Re: [RE-wrenches] Lead placment and length on new PV Panels

2022-03-25 Thread Jay via RE-wrenches
Hi william The technic I use is to build or buy custom lengths of jumpers. Then I can mount the MLPE exactly as I want with the wire routing to my preference. Yes it’s the most expensive route: more wire, more clips, but also the cleanest. And often the MLPE don’t have the same connectors a

Re: [RE-wrenches] Wire short?

2022-04-04 Thread jay via RE-wrenches
Hi Chris, Does this happen with all 4 sets of 2 in series modules? jay > On Apr 4, 2022, at 10:12 AM, Chris Daum via RE-wrenches > wrote: > > Hey folks: > > We have a problem we just can’t figure out. We have a customer in OK with a > simple array of eight Trina TSM 310-DD05H(II) modules,

[RE-wrenches] Fronius primo grid settings

2022-04-15 Thread Jay via RE-wrenches
I wonder if anyone can tell me which is the correct setting for 240v 60hz w/neutral on a fronius primo. The manual doesn’t have the same options as the inverter. I don’t need California or Hawaii settings. Thanks Jay ___ List sponsored by Redwood A

[RE-wrenches] Enphase

2022-04-15 Thread Jay via RE-wrenches
I’ve been following the enphase thread. I’ve used AP systems before and so far reliable and much less expensive. Their new DS3 inverters are much less expensive and larger capacity But to the point of starting voltage MPPT range and watts DS3 voltage range: DS3 S/L 16-60v, DS3 26-60v MPPT ra

[RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread jay via RE-wrenches
HI All I’ve got a project coming up that has specified a Schneider XW 80/600 controller. Its going to need RS. Is the only product still the Tigo TS4-A-F? thanks jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-w

Re: [RE-wrenches] OB Radian question

2022-05-07 Thread Jay via RE-wrenches
Get a section of 8” gutter. It will fit nicely under the inverter. Obviously cutting holes in the top for all the wire, inverter connections. I haven’t tried the vfx covers but it’s the same plastic insulated connectors, should fit. Jay > On May 7, 2022, at 6:12 PM, Kirk Herander via RE-wren

Re: [RE-wrenches] Sol-Ark 15k

2022-05-08 Thread Jay via RE-wrenches
Hi Chris, Can’t you increase the size of the KO’s? Jay > On May 7, 2022, at 7:17 PM, Chris Sparadeo via RE-wrenches > wrote: > >  > Jason, > > I think I agree with your interpretation of the wiring diagram. My hesitation > is, with a 1-1/4” KO for AC inputs, only choice seems to be a >24”

Re: [RE-wrenches] dual channel charge controllers?

2022-06-02 Thread Jay via RE-wrenches
Hi Kirk You didn’t give a lot of info but I don’t think there is a product that meets your requirements. I’m guessing its either 24v or 48v system with with a C40 controller. Personally I’d leave the old system as 20 year old modules are not cost effectively worth messing with. And if you

Re: [RE-wrenches] wire management on Qcell AC module

2022-06-02 Thread Jay via RE-wrenches
These modules are designed for racking w/o MLPE and the rest of the world that doesn’t use MLPE. And code in both 300.11 and 330 ish say that wires need to be supported between 6” and 12” ( I’m not sure which is the correct one to use, I’ve always been told to use 12”) from any box or termina

[RE-wrenches] Best peal and stick zip tie anchor

2022-06-08 Thread Jay via RE-wrenches
I’m wondering if anyone has ever used a high quality VHB zip tie attachment base on the center “ junction” box of a mid junction box panel. I’m just looking for options to anchor the wire on that perfect location, which has no attachment. And if you have what are the best parts to get. Wiri

Re: [RE-wrenches] Li Replacements for Lead-acid Bank

2022-06-10 Thread Jay via RE-wrenches
I agree with John A pretty simple fix is to install a relay on the AC side controlled by the AUX of the inverter. Jay > On Jun 10, 2022, at 6:17 AM, John Blittersdorf via RE-wrenches > wrote: > >  > Matt, I have several systems with the same mix working ok except that the > low battery c

Re: [RE-wrenches] Li Replacements for Lead-acid Bank

2022-06-10 Thread Jay via RE-wrenches
I would add that there is a big range in LVD in lithium batteries. Simpliphi has a really high one, others much lower which do work with older equipment and their LBCO settings. Jay > On Jun 10, 2022, at 9:15 AM, Jerry Shafer via RE-wrenches > wrote: > >  > Matt > Look at the fortress Eva

[RE-wrenches] wireless water tank level monitor

2022-06-16 Thread jay via RE-wrenches
Hi All, Does anyone have recommendations for a wireless water tank level monitor Looking for multiple levels, not just empty. It is strictly for monitoring, not control Could be cell service or internet ( which would be connected via wireless radio) and its offgrid Thanks in advance, jay __

Re: [RE-wrenches] GT inverter for SWWP turbine

2022-06-28 Thread Jay via RE-wrenches
Hi Jeremy, Sol ark and Outback skybox. Might be others. It might be tricky dealing with the wind machine w/o batteries. Jay > On Jun 28, 2022, at 4:12 PM, Jeremy Coxon via RE-wrenches > wrote: > > We have a customer who has a legacy off grid system which includes a SWWP > whisper 200.

Re: [RE-wrenches] Small Industrial Propane Generators

2022-06-29 Thread jay via RE-wrenches
Most of the other brands: Cummins/onan Kohler Seem to now start at 24kw for liquid cooled/1800 RPM, but really nice units, many options: To me the biggest reason to chose one is which has the closest/best service/warranty company. Jay > On Jun 29, 2022, at 8:54 AM, Michael Morningstar via

[RE-wrenches] Schneider XW+

2022-07-02 Thread Jay via RE-wrenches
Hi all A buddy called me with the following problem. He was given a 5548 XW manufactured in 2019 that doesn’t work. As best as we can figure it never worked. Still trying to get that info. In trying to diagnose, he noticed the transformer is rated at 0-28v and 0-120vac per leg out. I have pho

Re: [RE-wrenches] Leakage of current

2022-07-10 Thread Jay via RE-wrenches
Hi Ron I would check via clamp on meter to see if/which string of modules has current on it. Jay > On Jul 10, 2022, at 3:10 PM, Ron Young via RE-wrenches > wrote: > > I have a customer that has self installed an array on a metal roof using APS > Rapid shutdown devices. The roof rack is st

Re: [RE-wrenches] Enphase IQ7 versus IQ8

2022-07-12 Thread Jay via RE-wrenches
Hi Jason And if you don’t have the smart controller/battery system then you do not need this proprietary rapid shut down switch correct? Jay > On Jul 12, 2022, at 3:25 PM, Jason Szumlanski via RE-wrenches > wrote: > >  > Yes, they require a proprietary rapid shutdown switch that connects

[RE-wrenches] lithium in cold weather/heating

2022-07-21 Thread jay via RE-wrenches
HI All, As I get more calls for offgrid designs with lithium batteries I”m wondering what you all are doing to keep the batteries warm when it gets cold. For some of you 0 F will seem mild, others super cold. Doing a battery box and heating that or heating the whole inverter/battery shed? I

Re: [RE-wrenches] lithium in cold weather/heating

2022-07-22 Thread Jay via RE-wrenches
y use zero power to operate) we can find and set it at 55 >> degrees. No need for the insulated box or fretting about toasting $20K+ >> in batteries. It would be nice to find one with a thermostat that goes >> down to 45 degrees. >> >> Bill >> >> Feathe

Re: [RE-wrenches] Outback FXR: Battery voltage exceeds settings

2022-07-23 Thread Jay via RE-wrenches
Outback controllers have a tendency to be a bit slow. So they can definitely get higher than the set points but only for a second or two which is not going do damage anything. I’ve seen them do this. Especially if it’s a larger array, sealed batteries and when the batteries are full and a loa

Re: [RE-wrenches] Magnum inverter/generator integration problems

2022-07-25 Thread Jay via RE-wrenches
Hi Chris. I’m a bit confused about the breaker on the BMK. That’s the battery monitor? No breakers. If you mean the inverter, then check that both legs are working. I’ve had a similar issue in the past that turned out to be a bad 240v breaker. 1 side didn’t work, but because of how the magn

Re: [RE-wrenches] off-grid AC coupling feasibility

2022-07-31 Thread Jay via RE-wrenches
I also worry about getting the system to 64 hz. That is hard on motors and might be the cause of the Light pulsing you’re seeing drake. Jay > On Jul 31, 2022, at 10:08 AM, Drake Chamberlin via RE-wrenches > wrote: > >  > Yes, we have a system with AC and DC coupled arrays on an off-grid

Re: [RE-wrenches] Enphase String Breaker Heating Up

2022-08-04 Thread Jay via RE-wrenches
Seems to me this has come up before. With bad breakers as probable cause. I don’t know if the heat has caused buss damage Might go for CH or QO breakers instead BR style. Jay > On Aug 4, 2022, at 8:08 PM, Jerry Shafer via RE-wrenches > wrote: > >  > Jason > Is the installation designed fo

[RE-wrenches] Abandoned equipment

2022-08-15 Thread Jay via RE-wrenches
Hi All A question. Panels were shipped to me, and literally dropped off the truck, 6’. About 1/2 broken, others with probable unknown future issues. Company I bought from sent me another pallet no charge. It’s been 3 months and the stack of broken/damaged panels is still in my yard and no

[RE-wrenches] solar panel recycling

2022-08-17 Thread jay via RE-wrenches
Hi All, Some asked me a question about recycling of panels and I can’t exactly find out the answer. The companies here in the US that “recycle”. If I understand it right, they are: 1. removing the aluminum frames 2. grinding up the panels 3. removing the wires Then I don’t know what happen

Re: [RE-wrenches] 3 phase off-grid UL listed

2022-09-08 Thread Jay via RE-wrenches
Hi Mac Sol ark does, Schneider XWpro does, Outback vfxr does but only 9 which is 32kw That’s all I can think of Jay > On Sep 8, 2022, at 5:42 AM, Mac Lewis via RE-wrenches > wrote: > >  > Hello Wrenches, > > What inverter options are there for 3 phase, UL listed, off-grid inverter > syste

[RE-wrenches] sol ark 12kw question

2022-09-10 Thread jay via RE-wrenches
HI All I”m trying to figure out exactly how much PV/CC there is for off grid on the sol ark 12kw or 9kw off grid The manual says 6,500 and 6,500 watts but that is grid connected. It looks like its 6,500 max for offgrid? Is that correct? thanks in advance jay ___

Re: [RE-wrenches] Sol-Ark phase imbalances

2022-09-10 Thread jay via RE-wrenches
Hi Howie Here is an interesting youtube video about testing the sol ark vs XW pro. They use all sorts of loads and the sol ark does not come out well in my view, but I’ll let you decide. https://www.youtube.com/watch?v=-Ez4cbuy7IQ jay > On S

Re: [RE-wrenches] Rebuild/Replacement for Harris Hydro

2022-09-15 Thread Jay via RE-wrenches
I’d recommend contacting derik from high power hydro. 707-923-3507 He might have a replacement brass or SS runners and definitely has brushless motors Jay > On Sep 15, 2022, at 5:15 PM, David Palumbo via RE-wrenches > wrote: > >  > Wrenches, > > I have one of my old high head micro-hy

Re: [RE-wrenches] Rebuild/Replacement for Harris Hydro

2022-09-15 Thread Jay via RE-wrenches
His website is https://www.homehydro.com/ Jay > On Sep 15, 2022, at 5:28 PM, Jay wrote: > >  > I’d recommend contacting derik from high power hydro. > > 707-923-3507 > > He might have a replacement brass or SS runners and definitely has brushless > motors > > Jay > > >>> On Sep 15, 20

[RE-wrenches] Sun selector omni meter manual

2022-09-26 Thread Jay via RE-wrenches
Anyone have a manual for an ancient Sun Selector Omni Meter? I’ve got to go visit a site with one and it’s been about 20 years since I’ve worked on one and don’t have a manual, nor could I find on online Thanks in advance Jay ___ List sponsored by

[RE-wrenches] sol ark reliability question

2022-09-29 Thread jay via RE-wrenches
Hi All, I’ve got a question about how many folks are having issues with sol-ark products? the reason i ask is that i’ve got a friend, a good competent installer ( well versed in OB, Schneider, magnum) who’s had continuing nightmares with them. he’s got 2 systems each on is a stacked pair of 1

Re: [RE-wrenches] sol ark reliability question

2022-09-30 Thread Jay via RE-wrenches
t BMS interface seems hardy, > Would be good to know what issues he is having to accurately help > Jerry > > On Thu, Sep 29, 2022 at 7:01 AM jay via RE-wrenches > wrote: > Hi All, > > I’ve got a question about how many folks are having issues with sol-ark > products

Re: [RE-wrenches] heating pads for batteries

2022-09-30 Thread Jay via RE-wrenches
I’m looking at agricultural seedling mats. They are super tough,come in many sizes many come with thermostats. Reasonable flexible. Jay > On Sep 30, 2022, at 2:45 PM, Dana Orzel via RE-wrenches > wrote: > > Reptile heater pads? > > Dana Orzel > C: 208.721.7003 > E- d...@solarwork.com > >

Re: [RE-wrenches] sol ark reliability question

2022-10-04 Thread Jay via RE-wrenches
with a system we hadn't installed that >>> was quite vexing. Turned out to be a loose main DC connection to the >>> inverter. Bizarre behavior as the connection heated up and the resistance >>> varied. >>> >>> Ray Walters >>> >

Re: [RE-wrenches] Onboard PV Charging Kit for Electric Vehicle

2022-10-05 Thread Jay via RE-wrenches
Hi Cory What a beautiful truck. Would like to see the video of the solar extending My question, is it possible to go direct to the EV battery? he/she just wants to charge the ev right directly off the panels? And what voltage is the main battery. Jay > On Oct 5, 2022, at 1:01 AM, Corey Shal

Re: [RE-wrenches] Butt End Connector Warning

2022-10-06 Thread Jay via RE-wrenches
Hi drake Can you give us a part number or picture? Thx Jay > On Oct 6, 2022, at 7:33 AM, Drake Chamberlin via RE-wrenches > wrote: > > Our electrical supplier seamlessly transitioned from crimp on butt end > connectors, that were listed for CU and AL, to unmarked ones that were > approved

Re: [RE-wrenches] AC coupled grid tie only inverter

2022-10-08 Thread Jay via RE-wrenches
Hi Drake I remembered that they make this product or they did. https://www.magnum-dimensions.com/sites/default/files/MagDocs/64-00062%20Rev%20A%20%28ACLD-40%29_web.pdf ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-w

Re: [RE-wrenches] Simpliphi with SW inverters

2022-10-13 Thread Jay via RE-wrenches
I think we might have a naming issue I’m thinking William is talking about the Trace SW And I think Dave is talking about the Schneider SW Very different critters To Williams question you should be able to program it to meet their specifications. Jay > On Oct 13, 2022, at 9:49 AM, Dave Angel

[RE-wrenches] utility scale BESS

2022-10-26 Thread jay via RE-wrenches
HI All, I”m wondering if anyone has any direct information or can steer me towards actual information on 40’ BESS container systems. specifically the HVAC systems, number, size and sound from there. Thanks in advance. Jay ___ List sponsored by Re

Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Jay via RE-wrenches
Hi KrisCan you share what equipment is being used, watts of solar etc. ThxJayOn Nov 19, 2022, at 5:32 AM, Kristopher Schmid via RE-wrenches wrote:Greetings all,I have seen an issue on two different systems that I am hoping someone can shed some light on for me.  One was a 48 volt pack of 12 volt

[RE-wrenches] solar lease questions

2022-12-17 Thread jay via RE-wrenches
HI All, I”ve got a friend in hawaii, big island near Kona that is looking at a sun run lease and she’s asking me questions. I’m not that familiar with the electric rates nor the games that Sun Run is doing. They are pushing a 20 yr lease with the following system: 38 x 400 watt panels 2 x SE

Re: [RE-wrenches] Old Trace SW inverter connected to the grid.

2022-12-19 Thread Jay via RE-wrenches
The older versions of the SW didnt have the GTI plug or need it. What I find curious is what was said about the lineman that they measured current. If the lines were off, no way that inverter could power it up or even the transformer. I’d recommend checking current just to confirm what’s going on. 

Re: [RE-wrenches] Utility transformer limitations

2022-12-26 Thread Jay via RE-wrenches
If the utility is PG&E in my experience here is what happens They say yes or no to the interconnection. If no you have the option to request an engineering study to determine how much solar. That study is at your expense, paid in advance and the exact cost isn’t known until the study is done. Could

Re: [RE-wrenches] Utility transformer limitations

2022-12-26 Thread Jay via RE-wrenches
. JayOn Dec 26, 2022, at 10:12 AM, Christopher Warfel via RE-wrenches wrote: What happens if the study shows yes, that their no was wrong. Or does that never happen?😕 On 12/26/2022 12:48 PM, Jay via RE-wrenches wrote: If the utility is PG

[RE-wrenches] blue planet battery voltage vs SOC

2022-12-28 Thread jay via RE-wrenches
HI All, I’m trying to trouble shoot a remote system and wondering if anyone has a rough volts vs SOC for the the blue planet battery thx jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Addr

[RE-wrenches] Outback vfx 3648 question

2023-01-03 Thread Jay via RE-wrenches
Has anyone had a vfx sort of not pay attention to it charging current settings, I have a customer who’s older vfx will do the following Settings are 5 amps ac, 5 amp ac charge It’ll run at about 10 amps dc charging Then randomly go up to 30 amps dc then back down. Maybe 15 seconds Later go up

Re: [RE-wrenches] Outback vfx 3648 question

2023-01-03 Thread Jay via RE-wrenches
, the issue may also be in the temp compensation board inside the inverter.JerryOn Tue, Jan 3, 2023 at 6:16 AM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:Has anyone had a vfx sort of not pay attention to it charging current settings, I have a customer who’s older vfx will

Re: [RE-wrenches] Outback vfx 3648 question

2023-01-04 Thread Jay via RE-wrenches
onary > applications (ie normally grounded systems). > > John > >> On Tue, Jan 3, 2023 at 9:16 AM Jay via RE-wrenches >> wrote: >> >> Has anyone had a vfx sort of not pay attention to it charging current >> settings, >> >> I have a customer

[RE-wrenches] Problem Outback update

2023-01-06 Thread Jay via RE-wrenches
Hi all It turns out it was the voltage regulator in the generator. It was replaced and the inverter acts normally. Have a nice weekend Jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address:

Re: [RE-wrenches] Low Frequency transformer off-grid inverter options

2023-01-13 Thread Jay via RE-wrenches
Hi Mac The radian is low voltage transformer Based. Has hella surge capacity I would consider what web based monitoring system he wants and go with that platform. Regardless of system I’d install soft start/vfd on the larger units. Just easier on everything. The solark 12 doesn’t seem to be

[RE-wrenches] outback FM-100

2023-01-17 Thread jay via RE-wrenches
HI All, Does anyone have any updated info about when the FM-100 and Mate3S will be available? thx jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change

Re: [RE-wrenches] Remote battery disconnects

2023-01-27 Thread Jay via RE-wrenches
Good point Glenn. My question is if this system is in its own building. If so it is probably easier to convince the AHJ about not needing a remote battery disco. JayOn Jan 27, 2023, at 12:46 PM, Glenn Burt via RE-wrenches wrote: Does the AHJ really want the batteries disconnected from

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread jay via RE-wrenches
HI William B, That is a good point. And even beyond the potential CC damage, since your now potentially powering the inverter it could actually stay alive ( I’ve seen this happen ) or it can cause a voltage spike from the CC which can damage the inverter which I”ve also seen. I don’t know w

Re: [RE-wrenches] Remote battery disconnects

2023-02-03 Thread jay via RE-wrenches
As 480.7(B) says single and double homes, that going with the mike holt literal interpretation to me says that even if you have a remote power shed it would still require the remote disconnect. As that section doesn’t say that the power system is in the house or not. (A) doesn’t apply as the b

Re: [RE-wrenches] cable trays and battery cable

2023-02-05 Thread jay via RE-wrenches
Have you looked at https://www.snaketray.com/product-catalog/solar-snake-tray/ jay > On Feb 5, 2023, at 1:48 PM, Kirk Herander via RE-wrenches > wrote: > > All, > I'm just starting a 500kwh LFP battery system that requires a max.

[RE-wrenches] absolyte GP battery question/ sideways mounting.

2023-02-20 Thread jay via RE-wrenches
HI All, I was just contacted by someone who has a 6 yr old absolyte GP 100G33 battery that has lost a lot of capacity. The manual only lists a horizontal install, but this was installed on its side which I”m guessing was due to space issues. I am thinking that isn’t good for it, but hopefull

Re: [RE-wrenches] Voltage Rise

2023-02-23 Thread Jay via RE-wrenches
Hi DaveIt might be that the utility transformer is where the extra voltage rise is coming from?JayOn Feb 23, 2023, at 10:03 AM, Dave Tedeyan via RE-wrenches wrote:Hi All,I've got a customer who is having issues with high voltage at their house. This first became an issue after installing 23.1kw o

Re: [RE-wrenches] Trimetric on LiFe Blue

2023-03-07 Thread Jay via RE-wrenches
Hi Drake I’ve had success with amps turned off. Jay > On Mar 7, 2023, at 9:20 AM, Drake Chamberlin via RE-wrenches > wrote: > > Hello Lithium Battery Wrenches, > > A 48 V bank of 8, 12 V LiFe Blue batteries, 2 series sets of four in > parallel, for a 400 AH bank, is being monitored by a T

[RE-wrenches] Cell phone based relay control

2023-03-13 Thread Jay via RE-wrenches
Hi all Any recommendations for a cell phone controlled relay? Would be off grid. There is 12v already there. I’m trying to remote control a grundfos sqflex pump, only a dry dpst contact is required. Would be great to have access to the control via an app or web so that one could see if it’s

Re: [RE-wrenches] Cell phone based relay control

2023-03-13 Thread Jay via RE-wrenches
hes@lists.re-wrenches.org> wrote:https://www.amazon.com/Solenoid-Control-Wireless-Contact-T-Mobile/dp/B07Q7PKW5Z?th=1Larry CrutcherStarlight Solar Power Systems On Mar 13, 2023, at 12:47 PM, Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:Hi allAny recommendations for

Re: [RE-wrenches] Fire Sprinklers (was Re: Cell phone based relay control)

2023-03-14 Thread jay via RE-wrenches
HI Ray, I’d researched this when I lived in an area that was fire prone. I would recommend reading this info about the product and how it works and what it doesn’t work for. https://www.7thgenerationdesign.com/wp-content/uploads/2018/12/fire-WEEDS.pdf

[RE-wrenches] sol ark contact

2023-03-14 Thread jay via RE-wrenches
HI All, Does anyone have a very high up contact at sol ark? A few months ago I was writing about a buddy who had a stacked 12k. Hes a competent installer. It was designed by sol ark, All loads were included correctly. The system was monitored by sol ark Numerous board failures, incorrect firmwa

Re: [RE-wrenches] Off Grid Battery Charging

2023-03-16 Thread jay via RE-wrenches
HI Brad, I was just about to hit send on those exact wattages, yes completely agree. As a sort of joke, the self discharge of the batteries is probably more than what she could make in a day. Jay > On Mar 16, 2023, at 4:29 PM, Bradley Bassett via RE-wrenches > wrote: > > I tried this bac

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-03 Thread jay via RE-wrenches
Hi Danny Lots of variables. As the warranty is over, that is no longer a concern to deal with The fact that you’ve had 2 go bad at the 5 year point, usually means you can expect other failures soon. There are 2 options I’ve done. 1. is to hi grade the battery bank into best 16 batteries, but

[RE-wrenches] Enphase failure

2023-04-12 Thread Jay via RE-wrenches
Hi all I’m just starting to try and figure out a failed enphase system that was just noticed to be off line a few days ago. 12 x IQ7A 400 watt panels The install is 20’ from the main transformer/load center. 1000 amp commercial panel There is no monitoring because they couldn’t get cat 5 t

Re: [RE-wrenches] Enphase failure

2023-04-13 Thread Jay via RE-wrenches
A follow up on this I talked to a buddy at a large company that installs enphase. He said the issue is that the firmware fails without the web for updates. He’s seen it lots of times. Which means this project will have to get web connected to hopefully fix it. I haven’t found in the instr

[RE-wrenches] Free sunpump core

2023-04-14 Thread Jay via RE-wrenches
Hi all I inherited a sunpump model SDS-t-128 It just a core at this point, needs a complete rebuild. If anyone wants it contact me offsite. Just shipping charge. Jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-

[RE-wrenches] Lithium battery aging

2023-04-16 Thread Jay via RE-wrenches
Hi all I hope some of you might know the answer to these questions. When a Lithium battery ages, is its voltage reduced? If so by how much? Is the C rate reduced? Is the only change lower amp hours? And finally how does the BMS determine this reduction? How does it know it’s lower capaci

Re: [RE-wrenches] Lithium upgrade when Magnasine goes to float too soon

2023-04-18 Thread Jay via RE-wrenches
Hi MickI can’t find it in the manual but from memory the magnum won’t go into absorb unless the volts drop below some number, which I can’t find. Maybe tech support can help with that. I’ve been using eg4 server rack batteries. It’s hard to beat the price, built in display, modular design, UL liste

Re: [RE-wrenches] active vs apparent power readings with solar

2023-04-28 Thread Jay via RE-wrenches
Certainly could be the meter or how it’s being used. Like is the Electrican checking the main or output from the inverter?If the inverter output shows these numbers I’d check to make sure the inverter is in the correct grid connection  setting. JayOn Apr 27, 2023, at 5:13 PM, Dave Angelini Offgrid

Re: [RE-wrenches] problem using Radian on TOU metering

2023-05-02 Thread Jay via RE-wrenches
Which utility has such low rates? SMUD? Jay > On May 2, 2023, at 12:05 PM, Darryl Thayer via RE-wrenches > wrote: > >  > Hello, I apologize for perhaps a dumb question. I did go online to ask > Outback twice, no answer.System Radian 8 kW and Mate3 with 2 each 1.5 kW > solar arrays i

[RE-wrenches] Battery balancers

2023-05-15 Thread Jay via RE-wrenches
Hi All I’m wondering what the thoughts are on using or not balancers for 2 12v lithium in series for 24v system. The batteries don’t have any series communication. Kilovault if that matters. Not my design. It would seem to be a good idea, with victron having a good one. Thanks in advance

[RE-wrenches] Retail price lists

2023-05-16 Thread Jay via RE-wrenches
Hi All I have a question about how wrenches are dealing with charging for equipment as most prices of most equipment on line at or below wholesale. If people are marking it up, how much? what metric are people using? I think victron might be the only company I’ve actually seen a retail price

Re: [RE-wrenches] Fortress LFPs & ENVY 12kw inverter

2023-06-01 Thread Jay via RE-wrenches
Hi KirkIt’s the same Chinese company who makes both. Deye If I understand correctly sol ark’s exclusive arrangement with Deye ended. JayOn Jun 1, 2023, at 10:19 AM, Kirk Herander via RE-wrenches wrote:Hello All,I am sizing my first Fortress system, 18.5kwh LFPs w/ their new ENVY inverter. Or woul

Re: [RE-wrenches] Bonding Metal Roofs Part II

2023-06-06 Thread Jay via RE-wrenches
But isn’t the whole concept of RS to prevent the energizing of say a metal roof?The inverter sees a ground fault or ark fault. Trips off line, the RS activate and now it’s less than 80v. Isn’t that what it’s supposed to do?What is the purpose of grounding the metal roof?JayOn Jun 6, 2023, at 10:09

Re: [RE-wrenches] Schneider SCP / MPPT 80 600 / XW+ / Gateway questions

2023-06-11 Thread Jay via RE-wrenches
Hi greg There was just a thread that discussed you can’t use the scp to program the pro. Have to use insight. If I understand correctly. Hopefully others more knowledgeable will chime in about your other issues too. Good luck Jay > On Jun 11, 2023, at 11:37 AM, greg egan via RE-wrenches

[RE-wrenches] Fronius primo fan

2023-06-15 Thread Jay via RE-wrenches
Does anyone know where to get a replacement fan for a fronius promo 10kw? Thx Jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email add

[RE-wrenches] Lithium battery charge rate

2023-06-26 Thread Jay via RE-wrenches
Hi All I’m wondering if minimum charge amps for lithium is common or not? Or does it have to do with the cell shape: cylindrical vs prismatic vs pouch? A client purchased some EG4 batteries and they are getting a bit out of balanced. Tech support didn’t suggest higher volts or longer absorb but

Re: [RE-wrenches] Lithium battery charge rate

2023-06-27 Thread Jay via RE-wrenches
wrote:Hi Jay, Larry says is correct.  My experience, with cells and there BMS is they need to get up to top balance voltage then the BMS will stop charging the full cells and bring the remainder of cells up to fill charge.  My oldest set is about 6 years old, since I understood they have been fine

Re: [RE-wrenches] Parallel Homegrid Stack'd Busbar

2023-06-29 Thread Jay via RE-wrenches
FYIThe 12 and 15kw both have dual lugs on positive and negative battery inputs. On Jun 29, 2023, at 6:47 AM, Jason Szumlanski via RE-wrenches wrote:I was thinking the Midnite combiner, but it's a very big product for what we're trying to accomplish. I was hoping Polaris type tap connectors might

Re: [RE-wrenches] Pro Power saving device

2023-07-06 Thread Jay via RE-wrenches
And even if it did power factor correction most residential customers are not charged for power factor.  Zero savings. On Jul 6, 2023, at 12:27 PM, Dan Fink via RE-wrenches wrote:It's supposed to adjust power factor for the home loads with a teeny tiny capacitor in the overpriced plug-in box. Whi

[RE-wrenches] Lithium battery recommendation

2023-07-13 Thread Jay via RE-wrenches
Hi all I’m Looking for recommendations for a lithium battery. 48v. 150-200 kWh. System is probably going to be open comm, as the system has outback equipment. That could change but probably not. Remote monitoring is required even though it is a site with people 24/7. So far fortress and home

Re: [RE-wrenches] [EXTERNAL] Re: Lithium battery recommendation

2023-07-14 Thread Jay via RE-wrenches
l the way back, that didn't puke prematurely and have issues. Discover AES and Schneider for the win. Once they are set up, they just work.    On Thu, Jul 13, 2023 at 3:20 PM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote: Hi all I’m Looking for recommendations for a

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-20 Thread jay via RE-wrenches
HI All, I wanted to revisit this thread for one reason. If you turn off the inverter at the remote on/off with the AUX relay, then starting the generator won’t have any impact as the inverter is off. So someone will have to go and reset the AUX relay. Vs If you do a relay on the AC output, w

[RE-wrenches] Outback lithium LVD

2023-07-20 Thread Jay via RE-wrenches
I apologize in advance if this is a duplicate. I was contemplating the discussion about how to deal with an inverter that doesnt have the correct LBCO for a lithium LVD voltage. A suggested option for OB was to install a relay triggered by the AUX and controlling the inverter remote on/off sw

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-20 Thread Jay via RE-wrenches
back on the next day.  This is my concern on Solark installs, I just noticed that the inverter won't pass through PV, if it hits its LVD set point.  On 7/20/2023 3:04 PM, jay via RE-wrenches wrote: HI All, I wanted to re

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-21 Thread Jay via RE-wrenches
s its LVD set point.  On 7/20/2023 3:04 PM, jay via RE-wrenches wrote: HI All, I wanted to revisit this thread for one reason.

Re: [RE-wrenches] Inverter output fluctuations

2023-07-23 Thread Jay via RE-wrenches
Given that it worked fine for years it would appear that the XW+ has an issue. I don’t see how the SE could cause this. Is it still under warranty? What does Schneider say about the issue. JayOn Jul 22, 2023, at 10:33 PM, Howie Michaelson via RE-wrenches wrote:Michael, that is my last ditch choic

[RE-wrenches] Solar edge question

2023-08-02 Thread Jay via RE-wrenches
Hi all For all you SE experts. I got contacted from someone who has an offgrid system of a SE 7600A and battery. Works fine. They want to connect to grid power, which is right at the street because they want an EV. My question is, what do they need to make this a normal sell back and batte

Re: [RE-wrenches] Solar edge question

2023-08-02 Thread Jay via RE-wrenches
Storedge inverters. And the newer SE battery pack is also incompatible with the Storedge.On Wed, Aug 2, 2023 at 8:22 AM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:Hi all For all you SE experts. I got contacted from someone who has an offgrid system of a SE 7600A and battery.

[RE-wrenches] Wind machines

2023-08-17 Thread Jay via RE-wrenches
Hi all Is anyone making a good quality 1-2kw wind machine? All of my searches come up with nothing. Thanks in advance Jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.r

Re: [RE-wrenches] Wind machines

2023-08-17 Thread Jay via RE-wrenches
. On 8/17/2023 11:09 AM, Jay via RE-wrenches wrote: Hi all Is anyone making a good quality 1-2kw wind machine? All of my searches come up with nothing. Thanks in advance Jay ___ List sponsored by Redwood Alliance Pay

Re: [RE-wrenches] Wind machines

2023-08-17 Thread Jay via RE-wrenches
luck! Solar is cheap but boring!Dan FinkOwner, Buckville Energy Consulting LLCIREC Certified Instructor for PV and Small Wind InstallationNABCEP Certified PV System InspectorNABCEP PV Associatedanbo...@gmail.com970-672-4342 On Thu, Aug 17, 2023 at 9:11 AM Jay via RE-wrenches <re-wrenches@lis

Re: [RE-wrenches] Iron Edison Lithiums

2023-08-29 Thread Jay via RE-wrenches
Can you send pictures?  JayOn Aug 29, 2023, at 5:54 PM, Jeremy Rodriguez via RE-wrenches wrote: Leaking from somewhere mid way in the battery case I’m guessing.  The liquid followed a cable down to the BMS board and corroded it badly.  Jeremy Rodriguez  Solar Installation / Design All Sola

[RE-wrenches] sol ark AGS question

2023-09-14 Thread jay via RE-wrenches
Hi All, I have a client with a sol ark and it doesn’t have warm up or cool down, kind of amazing companies are going backwards in their tech. Has anyone come up with external fix for this? I am guessing the internal relay on the sol ark switches closed when it sees the correct volts/hz and o

Re: [RE-wrenches] Franklin Home Power

2023-09-16 Thread jay via RE-wrenches
I recently saw this. I haven’t used either, but its looks well done. https://signaturesolar.com/eg4-powerpro-ess-14-3-28-6kwh-capacity-eg4-18kpv-eg4-powerpro-wallmount-battery-9540-pending/

Re: [RE-wrenches] sol ark AGS question

2023-09-16 Thread jay via RE-wrenches
> <mailto:re-wrenches@lists.re-wrenches.org>> wrote: > Jay, wrenches > ASCO makes multiple ATS controls that can manage delays latching up and for > cool down. Most of the gensets have are programmed cool down after relay > opens so its not an issue. Generally on start

Re: [RE-wrenches] GT w/ BB

2023-09-18 Thread Jay via RE-wrenches
If 40kw is the peak and then there are new added loads, what 50-60kw?  If it was me I’d be designing the inverters to handle the 50/60 kw with future expansion capabilities beyond that. Then how much kWh of storage are you going to need or maybe are planning for?At some point maybe looking at a lar