Ken-
Thanks and will do.

Sent from my iPhone

On Sep 28, 2023, at 5:31 PM, Ken Wagoner <[email protected]> wrote:

 And I will be very interested to find what "code" they're referring to.

I submit that if one is to consider the spray foam insulation as unobstructed 
as defined by -13, then the deflector position relative to the bottom level of 
the foam is required to be between 1" and 12" per 10.2.6.1.1 ('22 edition).

If the bottom of the insulation is to be considered as obstructed, or the foam 
is between members which are obstructed, then the deflector must be 1" to 6" 
below the member, but no greater than 22" down from the ceiling/roof deck 
above, per 10.2.6.1.2 ('22 again).

I can't wait to learn the rationale behind such a requirement.

In short, remember my oft repeated mantra, whenever someone pops up with 
something like this:  Prove it.

keep the forum informed, ok?
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>
On 9/28/2023 2:12 PM, Brian Harris wrote:
The AHJ is supposed to be providing the “code” where this came from. Should be 
interesting.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Eric Rieve <[email protected]><mailto:[email protected]>
Sent: Thursday, September 28, 2023 2:54 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]><mailto:[email protected]>
Subject: [Sprinklerforum] Re: Spray Foam Insulation

Funny enough I was told the same a few years ago. His reasoning was that the 
uneven nature of the foam application could cause obstructions that weren’t 
readily apparent so extra clearance was warranted.

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Thursday, September 28, 2023 2:48 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Spray Foam Insulation

Anybody ever have an AHJ say you need 4” clearance from the bottom of spray 
insulation to the deflector?

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,wo5wYVtpGosaBntgPq_5rudqm8ADj3XpDv10H3ACDcs2pNvWgifdhkbEDh5cNdO54rGdJmuywOvI-uxu4wi0CjpghGrXuaIGLLlPSAjRPh_ujRUBa-eEnA,,&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935





_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to