Hi Chris,

Can’t you increase the size of the KO’s?

Jay

> On May 7, 2022, at 7:17 PM, Chris Sparadeo via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org> wrote:
> 
> 
> Jason,
> 
> I think I agree with your interpretation of the wiring diagram. My hesitation 
> is, with a 1-1/4” KO for AC inputs, only choice seems to be a >24” stub 
> conduit for 2/0 conductores to a fused disconnect. Not a fun pipe to bend…and 
> extra BOS seems like a less than ideal solution. 
> 
> Is this your conclusion as well? 
> 
>> On Sun, Apr 17, 2022 at 10:38 PM Darryl Thayer via RE-wrenches 
>> <re-wrenches@lists.re-wrenches.org> wrote:
>> Yes and no, I think this is a tap, "a tap shall be permitted anywhere along 
>> a feeder"  ' as long as it is less than a 10-foot rule or 25-foot rule 
>> ending in a listed OCPD with a rating sufficient to handle the maximum 
>> overcurrent'.  Service equipment residential is rated for fault currents of 
>> up to 10,000 amps withstand.    Refer to 240.4.B and 240.21 (B) (1 & 2) 
>> 
>>> On Sun, Apr 17, 2022 at 10:39 AM Jason Szumlanski via RE-wrenches 
>>> <re-wrenches@lists.re-wrenches.org> wrote:
>>> But this isn't a tap. It's a feeder conductor connected to an OCPD. 
>>> 
>>> I guess if you don't have a grid in or generator in or AC Coupled PV, you 
>>> could just call it an inverter output circuit and it could be sized 
>>> accordingly. But it would still need to be protected at it's source by an 
>>> appropriately rated OCPD. Don't get me wrong... I don't think there is a 
>>> real safety issue here, but I also don't see how the NEC allows the 
>>> conductor to be sized for anything less than 200A.
>>> 
>>> Jason 
>>> 
>>> 
>>>> On Sun, Apr 17, 2022, 11:29 AM Darryl Thayer via RE-wrenches 
>>>> <re-wrenches@lists.re-wrenches.org> wrote:
>>>> The tap rule says you can reduce to 10% of the nominal size for 10 feet 
>>>> and protect at the downstream OCPD or 25% for 25 feet for solar with 
>>>> multiple sources see 705
>>>> 
>>>>> On Sat, Apr 16, 2022 at 9:16 PM Jason Szumlanski via RE-wrenches 
>>>>> <re-wrenches@lists.re-wrenches.org> wrote:
>>>>> That's what I'm thinking. You would need to use a 200A conductor to a 
>>>>> separate load out OCPD before downsizing the wire. I guess there are pros 
>>>>> and cons, but it seems this is geared toward whole house backup for 200A 
>>>>> services. I'm eager to get an opportunity to use it in that scenario. 
>>>>> 
>>>>> Jason
>>>>> 
>>>>> 
>>>>> 
>>>>> 
>>>>>> On Sat, Apr 16, 2022, 10:06 PM Chris Sparadeo via RE-wrenches 
>>>>>> <re-wrenches@lists.re-wrenches.org> wrote:
>>>>>> Jason,
>>>>>> 
>>>>>> Any additional OCPD downstream of the 200A load output breaker could 
>>>>>> allow for a smaller wire size to be used at these terminals. For 
>>>>>> example, load output conductors run to a 100A main breaker panel board.  
>>>>>> Obviously depending on circumstances, a #4 copper could fit the bill. 
>>>>>> 
>>>>>> What I’m not extremely  excited about with the new design is that in an 
>>>>>> off-grid scenario with a generator and smart load, we would now need to 
>>>>>> integrate an AC disconnect for generator input (grid)  and either a 
>>>>>> fused disconnect or loads panel for any smart load output. With the 12K 
>>>>>> unit, the integrated breakers help cut down on BOS and install time. 
>>>>>> 
>>>>>> -Chris 
>>>>>> 
>>>>>>> On Sat, Apr 16, 2022 at 5:35 PM Darryl Thayer via RE-wrenches 
>>>>>>> <re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>> Hello, The overcurrent device is to protect the conductors.  you can 
>>>>>>> put any size wire, but you must protect with the overcurrent device.  
>>>>>>> REmember in solar equipment; you may have more than one supply source.  
>>>>>>> The DC best example is solar modules connected in parallel,      on
>>>>>>> 
>>>>>>>> On Fri, Apr 15, 2022 at 8:26 PM Jerry Shafer via RE-wrenches 
>>>>>>>> <re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>>> You must meet all expected source output potentials within the design 
>>>>>>>> and operating limits, as long as the distribution panel and connected 
>>>>>>>> wiring is rated for the max output of the protected source then you 
>>>>>>>> are good. A 200 ATS connected to a 10 kW genny does not require 2/0 as 
>>>>>>>> it will never meet that rating. Just remember its whatever the max 
>>>>>>>> output can be plus your margin.
>>>>>>>> 
>>>>>>>>> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches 
>>>>>>>>> <re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>>>> Hi Jason,
>>>>>>>>> 
>>>>>>>>> You bring up a valid point….in an off-grid scenario with the 15k do 
>>>>>>>>> you size the conductors to the continuous capacity, surge capacity or 
>>>>>>>>> the OCPD of the unit? 
>>>>>>>>> 
>>>>>>>>> -Chris 
>>>>>>>>> 
>>>>>>>>>> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches 
>>>>>>>>>> <re-wrenches@lists.re-wrenches.org> wrote:
>>>>>>>>>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC 
>>>>>>>>>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>>>>>>>>> 
>>>>>>>>>> 
>>>>>>>>>> 
>>>>>>>>>> 
>>>>>>>>>> 
>>>>>>>>>> 
>>>>>>>>>> 
>>>>>>>>>>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski 
>>>>>>>>>>> <ja...@floridasolardesigngroup.com> wrote:
>>>>>>>>>>> I'm not following the wiring diagrams for this new inverter. It has 
>>>>>>>>>>> 200A pass-through capability with an integrated 200A load 
>>>>>>>>>>> disconnect. But then it says the wire gauge for the load out wiring 
>>>>>>>>>>> can be #4 to 2/0. 
>>>>>>>>>>> 
>>>>>>>>>>> In an off-grid scenario where there is no generator, the max 
>>>>>>>>>>> continuous output is 62.5A, so I assume 80A circuit protection 
>>>>>>>>>>> could be used with 80A rated wire (#4), but how is that circuit 
>>>>>>>>>>> protection implemented if the 200A breaker is integrated? Do you 
>>>>>>>>>>> have to run a short piece of 2/0 to an external 80A rated OCPD and 
>>>>>>>>>>> then step down to #4?
>>>>>>>>>>> 
>>>>>>>>>>> Jason Szumlanski
>>>>>>>>>>> 
>>>>>>>>>>> 
>>>>>>>>>>> 
>>>>>>>>>>> 
>>>>>>>>>>> 
>>>>>>>>>>> 
>>>>>>>>>> _______________________________________________
>>>>>> 
>>>>> _______________________________________________
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> -- 
> Chris Sparadeo
> 
> 
> C_802-369-4458
> H_802-728-3059
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to