These aren’t really “designed”. You select one based on the required/desired flow and discharge throw (hose stream distance) you need to deal with the specific hazard.
To include one in a hydraulic calculation you would use an Equivalent K-factor for the monitor. Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | [email protected]<mailto:[email protected]> | www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$> 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS From: Luis Perea <[email protected]> Sent: Thursday, February 29, 2024 5:24 PM To: 'Discussion list on issues relating to automatic fire sprinklers' <[email protected]> Subject: [EXTERNAL] [Sprinklerforum] Monitors Good evening, I have a question for the group. Do you know if there is a chapter (NFPA) or data sheet (FM) to use as guidance to design / calculate Fire protection Monitors? [cid:[email protected]] Thank You ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.