Hi Chad 

Was the enphase monitoring able to locate the bad inverter? Or trial and error?

Jay

Peltz power. 

> On May 21, 2020, at 7:19 AM, Chad Waits <chadwa...@netzerosolar.net> wrote:
> 
> 
> Yeah. We've had them trip in the evening as well. Just never come back online 
> when the sun comes up. We've replaced breakers and meggered all wires. The 
> only solution we've found is isolating that one bad inverter and replacing it.
> 
> really frustrating.
> 
> Chad Waits
> President-Net Zero Solar
> Cell: (520) 270-4873
> 
> 
> 
>> On Thu, May 21, 2020 at 7:15 AM Jason Szumlanski 
>> <ja...@floridasolardesigngroup.com> wrote:
>> I'm guessing I don't have a bad inverter problem since this is occurring on 
>> two different strings. But I guess I can't rule it out.
>> 
>> I should also have mentioned that the breakers apparently trip in the middle 
>> of the night more often than not. I know that because the envoy goes 
>> offline. So this does not seem to be a power production issue. The inverters 
>> should be sleeping at the time that the breakers trip.
>> 
>> I also ruled out rain. The first couple of times I suspected something got 
>> wet, but subsequent tripping occurred during dry spells.
>> 
>>> On Thu, May 21, 2020, 10:12 AM Chad Waits <chadwa...@netzerosolar.net> 
>>> wrote:
>>> Hey Jason,
>>> 
>>> We have experienced this on multiple systems over the past 2 years. We have 
>>> one system where 1 inverter pops an entire sub offline that has 72 other 
>>> inverters in it (screenshots attached). The only way we have been able to 
>>> isolate the problem inverter(s) is to start first with isolating circuits, 
>>> and then unplugging individual inverters until the culprit is found. We've 
>>> had multiple cases escalated to top engineers and we have yet to get an 
>>> explanation of what is going on. Obviously something in the bad inverter(s) 
>>> is creating a catastrophic short but what is causing that has not been 
>>> revealed to us.
>>> 
>>> <Screen Shot 2020-05-21 at 7.10.24 AM.png>
>>> 
>>> <Screen Shot 2020-05-21 at 7.09.59 AM.png>
>>> 
>>> 
>>> I'd appreciate anything you may find out in your investigations.
>>> 
>>> Thanks!
>>> 
>>> Chad Waits
>>> President-Net Zero Solar
>>> Cell: (520) 270-4873
>>> 
>>> 
>>> 
>>>> On Thu, May 21, 2020 at 6:57 AM Jason Szumlanski 
>>>> <ja...@floridasolardesigngroup.com> wrote:
>>>> I'm trying to resolve an intermittent frustrating problem with and Enphase 
>>>> IQ system. There are three AC Branch circuits of 9 microinverters each 
>>>> coming into an Enphase AC combiner. 
>>>> 
>>>> What has been happening is one of the BR220 branch circuit breakers and 
>>>> the combine CH240 breaker in the main backfed load center have been 
>>>> tripping simultaneously. It has happened about four times in the last 6 
>>>> months. It was always the same branch circuit breaker, so we kept 
>>>> investigating that string, checking the junction box, trunk cable, and 
>>>> cap, etc. Finally we swapped out the BR220 breaker. 
>>>> 
>>>> Fast forward 4 weeks, and we got another call. This time a different 
>>>> branch circuit breaker and the main breaker tripped simultaneously. We 
>>>> checked that branch circuit and could not find any fault. It seems 
>>>> unlikely that two branch circuit breakers would be faulty, so we have now 
>>>> switched out the CH240 main breaker in hopes that it is the culprit.  
>>>> 
>>>> I'm not totally confident in this resolution and I have my fingers 
>>>> crossed. If that doesn't work, does anyone have any suggestions on another 
>>>> diagnostic step? These intermittent problems are a major hassle. One 
>>>> thought I had was to switch to a supply side interconnection with a 
>>>> fusible disconnect. Maybe the intermittent fault would blow one of the two 
>>>> line fuses so at least I could narrow it down to which line the fault is 
>>>> on if there is in fact a fault.
>>>> 
>>>> I have experienced two other tripping breaker issues with Enphase systems 
>>>> in the past. Neither of them were systems I installed. One turned out to 
>>>> be branch circuits that were not properly paired up and landed on 
>>>> different breakers. Another time we had an inverter with an internal fault 
>>>> which eventually"blew up" with a loud popping noise and smoke billowing 
>>>> out of it. That happened after resetting a trip breaker multiple times. 
>>>> This case seems to be unrelated to those issues. I'm perplexed. 
>>>> 
>>>> Jason Szumlanski
>>>> Florida Solar Design Group
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to