Are they referring to the exposed barrel length for dry heads in freezers?


Craig D. Hanson, CFPS
Fire Division Manager
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
*C:* 253.225.9977 | *E:* [email protected] | www.WC-3.com
<https://www.wc-3.com/>
*Teaming With Your Community to Make a Difference*


On Thu, Sep 28, 2023 at 3:56 PM Brian Harris <[email protected]>
wrote:

> Ken-
> Thanks and will do.
>
> Sent from my iPhone
>
> On Sep 28, 2023, at 5:31 PM, Ken Wagoner <[email protected]>
> wrote:
>
>  And I will be very interested to find what "code" they're referring to.
>
> I submit that if one is to consider the spray foam insulation as
> unobstructed as defined by -13, then the deflector position relative to the
> bottom level of the foam is required to be between 1" and 12" per
> 10.2.6.1.1 ('22 edition).
>
> If the bottom of the insulation is to be considered as obstructed, or the
> foam is between members which are obstructed, then the deflector must be 1"
> to 6" below the member, but no greater than 22" down from the ceiling/roof
> deck above, per 10.2.6.1.2 ('22 again).
>
> I can't wait to learn the rationale behind such a requirement.
>
> In short, remember my oft repeated mantra, whenever someone pops up with
> something like this:  Prove it.
>
> keep the forum informed, ok?
> *Ken Wagoner, SET*
>
>
> *Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri
> 64701-2235*
> *Phone: (760) 745-6181 *
> *Visit the website
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
> On 9/28/2023 2:12 PM, Brian Harris wrote:
>
> The AHJ is supposed to be providing the “code” where this came from.
> Should be interesting.
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssytemsinc.com <http://bvssystemsinc.com/>
>
>
>
>
>
> *From:* Eric Rieve <[email protected]> <[email protected]>
> *Sent:* Thursday, September 28, 2023 2:54 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers
> <[email protected]>
> <[email protected]>
> *Subject:* [Sprinklerforum] Re: Spray Foam Insulation
>
>
>
> Funny enough I was told the same a few years ago. His reasoning was that
> the uneven nature of the foam application could cause obstructions that
> weren’t readily apparent so extra clearance was warranted.
>
>
>
> *From:* Brian Harris <[email protected]>
> *Sent:* Thursday, September 28, 2023 2:48 PM
> *To:* [email protected]
> *Subject:* [Sprinklerforum] Spray Foam Insulation
>
>
>
> Anybody ever have an AHJ say you need 4” clearance from the bottom of
> spray insulation to the deflector?
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssystemsinc.com
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,wo5wYVtpGosaBntgPq_5rudqm8ADj3XpDv10H3ACDcs2pNvWgifdhkbEDh5cNdO54rGdJmuywOvI-uxu4wi0CjpghGrXuaIGLLlPSAjRPh_ujRUBa-eEnA,,&typo=1>
>
> Phone: 704.896.9989
>
> Fax: 704.896.1935
>
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing 
> list:https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]