Please note that US models on the Symo 24.0-3 come with integrated fusing
> on the terminal block, so what you are asking for may not be needed.
> SolarBos does make some rather nice pass thru combiners as well, the
> F6sk-1FF-4xp is the part number which we typically recommended. This is a
> “pass thru” version. There is a combiner version as well.
>
>
>
> Please note that the Fronius SnapInverter series (Galvo, Primo, Symo) are
> Nema4x, which have passed all required testing, including being sprayed
> with a hose with 65 GPM (Gallons per min) from a 1 inch nozzle from of 10
> feet for 5 minutes. Fronius International has investigated water ingress
> problems pertaining to our product. Statistics have shown that less than 1%
> of installations in the USA have experienced water ingress problems. The
> majority of these less than 1% of installations which experienced this,
> were found to be installation errors (over 90%). The problem is usually
> when there are multiple inverter installed on a site the same way, leading
> to multiple inverters with water ingress, (IE, Improper Torque on the
> datcom cover).
>
> If you have any questions, please contact me at technical support at
> 219-734-5500 <(219)%20734-5500>
>
> Thanks
>
> 
> -
>
> Chris Connell
>
>
>
> /  Team Leader
>
> /  Technical Support Dept.
>
> /  Fronius USA LLC
>
> /  6797 Fronius Drive  /  Portage, IN 46368/ USA
>
>
>
> /  Main: +1 (219) 734-5500 <(219)%20734-5500>
>
> /  Fax: +1 (219) 734-5502 <(219)%20734-5502>
>
> /  *connell.christop...@fronius.com *
> /  www.fronius.com
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] has anyone ever had this happen?

2018-01-23 Thread Chris Mason
I've done this once because the client had duty free concessions, he had to
have the manufacturer's invoices. I quoted him Cost plus 20 for the
materials plus a labour fee and a management fee.
He took the quote and I never heard from him again, guess he tried to buy
the goods at the same cost.
One way around this is to explain that you have confidential pricing and
giving that to them would break that agreement.
On the other hand, I work with a large company that handled the shipping
and brokerage, so they had to get my supplier invoices. But, and this may
work for you, I first signed a Per-Watt contract with them, so what they
seen afterwards didn't make any difference.
You can always edit the invoices to make them higher.



On Tue, Jan 23, 2018 at 2:48 PM, jay  wrote:

>
> HI All,
>
> I’ve had a large company want to do a project and they want me to invoice
> it as follows.  They said it had to do with knowing the cost of the system,
> but that doesn’t seem right to me. Now I don’t want to get screwed here,
> and it sure seems that could happen.
>
> I’m pretty sure I know what you all will say, but I feel like I needed to
> get a bit of a reality check.
> As I mostly do projects on a handshake, dealing with large companies isn’t
> too common for me.
>
>
> 1. give them wholesale pricing ( line item by item)
> 2. add margin, but small one is all they’ll accept
>
> Project is an off grid, no permits, in Mexico, remote site and pretty
> big:  16kw inverter, 9kw PV, etc.
>
> Thanks
>
> jay
>
> peltz power
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Is there a charge controller do this?

2018-01-29 Thread Chris Mason
PWM chargers should work fine, dial the generators to about 50V. Then the
batteries will charge to 50V float, and the solar will manage the stages
after that. 4 x 60A PWM charger should do what you want. You can buy a 20A
and see how that works so you don't waste much money.

On Sun, Jan 28, 2018 at 11:23 PM, Mac Lewis  wrote:

> Hello wrenches,
>
> I'm working on 3 off-grid telecom sites.  They are designed to operate
> solar only under most conditions but the project manager ordered a
> custom-built 48 VDC generators, intended to be used as the battery
> charger/backup power for the site.  These are ~20 kW generators, and can
> probably do about ~350Adc at 48 Vdc at the elevation that these are sited.
> The battery banks are 4 x 1000 Ahr GS Nanocarbon 48 battery strings and can
> gobble up the 350Adc easily when they are discharged.
>
> While discussing the generator operation with the generator supplier, we
> have found this generator isn't capable of charge control, or limiting its
> own output.  The charge control functionality isn't necessary at this site
> because we really just need it to keep things online until the sun returns,
> a simple 54 VDC float voltage would work.  However, without the generator
> being able to self-limit its output, we expect this generator to stall when
> started because it can't regulate its output current and will immediately
> become overloaded by the discharged batteries.
>
> I am trying to come up with some options to rectify this serious design
> issue.  One idea that immediately came to mind was putting in some parallel
> solar charge controllers between the DC generator output and the battery
> bank.  If the generator output could be dialed up to around 60-70 VDC,
> could parallel solar charge controllers be used for charge regulation?  It
> would be kind of like charging a 48 V battery bank from a 70 V battery
> bank.  MPPT isn't applicable, could the max current limit in the charge
> controller(s) be used to regulate charge rate?  Will the charge controllers
> blow up?  If not, what brand might work.  Each site has 8 x Midnite Classic
> 150s but I'm open to other manufacturers if it would work.  I am open to
> blowing up a charge controller in the shop but I thought it best to ask
> first.
>
> What are other ways to put this generator to use, and limit its load?
>
>
>
> Thanks for your input/comments
>
>
>
>
>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Auger for ground mount

2018-02-09 Thread Chris Mason
I'm taking on construction of a ground mount system of about 30KW. My
previous experience has entailed using a utility truck mounted auger for
the holes but that's expensive. The soil type here is fairly soft, not
rock.  There's no contractor available with a skid steer mounted auger. I
need at least four inch holes, three foot deep. Siz inch would be better.
What are the options? Any novel ideas?
We have a service truck with a 2 ton hydraulic crane, anything I can mount
to that? I don't mind fabricating brackets and mounts, welding parts to it.

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Auger for ground mount

2018-02-09 Thread Chris Mason
I have a two man gas powered unit, not very confident of it.

On Feb 9, 2018 11:55, "James "Jibril" Gustafson" 
wrote:

> Hi Chris,
>
> In the past I have had success with renting a skid steer with auger, or a
> mini excavator with auger.  With a little practice you can become
> proficient with the machines, the hardest pasrt is getting a plumb hole.
> The mini excavator is nice, with a thin digger bucket you can also do your
> trenching.  Is fun to learn how to operate these machines.
>
> Good Luck,
>
> Jibril
>
>
> On Fri, Feb 9, 2018 at 8:04 AM, Chris Mason 
> wrote:
>
>> I'm taking on construction of a ground mount system of about 30KW. My
>> previous experience has entailed using a utility truck mounted auger for
>> the holes but that's expensive. The soil type here is fairly soft, not
>> rock.  There's no contractor available with a skid steer mounted auger. I
>> need at least four inch holes, three foot deep. Siz inch would be better.
>> What are the options? Any novel ideas?
>> We have a service truck with a 2 ton hydraulic crane, anything I can
>> mount to that? I don't mind fabricating brackets and mounts, welding parts
>> to it.
>>
>> --
>> Chris Mason
>> NABCEP Certified Solar PV Installer™
>> Solar Design Engineer
>> Generac Generators Industrial technician
>>
>> www.cometsolar.com <http://www.cometenergysystems.com>
>> 264.235.5670 <(264)%20235-5670>
>> 869.662.5670 <(869)%20662-5670>
>> Skype: netconcepts
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenc...@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Auger for ground mount

2018-02-09 Thread Chris Mason
They require you contact a certified installer. That's not happening here.

On Fri, Feb 9, 2018 at 1:04 PM, Larry Brown  wrote:

> We have been using Techno Metal Posts Helical Piers with much success for
> many years
> Larry
>
> Larry Brown
> Sun Mountain
> 845-657-8096 <(845)%20657-8096>
> sunmount...@netstep.net
>
>
> Sent from my iPhone
>
> On Feb 9, 2018, at 11:48 AM, Chris Schaefer 
> wrote:
>
> While I've been using the Zilla platform with an auger attachment for a
> mini excavator with good luck. With that said I'm looking at Nuance Energy
> and their Osprey mount which requires a hammer drill. Anyone tried this yet?
>
> Christopher
>
> On Fri, Feb 9, 2018 at 11:35 AM, Jerry Shafer 
> wrote:
>
>> Chris
>> Azk around for a fence contractor, they generally have what you need
>> Jerry
>>
>> On Feb 9, 2018 5:05 AM, "Chris Mason" 
>> wrote:
>>
>>> I'm taking on construction of a ground mount system of about 30KW. My
>>> previous experience has entailed using a utility truck mounted auger for
>>> the holes but that's expensive. The soil type here is fairly soft, not
>>> rock.  There's no contractor available with a skid steer mounted auger. I
>>> need at least four inch holes, three foot deep. Siz inch would be better.
>>> What are the options? Any novel ideas?
>>> We have a service truck with a 2 ton hydraulic crane, anything I can
>>> mount to that? I don't mind fabricating brackets and mounts, welding parts
>>> to it.
>>>
>>> --
>>> Chris Mason
>>> NABCEP Certified Solar PV Installer™
>>> Solar Design Engineer
>>> Generac Generators Industrial technician
>>>
>>> www.cometsolar.com <http://www.cometenergysystems.com>
>>> 264.235.5670 <(264)%20235-5670>
>>> 869.662.5670 <(869)%20662-5670>
>>> Skype: netconcepts
>>>
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re
>>> -wrenc...@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenc...@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
>
> Chris Schaefer’s
> 
>
> *Tel/Fax 585-229-2083 <(585)%20229-2083> or Cell 585-748-1870
> <(585)%20748-1870> *
> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
> <http://www.solarandwindfx.com> ~ E-mail: ch...@solarandwindfx.com
> *
>
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Auger for ground mount

2018-02-10 Thread Chris Mason
I don't have that option, there isn't one available. I've been advised a
two person commercial grade gas driven auger will do it.

On Fri, Feb 9, 2018 at 11:56 PM, Darryl Thayer 
wrote:

> The last job I used a mini excavator with auger drive head and put in
> ground screws worked great only trouble was getting plumb,
>
> On Fri, Feb 9, 2018 at 11:13 AM, Chris Mason  > wrote:
>
>> They require you contact a certified installer. That's not happening here.
>>
>> On Fri, Feb 9, 2018 at 1:04 PM, Larry Brown 
>> wrote:
>>
>>> We have been using Techno Metal Posts Helical Piers with much success
>>> for many years
>>> Larry
>>>
>>> Larry Brown
>>> Sun Mountain
>>> 845-657-8096 <(845)%20657-8096>
>>> sunmount...@netstep.net
>>>
>>>
>>> Sent from my iPhone
>>>
>>> On Feb 9, 2018, at 11:48 AM, Chris Schaefer 
>>> wrote:
>>>
>>> While I've been using the Zilla platform with an auger attachment for a
>>> mini excavator with good luck. With that said I'm looking at Nuance Energy
>>> and their Osprey mount which requires a hammer drill. Anyone tried this yet?
>>>
>>> Christopher
>>>
>>> On Fri, Feb 9, 2018 at 11:35 AM, Jerry Shafer 
>>> wrote:
>>>
>>>> Chris
>>>> Azk around for a fence contractor, they generally have what you need
>>>> Jerry
>>>>
>>>> On Feb 9, 2018 5:05 AM, "Chris Mason" 
>>>> wrote:
>>>>
>>>>> I'm taking on construction of a ground mount system of about 30KW. My
>>>>> previous experience has entailed using a utility truck mounted auger for
>>>>> the holes but that's expensive. The soil type here is fairly soft, not
>>>>> rock.  There's no contractor available with a skid steer mounted auger. I
>>>>> need at least four inch holes, three foot deep. Siz inch would be better.
>>>>> What are the options? Any novel ideas?
>>>>> We have a service truck with a 2 ton hydraulic crane, anything I can
>>>>> mount to that? I don't mind fabricating brackets and mounts, welding parts
>>>>> to it.
>>>>>
>>>>> --
>>>>> Chris Mason
>>>>> NABCEP Certified Solar PV Installer™
>>>>> Solar Design Engineer
>>>>> Generac Generators Industrial technician
>>>>>
>>>>> www.cometsolar.com <http://www.cometenergysystems.com>
>>>>> 264.235.5670 <(264)%20235-5670>
>>>>> 869.662.5670 <(869)%20662-5670>
>>>>> Skype: netconcepts
>>>>>
>>>>> ___
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> List-Archive: http://www.mail-archive.com/re
>>>>> -wrenc...@lists.re-wrenches.org/maillist.html
>>>>>
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>>
>>>>>
>>>>>
>>>> ___
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive: http://www.mail-archive.com/re
>>>> -wrenc...@lists.re-wrenches.org/maillist.html
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>>
>>>>
>>>
>>>
>>> --
>>>
>>> Chris Schaefer’s
>>> 
>>>
>>> *Tel/Fax 585-229-2083 <(585)%20229-2083> or Cell 585-748-1870
>>> <(585)%20748-1870> *
>>> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>>> <http://www.

Re: [RE-wrenches] Li+ Systems Puerto Rico

2018-02-19 Thread Chris Mason
I live in a Caribbean Island and use off-grid solar with grid as backup
when available. We just went through Irma and lost power for three months.
I've lived these solutions.
I wouldn't use anything other than an Outback Radian for this with a DC
charge controller, but finding a good Lithium solution will take a little
work. We have 1100 Ah of Lead acid, but only use 20% of that. So 300Ah of
useable storage would have been adequate for Lithium and that's what we
will use later.
Relion looks promising.
Right now there is no good integrated Lithium solution.


On Mon, Feb 19, 2018 at 4:26 PM, Matt Partymiller <
m...@solar-energy-solutions.com> wrote:

> Ray,
>
> I think your biggest issue may be SolarEdge.  They told us the StorEdge
> unit would not start up without grid power.  We had an employee install
> one anyway on his tiny home.  He hooked it up to the grid initially to get
> it started (in back of shop where house was built).  He is not sure how
> sincere Solaredge's requirement is as he has turned off for periods since
> then and it still starts up.  We wish we had tried without the grid
> initially.  Let us know if that works should you go that route.
>
> Overall he enjoys the unit though he mentions his battery has shutdown a
> couple times when it has gotten below 15F (battery is on exterior as it is
> tiny home).  Probably not applicable for your installs.
>
> Matt
>
>
> On Mon, February 19, 2018 2:14 pm, Ray wrote:
> > Greetings Wrenches;
> >
> >
> > We are designing several systems for Puerto Rico, and while these will
> > eventually could be grid tied once the grid returns, they will need to
> > operate reliably in off grid mode possibly for a year or more.  What is
> > everyone's experiences with the Storedge and LG setup?  I've worked with
> > the regular Solaredge GT system and was quite impressed, but I've heard
> > the Storedge is not a good off grid option.  What are the issues, and has
> > anyone used the Storedge in longer term outages?
> >
> > Right now we are designing some smaller systems that will use Magnum
> > inverters with 24v and 48 v Li+ batteries from other manufacturers, like
> > Simpliphi and LiFe Blue. ( No GT, Backup only)  These are lower cost and
> > allow us to use more traditional off grid designs, but also have limited
> > charge and discharge current.  In order to make Li+ cost effective, we
> > have had to reduce the storage size in half compared to lead acid.  We
> > feel this is justifiable considering Li+'s ability to be discharged to
> > 100%, its voltage stability, and its higher efficiency.
> >
> >
> > All feed back is welcome, as we venture into less well charted
> > territory.  We just don't want to set up systems that are going to not be
> > functional in 5 to 8 years because of inferior AGM lead acid batteries.
> > We use HUP batteries for most larger off grid systems, but
> > these are not feasible because of their size and maintenance
> requirements.
> >
> >
> > Thanks,
> >
> >
> > Ray Walters
> >
> >
> > Remote Solar
> >
> >
> > ___
> > List sponsored by Redwood Alliance
> >
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> >
> > List-Archive:
> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.ht
> > ml
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> >
>
>
> Matthew Partymiller
> Solar Energy Solutions LLC
> (877) 312-7456
> m...@solar-energy-solutions.com
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS no load draw

2018-03-07 Thread Chris Mason
It's 10KVA, what else do you need to know?

On Wed, Mar 7, 2018 at 2:26 PM, jay  wrote:

> HI All,
>
> I’ve got someone asking me about powering a UPS model
>
> Liebert GXT4 UPS
>
> its a rack mounted unit.
>
> And I cannot find any power usage data on it.
>
> Would anyone maybe be able to hazard a guess or know a similar product
> that might have some numbers?
>
> And as I”m not familiar with this kind of product I just don’t have any
> ideas of power consumption.
>
> thanks
>
> jay
>
> peltz Power
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA Sunny Boy Display Window

2018-05-11 Thread Chris Mason
I now put HVAC foil tape over all windows to keep the sun off when I
install.

On Fri, May 11, 2018 at 4:00 PM, Ray  wrote:

> I've also used some special 3M sanding pads that go up to 10,000 grit.
> They are used for polishing airplane wind shields.  Enough elbow grease,
> you can get any result you want.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 5/11/18 1:48 PM, Jerry Shafer wrote:
>
> Wayne
> We use automotive grade polisher after a run with 1200 then 1800 the 2400
> wet sand paper, you must clean the surface before attempting to polish and
> then you need a powered cotton wheel, that works for us
> Jerry
>
> On Fri, May 11, 2018, 4:48 AM Wayne Irwin 
> wrote:
>
>> We have installed quite a few SB's over the years and are seeing a
>> growing number of fogged over display lenses.
>>
>> We've tried headlight polish with limited success.
>>
>> Other than purchasing a new lid from SMA does anyone have another
>> solution to restoring or replacing the window?
>>
>>
>> Wayne Irwin,
>> President
>> License #CVC56695
>> State Licensed Solar Contractor
>> Pure Energy Solar International Inc.
>> wa...@pureenergysolar.com 
>> http://PureEnergySolar.com
>> http://SolarChargingStation.net <https://solarchargingstation.net>
>> 352 377-6527 Office
>> 352 336-3299 Fax
>> 352 316-1637 Cell
>>
>> The Sun Is Always Shining!
>>
>> The content of this message is Pure Energy Solar Confidential. If you are
>> not the intended recipient and have received this message in error, any use
>> or distribution is prohibited. Please notify me immediately by reply e-mail
>> and delete this message from your computer system. Thank you.
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Raised racking system

2018-09-19 Thread Chris Mason
I'm quoting a job on a concrete roof with three foot parapet walls. I'd
like to raise the arrays about 24 inches above the roof to minimize
shading, does any one have a solution for this application?

-- 
Chris Mason
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Raised racking system

2018-09-20 Thread Chris Mason
That's what we are looking at, but it's harder to design for this
application, if I didn't have to cost it, I would just go with it.
We use it for ground mount, and it is the strongest racking for tough
conditions. I think it is what we will end up with.


On Wed, Sep 19, 2018 at 3:20 PM, Chris Worcester 
wrote:

> You might consider the SnapNrack Series 200 ground mount system, we
> adapted it to work well on a raised roof mount before.
>
>
>
> Chris Worcester
>
> Solar Wind Works
>
> NABCEP Certified PV Installer
>
> Office 530-582-4503
>
> Cell 530-448-9692
>
> www.solarwindworks.com
>
> ch...@solarwindworks.com
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Chris Mason
> *Sent:* Wednesday, September 19, 2018 10:08 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Raised racking system
>
>
>
> I'm quoting a job on a concrete roof with three foot parapet walls. I'd
> like to raise the arrays about 24 inches above the roof to minimize
> shading, does any one have a solution for this application?
>
>
>
> --
>
> Chris Mason
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Mate 3 shutdown

2018-10-11 Thread Chris Mason
Outback has been good at sending a crossover replacement, meaning the new
one arrives then you send back the old one. The MATE3 has problems, I have
replaced one twice.

On Wed, Oct 10, 2018 at 9:30 PM Jay  wrote:

> Hi Dana,
>
> If you look at the graphs, are they smooth or really kind of unclear ?
>
> How often do you clear the internal data?
>
> The mate 3 has a fatal flaw. Th internal data will over write code once
> memory is full.
>
> One indicator is locking up, another is the graphs looking unclear.
>
> It’s recommended to clear it at least every 6 months.
>
> And even with current firmware and clearing memory, I still see it happen.
>
> Jay
>
>
>
>
>
>
> On Oct 10, 2018, at 4:51 PM, Dana  wrote:
>
> My learned fellow Sparkies,
>
>
>
> I have at home off-grid Radian with Mate 3 monitor. Periodically &
> randomly my Mate 3 blanks out and requires a reboot (un-plug / re-plug).
> While this is not such a big deal to address, the total loss of ALL the
> performance & usage data is really concerning in the event that I need the
> data for a T/S.
>
>
>
> I have not called OB as there is no cell service at or near the system and
> to do so is a huge time killer back & forth & waiting to check again. I am
> convinced the brain trust here is the answer.
>
>
>
> Has anyone else experienced this?
>
> Any remedial action to correct this issue?
>
>
>
> Let me know & thanks.
>
>
>
>
> 
>
> Dana Orzel   NABCEP # 051112-136
>
> Cell - 208.721.7003 Email - d...@solarwork.com
>
> Great Solar Works, Idaho Incwww.solarwork.biz
>
> ID PV Contractor - # 028765 - ID PV Electrician # 028374
>
> "Responsible Technologies for Responsible People since 1988"
>
> Please consider the environment before printing this email.
>
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Generac Eco-Gen 6 kw

2018-11-12 Thread Chris Mason
What's the error on the controller

On Mon, Nov 12, 2018, 00:49 John Blittersdorf  Hello Wrenches,
>I have a customer with a Generac EcoGen 6kw that starts and runs for
> about 30 seconds and then shuts down with high engine temp error. The
> engine is stone cold so it must be a temp sensor failure.  Disconnecting
> the sensor or jumpering the two leads together makes no difference. Has
> anyone seen this issue?  The engine runs real smooth until it shuts down.
>
> John Blittersdorf
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 600 Vdc Transfer Switch

2018-12-19 Thread Chris Mason
How about this
https://www.crawfordelectricsupply.com/c/gea-thn3361-30a-3p-hd-ss-n1-600v-nonfuse-sw-7046


On Wed, Dec 19, 2018 at 8:50 AM Mac Lewis  wrote:

> Hello Wrenches,
>
> Does anyone have a recommendation for a DPDT 600 Vdc rated indoor transfer
> switch?  This would be for selecting from grid-tied inverter to off-grid
> charge controller during a power outage.  Its for a Morningstar 600Vdc
> charge controller that doesn't have  this feature built in.
>
> Thanks
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 600 Vdc Transfer Switch

2018-12-20 Thread Chris Mason
Sorry, correct, this is what I was looking for
https://www.crawfordelectricsupply.com/c/gea-tc10323r-100a-2p-dbl-thr-n3r-120-240v-nonfus-6875?pageView=detailed&searchTerm=transfer%20switch&searchEngagement=engaged&rowNumber=12&colNumber=1&fromSearchPage=true


On Wed, Dec 19, 2018 at 7:51 PM Glenn Burt  wrote:

> Not a transfer switch. That is a simple DC rated disconnect, like the
> Square D equivalent.
>
> A transfer switch allows one load to be powered by one of two sources – a
> multi-pole, double throw device.
>
>
>
> -Glenn
>
>
>
> *From:* RE-wrenches  *On
> Behalf Of *Chris Mason
> *Sent:* Wednesday, December 19, 2018 2:41 PM
> *To:* RE-wrenches 
> *Subject:* Re: [RE-wrenches] 600 Vdc Transfer Switch
>
>
>
> How about this
>
>
> https://www.crawfordelectricsupply.com/c/gea-thn3361-30a-3p-hd-ss-n1-600v-nonfuse-sw-7046
>
>
>
>
>
> On Wed, Dec 19, 2018 at 8:50 AM Mac Lewis  wrote:
>
> Hello Wrenches,
>
>
>
> Does anyone have a recommendation for a DPDT 600 Vdc rated indoor transfer
> switch?  This would be for selecting from grid-tied inverter to off-grid
> charge controller during a power outage.  Its for a Morningstar 600Vdc
> charge controller that doesn't have  this feature built in.
>
>
>
> Thanks
>
>
>
> --
>
>
>
>
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." *-Sócrates*
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
>
> --
>
> Chris Mason
>
> NABCEP Certified Solar PV Installer™
>
> Solar Design Engineer
>
> Generac Generators Industrial technician
>
>
>
> www.cometsolar.com <http://www.cometenergysystems.com>
>
> 264.235.5670
>
> 869.662.5670
>
> Skype: netconcepts
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Lithium Batteries

2019-05-03 Thread Chris Mason
I'd be very cautious about getting too cosy with any of these battery
companies, it seems their only aim is to get bought. Sonnen was acquired by
Shell Oil, Pika by Generac. I'm a generac dealer so I am exploring what
their intentions are.  I doubt Shell will be gung-ho to continue to support
solar, so where does that leave my Sonnen customers?
Make sure your customers are aware you don't know where this is going and
whether any of these guys will stay the course. Companies like trojan and
Outback are going to be around, but Fortress? Unlikely.




On Fri, May 3, 2019 at 4:34 PM  wrote:

> Hi Howie,
> Have you looked at Fortress Power batteries? We're about to install
> some and they look like a very decent battery. Google will get you the
> basic info to start.
>
>
> Daryl
> Penobscot Solar Design
>
>
>
> > Hi Folks,
> > About to spec my first Lithium battery backup job.  The client is not a
> > heavy user, but wants things done right more than being totally cost
> > effective.
> > We put in 14kW of net metered solar using SolarEdge and now he wants the
> > backup component. This was significantly oversized for his use, but he
> > wanted to be sure he was putting a bunch more back into the grid than he
> > was using (making up for past profligate power usage).  We will be using
> a
> > dual stacked XW 6848, mostly for enough backfeed capacity (we could wire
> > in
> > a transfer switch and only use 1 XW, but he'd prefer this setup instead).
> > I have narrowed down my choice for batteries to either:
> >
> >- (2) Iron Edison 200 amp hour batteries, or
> >- (3) Discover AES 130 amp hour batteries
> >
> > Advantages for the AES are that they integrate directly with the
> Schneider
> > Xanbus network so the Conext battery monitor provides direct insight into
> > the SOC and SOH of the batteries, and they have a slightly higher rated
> > cycle life so higher lifetime energy capacity.
> >
> > Advantages of the IronEdison are they come in a larger amp hour size
> > allowing for only needing 2 vs. 3 batteries, they have an integrated fuse
> > and disconnect, and from my sources are 1/3 less in price.
> >
> > If anyone has any thoughts on any of this, or corrections to my
> > comparison,
> > I'd greatly appreciate it.
> > ___
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> >
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> >
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Cutting rail

2019-06-14 Thread Chris Mason
.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> --
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049www.frenergy.net
>
>
>
> --
> [image: Avast logo] <https://www.avast.com/antivirus>
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com <https://www.avast.com/antivirus>
>
> <#m_-1000421553531502429_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Consolidating meters

2019-07-08 Thread Chris Mason
It's the consumer's right to have one point of metering and distribute the
power to their loads. I would not ask the utility, I would tell them I was
rewiring and wanted to have only one metering point. It's stupid to pay for
all those meters. Most customers don't realize there is a cost to having
multiple meters and the problems it causes when it comes to self
consumption. We regularly consolidate customers who have one meter for each
guest cottage or main house, once they understand the advantages they
rewire and tell the utility to remove the redundant meters.

On Thu, Jul 4, 2019 at 2:30 PM Andrew Truitt  wrote:

>
> Happy 4th Wrenches!  Has anyone ever been through the process of
> consolidating utility electric meters for a client?  We're talking to an
> HOA that has 15 meters throughout the community for common area loads
> (clubhouse, pool pump, lighting, fountain...) so they're paying a fixed
> monthly charge on each in addition to energy and demand charges.
> Consolidating to a single master meter (possibly with sub-metering) would
> likely lower their costs on its own, and (more importantly?) would improve
> the value proposition for a PV+ESS installation.  We're not sure if the
> community is served by a single or multiple transformers yet, but if it is
> just one then the process should be straightforward from a technical
> standpoint.  The interwebs tell me that some providers (seems like mostly
> co-ops) are open to this, but I can't find anything for this particular
> utility.
>
>
> Regards,
>
>
> Andrew Truitt
>
> www.dr.ventures
> d: 202.486.7507
>
> NABCEP Certified PV Installation Professional ID: 032407-66
> Colorado Journeyman Electrician License No.: 600132
>
> [image: Logo]
>
>
>
> The content of this email is confidential and intended for the recipient
> specified in message only. It is strictly forbidden to share any part of
> this message with any third party, without a written consent of the sender.
> If you received this message by mistake, please reply to this message and
> follow with its deletion, so that we can ensure such a mistake does not
> occur in the future.
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase and Tesla Powerwall

2019-07-26 Thread Chris Mason
es.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> List-Archive:
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>>
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>>
>>>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & 
>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:www.members.re-wrenches.org
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
> *Will White*
> Curriculum Developer
>
>
> e: w...@solarenergy.org
> w: www.solarenergy.org
> p: 802-272-3092
>
> NABCEP Certified PV Installation Professional
> # 093006-34
>
> *FACT:  If we covered 0.33% of the earth with solar panels, we could power
> the world with renewable energy.*
>
> Do you envision a world powered by renewable energy? Be the change
> <http://solarenergy.org/donate>.
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] solar inter row shading

2019-07-26 Thread Chris Mason
Sketchup with Skelion

On Fri, Jul 26, 2019 at 6:41 PM jay  wrote:

> HI All,
>
> I’m wondering if there is any programs/apps that do inter row shading?
> I can’t find any.
>
> RBI used to have one, it was really slick.
>
> Thanks
>
> jay
>
> peltz power
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Generac Warranty claim ECOGEN 15k (Dana)

2019-07-27 Thread Chris Mason
When you say it died, what was the problem?

On Sat, Jul 27, 2019 at 5:43 PM Jason Jackson <
ja...@hakaienergysolutions.com> wrote:

> Same experience here in Canada. We installed two Ecogens last year,
> against our better judgement.  Both were dead in under 12 months. One was
> rebuilt under warranty and promptly died again, no coverage in that case.
> Another was refused warranty as it has been used (sparingly) as prime power
> during construction, prior to being connected to the inverter system. No
> warranty if it's not connected to an inverter system on day 1! That model
> was promptly pulled from the market according to our local ASC, and has
> been replaced with something similar apparently.
>
> [image: hakaienergysolutions.com]
> <http://www.hakaienergysolutions.com?utm_source=appogee&utm_medium=email_sig&utm_campaign=signature>
> Jason Jackson, Energy Systems Designer
> Ph: 888 604 3128 xt. 101
> www.hakaienergy.ca
> <http://www.hakaienergy.ca?utm_source=appogee&utm_medium=email_sig&utm_campaign=signature>
>
>
> On Sat, Jul 27, 2019 at 2:07 PM 
> wrote:
>
>> Send RE-wrenches mailing list submissions to
>> re-wrenches@lists.re-wrenches.org
>>
>> To subscribe or unsubscribe via the World Wide Web, visit
>>
>> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>> or, via email, send a message with subject or body 'help' to
>> re-wrenches-requ...@lists.re-wrenches.org
>>
>> You can reach the person managing the list at
>> re-wrenches-ow...@lists.re-wrenches.org
>>
>> When replying, please edit your Subject line so it is more specific
>> than "Re: Contents of RE-wrenches digest..."
>> When responding to posts within the Digest, be sure to restore the
>> Subject: line to the original, and please edit out any extraneous lines
>> from the quoted message.
>>  Today's Topics:
>>
>>1. Re: Generac Warranty claim ECOGEN 15k (Dana)
>>2. solar inter row shading (jay)
>>3. Re: solar inter row shading (Chris Mason)
>>4. Re: solar inter row shading (Ray)
>>5. Re: solar inter row shading (William Miller)
>>
>>
>>
>> -- Forwarded message --
>> From: Dana 
>> To: "'RE-wrenches'" 
>> Cc:
>> Bcc:
>> Date: Fri, 26 Jul 2019 15:42:35 -0600
>> Subject: Re: [RE-wrenches] Generac Warranty claim ECOGEN 15k
>> Generwrecked strikes again! After 3 fires in the controllers & 2 more
>> engine meltdowns due to oil loss I would not touch a wreck.
>>
>>
>>
>> Dana Orzel  Great Solar Works, Inc.
>> C - 208.721.7003   d...@solarwork.com
>> Idaho Contractor - # 028765 Idaho PV # 028374
>> NABCEP # 051112-136   www.solarwork.com
>> "Responsible Technologies for Responsible People since 1988"
>>  Please consider the environment before printing this email.
>>
>>
>> -Original Message-
>> From: RE-wrenches  On Behalf
>> Of Maverick Brown
>> Sent: Friday, July 26, 2019 11:41 AM
>> To: re-wrenches@lists.re-wrenches.org
>> Subject: [RE-wrenches] Generac Warranty claim ECOGEN 15k
>>
>> Wrenches
>>
>> Any guidance on getting warranty claim approved when their denial reason
>> is the generic “unsafe” installation? There isn’t anything unsafe about the
>> 1.5 year install that I can see. The ECOGEN is connected to an Outback
>> Radian.
>>
>> Generator has 950 hours on it before the brushes melted down from being
>> exposed to engine oil.
>>
>> Thank you,
>>
>> Maverick
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>>
>>
>>
>> -- Forwarded message --
>> From: jay 
>> To: RE-wrenches 
>> Cc:
>> Bcc:
>> Date: Fri, 26 Jul 2019 14:59:06 -0700
>> Subject: [RE-wrenches] solar inter row shading
>> HI All,
>>
>> I’m wondering if there is any programs/apps 

Re: [RE-wrenches] 120/240 to 3 phase 120/208

2019-08-07 Thread Chris Mason
Yes, I just did it yesterday, but only if it is a 12 wire alternator. If
you open the connection box on top of the alternator, you will be able to
reconfigure the alternator.
However, that's only possible if the generator was built using a three
phase alternator connected in zig-zag to give single phase - which is very
common.
All the big generators I order are built this way.
If you give me more info on the generator I can tell you how to do it.
https://www.smokstak.com/forum/attachment.php?attachmentid=3483&d=1125167403


On Tue, Aug 6, 2019 at 10:20 PM Jay  wrote:

> Hi all
>
> Is there a way to convert a 120/240v generator to a 120/208 3 phase output?
>
> Thx
>
> Jay
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Grid tie w/o battery no sell back

2019-08-29 Thread Chris Mason
Outback Radian or Pika.

On Wed, Aug 28, 2019 at 9:41 PM Jay  wrote:

> are there any products out there that can do a grid tie w/o batteries but
> no sell back to the
> grid?
>
> Thx
> Jay
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Grid tie w/o battery no sell back

2019-08-30 Thread Chris Mason
I misunderstood the question the two options I listed are battery systems.
What I should have suggested as a solution was the Enphase microinverter
system with the Zero Export profile and Production CTs on the service to
the panel. That will do Zero Export so that all the power produced is self
consumed, there is virtually no exported power to the grid.

On Thu, Aug 29, 2019 at 9:16 AM Chris Mason 
wrote:

> Outback Radian or Pika.
>
> On Wed, Aug 28, 2019 at 9:41 PM Jay  wrote:
>
>> are there any products out there that can do a grid tie w/o batteries but
>> no sell back to the
>> grid?
>>
>> Thx
>> Jay
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
> Chris Mason
> Solar systems designer
> Generac Generators Industrial technician
>
> Comet Systems Ltd DBA Comet Solar
> Anguilla Cell  264.235.5670
> WhatsApp 264.235.5670
> Skype: netconcepts
> www.cometsolar.com <http://www.cometenergysystems.com/>
>


-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Strategies for staged startup of appliances

2019-09-12 Thread Chris Mason
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] seeking PV mounting advice to Shipping Container for Off-grid

2019-09-23 Thread Chris Mason
I have a bunch of containers, I put solar on a couple. I would weld tabs
onto the container so as to avoid penetrations. The worst thing about
containers is they leak, so holes in the top are a problem. In fact, I
would weld on tabs, put galvanized stringers cross at an angle, put
galvanized purloins along the length of the container, put galvanized
corrugated sheeting on the purloins and the racking of your choice on top.
That way the container roof won't rust and leak, you have your angle, and
the container will be cooler.

On Mon, Sep 23, 2019 at 11:12 AM Lorenzo Ortiz 
wrote:

> Check this company out. <https://boxpower.io/> They have a pretty slick
> solution.
>
> On Mon, Sep 23, 2019 at 6:12 AM Chris Schaefer 
> wrote:
>
>> G'Day All,
>>
>> I'm looking for anyone with advice that has mounted PV to a
>> shipping container roof with minimal to no roof penetrations. The container
>> will not be required to be transported with PV attached, only the racking
>> and only one time to project site. They will not be mounted flat but prefer
>> a 35 degree angle. I was thinking of Unirac's ULA series as they use to
>> have an adjustable leg. I'm not only seeking racking brands but also any,
>> "if I ever did this again I would..." advice.
>>
>> Thanks,
>> Christopher-
>>
>> Chris Schaefer’s
>> 
>>
>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>> <http://www.solarandwindfx.com> ~ E-mail: ch...@solarandwindfx.com
>> *
>>
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to exist when you take away from those who are
>> willing to work and give to those who would not."
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
>
> Loren Ortiz
> Technical PV Design Specialist - Commercial/Residential/Off-Grid
>
> lo...@cal-solar.com californiasolarco.com
>
> *Main: 530-274-3671 ext: 311 * *Fax: 530-274-7518*
>
>
>
>
>
> <https://californiasolarco.com/referral_form/>
> *Showroom located at: 149 E Main St. Grass Valley, CA 95945*
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fluke 87 replacement

2019-10-16 Thread Chris Mason
I have the same Hioki and I love it, the bluetooth logging feature is great
for quick surveys, I'm in and out faster than I can set up my Fluke 435
Analyzer.

On Mon, Oct 14, 2019 at 2:47 PM Will White  wrote:

> The Hioki CM4372 seems to be the best clamp-on amp meter for PV out there
> these days. 1,500 VDC, two current ranges, and a ton of other features
> including a bluetooth app that can do logging. Plus it's about the same
> price as a Fluke clamp-on amp meter.
>
> https://www.hioki.com/en/products/detail/?product_key=6362
>
> Thanks,
> Will
>
>   --
> *Will White*
> Curriculum Developer
>
>
> e: w...@solarenergy.org
> w: www.solarenergy.org
> p: 802-272-3092
>
> NABCEP Certified PV Installation Professional
> # 093006-34
>
> *FACT:  If we covered 0.33% of the earth with solar panels, we could power
> the world with renewable energy.*
>
> Do you envision a world powered by renewable energy? Be the change
> <http://solarenergy.org/donate>.
>
> On Mon, Oct 14, 2019 at 2:33 PM Chris Schaefer 
> wrote:
>
>> G'Day All,
>>
>> Well my 24 year old Fluke 87 finally passed. It was a great unit and fit
>> all my needs. Before I go out and buy another I thought I'd reach out to
>> see if any of my peers would suggest anything different or possibly a step
>> above in the Fluke family or another brand?
>>
>> Thanks,
>> Christopher-
>>
>> Chris Schaefer’s
>> 
>>
>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>> <http://www.solarandwindfx.com> ~ E-mail: ch...@solarandwindfx.com
>> *
>>
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to exist when you take away from those who are
>> willing to work and give to those who would not."
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
> *Will White*
> Curriculum Developer
>
>
> e: w...@solarenergy.org
> w: www.solarenergy.org
> p: 802-272-3092
>
> NABCEP Certified PV Installation Professional
> # 093006-34
>
> *FACT:  If we covered 0.33% of the earth with solar panels, we could power
> the world with renewable energy.*
>
> Do you envision a world powered by renewable energy? Be the change
> <http://solarenergy.org/donate>.
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 600V DC contactor

2019-11-23 Thread Chris Mason
https://www.amazon.com/Siemens-3TC48-17-0B-Pole-Contactor-600V/dp/B00WH0QNHA

I've done this with Sonnen previously, interrupted the inverter output to
precent power being sent back to the grid. You might look at to inverters
and interrupt one.

On Fri, Nov 22, 2019 at 11:47 PM Chris Sparadeo 
wrote:

> Hi wrenchers,
>
>
> I am currently on the look out for a DC contactor to suit my needs. A
> little background:
>
>
> Per Sonnen Batterie tech support’s recommendation I have installed a 10 kW
> SolarEdge HD Wave inventer coupled with the Sonnen Eco 12. Although the
> Sonnen Eco 12 uses an Outback Radian 8kW multimode inverter(of which
> Outback suggests to max AC couple input of 5kW) Sonnen says that AC PV
> input greater than 8kW will require a contactor  to interrupt a string or
> two of the grid interactive inverter so that it’s output will remain less
> than the max 8kW input. That’s fine and well, but when asked directly,
> Sonnen didn’t have a part # for the contactor and suggested that anything
> over 150V DC would be difficult to find. Anyone know of a 600V rated
> contactor that would suit the bill? Essentially the contactor would need to
> sense grid interruption (via a 15A-AC breaker) and open a 600 V rated DC
> string.
>
>
> I’ve done some preliminary searching and have come up empty handed. Any
> input would be greatly appreciated.
>
>
> Best,
>
>
> Chris
> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] automatic transfer switches

2019-11-26 Thread Chris Mason
If you only want to change over, why not use a contactor with three poles,
a NO and NC contact? that will switch instantly. Use Utility to power the
coil, it will switch to utility when the power is restored.

On Tue, Nov 26, 2019 at 2:57 AM Jerry Shafer 
wrote:

> There is the SMA Automatic transfer switch if you go with the SMA battery
> inverter and SMA pv inverter, it can be located seperate of the battery and
> inverter and will take up to 30 kwhrs. of capacity
> Just a thought
>
> On Mon, Nov 25, 2019, 10:52 PM Bill Hennessy  wrote:
>
>> hi folks--
>>
>> We're installing a grid-tied, battery backup system on a farm where the
>> service entrance is on a pole in the yard. At the single-phase, 240v,
>> service entrance, there are two main breaker subpanels--one going to the
>> house and one to the barn. The buildings are each about 100 feet away from
>> the pole in opposite directions. The PV/battery system is located in the
>> barn. When utility power is lost and the battery backup kicks in, we are
>> looking for a way to bypass the house subpanel at the pole so it won't
>> backfeed the grid.
>>
>> When the grid drops out, we need to tie the backup power coming from the
>> barn to the line going to the house. We're thinking an automatic transfer
>> switch installed at the pole will do the job, but the transfer switches
>> seem to have built in delays to work with starting a generator. The
>> switch does not have to be service entrance rated.
>>
>> It looks like the Asco 300 series has time delay adjustments, but it is
>> pricey and has a seven-week lead time. (Thank-you PG&E)
>>
>> The battery backup system will switch over in milliseconds and we were
>> hoping to find something similar for the transfer operation at the pole.  
>> We're
>> looking for something simple--hopefully a basic transfer switch that will
>> quickly switch and drop out when grid power is restored.
>>
>> Would appreciate any thoughts or suggestions.
>>
>> regards, bill
>>
>> Bill Hennessy
>> Berks Solar, LLC
>> 371 Centennial Rd
>> Mertztown, PA 19539
>>
>> o 610 682 4300
>> c 484 560 4666
>> NABCEP certified installer
>> PA contractor #44411
>> www.berkssolar.com
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] automatic transfer switches

2019-11-29 Thread Chris Mason
If you are doing it on the AC side, a Generac transfer switch has the
capability and is designed to do this. It's easy to rig an interface as I
discussed privately with Bill.

On Fri, Nov 29, 2019 at 1:29 AM Jerry Shafer 
wrote:

> Wrenches
> Need to be careful here to use something that has the interrupt KVA rating
> required to prevent an arc in the event of an under load opening with the
> switch proper AIC rating 10,000 or more, last thing I think you want is to
> have that kind of liability on products that are not designed for that type
> of use. But thats just me.
> NABCEP PV Inspector
> California Solar contractor
> Jerry
>
> On Mon, Nov 25, 2019 at 8:52 PM Bill Hennessy  wrote:
>
>> hi folks--
>>
>> We're installing a grid-tied, battery backup system on a farm where the
>> service entrance is on a pole in the yard. At the single-phase, 240v,
>> service entrance, there are two main breaker subpanels--one going to the
>> house and one to the barn. The buildings are each about 100 feet away from
>> the pole in opposite directions. The PV/battery system is located in the
>> barn. When utility power is lost and the battery backup kicks in, we are
>> looking for a way to bypass the house subpanel at the pole so it won't
>> backfeed the grid.
>>
>> When the grid drops out, we need to tie the backup power coming from the
>> barn to the line going to the house. We're thinking an automatic transfer
>> switch installed at the pole will do the job, but the transfer switches
>> seem to have built in delays to work with starting a generator. The
>> switch does not have to be service entrance rated.
>>
>> It looks like the Asco 300 series has time delay adjustments, but it is
>> pricey and has a seven-week lead time. (Thank-you PG&E)
>>
>> The battery backup system will switch over in milliseconds and we were
>> hoping to find something similar for the transfer operation at the pole.  
>> We're
>> looking for something simple--hopefully a basic transfer switch that will
>> quickly switch and drop out when grid power is restored.
>>
>> Would appreciate any thoughts or suggestions.
>>
>> regards, bill
>>
>> Bill Hennessy
>> Berks Solar, LLC
>> 371 Centennial Rd
>> Mertztown, PA 19539
>>
>> o 610 682 4300
>> c 484 560 4666
>> NABCEP certified installer
>> PA contractor #44411
>> www.berkssolar.com
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Offgrid Generators?

2020-02-28 Thread Chris Mason
Ray,
I'm a Generac dealer. Why are you having support problems? Generac has a
large dealer network, if the unit is under warranty you should have no
problem getting it fixed. Did you buy through a dealer and have them
install it? Why are the services expensive?

What failures are you seeing?

There is a hole in the market for products in this application. Virtually
no-one makes an affordable ~10KW diesel enclosed 2 wire start 1,800 rpm
reliable diesel generator. I once ordered, on spec, a 9KW Perkins engine
liquid cooled enclosed diesel from a factory in China I deal with. I sold
it to a customer that ran it 18 hours a day on 100% load, to power his
restaurant refrigeration outside service hours. It lasted him years, it
must have thousands of hours on it.
I think the big problem in the US is getting permits for diesel generators.



On Thu, Feb 27, 2020 at 6:25 PM Ray  wrote:

> I know we have covered this before, but I just continue to be
> disappointed with the Generac Ecogen.  Very high failure rate, and
> support is poor.  Service requires expensive on site service. Also the
> no load AC draw and programming setup is just not off grid ready at
> all.  I'm still not seeing any other great choices, though.  Here's some
> other possibilities:
>
> 1) Quality portable, like the Honda EU 7000i or Northstar with Honda
> motor.  Not the best choice especially for autostart, no propane, but at
> least they can take it in to the shop if it goes down.
>
> 2) Kubota (or MQ) diesel. expensive, and possible cold weather start
> issues?
>
> 3) 20+ kW water cooled, 1800 rpm propane model.  Overkill, expensive,
> but probably will last a really long time.
>
> 4) Similar Home standby unit, but Kohler brand.  Kohler used to be
> great, but now a days I'm not so sure.
>
> I just can't keep recommending a generator I know has been giving other
> customers trouble.  Any new ideas on this age old problem?
>
> --
> Ray Walters
> Remote Solar
> 303 505-8760
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Offgrid Generators?

2020-02-28 Thread Chris Mason
William,
Generac has a structure where box stores like HD and Lowes sell the
residential generators and arrange local certified dealers to perform the
installation, warranty and service work. The dealers are not real fond of
it but Generac can't get to be the largest brand relying on dealers for
sales. Generac is pretty good on compensating dealers for warranty work so
there are a number of dealers that make their living on installation,
servicing and warranty work.

On Thu, Feb 27, 2020 at 10:20 PM William Miller 
wrote:

> Ray, Wrenches:
>
> My experience with Generac is similar to yours.  Coincidentally, I just
> received an invite from our local Greentech to attend a Generac training.
> Apparently Greentech thinks they should sell generators.  This sounds like
> a
> bad fit for a supply house.
>
> When I politely declined the invitation, I mentioned that with any big
> ticket item, especially one with moving parts, I like to create a
> relationship with whoever will be servicing that item.  This starts with
> buying the unit from a reputable local shop.  If you subscribe to this
> theory,  the brand of generator you choose should have someone to service
> it
> within reasonable range.  This may narrow your choices.
>
> William
>
> PS:  The smallest generator I have purchased lately is a 12kw vertical
> crankshaft Kohler.  It gets minimum hours but seems to run OK.
>
> W
>
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com
> CA Lic. 773985
>
> -Original Message-
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of Ray
> Sent: Thursday, February 27, 2020 2:26 PM
> To: RE-wrenches
> Subject: [RE-wrenches] Offgrid Generators?
>
> I know we have covered this before, but I just continue to be
> disappointed with the Generac Ecogen.  Very high failure rate, and
> support is poor.  Service requires expensive on site service. Also the
> no load AC draw and programming setup is just not off grid ready at
> all.  I'm still not seeing any other great choices, though.  Here's some
> other possibilities:
>
> 1) Quality portable, like the Honda EU 7000i or Northstar with Honda
> motor.  Not the best choice especially for autostart, no propane, but at
> least they can take it in to the shop if it goes down.
>
> 2) Kubota (or MQ) diesel. expensive, and possible cold weather start
> issues?
>
> 3) 20+ kW water cooled, 1800 rpm propane model.  Overkill, expensive,
> but probably will last a really long time.
>
> 4) Similar Home standby unit, but Kohler brand.  Kohler used to be
> great, but now a days I'm not so sure.
>
> I just can't keep recommending a generator I know has been giving other
> customers trouble.  Any new ideas on this age old problem?
>
> --
> Ray Walters
> Remote Solar
> 303 505-8760
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Offgrid Generators?

2020-02-28 Thread Chris Mason
Generac also has a nice 15KW Diesel Protector unit, that'll keep the lights
on very nicely, is relatively inexpensive and I haven't heard any
complaints about them failing. We had one Protector Diesel with a failed
fuel pump solenoid but I changed it out under warranty and there hasn't
been any other issues.
Of course they are not $4,000, you are not going to get a liquid cooled
generator for under $10,000.

On Thu, Feb 27, 2020 at 6:25 PM Ray  wrote:

> I know we have covered this before, but I just continue to be
> disappointed with the Generac Ecogen.  Very high failure rate, and
> support is poor.  Service requires expensive on site service. Also the
> no load AC draw and programming setup is just not off grid ready at
> all.  I'm still not seeing any other great choices, though.  Here's some
> other possibilities:
>
> 1) Quality portable, like the Honda EU 7000i or Northstar with Honda
> motor.  Not the best choice especially for autostart, no propane, but at
> least they can take it in to the shop if it goes down.
>
> 2) Kubota (or MQ) diesel. expensive, and possible cold weather start
> issues?
>
> 3) 20+ kW water cooled, 1800 rpm propane model.  Overkill, expensive,
> but probably will last a really long time.
>
> 4) Similar Home standby unit, but Kohler brand.  Kohler used to be
> great, but now a days I'm not so sure.
>
> I just can't keep recommending a generator I know has been giving other
> customers trouble.  Any new ideas on this age old problem?
>
> --
> Ray Walters
> Remote Solar
> 303 505-8760
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Offgrid Generators?

2020-03-03 Thread Chris Mason
Ray,
Let me try to address some of those issues for you.
1) You can get the activation code before you take it to site, you just
need the serial number. Generac has a good warranty policy but they need to
know where the generator is and when it is installed to be able to provide
that.
2) An electrician can connect the wires but you would not believe the
installations we have seen, done by licensed electricians. We have a dealer
forum where installers post pictures of installations they find, and the
mistakes are criminal and dangerous. I once found a propane 20KW generator
running side a shipping container, doors closed.
3) Generac does not do direct support for generators, they require
customers call a dealer. The dealer can then call Generac, and often does.
I can't even call them if my certification expires.
4) If the generator is under warranty, you may not pay anything, depending
on the coverage. Generac is offering up to ten year warranties. But once it
is out of warranty, you will have to pay. Dealers don't work for free. The
average electrician won't be able to diagnose problems reliably on these
generators.
The residential air cooled generators are very reliable and rarely have
problems if well maintained. Techs should be traveling with common parts, I
bring a controller and a few other parts so I can solve the problem in one
go.
Blown engines are rare, but they do happen. Generally in the first few
hours, so under full warranty and replacement is generally done at
Generac's expense.
If you do have issues, contact me and I will try to help you.










On Fri, Feb 28, 2020 at 4:41 PM Ray  wrote:

> Some of the issues have been Generac not providing a simple wiring
> schematic, nor simply labeling the 2 start wires.  2nd is requiring either
> internet connection or a call in to get the start code.  Both have been
> very problematic in remote locations with no phone service.  Totally
> unnecessary.  We don't need a Generac tech just to connect wires, I'm the
> licensed electrician.  Last time I called Generac, (control error not
> listed in the manual) they insisted I needed to call in a service tech, and
> offered zero trouble shooting.  I fixed the problem by pulling the fuse and
> resetting the controller.  3rd, service requires a long expensive trip by
> the service tech, who then diagnoses the problem, has to order the parts
> and return weeks later. This means every issue takes 2 round trips to
> resolve.  If its a bigger issue, it requires a truck lift to haul the 500
> lb unit in to the shop.  We're hearing $500 just to get the generator to
> the shop, then another $500 to reinstall it after.
>
> Failures have included several catastrophic engine failures, blowing oil
> every where, some of these have been in the first few hundred hours. Lots
> of control issues, one recently had voltage that varied from 90 to 130, 45
> to 70 Hz, and the inverter wouldn't even connect to it.
>
> I quit selling generators a long time ago, because I didn't want the
> service liability.  I'm not a mechanic, and I don't want to be.  I do
> however, need a generator I can recommend in good faith.  The Ecogen has
> made us look pretty bad.  Glad I didn't sell them, but then I've seen some
> large water cooled unit that worked well.
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 2/28/20 5:14 AM, Chris Mason wrote:
>
> Ray,
> I'm a Generac dealer. Why are you having support problems? Generac has a
> large dealer network, if the unit is under warranty you should have no
> problem getting it fixed. Did you buy through a dealer and have them
> install it? Why are the services expensive?
>
> What failures are you seeing?
>
> There is a hole in the market for products in this application. Virtually
> no-one makes an affordable ~10KW diesel enclosed 2 wire start 1,800 rpm
> reliable diesel generator. I once ordered, on spec, a 9KW Perkins engine
> liquid cooled enclosed diesel from a factory in China I deal with. I sold
> it to a customer that ran it 18 hours a day on 100% load, to power his
> restaurant refrigeration outside service hours. It lasted him years, it
> must have thousands of hours on it.
> I think the big problem in the US is getting permits for diesel generators.
>
>
>
> On Thu, Feb 27, 2020 at 6:25 PM Ray  wrote:
>
>> I know we have covered this before, but I just continue to be
>> disappointed with the Generac Ecogen.  Very high failure rate, and
>> support is poor.  Service requires expensive on site service. Also the
>> no load AC draw and programming setup is just not off grid ready at
>> all.  I'm still not seeing any other great choices, though.  Here's some
>> other possibilities:
>>
>> 1) Quality portab

Re: [RE-wrenches] Charging a Bolt with an SW

2020-06-07 Thread Chris Mason
I had a Nissan Leaf and a 240v charger, we had no problem using our Radian
to charge it during the day.

On Sat, Jun 6, 2020, 22:11 Hilton Dier III  wrote:

> The issue with EV chargers is that they create a lot of reactive power.
> Think of it as "slosh" in the waveform. That means that charging at 2,000
> watts sloshes a lot more than 2kW through the cable, plug, outlet, and from
> the inverter. If you've got a reasonably good sinewave inverter the charger
> will like it fine. However, the inverter might not like the charger if you
> cut things too close. Make sure to have a lot of top end left in your
> inverter. Always use a transformer based inverter. The SW series has a big
> chunk of metal in it, so that's good. At 120V the Bolt will only draw 1440
> watts max.
>
> An aftermarket Bolt 240V charger can draw up to 32 amps. That's 7.7 kW, so
> too big for an SW. Treat it more like 40 amps. The OEM 120/240 EVSE (smart
> charging cord) that comes with the car can draw 8 or 12 amps at 120V or 12
> at 240V. Assume that the 8 amps is really 12 and the 12 is really 15 or a
> bit more. I have seen 15 amp plugs and outlets with the hot prong melting
> plastic around it. The plug on the OEM EVSE is 20A rated but make sure your
> outlet is as well.
>
> --
> Hilton Dier III
> Missisquoi River Hydro
> Renewable Energy Design
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Charging a Bolt with an SW

2020-06-08 Thread Chris Mason
mp; settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Unknown rail.

2013-07-31 Thread Chris Mason
SnapNRack

Chris Mason
Comet Systems
Anguilla (264) 235-5670
St. Kitts  (869) 662-5670
skype netconcepts

NABCEP Certified Solar PV Installer™
Renewable Energy Systems professional
Generac Generators Factory technician
On Jul 31, 2013 4:21 PM, "All Solar"  wrote:

> Can anyone please identify the rail on the photo?
>
> Regards
> Jeremy Rodriguez
> AllSolar
>
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand!
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PV Assist

2013-08-17 Thread Chris Mason
Well said, WIlliam. Just because we are installing solar does not mean all
our intent is "green" I provide solar systems and generators, I am a
provider of engineering solutions. I do not judge clients based on their
green qualifications, just on their ability to pay me. We are in business
to provide engineering solutions.
By the way, William, have you looked at the SMA Fuel Saver solutions? I am
proposing that technology for an industrial customer whose plant runs
entirely off generators.


On Fri, Aug 16, 2013 at 8:56 PM, William Miller wrote:

> **
>
> Friends:
>
> I am a bit surprised at the responses I have gotten on this thread.  I
> appreciate the technical advice and I don't mind the polite philosophical
> discussion like the one below.  However, I received one reply, fortunately
> off-line, that was not very polite, to say the least.
>
> I have been advised to abandon the clients that don't fit someone's
> criteria of green living.  I don't think this is appropriate advice,
> especially if the adviser does not know what the whole story is.
>
> For example, one of the aforementioned clients was sold a bill of goods by
> a now defunct local installer. He retired, bought the property, moved in
> with a generator and then waited way too long for the scam artist to build
> a system that would "power everything with the rays of the sun."
>
> Tens of thousands of dollars later the client fired the scammer and asked
> me to help as best I could.  He is on a fixed income, he lives with
> extended family, the daughter has severe health problems, the son in law is
> out of work, etc..  My client is in a tight situation, with no good
> choices.
>
> Yes, I could tell the guy f*** you, you don't meet my standards.  But I am
> not that kind of person.  I am trying to help the customer get by as best
> he can by working as a team.  This, my friends, is the professional and
> humane thing to do, and I make no apologies.
>
> Have a nice weekend everyone.
>
> William Miller
>
> PS:  the "good" customers are not necessarily the greenest people, they
> are the ones that reduce consumption as best they can, do their homework,
> trust me and pay on time.
>
> Wm
>
>
>
>
>
> -Original Message-
> From: re-wrenches-boun...@lists.re-wrenches.org [
> mailto:re-wrenches-boun...@lists.re-wrenches.org
> ] On Behalf Of penobscotso...@midmaine.com
>
> Sent: Friday, August 16, 2013 3:22 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] PV Assist
>
> Honestly, William, in these type of cases I usually walk away from the job
> if the customer isn't willing to reduce where possible. There is no such
> thing as a completely fool proof off grid PV system. Like a good lawyer,
> the best way to have a stellar record is to know which cases to
> takejust one man's opinion of course, but we get approached for many
> systems like this, particularly in the Caribbean and I have learned that
> there is such a thing as a good solar customer and also a bad solar
> customer.
>
> Daryl
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1000 V meters?

2013-08-22 Thread Chris Mason
We're doing all 1000V work these days. I use a Extech EX730 True RMS
800-Ampere AC/DC Clamp
Meter<http://www.amazon.com/gp/product/B000BF53YM/ref=wms_ohs_product?ie=UTF8&psc=1>
which
is very inexpensive and works great.
We also use a Seaward Solar PV150 solar test kit for testing strings.


On Thu, Aug 22, 2013 at 4:03 PM, August Goers  wrote:

> Hi Wrenches,
>
>
>
> It's new tool time!
>
>
>
> We're starting engineering for our first 1000 V small and medium
> commercial systems. There are all kinds of details to consider when making
> the jump to 1000 VDC but I'm wondering if any of you have good ideas for a
> 1000 V multimeter. I'm looking at the Fluke 376 which also measures AC and
> DC current but it is a bit expensive. The Fluke T5 is much cheaper,
> measures 1000 VDC, but doesn't measure DC current. Anyone have a meter that
> they like that can handle 1000 V?
>
>
>
> Best,
>
>
>
> August
>
>
>
> *August Goers*
>
> Luminalt Energy Corporation
>
> o: 415.641.4000
>
> m: 415.559.1525
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1000 V meters?

2013-08-23 Thread Chris Mason
I bought the EX730 for the DC current measuring capabilities but realized
it would read 1000V DC systems on the job. It works fine. I don't need
precise measurements, just to compare strings to ensure all strings are
about equal.

If I bought it again, I would get the EX840. It's 1000V CAT IV.
I have a number of Extech units, they are fine.


On Fri, Aug 23, 2013 at 4:03 PM, August Goers  wrote:

> Hi Chris,
>
>
>
> It looks like the Extech EX730 is only rated up to 600 V but the Seaward
> PV150 is good up to 1000 V. Thanks for forwarding, I'll definitely check
> both of these out. I've had some bad luck with brands other than Fluke -
> meters going haywire or inaccurate readings right when I really needed
> them. So, I'm inclined to shell out the extra cash for a Fluke but I'm sure
> some other brands are fine as well.
>
>
>
> Best,
>
>
> August
>
>
>
>
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Chris Mason
> *Sent:* Thursday, August 22, 2013 6:05 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] 1000 V meters?
>
>
>
> We're doing all 1000V work these days. I use a Extech EX730 True RMS
> 800-Ampere AC/DC Clamp 
> Meter<http://www.amazon.com/gp/product/B000BF53YM/ref=wms_ohs_product?ie=UTF8&psc=1>
>  which
> is very inexpensive and works great.
>
> We also use a Seaward Solar PV150 solar test kit for testing strings.
>
>
>
> On Thu, Aug 22, 2013 at 4:03 PM, August Goers  wrote:
>
> Hi Wrenches,
>
>
>
> It's new tool time!
>
>
>
> We're starting engineering for our first 1000 V small and medium
> commercial systems. There are all kinds of details to consider when making
> the jump to 1000 VDC but I'm wondering if any of you have good ideas for a
> 1000 V multimeter. I'm looking at the Fluke 376 which also measures AC and
> DC current but it is a bit expensive. The Fluke T5 is much cheaper,
> measures 1000 VDC, but doesn't measure DC current. Anyone have a meter that
> they like that can handle 1000 V?
>
>
>
> Best,
>
>
>
> August
>
>
>
> *August Goers*
>
> Luminalt Energy Corporation
>
> o: 415.641.4000
>
> m: 415.559.1525
>
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
>
>
> --
> Chris Mason
>
> President, Comet Systems Ltd
>
> www.cometenergysystems.com
>
> Cell: 264.235.5670
>
> Skype: netconcepts
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] double-insulated PV wire

2013-08-31 Thread Chris Mason
Aee Solar sells it, we bought a lot. Don't forget the normal cable gland
holes will be too small, you have to buy special units. I ended up buying
those from the UK.


On Fri, Aug 30, 2013 at 2:59 PM, Marco Mangelsdorf wrote:

> Hola,
>
> ** **
>
> Any recommendations where I can find rolls of #10 double-insulated PV wire
> (for use with transformerless inverters) in the South S.F. Bay Area?
>
> ** **
>
> Thanks,
>
> marco
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA WebBox - Bluetooth vs RS485

2013-08-31 Thread Chris Mason
I have three in use since about two weeks ago. One webbox has nine Sunny
Tripower inverters on it. I love love love them. No cabling and tremendous
range. I have had to change the Bluetooth ID to distinct values because the
inverters on the next building about 200' away showed up as new devices.


On Fri, Aug 30, 2013 at 3:11 PM, Dave Click  wrote:

> Have folks been having good experiences with the SMA Bluetoothed WebBox,
> or should I stick with the standard 485 edition? I'm guessing it'll be
> about a 20' max triangle between the SB1TL, WebBox, and SensorBox.
> Likely using a Sprint modem for the internet connection.
>
> Thanks in advance and hope everyone has a nice weekend!
> Dave
> __**_
> List sponsored by Home Power magazine
>
> List Address: 
> re-wrenc...@lists.re-wrenches.**org
>
> Change email address & settings:
> http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive: http://lists.re-wrenches.org/**pipermail/re-wrenches-re-**
> wrenches.org<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.**htm<http://www.re-wrenches.org/etiquette.htm>
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Off Grid LP Gen advice

2013-09-14 Thread Chris Mason
Generac Ecogen is your best choice. It was specifically designed for the
long runs associated with charing batteries for off-grid work.


On Sat, Sep 14, 2013 at 11:58 AM, Dave Palumbo  wrote:

> Wrenchsters,
>
> ** **
>
> Looking for a good quality, long lasting, LP gas genset for my off grid
> rental house. 6 to 8kW. Full power at 120Vac would be nice. In the past
> some have recommended a Coleman off grid model as I remember. I’m also
> wondering how the smaller Kohlers, and the like, have been holding up for
> off grid use over the past few years.
>
> ** **
>
> This for northern Vermont where even with C/8 PV to battery charge rate we
> need to run the generator about 250 hours per year as the cloud cover is
> dense for weeks at a time.
>
> ** **
>
> Thanks,
>
> ** **
>
> Dave Palumbo
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Warranty Question (was Li-I question)

2013-09-20 Thread Chris Mason
; etiquette:
> >> www.re-wrenches.org/etiquette.htm
> >>
> >> Check out participant bios:
> >> www.members.re-wrenches.org
> >>
> >
> > ___
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Change email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> >
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3-Phase Service, One Phase Fails

2013-09-24 Thread Chris Mason
Real simple. A contactor with a phase loss detector gadget.

Chris Mason
Comet Systems
Anguilla (264) 235-5670
St. Kitts  (869) 662-5670
skype netconcepts

NABCEP Certified Solar PV Installer™
Renewable Energy Systems professional
Generac Generators Factory technician
On Sep 24, 2013 11:12 AM, "Karl Jaeger"  wrote:

>  Greetings Esteemed Wrenches,
>
> We are building a 35.75kW project with (6) Power One 6000’s. The service
> is a 240 delta. The utility is requiring (late in the game) that if one leg
> of the service is lost, all inverters must shut down. Of course, we have
> two inverters that do not shut down in that circumstance because they are
> only tied into the other two phases. SMA has a good (cheap) option to deal
> with this, SMA Power Balancers. With other inverters this can be
> accomplished by installing an ATS with an integrated controller by
> programming in the unacceptable phase imbalance (expensive). Does anyone
> have experience with this requirement and/or have a good (cheaper) solution?
> 
>
> Thank you in advance!
>
> ** **
>
> Karl Jaeger
>
> LightWave Solar 
>
> Nashville, TN
>
> ** **
>
> ** **
>
> ** **
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3-Phase Service, One Phase Fails

2013-09-24 Thread Chris Mason
I have felt for some time that inverters should have a logic control to
turn them off. "Short contact A to ground to disable inverter" type of
interface. If we had that, we could implement generator protection very
simply.

For your application, I see these being used in 3 phase pump control
systems.
http://www.taylorphaseguard.com/
Let me know if you need any more information.


On Tue, Sep 24, 2013 at 12:56 PM, Chris Mason
wrote:

> Real simple. A contactor with a phase loss detector gadget.
>
> Chris Mason
> Comet Systems
> Anguilla (264) 235-5670
> St. Kitts  (869) 662-5670
> skype netconcepts
>
> NABCEP Certified Solar PV Installer™
> Renewable Energy Systems professional
> Generac Generators Factory technician
> On Sep 24, 2013 11:12 AM, "Karl Jaeger" 
> wrote:
>
>>  Greetings Esteemed Wrenches,
>>
>> We are building a 35.75kW project with (6) Power One 6000’s. The service
>> is a 240 delta. The utility is requiring (late in the game) that if one leg
>> of the service is lost, all inverters must shut down. Of course, we have
>> two inverters that do not shut down in that circumstance because they are
>> only tied into the other two phases. SMA has a good (cheap) option to deal
>> with this, SMA Power Balancers. With other inverters this can be
>> accomplished by installing an ATS with an integrated controller by
>> programming in the unacceptable phase imbalance (expensive). Does anyone
>> have experience with this requirement and/or have a good (cheaper) solution?
>> 
>>
>> Thank you in advance!
>>
>> ** **
>>
>> Karl Jaeger
>>
>> LightWave Solar 
>>
>> Nashville, TN
>>
>> ** **
>>
>> ** **
>>
>> ** **
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SHW - parallel tanks

2013-09-24 Thread Chris Mason
Nathan,
I would love to see the schematic of how that works, we run into these
issues occasionally.


On Tue, Sep 24, 2013 at 7:55 PM, Nathan Stumpff wrote:

> Kirk,
>
> ** **
>
> We install this standard on basically all of our two tank systems. Small
> circulator w/ check valve from domestic tank HOT to solar preheat tank
> COLD. The ‘makeup’ water for that line is the one already installed,
> preheat HOT to domestic COLD. It operates on a delta-T control on both
> tanks, so if the preheat tank is warmer than the domestic tank, it moves
> that hot water from preheat to domestic. Benefits are increased solar
> storage (domestic tank becomes usable storage,) cooler preheat tank temps
> (so better collector efficiencies,) and no backup running when there is low
> DHW usage and the domestic tank cools off before the preheat tank.
>
> ** **
>
> The controls we use (RESOL) have this function preprogrammed, but any
> controller with a spare delta-T relay could be used if you have sensors on
> both tanks.
>
> ** **
>
> Works like a champ on really simple systems, we have had to monkey around
> and do some multi-tiered controls on systems with several heat sources to
> keep it from running at inappropriate times.
>
> ** **
>
> I’d be happy to share some drawings off-list if you like.
>
> ** **
>
> Cheers,
>
> -Nathan
>
> ** **
>
> --
>
> Nathan J. Stumpff
>
> NABCEP Certified PV Installation Professional #091209-175
>
> NABCEP Certified Solar Heating Installer #032412-14
>
> Project Manager | Arctic Sun, LLC
>
> nat...@arcticsun-llc.com  | (907) 457-1297
>
> www.reina-llc.com | www.arcticsun-llc.com
>
> [image: Description: ZA102637861] <http://www.facebook.com/ArcticSunLLC>**
> **
>
> ** **
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Kirk Herander
> *Sent:* Tuesday, September 24, 2013 2:19 PM
> *To:* RE-wrenches
>
> *Subject:* [RE-wrenches] SHW - parallel tanks
>
> ** **
>
> Hi,
>
> ** **
>
> Every summer I get a few calls from annoyed hot water customers who can’t
> stand hearing their boiler fire merely to keep the indirect tank up to
> setpoint temperature, when of course the solar preheat tank is at 160
> degrees or better at mid-day. So what’s the best way to transfer heat, in
> essence temporarily putting the tanks in parallel, from the solar tank to
> indirect? I can think of a few possibilities using a circulator and
> temperature controller, and a additional connection between the tanks, such
> as the tank drains plumbed together as a return line, but where is the best
> place to locate the circulator in a standard preheat arrangement (i.e. hot
> output of solar preheat plumbed to cold input of indirect tank)?
>
> ** **
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
> ** **
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] transformerless inverters and conductor colors

2013-09-24 Thread Chris Mason
Just brought it up with AEESolar and they can supply red and black PV Wire.
In reference to marking the conductor polarity with tape, wouldn't that
fall foul of the NEC rule that only allows wire colouring on conductors
larger than #6?


On Tue, Sep 24, 2013 at 2:17 AM, Ray Walters  wrote:

>  All Cable and probably other companies can add striping and marking to
> any wire you need.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer303 505-8760
>
> On 9/23/2013 10:57 PM, d...@energysolarnow.com wrote:
>
> Marco- You should not transition to THHN wire at all for the DC run. The
> PV wire is double insulated for a good reason- the transformerless
> inverters are such suckers for a ground fault that they need the extra
> protection. That's why the NEC specifies PV wire.
> I recently did an installation like you wrote, with a transition at the
> j-box. This developed an intermittent ground fault when wet, and when the
> P1 inverter failed it was deemed out of warranty.  Learn from my mistake--
> use PV wire all the way to the inverter.
>
>  That said, does anyone know where to get 1000 volt PV wire in colors
> other than red, black, and white?
> It would be nice to color code the positive runs like is possible with
> colors of THHN.
> I'm thinking of buying spools of white and spraying plastic paint on them
> for a striped color coding.
>
>  Don Barch
> Energy Solar
>
>
>   Message: 3
> Date: Mon, 23 Sep 2013 09:27:30 -1000
> From: "Marco Mangelsdorf" 
> To: "'RE-wrenches'" 
> Subject: [RE-wrenches] transformerless inverters and conductor colors
> Message-ID: <01ceb892$f3e41470$dbac3d50$@com>
> Content-Type: text/plain; charset="us-ascii"
>
> Hi all,
>
> We're doing more and more installs with TL inverters (SMA and P1).
>
> I'm using double-insulated wire from the array string to the first
> enclosure, as in j-box, and then transitioning to standard THHN/THWN wire.
>
> 
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:www.members.re-wrenches.org
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] ECO GEN ALERT

2013-09-25 Thread Chris Mason
Drake,
As a Generac service dealer, I brought your generator problem to the
attention of Generac's managers. They had a couple of comments:
1) The activation issue sounds like a misunderstanding. Activation is only
a data gathering process, I normally do it online (
https://www.activategen.com/ ). There is no reason why you could not do it
on behalf of the customer.
The activation reps do not handle service calls.

2) The oil hose issue should have resulted in a shutdown which would have
been simple to remedy. There's no record of generators being damaged by
this issue. However, if this is what happened, Generac is very good about
warranty repair and would be very responsive. I would call the nearest
Generac dealer and let them file a warranty claim. It does not matter that
the generator was not purchased from the dealer, all dealers are required
to handle warranty for any generator as they get paid to repair the units.
Generac will advise the dealer how to proceed. You seem to indicate Generac
did not want to replace the unit but I also get the feeling no tech has
looked at the unit yet. You have to follow the process. Generac will
determine the best course of action once they know the details.

Feel free to pass on any issues you are having resolving this issue. I can
get the service manager involved if you feel you are not getting adequate
response but you do need to get a service dealer involved before any
repairs or replacements can be discussed.

Chris




On Tue, Sep 24, 2013 at 10:34 AM, Drake <
drake.chamber...@redwoodalliance.org> wrote:

>  Wrenches,
>
> An unknown quantity of Generac EcoGens went out of the factory with
> incorrectly connected oil lines. We are working with Generac now,
> concerning a new unit that destroyed itself on its first run.
>
> After we hooked the machine up and left, the customer manually started the
> machine the following day. We were not able to do the startup because we
> did not have *all the information* needed for Generac to provide us with
> the access code needed to start the unit. The representative told me she
> would give me the code, but that it would void the warranty!  Beware of the
> many EcoGen warranty loopholes!
>
> After providing the necessary information to Generac and receiving the
> access code, my client started the unit and watched happily as the machine
> ran quietly and charged the batteries at twice the rate of her old unit.
> She went about her chores, and 2 hours later noticed that the yard had a
> tremendous amount of smoke in it. The generator was pouring out smoke. The
> lid of the enclosure was too hot to touch.
>
> The machine was seriously damaged. Much of the oil was blown out.*Neither the 
> over-temperature nor the low engine oil shutdown functioned to
> protect the unit*.
>
> We are asking Generac to provide a new unit, not repair the flawed one, as
> the amount of overheating could have damaged unknown components. We
> understand that Generac would prefer to repair instead of replace.
>
> Under the circumstances, it would be wise to monitor a new EcoGen for much
> longer than would normally be required after startup. How long?  I don't
> know. I'd wait two hours to feel safe.
>
> Best,
>
> Drake
>
> Drake Chamberlin
> *Athens Electric LLC
> OH License 44810
> CO License 3773
> NABCEP Certified Solar PV Installer
> 740-448-7328
> *http://athens-electric.com/
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] ECO GEN ALERT

2013-09-28 Thread Chris Mason
they are not going to pay for someone's time that is not a service tech.
I'd be pretty happy just to get the replacement shipped to me.


On Sat, Sep 28, 2013 at 11:26 AM, Larry Crutcher, Starlight Solar Power
Systems  wrote:

> It's good to see this response instead of the all to often "not our fault"
> excuse. Any chance they will pay for your time? Shipping?
>
> Larry Crutcher
>
>
>
>
> On Sep 28, 2013, at 7:22 AM, Drake 
> wrote:
>
>  Chris,
>
> Generac has stated that the Eco Gen will be replaced.  *Thank you* for
> your help, and for the help of Frank Moreno who you notified of the issue.
>
> Best regards,
>
> Drake
>
>
> Drake Chamberlin
> Athens Electric LLC
> OH License 44810
> CO License 3773
> NABCEP Certified Solar PV Installer
> 740-448-7328
> http://athens-electric.com/
>
>
> At 06:34 PM 9/25/2013, you wrote:
>
> Drake,
> As a Generac service dealer, I brought your generator problem to the
> attention of Generac's managers. They had a couple of comments:
> 1) The activation issue sounds like a misunderstanding. Activation is only
> a data gathering process, I normally do it online (
> https://www.activategen.com/ ). There is no reason why you could not do
> it on behalf of the customer.
> The activation reps do not handle service calls.
>
> 2) The oil hose issue should have resulted in a shutdown which would have
> been simple to remedy. There's no record of generators being damaged by
> this issue. However, if this is what happened, Generac is very good about
> warranty repair and would be very responsive. I would call the nearest
> Generac dealer and let them file a warranty claim. It does not matter that
> the generator was not purchased from the dealer, all dealers are required
> to handle warranty for any generator as they get paid to repair the units.
> Generac will advise the dealer how to proceed. You seem to indicate
> Generac did not want to replace the unit but I also get the feeling no tech
> has looked at the unit yet. You have to follow the process. Generac will
> determine the best course of action once they know the details.
>
> Feel free to pass on any issues you are having resolving this issue. I can
> get the service manager involved if you feel you are not getting adequate
> response but you do need to get a service dealer involved before any
> repairs or replacements can be discussed.
>
> Chris
>
>  ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Generator automatic disconnect

2013-09-30 Thread Chris Mason
Why not utilize the Generac Smart switch and load management module? It
will disconnect up to four circuits based on load.


On Mon, Sep 30, 2013 at 4:02 PM, Larry Crutcher, Starlight Solar Power
Systems  wrote:

> Wrenches,
>
> I want to use the Ecogen 6kW generator on a large off grid system. The
> location has very few overcast or rainy days and the generator will rarely
> be needed. My concerns is nuisance tripping the generator output breakers
> if the household load exceeds 6kW. The power system control has a feature
> for reducing the AC current used to charge the batteries but does not have
> a feature for disconnecting the AC input based on input load.
>
> Does anyone have a solution for monitoring AC load from the generator and
> disconnect it if overloaded? It must automatically reconnect after a short
> timeout.
>
> Thank you,
> Larry Crutcher
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Generator automatic disconnect

2013-10-01 Thread Chris Mason
Generac also makes a 20kw.

Chris Mason
Comet Systems
Anguilla (264) 235-5670
St. Kitts  (869) 662-5670
skype netconcepts

NABCEP Certified Solar PV Installer™
Renewable Energy Systems professional
Generac Generators Factory technician
On Oct 1, 2013 11:16 AM, "Ray Walters"  wrote:

> Sounds like they need a 20 Kw Kohler. Hot Tub in the future?  They'll love
> their Kohler.  The Generac is just way too small to even consider IMHO.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
>
> On 10/1/2013 8:11 AM, Larry Crutcher, Starlight Solar Power Systems wrote:
>
>> William, Chris, Ray, Allan, et al.
>>
>> Gen support would be ideal but this inverter setup will be a quad pack of
>> Magnum 4024PAE (120/240 split; 16kW). Their New MSH inverter is single
>> phase only and can not be stacked.
>>
>> While disabling load(s) is the antithesis of the desired outcome, I'll
>> review this possibility further.
>>
>> Using a separate charger could work but it would need to be about 200A @
>> 32V which would add quite a bit of cost and be hard to sell since the
>> Magnum inverters already have 4 high quality charges included.
>>
>> A larger generator might be necessary if the customer won't agree to load
>> shedding. Their plans are to expand the loads over time, operate a
>> business, install a hot tube and more. Of course I have pushed the concept
>> that conservation is paramount. The PV array and inverters are being
>> oversized now for the future growth.
>>
>> My ideal solution...Since Magnum inverters monitor the AC input and
>> control it based on quality of power, it seems to me that there could be a
>> setting for disconnecting the AC input if loads exceed a setpoint. Change
>> in control software would be great.
>>
>>
>> Thank you,
>> Larry
>>
>>
>>
>> On Sep 30, 2013, at 4:14 PM, William Miller 
>> wrote:
>>
>> Larry:
>>
>> Maybe a better approach might be to use an inverter with "Gen-support."
>> That is unless a system already exists that does not have this feature.
>>
>> Plan B:  use the gen start signal to disable one or more of the larger
>> loads.
>>
>> I know this is not what you asked for, just trying inject some different
>> ideas.
>>
>> William
>> -Original Message-
>> From: 
>> re-wrenches-boun...@lists.re-**wrenches.org
>> [mailto:re-wrenches-bounces@**lists.re-wrenches.org]
>> On Behalf Of Larry
>> Crutcher, Starlight Solar Power Systems
>> Sent: Monday, September 30, 2013 1:02 PM
>> To: RE-wrenches
>> Subject: [RE-wrenches] Generator automatic disconnect
>>
>> Wrenches,
>>
>> I want to use the Ecogen 6kW generator on a large off grid system. The
>> location has very few overcast or rainy days and the generator will rarely
>> be needed. My concerns is nuisance tripping the generator output breakers
>> if
>> the household load exceeds 6kW. The power system control has a feature for
>> reducing the AC current used to charge the batteries but does not have a
>> feature for disconnecting the AC input based on input load.
>>
>> Does anyone have a solution for monitoring AC load from the generator and
>> disconnect it if overloaded? It must automatically reconnect after a short
>> timeout.
>>
>> Thank you,
>> Larry Crutcher
>> __**_
>> List sponsored by Home Power magazine
>>
>> List Address: 
>> re-wrenc...@lists.re-wrenches.**org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> List-Archive: http://lists.re-wrenches.org/**pipermail/re-wrenches-re-**
>> wrenches.org<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.**htm<http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> __**_
> List sponsored by Home Power magazine
>
> List Address: 
> re-wrenc...@lists.re-wrenches.**org
>
> Change email address & settings:
> http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archiv

Re: [RE-wrenches] Generator automatic disconnect

2013-10-01 Thread Chris Mason
I haven't been a dealer long enough to remember the problems you refer to.
We don't have the sales volume to be able to speak with authority on faults
statistics but I get the impression that the quality of Generac units has
improved a lot over the last couple if years. Most of our problems are
related to lightning and bad power from the utility.

One of the problems with these air cooled units, from any manufacturer, is
the unrealistic expectations of the buyers. People want to spend $3,000 and
get a whole house generator with service rated transfer switch, and they
think that it will perform like a prime mover. The air cooled units are
good for about five or six years of occasional use. I have Kohler units
that have failed at about that period. The whole point of the ecogen is the
longer run times due to the large oil reservoir.

I have a 10 year old Lister Petter diesel with a Stamford 16KW alternator
at my warehouse that will run 20,000 hours before it needs a strip down.
Generac sells very good industrial diesels, but they cost 6 times as much
as an air cooled, so no homeowner will buy them.
Most people do not need a heavy duty generator and I see so many businesses
here over specify their generators and spend way more than they need to. I
visited a store that bought a 200KVA genset so they could run air
conditioning, but turned the air conditioning off because the electricity
cost was too expensive. Their operational load was only about 20KVA.


Anyway, I think you will find the new Generac units are very affordable and
reliable, as long as your customers have realistic expectations.








On Tue, Oct 1, 2013 at 2:29 PM, Allan Sindelar <
al...@positiveenergysolar.com> wrote:

>  Chris,
> I consider the Ecogen to be a singular model, specifically developed in
> partnership with the Propane Reliability Council for off grid applications,
> in one size and structure only at present. Early on, I put my rep on the
> line here in saying "hey, Generac has had a well-deserved bad reputation on
> this list, but take a look at this new model." There has been a lot of
> discussion about it on this list, and the general consensus is that it is
> proving itself to be a well made product.
>
> As far as I can see, though, I'll wait until I hear (on this list
> especially) that other sizes and models are proving up as good, reliable
> machines with no fundamental design flaws before extending the Ecogen's
> good reviews to the entire line. I never sold Generac, and haven't had
> reason to work with their other models in years. The few from back then
> were problematic, as others have discussed here.
>
> You have been one of their installing dealers for many years, haven't you?
> Have you had consistently good experiences with them? What issues have you
> dealt with over the years?
> Thanks, Allan
>
>
>  ** ** ** ** **
>
> *Allan Sindelar*
> *al...@positiveenergysolar.com* 
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder, *Positive Energy, Inc.*
>
> A Certified B CorporationTM
> 3209 Richards Lane**
> **Santa Fe**, **New Mexico** **87507
> *505 424-1112 office 780-2738 cell*
> *www.positiveenergysolar.com* <http://www.positiveenergysolar.com/>
>
>
>  **
> On 10/1/2013 9:40 AM, Chris Mason wrote:
>
> Generac also makes a 20kw.
>
> Chris Mason
> Comet Systems
> Anguilla (264) 235-5670
> St. Kitts  (869) 662-5670
> skype netconcepts
>
> NABCEP Certified Solar PV Installer™
> Renewable Energy Systems professional
> Generac Generators Factory technician
> On Oct 1, 2013 11:16 AM, "Ray Walters"  wrote:
>
>> Sounds like they need a 20 Kw Kohler. Hot Tub in the future?  They'll
>> love their Kohler.  The Generac is just way too small to even consider IMHO.
>>
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer,
>> Licensed Master Electrician
>> Solar Design Engineer
>> 303 505-8760
>>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Eaton bolt on panel modifications

2013-10-04 Thread Chris Mason
Check on Ebay, people often sell excess parts for panels.


On Fri, Oct 4, 2013 at 2:12 AM, William Miller wrote:

> Friends:
>
> ** **
>
> I need to modify an Eaton 400 amp panelboard for an industrial off-grid
> system.  I need 3 150 amp 2 pole breakers and a few of the clips used to
> connect the bolt-on breakers to the busses (“Provisions,” they are called).
> 
>
> ** **
>
> I was informed by the Eaton rep that the cost to replace the entire
> interior of the panelboard was cheaper than buying a few clips.  It was
> explained that buying “loose parts” was more expensive than buying an
> entire bus system.  I just cannot believe this.  
>
> ** **
>
> Has anyone purchased the clips for Eaton before?  Know a good Eaton dealer?
> 
>
> ** **
>
> Thanks in advance.
>
> ** **
>
> William Miller
>
> ** **
>
> ** **
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 15k Guardian

2013-10-06 Thread Chris Mason
Send me the model and serial number, I will get it for you.


On Sat, Oct 5, 2013 at 1:03 AM, Mac Lewis  wrote:

> Hi Wrenches,
>
> Does anyone have a service manual for an older 120/240 15 kW Generac
> Guardian generator?  It has a very simple 5 light user interface board.  It
> is well out of warranty, but I'd like to help these folks out if I can.
>
> I am not a generac dealer, so I can't get any help from them
>
> Thanks in advance
>
> --
>
>
>
> Mac Lewis
>
> *
>
> "Yo solo sé que no sé nada." -Sócrates
> *
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Teck 90

2013-10-12 Thread Chris Mason
http://www.southwire.com/products/CSATeck90PowerCable.htm


On Wed, Oct 9, 2013 at 2:11 PM, Ray Walters  wrote:

>  How is TEK 90 referenced in the NEC?  Does it meet the qualifications to
> be used inside an attic for instance?
> Finally the onestopbuy link was very light on info;  are the cables inside
> stranded or solid?
>
> Thanks,
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer303 505-8760
>
> On 10/9/2013 12:02 PM, Hilton Dier III wrote:
>
> William,
>
> We get it with two pairs of color coded #8 copper and a #10 ground. Off
> the shelf you can get #14, #12, #10, #8, and #6 and on up to 500 MCM. The
> 14-10 go up to 10 conductors and the 8 and 6 go up to 4 conductors.
>  Here's a URL, not the cheapest place, but to give you an idea:
> http://www.onestopbuy.com/wire-cable/Product-Price-Code-TK-40629.aspGraybar 
> had the best price for us.
>
> You can also get it custom in big quantities from some manufacturers.
>
> If you support it every 18" or so it stays straight. The end connectors
> are a bit of a PITA to assemble. The key is to cut the end of the armor
> cleanly and as directed and then disassemble the connector and put it on
> piece by piece. Takes a couple of minutes.
>
> Hilton
>
> --
> Hilton Dier III
> Renewable Energy Design
> Partner, Solar Gain LLC
> 453 East Hill Rd.
> Middlesex, VT 05602
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:www.members.re-wrenches.org
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fronius Installer Support Sucks- but who else?

2013-10-16 Thread Chris Mason
SMA just came out with their Sunny Tripower line for the US. I love the
Tripower line, I have been buying the European ones for one of our projects
and they are the greatest. I love the Bluetooth connectivity, so much
easier than running Cat5 to inverters.

http://www.sma-america.com/en_US/products/grid-tied-inverters/sunny-tripower/sunny-tripower-12000tl-us-15000tl-us-2tl-us-24000tl-us.html



On Wed, Oct 16, 2013 at 3:15 PM,  wrote:

> Jeff- Sorry to hear about your frustration with Fronius. And thanks Bob-O
> for posting their tech support number.
> Recently I had to get this number from AEE since it is not listed in the
> Fronius manuals.
> A new installation with a pair of 11.4-3 phase Delta inverters refused to
> come up and detect the grid. A call to Barry at tech support solved the
> problem-- press the Menu button 5 times and enter a secret code number.
> This was of course undocumented in their manual. No reason for this kind of
> opaque secrecy.
> But is there any other option for 240 VAC 3-phase Delta inverters?
> (Except for Sunny Tower with single phase inverters.)  I'm about to buy
> some more for another new installation with the same service
> Thanks
> Don Barch
> Energy Solar
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fronius Installer Support Sucks- but who else?

2013-10-16 Thread Chris Mason
The range has been excellent, I can park 20' away and adjust the parameters
of the inverters and gather data.


On Wed, Oct 16, 2013 at 4:00 PM, Isaac Opalinsky <
david.opalin...@sunpower.com> wrote:

>  How have you found the range of the Bluetooth?  Have you had flexibility
> with the relative location of the inverter/monitoring components?
>
> ** **
>
> *Isaac Opalinsky *| Technical Trainer | *SunPower Corporation*
>
> Desk 443-569-3476 | Cell 443-277-6286
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] smaller 3-phase commercial inverters

2013-10-18 Thread Chris Mason
Probably because these small three phase inverters are adapted European
designs. In Europe, three phase 415 is normal. The Tripowers have an upper
voltage range of 480V so adapting them to the US is pretty easy. To adapt
to 208, all the power boards, terminals, and cabling would need to be twice
the size, so a total redesign is required. I suspect that the larger
Tripowers could never be 208V because of the currents.



On Fri, Oct 18, 2013 at 12:31 AM, Marco Mangelsdorf wrote:

> Yeah, lots more choices out there in the 10+ to 30 kW range….but pretty
> much all of the larger capacity models only come at 480V.
>
> ** **
>
> Anyone know why?  We have way more 120/208V applications here in Hawaii
> than 277/480.
>
> ** **
>
> marco
>
> ** **
>
> Chris Mason wrote:
>
> ** **
>
> >SMA just came out with their Sunny Tripower line for the US. 
>
> ** **
>
> Yes those are interesting. But they are only for 480 Wye, not 240
> Delta.
>
> Is the Fronius 11.4-3 the only 3-phase inverter that can work with 240
> 3-phase with a hi-leg (stinger)?
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] smaller 3-phase commercial inverters

2013-10-18 Thread Chris Mason
The Aurora 10K PVI are available in 208V.
http://www.power-one.com/sites/power-one.com/files/documents/renewable-energy/datasheet/pvi-100-i-nadatasheet.pdf



On Fri, Oct 18, 2013 at 12:31 AM, Marco Mangelsdorf wrote:

> Yeah, lots more choices out there in the 10+ to 30 kW range….but pretty
> much all of the larger capacity models only come at 480V.
>
> ** **
>
> Anyone know why?  We have way more 120/208V applications here in Hawaii
> than 277/480.
>
> ** **
>
> marco
>
> ** **
>
> Chris Mason wrote:
>
> ** **
>
> >SMA just came out with their Sunny Tripower line for the US. 
>
> ** **
>
> Yes those are interesting. But they are only for 480 Wye, not 240
> Delta.
>
> Is the Fronius 11.4-3 the only 3-phase inverter that can work with 240
> 3-phase with a hi-leg (stinger)?
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Elliot Power Systems MPSG-12

2013-10-23 Thread Chris Mason
Most gensets are combinations of other manufacturers products, such as a
Perkins engine with a Stamford alternator in a housing with a controller.
Very few generator manufacturers make their own controllers. You need to
find the manufacturer and model of the controller, the genset is
irrelevant. Once you get that you should be able to find the documentation.


On Wed, Oct 23, 2013 at 4:21 AM, Mac Lewis  wrote:

> Hello wrenches,
>
> Does anyone have any information on an Elliott Power Systems Generator
> MPSG-12, 12 kW stand by generator?  It was put in by another installer
> about 7 years ago and they are not in business any longer.  It seems to run
> well, but I can't make the two-wire start work.  It was wired in what
> looked like a two wire start configuration.  There are two 20+ pin terminal
> blocks with no documentation.
>
> Any info would help.
>
> Thanks in advance
>
> --
>
>
>
> Mac Lewis
>
> *
>
> "Yo solo sé que no sé nada." -Sócrates
> *
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] wrenches] Hidden freight damage

2013-11-05 Thread Chris Mason
claim. They simply cited that the shipment had been
> signed for without noting damage.
> It is clear to me that the carrier was responsible for the damage, yet
> apparently because the damage was hidden and the BOL was signed, they can
> leave me holding the bag for a significant amount of money.
>
> This particular incident could have been worse, but it is the first time
> I've had it happen and it certainly makes me worried about future
> deliveries. It suddenly seems like an unacceptable liability to have others
> sign for my deliveries without a thorough inspection.
>
> I asked my distributor whether the shipments have any insurance on them,
> and the person I spoke with didn't know the answer. So my $50 Ebay shipment
> is insured, but my $50,000 worth of equipment isn't? My insurance agent
> says that I can make a claim on my commercial insurance, but advised
> against it in this case, since the loss was only around $1K, and is
> guaranteed to raise my future premiums.
>
> I know that things get damaged or lost all the time in shipment, and I'm
> wondering how other businesses handle it.  Businesses that do larger volume
> must have damaged freight all the time.  Is it just impossible to get
> freight companies to take responsibility for damage that is not immediately
> evident, since they are acting as judge on their own behalf?  Do you just
> refuse to sign the bill of lading until you've examined all the contents of
> the packages (this is a logistical nightmare in most cases)?  Do you just
> chalk it up to the cost of doing business and/or make claims to your
> commercial insurance?
>
> Would appreciate your thoughts / experiences with this issue.
> Thanks. - Luke
>
> Luke Christy
>
> NABCEP Certified PV Installation Professional™: Certification #031409-25
> NABCEP Certified Solar Heating Installer™: Certification #ST032611-03
>
> CoSEIA Certified PV Installer
>
> Solar Gain Services, LLC
> PO Box 531
> Monte Vista, CO. 81144
> sgsrenewab...@gmail.com
> 719.588.3044
> www.sgsrenewables.com
>
>
>
>
>
>
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>*t...@swnl.net*   *www.SWNL.net*
>  Solarwinds Northernlights
> *   Serving Mid Coast Maine & Northern California*
> * 207-832-7574 <207-832-7574>   Cl. 610-517-8401
> <610-517-8401>  *
>   *Blair "TUMP" May*
>
> *     MAINE'S CHARTER   *   *
> NABCEP"Certified PV Installer"*
>
>
> *    MAINE'S CHARTER    **
> Trace Xantrex "Certified" Dealer / Installer"*
>
>
>
>   ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:www.members.re-wrenches.org
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PV Wiring methods

2013-11-15 Thread Chris Mason
protected
>> >> from damage, you have a great chance of a reliable, safe lifetime of
>> >> service.  How can you guarantee that your leads will stay protected
>> >> after
>> >> the ties fail?  Studies show that even UV resistant wire ties will
>> >> fail well
>> >> before the life expectancy of the system has expired.  When the ties
>> >> fail,
>> >> your PV leads are hanging on the roof.  Even before the ties fail,
>> >> rodents
>> >> can chew on them.  Conduit was invented for a reason and we should be
>> >> using
>> >> it.
>> >>
>> >>
>> >> I agree that arc-fault breakers will improve the situation, but I
>> >> don't
>> >> think any form of OCPD is a substitute for good wiring practices.  I
>> >> think
>> >> wire protection is just as important on PV circuits as it is on any
>> >> other
>> >> high voltage circuit.  Try getting away with wiring a rooftop air
>> >> conditioning unit by tying the conductors to some metal framework with
>> >> plastic ties and see how long it takes to get red-tagged by your local
>> >> inspector.
>> >>
>> >>
>> >> I suspect we've gotten to where we are on lax wire protection
>> >> standards for
>> >> two reasons:
>> >>
>> >> 1.In the early days, PV was low voltage, 12 to 24 volts, and was
>> >> treated
>> >> as such, even though current capabilities exceeded that of
>> >> conventional low
>> >> voltage thermostat, door-bell and telephone wiring.
>> >>
>> >> 2.It is my understanding that PV wiring standards in Europe are
>> >> not
>> >> stringent, and European demand drove the PV market for many years.
>> >> Products
>> >> were built to satisfy the European market and US standards had to work
>> >> with
>> >> the equipment available.
>> >>
>> >>
>> >> Some would say: "if it is under the array, it is protected."  We have
>> >> seen
>> >> PV wire getting damaged under arrays and it is possible to get damaged
>> >> under
>> >> BPIV components as well.  I believe that protecting PV wire is more
>> >> important than protecting conventional AC circuit wiring because PV
>> >> circuits
>> >> are more prone to create and sustain arcing.
>> >>
>> >>
>> >> Some say that protecting PV wire in conduits will add too much expense
>> >> to PV
>> >> installations.  Consider the cost of fires and, inevitably, injuries
>> >> and
>> >> deaths.  One news story about an obscure, rarely used product is
>> >> already
>> >> causing many of us headaches.  Statistically, it is inevitable that
>> >> more
>> >> accidents will happen. I don't want that on my conscience.
>> >>
>> >>
>> >> I would suggest that we need to expand the discussion beyond fire
>> >> hazards.
>> >> I also worry about electrocution hazards in high voltage PV circuits.
>> >> Good
>> >> wire protection is essential in preventing contact with high voltages.
>> >>
>> >>
>> >> Unprotected PV wiring is an irresponsible practice.  I am fighting an
>> >> uphill
>> >> battle to develops methods to protect PV wiring because the industry
>> >> is not
>> >> helping at all.  The trend has been to make it harder to protect
>> >> wiring.
>> >> This trend will result in accidents.  I think we should do better.
>> >>
>> >>
>> >> Sincerely,
>> >>
>> >>
>> >> William Miller
>> >>
>> >>
>> >>
>> >> From: re-wrenches-boun...@lists.re-wrenches.org
>> >> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill
>> >> Brooks
>> >> Sent: Monday, November 11, 2013 3:38 PM
>> >> To: 'RE-wrenches'
>> >> Subject: Re: [RE-wrenches] RE-wrenches Digest, Vol 6, Issue 423
>> >>
>> >>
>> >> William and David,
>> >>
>> >>
>> >> This particular problem goes away with arc fault detection. The longer
>> >> we
>> >> wait to introduce arc fault detection into our systems, the more we
>> >&

Re: [RE-wrenches] Busbar rating with multiple main breakers

2013-12-19 Thread Chris Mason
The 120% rule refers to source breakers, not load breakers.


On Thu, Dec 19, 2013 at 3:16 PM, SunHarvest  wrote:

>  Hi guys -
>
> Concerning the 120% rule: I've encountered several circumstances recently
> where a 400A nameplate-rated (listed on inside label) main panel has two
> 200A main breakers. One of the breakers will be feeding the busbar in the
> main and the other will feed a subpanel. I had previously thought the main
> busbar is rated at the nameplate rating (400A in this case) regardless of
> quantity of main breakers. My lead electrician says the main busbar in
> these types of panels is derated to 200A because of the split. However, I
> have two other reliable electrician friends who disagree with my lead
> electrician. One of my C10 buddies says it depends on whether or not the
> busbar in the main is broken up into 2 sections (200A) or it is continuous
> (400A). Can anyone clear up, beyond doubt, our disagreement?
>
> Thanks!
>
> Eric Stikes
> SunHarvest
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Xantrex 6048 installation for house with existing automatic generator design assistance

2013-12-30 Thread Chris Mason
A house with 2 x 400A panels draws a maximum of 20A? There's something
wrong in your numbers.


On Mon, Dec 30, 2013 at 5:45 PM, Christopher Warfel <
cwar...@entech-engineering.com> wrote:

> I am working on a project that requires someone with more experience than
> I have in generators and transfer switches.
>
> Would you please contact me off line if interested
>
> Currently
>
> Utility fed house with two 400 amp panels.  Maximum total house current
> drawn over a long monitoring period is 20 amps. Owner wanted these panels
> so almost every load is on its own breaker.
>
> The house also has a 25kVa generator on an automatic transfer switch.
>
>
>
> Proposed
>
> Installing two 3.2kW arrays each on its own Xantrex 80amp600Vdc charge
> controller.
>
> Battery backup system to take through momentaries and short duration (1
> day? outages)
>
> Want to use existing generator to charge batteries and power house in the
> event of utility outage, and batteries are at low voltage state.
>
> Required to automatically revert to Current situation if inverter fails
> and no one is home. [This is the part that I need assistance on]
>
> Thank you, Chris
>
>
>
>
>
> --
>
> Christopher Warfel, P.E.
> ENTECH Engineering, Inc.
> Energy Utilization Experts
> (401)466-8978
>
> The information contained within this communication shall
> be considered confidential and shall not be retransmitted
> without knowledge of the sender. Please contact us if
> this email reached you in error. Thank you.
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Outback 200 RE

2014-01-18 Thread Chris Mason
We don't do a lot of off-grid systems so I am short on experience with
battery systems. I have a 8KW Radian system for which I am considering
Rolls Surrette or Outback 200RE AGM batteries. I know people like the
Surrettes, what is the experience with the outback battery system?

-- 
Chris Mason
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback 200 RE

2014-01-18 Thread Chris Mason
This is for an off-grid system.


On Sat, Jan 18, 2014 at 8:07 PM, Jerry Shafer wrote:

> For for grid tie system l I would only use AGM weather it be interstate or
> rolls and amps per buck is better over time
> Jerry
> On Jan 18, 2014 3:16 PM, "Chris Mason" 
> wrote:
>
>> We don't do a lot of off-grid systems so I am short on experience with
>> battery systems. I have a 8KW Radian system for which I am considering
>> Rolls Surrette or Outback 200RE AGM batteries. I know people like the
>> Surrettes, what is the experience with the outback battery system?
>>
>> --
>> Chris Mason
>>
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback 200 RE

2014-01-19 Thread Chris Mason
The project is hybrid, the house has utility power at the moment.
I was looking for feedback on the product, I haven't heard comments on the
Outback RE battery system.
In the end I recommended a single string of TROJAN, IND9-6V. We will revert
to grid at 80% DOD.
The house is tropical, high in the mountains and doesn't use a lot of power.





On Sun, Jan 19, 2014 at 9:22 PM, Allan Sindelar <
al...@positiveenergysolar.com> wrote:

>  Tom,
> I may be mistaken, but if I understood you correctly you have missed
> something. The Radian is available only in 48v, so four 12V 200 Ah
> batteries is eight kilowatt-hours of storage to 80% maximum DoD. Yes, it's
> small (my off grid home has 26 kW) but one or two strings may be adequate,
> depending on the customer's application and needs.
> Allan
>
>   *Allan Sindelar*
> *al...@positiveenergysolar.com* 
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder, *Positive Energy, Inc.*
>
> A Certified B CorporationTM
> 3209 Richards Lane
> Santa Fe, New Mexico 87507
> *505 424-1112 <505%20424-1112> office 780-2738 cell*
> *www.positiveenergysolar.com* <http://www.positiveenergysolar.com/>
>
>
>   On 1/19/2014 6:12 PM, Tom Duffy wrote:
>
>  Hi Chris
>
>
>
> For an off grid system a 200AH 12 volt battery is rather small without
> resorting to parallel strings.
>
>
>
> Three strings is only 600AH which is still on the small side, so one might
> ask why the 8K inverter?
>
>
>
> The OutBack cabinet is fine for a back-up grid-tied system, not really a
> full off grid house
>
>
>
> Without starting a big discussion, I would stick to a single series string
> sized to the load for three days autonomy.
>
>
>
> 200AH is usually a rather small weekend cabin and 600AH would be a smaller
> medium sized house.
>
>
>
> Kind regards
>
>
>
> *Tom Duffy*
>
> *Senior Solar Design Engineer*
>
> [image: Real-logo-X-195]
>
> *E-Mail: **t...@thesolar.biz *
>
> *Panama Office: **507-6126-1253*
>
> *Direct Toll Free:**888-503-6772 <888-503-6772>*
>
> *International: **575-539-2111 <575-539-2111>*
>
> *SKYPE Address: **thesolarbiz*
>
> *Although no trees were killed in the sending of this message, a large
> number of electrons were terribly inconvenienced.*
>
>  *Confidentiality Notice*: This message including any attachments is for
> the sole use of the intended recipient and may contain confidential and
> privileged information. Any unauthorized review, use, disclosure or
> distribution is prohibited. If you are not the intended recipient, please
> contact the sender and delete any copies of this message.
>
>
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [
> mailto:re-wrenches-boun...@lists.re-wrenches.org]
> *On Behalf Of *Chris Mason
> *Sent:* Saturday, January 18, 2014 6:16 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Outback 200 RE
>
>
>
> We don't do a lot of off-grid systems so I am short on experience with
> battery systems. I have a 8KW Radian system for which I am considering
> Rolls Surrette or Outback 200RE AGM batteries. I know people like the
> Surrettes, what is the experience with the outback battery system?
>
>
>
> --
> Chris Mason
>
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:www.members.re-wrenches.org
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback 200 RE

2014-01-20 Thread Chris Mason
So back to the question...has anyone had experience with the Outback 200RE?
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Very small PV systems for surveillance or other "micro" loads

2014-01-21 Thread Chris Mason
You can use the systems designed for solar street lights. TIny controllers,
small panels and everyhting mounted on a pole.


On Tue, Jan 21, 2014 at 9:07 AM, Jason Szumlanski wrote:

> That's the answer I thought I'd get from most. It's hard to explain the
> "days of autonomy" and extended bad weather to people. Most just say, "why
> don't you just make a recommendation." That puts me in a spot where I want
> to overbuild, which drives up cost.
>
> The other challenge is getting people to tell you the real story about
> what they plan to plug in. They think 100W @ 120V continuous load 24 hours
> a day sounds like a very small load. When you hit them with a ~1kW system
> with a ~10kWh battery (with ample reliability factors considered), they
> freak out. Then you find out that the camera they wanted to plug in only
> draws 18W @ 12V (no inverter required). That's a big difference.
>
>
> Jason
>
>
> On Mon, Jan 20, 2014 at 3:46 PM, Larry Crutcher, Starlight Solar Power
> Systems  wrote:
>
>> Jason,
>>
>> We get quite a few of these from US Border Patrol, GM Proving Grounds and
>> other agencies. I always do custom design since every job has different
>> parameters like days of autonomy or remote monitoring/control (SCADA).
>>
>>
>> Larry Crutcher
>>
>>
>>
>>
>> On Jan 20, 2014, at 1:17 PM, Jason Szumlanski 
>> wrote:
>>
>> What do you do for very small off-grid systems that people want for
>> specific equipment? Do you have a "go-to" configuration, or do you size and
>> design everything custom?
>>
>> For example, I frequently get, "I want to run cameras at a remote site
>> and the total requirement is 100W, 24 hours a day."
>>
>> It's not economical to reinvent the wheel every time.
>>
>>
>> Jason Szumlanski
>> Fafco Solar
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback 200 RE

2014-01-22 Thread Chris Mason
This is what the customer decided on.
What kind of life do you expect?


On Tue, Jan 21, 2014 at 10:20 AM, Tom Duffy  wrote:

>  Chris
>
>
>
> Yes they seem to be a well-made good quality battery, and we have not had
> any problems in properly designed and programed systems.
>
>
>
> Kind regards
>
>
>
> *Tom Duffy*
>
> *Senior Solar Design Engineer*
>
> [image: Real-logo-X-195]
>
> *E-Mail: **t...@thesolar.biz *
>
> *Panama Office: **507-6126-1253*
>
> *Direct Toll Free:* *888-503-6772 <888-503-6772>*
>
> *International: **575-539-2111 <575-539-2111>*
>
> *SKYPE Address: **thesolarbiz*
>
> *Although no trees were killed in the sending of this message, a large
> number of electrons were terribly inconvenienced.*
>
>  *Confidentiality Notice*: This message including any attachments is for
> the sole use of the intended recipient and may contain confidential and
> privileged information. Any unauthorized review, use, disclosure or
> distribution is prohibited. If you are not the intended recipient, please
> contact the sender and delete any copies of this message.
>
>
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Chris Mason
> *Sent:* Monday, January 20, 2014 7:58 PM
>
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Outback 200 RE
>
>
>
> So back to the question...has anyone had experience with the Outback
> 200RE?
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tray cable with PV-Wire on roof

2014-01-28 Thread Chris Mason
We use HDG cablofil with tray cover.

Chris Mason
Comet Systems
Anguilla (264) 235-5670
St. Kitts  (869) 662-5670
skype netconcepts

NABCEP Certified Solar PV Installer(tm)
Renewable Energy Systems professional
Generac Generators Factory technician
On Jan 28, 2014 4:21 PM, "Davis Terrell"  wrote:

>Wrenches,
>
>
>
> Anyone have any experiences with running #10 PV-Wire in a cable tray on a
> sloped (albeit slight) roof?  I have to collect a number of home runs along
> a 180' stretch of roof and would prefer not to transition on the roof or
> penetrate the roof.  I searched the archives and found a few mentions, but
> not much info.  Any problems with inspections?  Also, what are thoughts
> about fabricating an Aluminum "shroud" of sorts to keep UV off the wires?
> Thanks in advance,
>
>
>
>
>
> Davis Terrell
>
> Project Manager
>
> Green Earth Energy
>
> da...@mckernongroup.com
>
> office: (802) 247-1200
>
> mobile: (802) 989-1661
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Long transmission line inductance and LED light flicker

2014-02-02 Thread Chris Mason
You should rent or borrow a power quality analyzer to look at the phase
angles and harmonic distortion throughout the day. A scope will also help
to allow you to look at the waveform of the inverter produced electricity.
You need to properly identify the cause of the problem before you invest in
any equipment.

Resistive loads will not change phase angles. Only capacitive or inductive
loads can do that. However, LEDs work fine in commercial installations
where 0.8 power factors are common so I doubt that is your problem.
It is more likely that badly formed waveforms cause switching issues for
the LED's driver electronics. Filtering may help.

Line to Line capacitors are probably not going to help, but Line to Earth
capacitors could act as a high pass filter to shunt noise to ground.



On Sun, Feb 2, 2014 at 4:39 PM, Troy Harvey wrote:

>
>
> We've got a PV system that has long lines from the inverters to the house
> (1000 ft or so). While the wires are properly sized (2x350MCMs), it
> inherently has a lot of inductance due to the line-length. What We are
> noticing is that dimmable LED lights flicker anytime a new load turned on,
> even if that load is purely resistive and the overall current draw is small
> (20 amps or so). What I "think" is happening is the LED dimmer circuits get
> their cue from phase delays, and that the inductance of the line length
> causes some phase jitter everytime a load is applied - thus causing flicker.
>
> Has anyone dealt with this issue successfully (other than switching
> to incandescent lights)? Would a static capacitor bank at the house do the
> trick, or do we need some type of active PFC? And if static did you have
> any issues with constant power draw from the capacitors?
>
>
>
> Troy Harvey
> -
> Heliocentric
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Best Ground Racking?

2014-02-06 Thread Chris Mason
his 
>> story<http://r20.rs6.net/tn.jsp?f=001DOU7toids4P6EbtZ8amZnWIPqfwSVSQprZxgWcCDNMwVujGRFeNr6kDDQxv8reDLHOjQsU5ZAbim7nwyi2LH1WCwpxjpydyrqtwAXR7rGEE1Vv9y6CHdApOn8xu7viO-boKxfR0vxuRWZuQZUsi31k7EuNfvsnYtZxiDLh9hiU2snspkUXkwVWlu0bEQXhPr6iN048ijV9vyy42Nc0lSkRY8eR4Vuhj1x9WG_J42Nw3BUMy2LRo8bPk83rGlFxOIi3a3_xZ86ubEYbyk1MwQDdKVfXOrZiplaNIIzrDh6n_xz1PO28GP4feFeQCk2gd8l_yy_pAgMdOHcKD_IDW7y6eRVPj8LA5FS7-3nIgC4egIz2vMLcdeRCtjg_WNZoRohptTtbcFtULUCOupqpn91wIENm--baFFvHj0TycL7wMKVBZI340LaA==&c=-PYi8jywk0XKsL2vpOkRGCzs2UwO52AqIXjyxYLdwi6HgzYpVBBpKQ==&ch=UHlwvhDu_eij1qcoWtW5qiGLvNITtkXGLCqG4RSjo4k9OQWUYTpu8w==>
>>
>> Wm
>>
>>
>>
>>
>>
>> On Feb 4, 2014, at 4:45 PM, Kelly Larson  wrote:
>>
>> Thanks, Aaron.  How are you handling wire  management and connection to
>> the ground?
>>
>> Blessings,
>> Kelly
>>
>> On Feb 4, 2014, at 2:41 PM, Aaron Mandelkorn wrote:
>>
>> I like SnapNrack 200 Series as well as DPW Solar Multi Pole Mount.
>>
>> On Feb 4, 2014, at 3:28 PM, Kelly Larson  wrote:
>>
>>
>> Hi,
>>
>> We are looking to install some 4KW ground mounted arrays.  What racking
>> are you using?  Best ground connection?  Wire management?  The shows have
>> so many choices, and I keep doing the same ol thing...
>>
>> Blessings,
>> Kelly
>>
>> Kelly Larson
>> Electrical Engineer
>> NABCEP Certified Solar PV Installation Professional
>> IREC Certified Master Trainer
>> CA Electrical Contractor# 868189
>> SolarKelly.com <http://solarkelly.com/>
>>
>> ___
>>
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Subject: Re: Best Ground Racking?

2014-02-06 Thread Chris Mason
Probably Permatex.


On Thu, Feb 6, 2014 at 4:55 PM, Ray Walters  wrote:

> We use Anti- Seize Lubricant made by Permalex.  I get it at the auto parts
> store.  I have an 8 oz. bottle with built in brush on applicator.
> Definitely recommended on all SS hardware.  I took apart another
> installer5's rack to add modules, and half the bolts were ruined and had to
> be replaced.
> I recommend a torque wrench too, its super easy to over5 tighten the SS
> hardware.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
>
>
> On 2/6/2014 11:20 AM, Jason Andrade wrote:
>
>> there are a lot of stainless bolts, I use pentrox as a anti galling
>> compound, what do other people use?
>>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Subject: Re: Best Ground Racking?

2014-02-06 Thread Chris Mason
This is the stuff. Be prepared for it to get everywhere, it's really messy
(or maybe I am).

http://www.amazon.com/Permatex-80078-Anti-Seize-Lubricant-Bottle/dp/B000AAJTXY/ref=sr_1_1?ie=UTF8&qid=1391721840&sr=8-1&keywords=permatex+anti-seize+lubricant




On Thu, Feb 6, 2014 at 5:21 PM, Chris Mason wrote:

> Probably Permatex.
>
>
> On Thu, Feb 6, 2014 at 4:55 PM, Ray Walters  wrote:
>
>> We use Anti- Seize Lubricant made by Permalex.  I get it at the auto
>> parts store.  I have an 8 oz. bottle with built in brush on applicator.
>> Definitely recommended on all SS hardware.  I took apart another
>> installer5's rack to add modules, and half the bolts were ruined and had to
>> be replaced.
>> I recommend a torque wrench too, its super easy to over5 tighten the SS
>> hardware.
>>
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer,
>> Licensed Master Electrician
>> Solar Design Engineer
>> 303 505-8760
>>
>>
>> On 2/6/2014 11:20 AM, Jason Andrade wrote:
>>
>>> there are a lot of stainless bolts, I use pentrox as a anti galling
>>> compound, what do other people use?
>>>
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
>> wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> --
> Chris Mason
> President, Comet Systems Ltd
> www.cometenergysystems.com
> Cell: 264.235.5670
> Skype: netconcepts
>



-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Solaredge inverters w/ backup generator

2014-02-09 Thread Chris Mason
That's total nonsense. Most of our installs involve a generator, as
generators are very common here due to intermittent electrical supply and
hurricanes. We also sell and install generators and I am a tech.
A decent heavy generator will produce electricity that will fall within the
IEEE 1547 specifications for grid tied interconnections. Additionally, in
our area, we alter those settings to widen the windows as the electricity
supply on an island is not as stable as a large grid.

My rule of thumb is that no lockout is required if there is no risk of
backfeeding the generator, that is, if the load will always exceed the
solar output by a reasonable factor. We have customers that have constant
loads in the 40 to 80KW range, and so 20KW of PV will never cause a
problem. Residential is the larger issue, as there is often no load.
A generator's output is controlled by the Automatic Voltage Regulator or
AVR. It senses the voltage at the terminals of the alternator and changes
the excitation to keep the voltage constant.
Usually the generator's controller has voltage sensing and will stop the
generator if the voltage exceeds limits.
If the solar inverter is making power and there is no load, it will
increase the voltage until it finds enough load, or trips. If the generator
sees the increased voltage and the AVR cannot reduce the excitation enough
to control it, the controller MAY shut down the generator.
A generator's controller and AVR presumes it is the only source of power on
the electrical system. The inverter presumes it is connected to an
infinitely large grid system that can absorb all power generated.

Our usual solution is to put a contactor in front of the inverter
controlled by voltage from the generator, or ideally by a contact on the
transfer switch.

It may be possible to program the generator to run faster or slower so as
to keep the frequency outside the inverter limits, but you run the risk
that a future tech will adjust the inverter or generator.





On Sat, Feb 8, 2014 at 11:32 AM, Kirk Herander  wrote:

> Hello,
>
>
>
> I recently posed the question to Solaredge tech support, wondering if
> their inverter, in this case a 20kw 480 3-phase, would have any issues if
> it were connected to an AC panel backed up by a generator. They told me no
> problem, for the inverter's anti-islanding will work if it sees the
> "generator frequency" and therefore will not try to push PV power to the
> panel. But isn't 60 hz, 60hz regardless of origin? There's got to be more
> to it than that. I question this because I asked the same to SMA several
> years ago and they were hard-set against connecting Sunnyboys to a panel
> with generator backup, so I always would establish the point of
> interconnection upstream of the generator feed. Comments? Thanks.
>
>
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Charging a HUP

2014-02-09 Thread Chris Mason
A 12KW generator can produce 250A at 48V, and the breaker should be 12KW
*125% or 62.5 amps.
You may have an unbalanced load, you probably can only put 6KW per leg of
the 240V feed.


On Sat, Feb 8, 2014 at 2:46 AM,  wrote:

> Hi All,
>
> 3 VFX 3648
> 2 FM 80
> 6.5 kw solar
> 12 kw generator
> PSX 240 on generator output and VFX stacking
> Mate 3
> HUP 1690 ah
>
> System design considering 45 amp charge current from each VFX totaling 135
> amps. (135 x ~55v = 7.42kw)  Potential charge current from 2 arrays and FM
> 80's, 90 - 100 amps. On a good day, reasonable to expect 200+ amps?
> Have not been able to exceed 90 amps for more than 30 minutes, with the
> generator putting out about 9 kw before it's 70 amp 2pole breaker trips. L1
> 42 amps, L2 37 amps. 5 amps neutral. Load banked to 12.3 kw (51 amps @
> 240v) resistive without breaker trip.
> I have had to dial back the maximum charge current in the Mate 3 to 12
> amps each on two of the inverters (L1 and L2) and 8 on inverter 3 to keep
> the generator from tripping out when customer turns on the microwave or
> coffee pot. In effect, 42 amps charge @ 240 v = 7.6 kw. At the battery, I'm
> only seeing 80 amps of charge current. Running loads are typically less
> than 1 kw but there has been a of construction going on with chop saws and
> compressors creating annoying spikes that are easily handled by the
> inverters when the generator is off.
> I don't want to kill this new battery by not feeding it properly! I would
> have put in a larger generator, but the owner bought the 12 kw before
> deciding on the new battery. I thought the 12 would be merely adequate, but
> not so
> Any suggestions?
>
> Thanks!
>
> Bruce Fiero-RMI
>
>
>
>
>
> *"I'd put my money on the sun and solar energy. What a source of power! I
> hope we don't have to wait until oil and coal run out before we tackle
> that." T. Edison, 1931*
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Charging a HUP

2014-02-09 Thread Chris Mason
ase: 3697/7076 - Release Date: 02/08/14
> --
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
> --
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 208 V 240 in residential applications

2014-02-09 Thread Chris Mason
Yes, no problem. Lots of commercial installations are 208.

Chris Mason
Comet Systems
Anguilla (264) 235-5670
St. Kitts  (869) 662-5670
skype netconcepts

NABCEP Certified Solar PV Installer(tm)
Renewable Energy Systems professional
Generac Generators Factory technician
On Feb 9, 2014 4:20 PM,  wrote:

> Friends:
>
>
>
> I feel sort of stupid asking this, but it has never come up for me before:
>
>
>
> I have inherited an off-grid install gone-wrong.  The system is 208 three
> phase with Sunny Boys and Sunny Islands on a mini grid.  It was designed as
> three phase.  I presume this was to increase capability with stacked SMA
> inverters.
>
>
>
> Will the household appliances (small cooktop, booster pump, well pump) run
> as well on 208 as 240?
>
>
>
> I always do my research before wasting all of your time.  The web
> delivered a lot of "forums" wherein opinions were expressed, but little
> hard data from bona fide professionals.  I also did some calculations, see
> below.  I downloaded a manual from a random electric range and saw it was
> specified as 240 or 208.
>
>
>
> Watts
>
> 4000
>
>
>
>
>
>
>
>
>
> Volts
>
> 240
>
> 208
>
> Amps
>
> 16.67
>
> 19.23
>
> % Difference in amps
>
> 13.33%
>
>
>
>
>
> I am fairly comfortable that this is not an issue, but would like some
> confirmation.  Thanks in advance.
>
>
>
> William
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Charging a HUP

2014-02-10 Thread Chris Mason
What apparent power readings are you getting?


On Mon, Feb 10, 2014 at 3:11 AM,  wrote:

> We dialed the inverters back to 3.6 kw charge and got a full bulk and EQ
> with no breaker trip today. Finally got the SG back up to 1.275 - 1.285
> after 4 hours @ 61.5. It had me real nervous for a week, being able to get
> bulk voltage but still only 1.220 - 1.223 SG.
> Now looking at putting in a capacitor bank to correct some of the power
> factor issues of the inverter/chargers so I can get more useable kw out of
> the genset.
>
> Thanks for your suggestions!
>
> Bruce Fiero-RMI
>
>
>
> *Willpower Electric LLC*
>
>
>   Original Message 
> Subject: Re: [RE-wrenches] Charging a HUP
> From: 
> Date: Sun, February 09, 2014 12:04 pm
> To: "RE-wrenches" 
>
> Yes Chris. I've got about 42 on one leg and 35-37 on the other. The
> transformer keeps the legs balanced to within about 5 amps.
>
> Bruce
>
>   Original Message 
> Subject: Re: [RE-wrenches] Charging a HUP
> From: Chris Mason 
> Date: Sun, February 09, 2014 11:13 am
> To: RE-wrenches 
>
> So the breaker is not the generator output breaker?
> I would put a clamp amp meter on the breaker leads set on Max to record
> the maximum current when it trips.
>
>
> On Sun, Feb 9, 2014 at 2:23 PM,  wrote:
>
>> True that on the DC genset, Kevin, but more or less removes the bypass
>> option. Strongly considered breaker replacement as many are susceptible to
>> harmonics, but a real PIA on this generator and haven't gotten around to it
>> yet. Also going to run the gen shed ventilators off the line side of the
>> gen when I replace the breaker to avoid overheating when breaker trips!
>>
>> Bruce
>>
>>   Original Message 
>> Subject: Re: [RE-wrenches] Charging a HUP
>> From: "Kevin Pegg" 
>> Date: Sun, February 09, 2014 9:39 am
>> To: "RE-wrenches" 
>>
>> "Has anybody scoped ac line to VFX's under full charge load? I'm curious
>> about harmonics possibly being the culprit "
>>
>> Yes, it's pretty nasty. This is why we stopped using Outback products for
>> off-grid sites with significant use of generator charging. Not only are the
>> chargers really wimpy, we found all manner of harmonics caused by the
>> charger circuit. Loads ran fine on inverter; fine on generator but would
>> not run at all or reliably with gen running in charge mode.
>>
>> It took some time to figure this out. Ended up having to tear out several
>> new outback systems & replace with another brand to keep customers happy.
>>
>> What we have done successfully for sites where the customer doesn't want
>> to replace the Outback is install a bank of external battery chargers, ie
>> the Iota DLS series and use those for gen charging purposes only.
>> Sub-optimal in a lot of respects but that's what happens when a client buys
>> hardware and says "make it all work". A DC genset would be way more
>> efficient.
>>
>> Another thought have you tried another breaker on the gen? Weak breakers
>> do happen, have seen that on brand new gensets.
>>
>> Kevin
>>
>> -Original Message-
>> *From:* re-wrenches-boun...@lists.re-wrenches.org [
>> mailto:re-wrenches-boun...@lists.re-wrenches.org
>> ]*On Behalf Of *br...@willpowerelect.com
>> *Sent:* February 9, 2014 9:28 AM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] Charging a HUP
>>
>> Roger the 136-272 charge amps, and the theoretical max of 295 with this
>> system. Hoping for reality of 160 - 200. Fortunately it's a 'good' customer
>> with very efficient running loads, just a bit of a power tool habit and the
>> hydronic heating recirc pump loads. Unfortunately, there have been 3 trades
>> on site recently using power while I'm trying to get the battery filled up!
>> but generally about 3x solar/useage during fair weather.
>> With 3 inverters, this week I'm trying #3 with full charging, 1 and 2 at
>> about 60%. #1 should carry most of the load demands, #3 most of the charge
>> demand. I also found a spot in the Mate 3 to set maximum charging kw and I
>> set that to 7kw. Maybe that will help gen overload.
>> Has anybody scoped ac line to VFX's under full charge load? I'm curious
>> about harmonics possibly being the culprit between a 12.3 kw load bank not
>> tripping the breaker, and a 5-6 kw charging load tripping the breaker...
>>
>> Bruce
>>
>>   Original Message 
>> Su

Re: [RE-wrenches] Outback Chargers

2014-02-11 Thread Chris Mason
One of the issues to be aware of is power factor, and most people will not
be able to determine power factor. If the Outback operates at a poor power
factor, your 10KW generator will become a about a 6KW generator. A lot of
the current will be wasted and will not produce charging power.



On Tue, Feb 11, 2014 at 11:25 AM, jay peltz  wrote:

> Hi Matt,
>
> With two systems on the thread right now with pretty much the same
> problem, I am suspecting a problem with one or more inverters. Most all the
> Outback inverter issues I've have been have been on stacked systems.
> Having installed a lot of these inverters I have yet to see the exact
> problems cited here.  Usually I've seen it with much smaller generators vs
> inverter size, but not with what I would call properly oversized units.
>  And because it is with charger issues, turning down the charge rate, but
> leaving generator size accurate has proved to be quite successful.
>
> I would try to run the inverters such that you can test to see how they
> are each working.
> For the quad stack, try 2 at full tilt, then the other 2 and see if you
> can find something there, might take some rewiring to test all combos.
> For the tri stack, well you get the drift.
>
> jay
> peltz power
>
>
>
> On Feb 10, 2014, at 5:09 PM, m...@solar-energy-solutions.com wrote:
>
> > Wrenches,
> >
> > Based on Kevin's comments about Outback Chargers in the HUP thread I am
> > hopeful that some of you well-versed in the off grid world can assist.
> > Particularly I am curious if others can confirm deficiencies with Outback
> > chargers and suggest strategies for overcoming these deficiencies.
> >
> > I currently have an off grid site with significant charging difficulty.
> > The site has been online around eight years with a quad VFX3648 stack.
> > Around six months ago the client began experiencing more generator issues
> > (he had certainly had occasional problems before but engine overruns
> > became almost a weekly occurrence which, considering the client is only
> > there on the weekends except during hunting season, is not good).  The
> > client decided to buy a new generator based on a comment from Outback.
> > They suggested his old 15 kW Briggs with mechanical governor should have
> > the governor replaced with an electronic governor.  This couldn't be done
> > so he bought a new GE 20 kW with electronic governor.  The GE does not
> > work with the Outback chargers at all (sounds like immediate overrun) but
> > will run the home just fine (and pass-thru Outback with chargers off).
> >
> > I am about at the point of asking the client to buy Iotas.  However, we
> > have a Honda 6500 that has worked as a backup generator for this system
> > and that has worked for other Outback systems we have installed.  The
> > Honda no longer works well with this Outback system (routinely
> disconnects
> > after a few minutes charging and won't charge more than a few amps per
> > port).  Something has obviously changed for the Honda to no longer work
> > well and I am beginning to think that maybe I am missing something else.
> > We have checked grounding and switched around inverters to run off dual
> > stacks without any noticeable difference.  The client has tried three
> > separate generators at this point and none work very well.  After eight
> > years the batteries aren't in great shape but they hold a charge and
> > should be capable of more years of service (Surrette YS).  Outback tech
> > support seems willing to listen and empathize but incapable of helping me
> > identify the issue.
> >
> > Any advice is welcome.
> >
> > Thanks,
> >
> > Matt
> >
> >
> >
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Solaredge inverters w/ backup generator

2014-02-14 Thread Chris Mason
The "Door Open" switch is a very useful feature. I am trying to get Fronius
to put a digital shutdown terminal on its CL line of inverters, or all
inverters preferably. We need to pressure all the inverter manufacturers to
provide a logic in or dry contact method of shutdown.
Most ATS will provide a N/O dry to indicate position.


On Thu, Feb 13, 2014 at 10:21 PM, Jerry Shafer wrote:

> I have done systems in Hawaii, here is one with a 30 k PV system and with
> a 250k Cummins back up genny. We have a contactor in the ATS that will open
> if the genny is operating, this in turn sends a door open signal to the
> Satcon shutting it down I don't want anything effecting the genset
> operation so with the open created in the ATS it tricks the inverter to
> shut off safely. We as a policy will not run a genset and PV unless as a AC
> coupling system and you have some active over voltage like freq and voltage
> triggers.
> Jerry
> On Feb 8, 2014 7:31 AM, "Kirk Herander"  wrote:
>
>> Hello,
>>
>>
>>
>> I recently posed the question to Solaredge tech support, wondering if
>> their inverter, in this case a 20kw 480 3-phase, would have any issues if
>> it were connected to an AC panel backed up by a generator. They told me no
>> problem, for the inverter's anti-islanding will work if it sees the
>> "generator frequency" and therefore will not try to push PV power to the
>> panel. But isn't 60 hz, 60hz regardless of origin? There's got to be more
>> to it than that. I question this because I asked the same to SMA several
>> years ago and they were hard-set against connecting Sunnyboys to a panel
>> with generator backup, so I always would establish the point of
>> interconnection upstream of the generator feed. Comments? Thanks.
>>
>>
>>
>> Kirk Herander
>>
>> VT Solar, LLC
>>
>> dba Vermont Solar Engineering
>>
>> NABCEPTM Certified Inaugural Certificant
>>
>> NYSERDA-eligible Installer
>>
>> VT RE Incentive Program Partner
>>
>> 802.863.1202
>>
>>
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Spacing between ground mounted sub-arrays at 48.5 degrees N latitude

2014-02-16 Thread Chris Mason
I use Sketchup for these calculations now. It will do real shadows at any
time of any day you want.
If you are not familiar with it, send me the exact Google Earth coordinates
and I will mock something up for you.


On Sun, Feb 16, 2014 at 5:35 PM, Bob Clark  wrote:

> Wrenches:
>
> I have a customer who wants 40 solar modules on ground mounts (not poles)
> in an area that slopes to the ESE at 7 degrees.  Putting these modules on
> one ground mount assembly so that the modules are in a 0 degree slope East
> to West would leave the east end about 20 feet in the air.  Not acceptable
> as the customer wants a profile as low as possible for aesthetic reasons
> plus the wind can be quite strong on occasion.
>
> So, I am trying to figure out how far apart 5, 8 module sub-arrays
> (landscape orientation 2 E-W by 4 N-S tilted at 35 degrees S from the
> horizontal) would have to be North to South and East to West so that they
> are low profile yet do not shade each other on the winter solstice at 48.5
> degrees N latitude.  These calculations are complicated by the ground
> sloping to the ESE at 7 degrees.
>
> Can anyone point to an online calculator that takes into account the slope
> of the ground?  Or can anyone help me with the geometry of this situation.
>  I have gone around in circles and thoroughly confused myself.
>
> Thanks in advance.
>
> Bob Clark
> bcl...@solar-wind.us
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Spacing between ground mounted sub-arrays at 48.5 degrees N latitude

2014-02-17 Thread Chris Mason
If you are using Sketchup for solar, you should be using the Skelion
plugin. It will compute and draw the solar modules on any surface based on
your preferred module, tilt angle and azimuth. We do all our quotes this
way.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Back feed from Radian.

2014-02-17 Thread Chris Mason
.members.re-wrenches.org
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Trojan IND9-6V settings with Outback FX and Flexmax 60

2014-02-19 Thread Chris Mason
I just switched a customer from VRLA batteries to Trojan IND9. I changed
all the battery settings to the numbers recommended by Trojan but I would
be interested to hear any recommendations from experience. Please let me
know if you have experience with the charge and discharge settings for this
combination.

-- 
Chris Mason
President, Comet Solar
www.comets <http://www.cometenergysystems.com>olar.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Project management tool

2014-02-21 Thread Chris Mason
The term Project Management can be applied to a wide range of tools and
methodology. If your needs are only to track tasks, I would use Wunderlist
as it can be installed on every device and lists can be shared.
If you want a real PM tool, Microsoft Project is the midrange tool of
choice. There are a ton of industry specific platforms that you could use
but they are mainly for large enterprises.

The problem with PM software is you need time to design and administrate
the data. In a lot of projects there is a dedicated person who coordinates
all the contractor and subcontractor tasks. It is a full time job. I would
be careful about launching into a PM tool that you are not familiar with
while already overwhelmed. It will suck up a load of your time and return
you very little gain in efficiency.
If you have a number of people to coordinate and you think PM software to
be the best way, hire a consultant to select and implement the application.


On Thu, Feb 20, 2014 at 9:37 AM, Advanced Energy Solutions <
t...@aessolar.com> wrote:

> Good day,
> I have the excitement of having many installations but at 12 ( and 2 of
> them 100kw) and more coming I am looking for a way to better manage
> projects.
>
> Do you have a program you would recommend for helping me manage projects?
> I am getting overwhelmed.
>
> --
> Stay Energized, PEACE>
> Aur J Beck,
> NABCEP Certified Solar PV Installer(tm) 032611-24
> NABCEP Certified PV Technical Sales(tm) PVTS032412-6
> chief tech of Energy Network (Green Geek Squad*(tm) *)
> Advanced Energy Solutions Group, Inc
> (618) 893-1717(618) 893-1717 | (800) 229-0453(800) 229-0453  |
> www.AESsolar.com <http://www.aessolar.com/> | 
> t...@aessolar.com
>
> We Empower YOU to Get Energized!
>
> Be an Energy Patriot
>
> Living on Earth is Expensive, but it does include a FREE trip around the
> Sun!
>
> Oil Addicts Anonymous International (a real 12 step program)
> www.IamanOilAddict.org <http://www.iamanoiladdict.org/>
>
> This communication is the property of Advanced Energy Solutions Group, Inc
> and is intended only for use by the recipient identified. If you have
> received this communication in error, please immediately notify the sender
> and delete the original communication. Any use of this message without the
> Advanced Energy Solutions Group, Inc's consent is prohibited.
> ü Please consider the environment before printing this email.
>  Call
> Send SMS
> Add to Skype
> You'll need Skype CreditFree via Skype
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] conductors and the 120% rule

2014-03-04 Thread Chris Mason
The conductors have to be rated for 200A as normal. Fault current can only
come from the grid.
While the total available current on the bus of a panel is the total of the
source breakers, in the conductors, grid and solar power cancel out and the
total is not the sum of the two.


On Tue, Mar 4, 2014 at 1:05 PM, Kirk Herander  wrote:

> Hello,
>
> I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp
> breaker. My inverter breaker feeding the sub panel is 60 amps. So 225 a bus
> x 1.2 = 270 amps. That's less than the sum of the two breakers of 260 amps,
> so no issue there. The conductors between sub and main panel have to be
> rated for at least 260/1.2 = 217 amps, correct? Is this 217 amps before or
> after derating the conductor?
>
>
>
>
>
> Kirk Herander
>
> VT Solar, LLC
>
> dba Vermont Solar Engineering
>
> NABCEPTM Certified Inaugural Certificant
>
> NYSERDA-eligible Installer
>
> VT RE Incentive Program Partner
>
> 802.863.1202
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery spill containment

2014-03-10 Thread Chris Mason
Spill containment should be plastic.


On Mon, Mar 10, 2014 at 7:41 PM, RE Ellison  wrote:

> If you look at the bottom of the steel battery boxes they generally have
> drain holes in them!
>
> They are intended to contain the battery cases not the electrolyte
>
> If you want to contain the electrolyte go to a sheet metal shop and have
> them build a case to set the battery case in
>
> Braze or silver solder all of the connections all the joints and they
> should be good.
>
>
> Bob Ellison
>
> On Mar 10, 2014, at 5:32 PM, Jerry Shafer 
> wrote:
>
> The Hawkers we use come in steel containers already with the battery
> inside if this the same then you should be compliant. You can also have
> plastic containers made we use TAP Plastics they can custom build you a box
> that fits your location.
> On Mar 10, 2014 1:31 PM, "Tump"  wrote:
>
>> Quick cable does have a battery matt material that does both; item #
>> 510171-008 72'X96" THEY ALSO HAVE 42X 52 CONTAINMENT PALLET PART # 510250
>> hit cap lock by accident! www.quickcable.com
>> On Mar 10, 2014, at 3:54 PM, Glenn Burt wrote:
>>
>> William,
>>
>> Look at your local building and fire codes to see if this is a
>> requirement.
>> Here in NY, the local fire code requires "Spill Control and
>> Neutralization"
>> when batteries with "free-flowing liquid electrolyte" are installed.
>>
>> Good Luck,
>> Glenn
>>
>> -Original Message-
>> From: re-wrenches-boun...@lists.re-wrenches.org
>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
>> Miller
>> Sent: Monday, March 10, 2014 11:57 AM
>> To: RE-wrenches
>> Subject: [RE-wrenches] Battery spill containment
>>
>> Friends:
>>
>> Am I under any obligation to provide a spill containment system under an
>> array of flooded batteries?  If so, what do you recommend under a 8' x 11'
>> array of Hawkers?  William ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>  *t...@swnl.net*   *www.SWNL.net*
>>  Solarwinds Northernlights
>> *   Serving Mid Coast Maine & Northern California*
>> * 207-832-7574 <207-832-7574>   Cl. 610-517-8401
>> <610-517-8401>  *
>>   *Blair "TUMP" May*
>>
>>
>> *     MAINE'S CHARTER   *   *
>> NABCEP"Certified PV Installer"*
>>
>>
>> *   MAINE'S CHARTER   **
>> Trace Xantrex "Certified" Dealer / Installer"*
>>
>>
>>
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:

Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal roof

2014-03-14 Thread Chris Mason
Typically when capacitance is a problem, the answer is inductance. Have you
looked at adding some chokes between the DC negative and ground to
counteract the capacitance?


On Thu, Mar 13, 2014 at 10:31 PM, Marco Mangelsdorf wrote:

>  Friends,
>
>
>
> We have run across an odd technical problem at our commercial install at a
> laundromat on our island.   Attached is the description of the issue from
> SMA.  We don't know much except that we are switch out the TL inverters to
> the old style US inverters because SMA has no fix for the phantom ground
> tripping.  The issue is beyond our feeble understanding.
>
>
>
> Any observations to share?
>
>
>
> Thanks,
>
>
>
> marco
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Autocad

2014-03-14 Thread Chris Mason
D'assault Systeme offers a free CAD program Draftsite, that reads and
writes Autocad files. We use it for our drawings. The commands are all the
same as Autocad so you can learn for free. They also have tremendous
tutorials.
http://www.3ds.com/products-services/draftsight/overview/


On Fri, Mar 14, 2014 at 4:28 PM, Jason Szumlanski wrote:

> I'm pretty sure the free version of Skelion will do the roof layout. You
> just don't get some of the other nifty features. Oddly enough, the most
> important features we use are free.
>
> Jason Szumlansk
> i
>
>
>
> On Wed, Mar 12, 2014 at 8:43 PM, Bill Hoffer  wrote:
>
>> William
>>
>> I second using Sketchup and Layout for $500 .  I have seen the add on
>> Roof Pro Plug in and Skelion ( $199) demo  that lays out the array  and
>> links to PVwatts for power analysis.  Plus Combined with google earth ,
>> does great shading analysis I.  I think you can do a quick design in an
>> hour and Autocad would be days!  Stay away from Autocad unless you really
>> need it for large commercial jobs and like Jason said it is required to
>> interact with other trades! Plus Solar Energy Engineering is starting a web
>> based training for using it for solar projects.  It really is pretty cool
>> and a lot more flexible than overpriced and overly complicated Autocad.
>>  Autocad light woudl be my first choice, no way you need the full blown
>> version.
>>
>> Bill
>>
>>
>> On Wed, Mar 12, 2014 at 4:16 PM, Jason Szumlanski 
>> wrote:
>>
>>> Unless there is a compelling reason to use AutoCAD, like
>>> interoperability with other trades and professions, consider Sketchup Pro
>>> and Layout from Trimble. $500.
>>>
>>> I learned it over a weekend, and with the Instant Roof Pro plugin ($39)
>>> I was making convincing and accurate renderings in almost no time. Note:
>>> Instant Roof, a necessary plugin for roof modeling, has not been updated
>>> for Sketchup 2014, so download 2013 for now. The author is working on it.
>>>
>>> Jason Szumlanski
>>>
>>> Fafco Solar
>>>
>>>
>>>
>>>
>>>  On Wed, Mar 12, 2014 at 7:09 PM, William Miller <
>>> will...@millersolar.com> wrote:
>>>
>>>>  Friends:
>>>>
>>>>
>>>>
>>>> The 3D CAD software I have been using is obsolete.  I have decided to
>>>> upgrade to Autocad.  I am temporarily using an educational copy while I
>>>> learn, but  I need to purchase a copy.
>>>>
>>>>
>>>>
>>>> Before I go out and plunk down $4k, I need to do some research:
>>>>
>>>>
>>>>
>>>> Do I have to expect to pay that much?
>>>>
>>>>
>>>>
>>>> Where is a good place to purchase?
>>>>
>>>>
>>>>
>>>> Are there copies of one generation old programs available?
>>>>
>>>>
>>>>
>>>> I am a self teacher but I use printed texts.  What is your favorite
>>>> Autocad reference?
>>>>
>>>>
>>>>
>>>> Thanks everyone!
>>>>
>>>>
>>>>
>>>> William
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> [image: Gradient Cap_mini]
>>>>
>>>> Lic 773985
>>>>
>>>> millersolar.com (hyperlink)
>>>>
>>>> 805-438-5600
>>>>
>>>>
>>>>
>>>>
>>>
>>>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1000V rated equipment

2014-03-21 Thread Chris Mason
What current rating are you looking for?


On Fri, Mar 21, 2014 at 12:27 PM, Nathan Charles <
nchar...@paradiseenergysolutions.com> wrote:

> Hi Wrenches,
>
> Has anybody had success finding 1000V rated din rail mount DC disconnects
> or Contactors that are UL or ETL listed?
>
> Best,
>
> --
> Nathan Charles
> Engineer
> NABCEP Certified PV Installation Professional #042013-20
> Paradise Energy Solutions
> (717) 283-2021 direct
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal roof

2014-03-26 Thread Chris Mason
If the problem is capacitive, it ought to be possible to fit a high
resistance conductor between ground and the center point of the arrays to
discharge the capacitive charge without affecting power performance.


On Wed, Mar 26, 2014 at 6:13 AM, Glenn Burt  wrote:

>  I wonder if it is the capacitive charge common on larger arrays that is
> seen as a problem.
>  --
> From: Jeff Irish 
> Sent: 3/25/2014 21:33
>
> To: RE-wrenches 
> Subject: Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal
> roof
>
>  August,
>
> We're seeing multiple inverters with the same error, and not getting the
> best of answers or support from SMA on fixing the problem so far.  And this
> is not a metal roof; it's PanelClaw on EPDM.
>
> Jeff Irish
> Hudson Solar
>  --
> *From:* re-wrenches-boun...@lists.re-wrenches.org [
> re-wrenches-boun...@lists.re-wrenches.org] on behalf of August Goers [
> aug...@luminalt.com]
> *Sent:* Tuesday, March 25, 2014 8:41 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Unusual problem with SMA TL inverter on
> metal roof
>
>   Hi Marco,
>
>
>
> Did you ever make any progress on this issue? We're having an interesting
> issue with one of the new Sunny Tri-Power inverters (a 24 kW unit in this
> case) where we get an error "residual current too high." We've only done a
> little troubleshooting so far but I don't think we have a ground fault.
>
>
>
> Best,
>
>
>
> August
>
>
>
> Luminalt
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Marco
> Mangelsdorf
> *Sent:* Friday, March 14, 2014 9:56 AM
> *To:* 'RE-wrenches'
> *Subject:* Re: [RE-wrenches] Unusual problem with SMA TL inverter on
> metal roof
>
>
>
> Probably not.
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [
> mailto:re-wrenches-boun...@lists.re-wrenches.org]
> *On Behalf Of *RE Ellison
> *Sent:* Friday, March 14, 2014 1:24 AM
> *To:* 'RE-wrenches'
> *Subject:* Re: [RE-wrenches] Unusual problem with SMA TL inverter on
> metal roof
>
>
>
> Is the metal roof grounded? Just a fast thought.
>
>
>
> bob
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [
> mailto:re-wrenches-boun...@lists.re-wrenches.org]
> *On Behalf Of *Marco Mangelsdorf
> *Sent:* Thursday, March 13, 2014 10:31 PM
> *To:* 'RE-wrenches'
> *Subject:* [RE-wrenches] Unusual problem with SMA TL inverter on metal
> roof
>
>
>
> Friends,
>
> [The entire original message is not included.]
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1000V System Wiring Details

2014-03-26 Thread Chris Mason
All the European spec inverters I have used would shut down at 600V so
that's not a great idea.
On systems with long runs, we use a fused switched combiner and run 1KV #6
for the home runs. But that's for very long runs. You can put a lot of
power over a #10 PV Wire at 800V working voltage.


On Wed, Mar 26, 2014 at 10:31 PM, August Goers  wrote:

> Hi Dave,
>
> We've run all the way home with 1000 V PV wire and only made splices with
> Amphenol MC4-type 1000 V connectors. Going forward, we are going to strive
> to put inverters on the roof to minimize the expense of dealing with the
> 1000 V runs. Another interesting idea is to use the 1000 V inverters but
> just run them below 600 V and use standard 600 V wiring products. On a
> separate note, we have a lot of 208 VAC applications in the Bay Area and
> all these new neat TL inverters only run at 480 V. Someone from SMA
> recently pointed out that we can source 480 to 208 V transformers for a
> reasonable cost - we might look into that as well.
>
> Best,
>
> August
>
>
>
> *August Goers*
>
> Principal
>
> Luminalt Energy Corporation
>
> o: 415.641.4000
>
> m: 415.559.1525
>
> www.luminalt.com
>
>
>
>
> On Wed, Mar 26, 2014 at 3:01 PM, Dave Click wrote:
>
>> Hi Wrenches-
>>
>> If you're installing 1000V systems, are you running continuous PV WIRE
>> all the way to your inverters? If not-- what splices have you found (aside
>> from MC4s and similar) that are listed for 1000V? And when transitioning
>> from PV WIRE to a cheaper conductor, what 1000V options exist beyond USE-2?
>>
>> Thanks!
>> Dave
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
>> wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



  1   2   3   4   5   >