HI William B,

That is a good point.  And even beyond the potential CC damage, since your now 
potentially powering the inverter it could actually stay alive ( I’ve seen this 
happen ) or it can cause a voltage spike from the CC which can damage the  
inverter which I”ve also seen.


I don’t know what that section of the code is trying to do, but its doing it 
extremely  poorly.

jay




> On Jan 28, 2023, at 3:32 PM, William Bryce via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org> wrote:
> 
> All
> 
> One thing that no one is talking about is what happens to the MPPT charge 
> controllers when the Battery Disconnect trips when the charge controllers are 
> under full load. 
> Many will blow up. Try turning off the battery breaker on a SolaArk  when the 
> charge controllers are maxed, and see if you get lucky.
> 
> On Sat, Jan 28, 2023 at 3:27 PM William Miller via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org 
> <mailto:re-wrenches@lists.re-wrenches.org>> wrote:
> Jeremy:
> 
>  
> Thanks for posting the code references for those that had never looked them 
> up.
> 
>  
> Chris:
> 
>  
> What do you mean by “a disconnect for AC wiring, not specific to which or 
> both panel types”?
> 
>  
> All:
> 
>  
> Code references are handy when receiving edicts from building officials, but 
> not required, IMHO, for two reasons:  The contractor should already be versed 
> in the codes and, building departments can mandate their own requirements 
> above and beyond the code.
> 
>  
> It may seem redundant to require an AC disconnect for premise wiring as well 
> as a DC battery disconnect.  In most cases if you disconnect the inverter 
> from the batteries the AC power goes off.  However if the generator is 
> running at the time, some battery inverters can operate when disconnected 
> from batteries.  So to completely de-energize all components of an off-grid 
> home you need to disconnect the generator and the battery leads.
> 
>  
> In this case the home is required to have fire sprinklers.  There is pressure 
> pump to provide flow to these fire sprinklers-- said pump being powered by 
> the inverter/battery system.  I am going to apply for a waiver to remove the 
> DC disconnect requirement on the grounds that the pressure pump is essential 
> fire suppression equipment.  Instead I will propose to supply an AC 
> disconnect (meeting all requirements for accessibility and marking) that will 
> disconnect all premise wiring except the pressure pump. 
> 
>  
> By the way, I will of course be trying to apply the logic that the voltage 
> specification is for nominal battery voltage and this project having a 
> nominal 48 volt bank does not require the battery disconnect.
> 
>  
> I will let the group know what response I receive.  Regardless of how this 
> works in this jurisdiction, I think these are both valid arguments worth 
> trying in any jurisdiction requiring the battery disconnect.  Some officials 
> are amenable to dialog and negotiation and some are less so.
> 
>  
>  
> William Miller
> 
>  
> Miller Solar
> 
> 17395 Oak Road, Atascadero, CA 93422
> 
> 805-438-5600
> 
> www.millersolar.com <http://www.millersolar.com/>
> CA Lic. 773985
> 
>  
>  
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org 
> <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Jeremy 
> Rodriguez via RE-wrenches
> Sent: Saturday, January 28, 2023 10:12 AM
> To: cwar...@entech-engineering.com <mailto:cwar...@entech-engineering.com>; 
> RE-wrenches
> Cc: Jeremy Rodriguez
> Subject: Re: [RE-wrenches] Remote battery disconnects
> 
>  
> 
> 
> 2020 Code Language:
> 
> 480.7 DC Disconnect Methods.
> 
> (A) Disconnecting Means. A disconnecting means shall be provided for all 
> ungrounded conductors derived from a stationary battery system with a voltage 
> over 60 volts dc. A disconnecting means shall be readily accessible and 
> located within sight of the battery system.
> 
> N (B) Emergency Disconnect. For one-family and two-family dwellings, a 
> disconnecting means or its remote control for a stationary battery system 
> shall be located at a readily accessible location outside the building for 
> emergency use. The disconnect shall be labeled “EMERGENCY DISCONNECT”.
> 
> N (C) Disconnection of Series Battery Circuits. Battery circuits exceeding 
> 240 volts dc nominal between conductors or to ground and subject to field 
> servicing shall have provisions to disconnect the series-connected strings 
> into segments not exceeding 240 volts dc nominal for maintenance by qualified 
> persons. Non-load-break bolted or plug-in disconnects shall be permitted.
> 
>  
> Jeremy Rodriguez 
> 
> Solar Installation / Design
> 
> All Solar, Inc.
> 
> 1453 M St. 
> 
> Penrose Colorado 81240
> 
>  
> Sent by Jeremy's iPhone. Sorry for typos and shorthand. 
> 
> 
> 
> 
> On Jan 28, 2023, at 7:28 AM, Christopher Warfel via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org 
> <mailto:re-wrenches@lists.re-wrenches.org>> wrote:
> 
> 
> 
> Seems confusing that the AHJ is requiring a disconnect for AC wiring, not 
> specific to which or both panel types, and then a dc disconnect with no code 
> reference.  Was trying to convey a reasonable, safe approach.  A lot of bad 
> information from fire department solar consultants making a lot of money fear 
> mongering, which has led to this type of situation.  Chris
> 
> On 1/27/2023 3:35 PM, William Miller via RE-wrenches wrote:
> 
> Glenn:
> 
>  
> As I wrote, a DC disconnect is required.  Here is an excerpt from the Q&A 
> with the building official:
> 
>  
> 4.   Will you be requiring an external disconnect to disconnect the AC output 
> of the inverter system from premise wiring?
> 
> Yes, as required per 230.85
> 
> 5.   Will you be requiring an external disconnect to disconnect batteries 
> from the inverters?
> 
> Yes
> 
>  
> If the DC disconnect was not required I would not be wasting everyone’s time 
> with my post.  I try to be careful about that, researching on my own before 
> posting and trying to make my questions very clear.  I also try not to 
> embarrass myself with dumb questions, but that does happen occasionally…
> 
>  
> William
> 
>  
> Miller Solar
> 
> 17395 Oak Road, Atascadero, CA 93422
> 
> 805-438-5600
> 
> www.millersolar.com <http://www.millersolar.com/>
> CA Lic. 773985
> 
>  
>  
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org 
> <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Glenn Burt 
> via RE-wrenches
> Sent: Friday, January 27, 2023 11:46 AM
> To: William Miller via RE-wrenches
> Cc: Glenn Burt
> Subject: Re: [RE-wrenches] Remote battery disconnects
> 
>  
> Does the AHJ really want the batteries disconnected from conductors, or does 
> he really just want the inverters to stop operating and producing AC within 
> the house?
> 
> Obviously there is a big difference here and it may be changing as the code 
> evolves.
> 
>  
> -Glenn
> 
> Sent from my 'smart'phone, so please excuse typos and spelling errors.
> 
>  
> ------ Original message------
> 
> From: William Miller via RE-wrenches
> 
> Date: Fri, Jan 27, 2023 2:26 PM
> 
> To: RE-wrenches;
> 
> Cc: William Miller;
> 
> Subject:[RE-wrenches] Remote battery disconnects
> 
>  
> Friends:
> 
>  
> We have a large-ish residential off-grid system install coming up.  The AHJ 
> has said they will require a remote battery disconnect.  I suspect there will 
> be fire sprinkler controls and a pressure pump that would become inoperable 
> if this system were engaged.  In this case we will apply for a waiver.
> 
>  
> The last time this was discussed here as far as I can find was October of 
> 2020.  At that time no one suggested any specific battery disconnect 
> equipment. 
> 
>  
> To further clarify my needs:  There will be 4 or 5 Radian 8048 inverters (5 
> or 6 4/0 battery circuits, ~350A each) and two 175 amp PV recombiner outputs. 
>  That is 6 poles of high amperage DC disconnects.    
> 
>  
> The battery array will be either a UnigyII VRLA or a lithium of a brand yet 
> to be determined.  In the case of lithium we will look for a system that can 
> remotely enable a BMS shutdown.  In the case of a VRLA lead-acid, we will not 
> have that luxury.
> 
>  
> I have done some considerable research and have not found viable, high 
> amperage, remotely activated shutdown equipment.
> 
>  
> I am wondering what hardware others may be using to achieve remote battery 
> disconnecting in these types of cases..
> 
>  
> William
> 
>  
> Miller Solar
> 
> 17395 Oak Road, Atascadero, CA 93422
> 
> 805-438-5600 <tel:805-438-5600>
> www.millersolar.com <http://www.millersolar.com/>
> CA Lic. 773985
> 
>  
>  
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to