Icynene foam perhaps, is now sold by Huntsman. There are a number of formulations but they are all a foamed plastic. According to the ICC ESR-1826, https://huntsmanbuildingsolutions.com/en-US/sites/en_us/files/2023-02/ESR-1826.pdf, all of the Huntsman Icynene product line has to be covered or encased within an assembly to have any kind of fire resistance rating.
Plastic foams burn pretty well, with a bunch of bad smoke to, so it is surprising you were unable to see that. Perhaps your sample had been coated with the required coatings listed in the ICC ESR-1826. The only foam I’ve seen that does not burn was a Phenolic foam panel. That is the foam that acid rotted out umpteen commercial building steel roofs because the water it absorbs becomes a super low Ph, like 2 or 3. If you run into a vendor of this, for example sold as HVAC duct panels, cut some small samples. Put one in a jar of water. In months it will gradually sink and the water ph will be 2 or 3. You will not be able to get a sample of this to burn using any practical means. It is surprising one sees these foamed plastics used exposed or hardly encased in an assembly in building construction even after we see numerous media coverages of high-rises quickly going up in smokey flames like dried out Christmas trees. > On Oct 2, 2023, at 5:53 AM, <[email protected]> > <[email protected]> wrote: > > I did that once when I was told , I think isonene or something or other would > not burn that was used in this application. > > It di dnot. I tried really hard too. > > R/ > Matt > > Please rate our customer service > <https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication> > > Matthew J. Willis, CWBSP, CET > Engineering Manager – Southwest Region > FERGUSON FIRE DESIGN, LLC > A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC > 3508 Hwy. 557 > West Monroe, LA. 71292 > C: 307-236-8249 > [email protected] <mailto:[email protected]> > www.FergusonFire.com <http://www.fergusonfire.com/> > > > From: AKS-Gmail-IMAP <[email protected] <mailto:[email protected]>> > Sent: Sunday, October 1, 2023 2:09 PM > To: Discussion list on issues relating to automatic fire sprinklers > <[email protected] > <mailto:[email protected]>> > Subject: [Sprinklerforum] Re: Spray Foam Insulation > > While you are at it, cut off about a 1” cube of the foam. Skewer that cube on > a wire and put a match to it all within a controlled, well ventilated, > non-combustible environment nowhere near the job site. Film the event with > your phone. You may be wanting to show it. > > Allan Seidel > St. Louis, MO > > > On Sep 28, 2023, at 4:54 PM, Brian Harris <[email protected] > <mailto:[email protected]>> wrote: > > Ken- > Thanks and will do. > > Sent from my iPhone > > > On Sep 28, 2023, at 5:31 PM, Ken Wagoner <[email protected] > <mailto:[email protected]>> wrote: > > And I will be very interested to find what "code" they're referring to. > > I submit that if one is to consider the spray foam insulation as unobstructed > as defined by -13, then the deflector position relative to the bottom level > of the foam is required to be between 1" and 12" per 10.2.6.1.1 ('22 > edition). > > If the bottom of the insulation is to be considered as obstructed, or the > foam is between members which are obstructed, then the deflector must be 1" > to 6" below the member, but no greater than 22" down from the ceiling/roof > deck above, per 10.2.6.1.2 ('22 again). > > I can't wait to learn the rationale behind such a requirement. > > In short, remember my oft repeated mantra, whenever someone pops up with > something like this: Prove it. > > keep the forum informed, ok? > Ken Wagoner, SET > Parsley Consulting > 500 West Mechanic Street > Harrisonville, Missouri 64701-2235 > Phone: (760) 745-6181 > Visit the website > <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1> > On 9/28/2023 2:12 PM, Brian Harris wrote: > The AHJ is supposed to be providing the “code” where this came from. Should > be interesting. > > Brian Harris, CET > BVS Systems Inc. > bvssytemsinc.com <http://bvssystemsinc.com/> > > > From: Eric Rieve <[email protected]> <mailto:[email protected]> > Sent: Thursday, September 28, 2023 2:54 PM > To: Discussion list on issues relating to automatic fire sprinklers > <[email protected]> > <mailto:[email protected]> > Subject: [Sprinklerforum] Re: Spray Foam Insulation > > Funny enough I was told the same a few years ago. His reasoning was that the > uneven nature of the foam application could cause obstructions that weren’t > readily apparent so extra clearance was warranted. > > From: Brian Harris <[email protected] > <mailto:[email protected]>> > Sent: Thursday, September 28, 2023 2:48 PM > To: [email protected] > <mailto:[email protected]> > Subject: [Sprinklerforum] Spray Foam Insulation > > Anybody ever have an AHJ say you need 4” clearance from the bottom of spray > insulation to the deflector? > > Brian Harris, CET > BVS Systems Inc. > bvssystemsinc.com > <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,wo5wYVtpGosaBntgPq_5rudqm8ADj3XpDv10H3ACDcs2pNvWgifdhkbEDh5cNdO54rGdJmuywOvI-uxu4wi0CjpghGrXuaIGLLlPSAjRPh_ujRUBa-eEnA,,&typo=1> > Phone: 704.896.9989 > Fax: 704.896.1935 > > > > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > <https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org> > To unsubscribe send an email to [email protected] > <mailto:[email protected]> > > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > <https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org> > To unsubscribe send an email to [email protected] > <mailto:[email protected]> > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > <https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org> > To unsubscribe send an email to [email protected] > <mailto:[email protected]> > > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > <https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org> > To unsubscribe send an email to [email protected] > <mailto:[email protected]>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]