In my experiance if the combiner is in the sun breakers will be hot
breakers are a thermal device and should be kept at room temperature.  Try
substituting the HCAC type breaker for the stanard breaker

On Thu, May 21, 2020, 8:57 AM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:

> I'm trying to resolve an intermittent frustrating problem with and Enphase
> IQ system. There are three AC Branch circuits of 9 microinverters each
> coming into an Enphase AC combiner.
>
> What has been happening is one of the BR220 branch circuit breakers and
> the combine CH240 breaker in the main backfed load center have been
> tripping simultaneously. It has happened about four times in the last 6
> months. It was always the same branch circuit breaker, so we kept
> investigating that string, checking the junction box, trunk cable, and cap,
> etc. Finally we swapped out the BR220 breaker.
>
> Fast forward 4 weeks, and we got another call. This time a different
> branch circuit breaker and the main breaker tripped simultaneously. We
> checked that branch circuit and could not find any fault. It seems unlikely
> that two branch circuit breakers would be faulty, so we have now switched
> out the CH240 main breaker in hopes that it is the culprit.
>
> I'm not totally confident in this resolution and I have my fingers
> crossed. If that doesn't work, does anyone have any suggestions on another
> diagnostic step? These intermittent problems are a major hassle. One
> thought I had was to switch to a supply side interconnection with a fusible
> disconnect. Maybe the intermittent fault would blow one of the two line
> fuses so at least I could narrow it down to which line the fault is on if
> there is in fact a fault.
>
> I have experienced two other tripping breaker issues with Enphase systems
> in the past. Neither of them were systems I installed. One turned out to be
> branch circuits that were not properly paired up and landed on different
> breakers. Another time we had an inverter with an internal fault which
> eventually"blew up" with a loud popping noise and smoke billowing out of
> it. That happened after resetting a trip breaker multiple times. This case
> seems to be unrelated to those issues. I'm perplexed.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to