My first experience with gels was bad enough to make me swear off them and that
was 18 years ago. I am sure they have I improved but most of my work is off
grid and flooded work best in that use.
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re
I ran it and it seemed fine but 30 days into the install it is making a
frying type sound and the generator is behaving strangely.
Any ideas?
Thanks,
Bob Ellison
_
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1136 / Virus Database: 422/3212 - Release
hey bought a huge generator instead !
Sent from my iPod
Bob Ellison
On Nov 3, 2010, at 12:51 AM, William Miller
wrote:
Friends:
Speaking of life expectancy, has anyone had experience with SW
inverters in a coastal environment?
William Miller
__
I have a customer who wants to grid tie a 120 volt dc system
Does anyone know of an inverter that can do this?
Thanks
Bob ellison
>
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & setting
Mick,
I am afraid that is what he wants to do, I am also getting the impression
that his power bill is just a few bucks so I don't see a need. He does.
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
send it to the grid.
I am supposed to meet him tomorrow and hope to have more info afterwards.
Thanks,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Peter
Parrish
Sent: Monday, November 15, 2010 8:38 PM
To
ehalf Of Glenn Burt
> Sent: Monday, November 15, 2010 5:29 PM
> To: 'RE-wrenches'
> Subject: Re: [RE-wrenches] 120 volt grid tie inverter
>
> I think there is still an SMA 700W inverter available that
> uses 120VAC.
> -Glenn
>
> -Original Message-
> From: r
upper limit is about 6' but I am unsure on the lower limit.
Any ideas?
Thanks,
Bob Ellison
_
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1170 / Virus Database: 426/3281 - Release Date: 11/26/10
___
List
18 years ago I did things differently than I do it now but when you consider
these have to last 30 + years I am more comfortable with the wires protected
by conduit.
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.or
look as good on the wall either.
Want to speed up battery charging add more inverter / chargers. You could
probably add 2- 4024 Magnums as well as the SW to that large a battery bank
and be fine, but you would want to balance that one..
Later,
Bob Ellison
From: re-wrenches-boun
With the amount of lead in a battery bank it changes temperature very
slowly. Both gaining and losing heat is a very slow process.
I have never insulated battery banks, if in a cold area like here we size
them larger for the slower reaction time in the winter anyway. Part of the
reason being that
is a problem or not seems to depend on the customers
attitude, but it can be annoying.
At least they are still made here, and the service is good!
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Beha
good inverters they just have these 2 warts that
really should be improved
Merry Christmas,
Bob ellison
Sent from my iPod
Bob Ellison
On Dec 24, 2010, at 11:00 AM, jay peltz wrote:
> Hi Bob,
>
> Thanks for the input.
>
> When you say "slow to recover from a voltage drop&
about 50% of
capacity. Sorry I do not have many examples of this. but I do not have any
contra indictating examples.
--- On Thu, 12/23/10, bob ellison wrote:
> From: bob ellison
> Subject: Re: [RE-wrenches] Component Choices for MY RV - Apollo Solar?
> To: "'RE-wrenches&
>From memory it seems that the max voltage listed in the manual for the Sun
>Saver MPPT is 35 volts but I don’t have it handy.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Starlight
Solar, Larry Crutche
night was -32 F. They use a propane wall heater to keep the temp in the 40's
to 50's or better sometimes and starting is not a problem. It's just one of
the costs of a generator in a cold area.
More of my .02 worth!
Later,
Bob Ellison
From: re-wrenches-boun...@l
If they are too tight this can happen also. I have asked my battery
distributor about torques in the past with no definite answers.
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nathan Jones
e web sites.
Thanks,
Bob Ellison
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wre
t or you get to add
the custom epoxy to the plastic handle to stop the leaks...
Just my .02 worth.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Joel
Davidson
Sent: Saturday, April 02, 2011 11:59 AM
To: RE-w
r. You can almost use it as a fan!
Good night,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Monday, April 04, 2011 11:06 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Slow clocks
Todd:
I gues
I have been using buss bars for 12 years or so and about 8 years ago started
to add a class T fuse to the connection at each buss bar in most systems.
I have seen thermal runaway hit the industrial batteries I service.
It would be best to avoid it in a battery box if at all possible.
Do a
I believe Roy has a customer with a huge battery bank that air conditioned
the battery room. He ran the numbers and the air conditioning actually made
sense.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of R Ray
Are they Ni-cad or could they be Ni-Fe (nickel iron)
My understanding is that the Edison cells are nickel iron, but I could be
wrong.
Ni-cad's are very toxic, and a disposal problem.
ni-fe is based on a alkaline (lye) electrolyte and easy to render harmless.
Bob Ellison
Fro
¾ fire rated dry wall!
Yep, that helps.
Just thought I would add this to the list, because they are out there.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Saturday, May 07, 2011 7:26 PM
To
you on the roof and alive
long enough to finish the job.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Darryl
Thayer
Sent: Sunday, May 08, 2011 1:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Working on m
ectly together, when possible.
I like this, mind if I "liberate" it?
"Sent from a 'smart' phone, with tiny keys. Please excuse shortcuts and
typos."
Thanks,
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wr
that road. If you
cut it off is there enough room to get a nut and lock washer on the
remaining stud?
Overall the easy cure is probably replacement, anything else is iffy. But if
it works it saves you the cost of a battery.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
This will make it interesting to everybody with a grid tie inverter, can we
open up the specs to let them work with the "new test variation"? The other
option is that the inverters will spend a lot more time off line.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
://www.ussolarmounts.us/index.html
Just so you could check it out,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Loesch
Sent: Saturday, June 25, 2011 7:28 AM
To: RE-wrenches
Subject: [RE-wrenches] Wire
the
recalibration business until they get it repaired.
The recalibration is free, the parts you will pay for. Not a bad deal all
things considered.
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of The
.
www.hardydiesel.com
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of mac Lewis
Sent: Thursday, July 28, 2011 8:44 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Recommendations for a good diesel
The only choice is metal, or maybe tile.
Use a water dump arrangement to get the first flow to catch the dirt off the
roof that is in the first flow.
You're on an island so salt is a consideration also, as you know that gets
everywhere.
It's a lot easier to put panels on a metal roof than on til
s not bothered by a breaker, open or closed.
Just my .02 worth,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Rich Nicol
Sent: Tuesday, September 13, 2011 6:17 AM
To: 'RE-wrenches'
Subject: [RE-wrenches
circuit and it
fails nothing good will happen.
Best to be on the safe side.
Later,
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse Dahl
Sent: Tuesday, September 27, 2011 11:11 PM
To: RE-wrenches
ust a quick thought stream,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Eric Thomas
Sent: Sunday, October 02, 2011 12:15 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Invert first?
Wrenches
ed to hate the bleeding edge!
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink
Sent: Sunday, October 02, 2011 1:37 PM
To: penobscotso...@midmaine.com
Cc: RE-wrenches
Subject: Re: [R
Peter,
Is this for use outside on terrain (like at a job site getting supplies to a
roof) or inside on a concrete floor? It makes a difference on the tires and
suspension as well as the rating.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
several hours, depending on the battery bank size.
Charging it to 25.4 is nothing in the long run.
Give them a LONG full charge, what are the inverters? Does it ever get an EQ
charge?
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org
I HAD one installed and the inspector would not let me use an inline fuse
(seems like it was a 1 amp) so we had to run it from a breaker and it locked
up and let the smoke out of it.
Just another experience,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re
Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>
On 10/20/2011 4:09 PM, bob ellison w
from
hitting the bare wire ends, not from keeping them from coming apart.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Friday, October 21, 2011 7:32 PM
To: RE-wrenches
Subject: Re: [RE-wre
I downloaded the spec sheets on the DC generator, it's either LP or natural
gas. Also it's regulated to 26 volts or 52 volts, so it's about useless to
charge batteries in an off grid system, unless you just need to feed power
to the battery bank.
Bob Ellison
From: re-wrenches-b
ob O's units to use.
As usual just my .02 worth.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of R Ray
Walters
Sent: Monday, October 24, 2011 10:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Cummins DC gen
What are you running for combiner boxes and wire to run at 1000 volts?
Seems that I remember that fuses are only good for 600 volts and most boxes the
same limit?
What are you using?
Just wondering,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
If you need a charger capability, look at the magnum MMS1012. Up to a 50 amp
charger and it's a sinewave, don't bother with the modifieds. Sleep mode can
go down to 5 watts I think.
The Morningstar mppt is a good small controller that works well
Later,
Bob
From: re-wrenches-boun...@lists.re
experience than I
have.
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allen
Frishman
Sent: Tuesday, December 06, 2011 3:30 AM
To: RE-wrenches
Subject: [RE-wrenches] GEC and EGC Advice
Fellow Wrenchers,
I
Hi Allan,
I have several part reels of 4 twisted pair Belden that I use for e meters.
It is shielded, static line, direct burial and all the good stuff.
Always best run alone to keep the signal from getting scrambled but it you
usually run it together, so be it..
Let me know,
Bob
__
Anybody storing fuel wants to be filling the tanks and treating them NOW, it
will probably not be this low in the fall.
It is nice to pick up the chain saw, mower or tiller and have it start with no
major headaches after a year layover!
Just from my testing and experience,
Bob Ellison
Does anyone have the wiring diagram for the Trace SW4024 relay with the 2
level terminal block as opposed to the direct relay connections?
We can't find any manuals that don't show the relays.
Thanks,
Bob
___
List sponsored by Home Power magazine
Have you tried "Quick Cable" I think you will need to vent and lock it
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Yago
Sent: Thursday, December 29, 2011 11:53 PM
To:
Mount a BRUSHLESS fan inside the box blowing out into the pipe, do not
pressurize the box, that will blow gasses into the room, it is bound to
leak. Use screened vents to keep out the critters.
I use a Carlon 6x6x4 box to mount the fan and vent, also don't mount the
relay if you use one, in the bat
I would suggest the best gear for the situation and just refuse to use the
substandard stuff, if you can. It’s not worth a fire or worse.
I have lost jobs for not letting the customer spec gear for me, I get over it.
I either do it right or not at all.
Later,
Bob Ellison
From: re
de of the box.
Happy New Year,
Bob Ellison
Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Richard L
Ratico
Sent: Saturday, December 31, 2011 2:47 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] ba
ut it gets corroded at some point, and I hate
cleaning 1 terminal or 20!
Later,
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry
Crutcher, Starlight Solar Power Systems
Sent: Thursday,
5 Honda engines with propane
conversions.
There are companies that do the conversions and just handle the warranty on
their own.
Just another opinion,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Sent
dead short.
Needless to say things did not go well after that.
The factory has sent me all the manuals, the engine manual is great but the
problem is the alternator and the manufacturer has nothing on it, not a
thing.
Thanks,
Bob Ellison
combine heat output and power in houses.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Sent: Tuesday, January 17, 2012 9:19 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Request for Gennie
Am I safe to assume you are looking for buss bars to connect the batteries?
I get the copper stock and custom drill them to match the install.
If you are connecting the batteries together use good heat shrink (glue
filled) between the connections.
Bob Ellison
-Original Message-
From: re
It only looks like a higher current, the actual power into the bank is the
same.
100 amps @ 12 volt is the same as 50 amps @ 24 volts and 25 amps @ 48 volts.
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org
The XL-1 problem is cured with the Classic.
Bob
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of R Ray
Walters
Sent: Tuesday, January 17, 2012 1:38 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 24 vs. 48
Th
Is the wear all on 1 brush or are both wearing the same?
Are the slip rings smooth as glass?
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of mac Lewis
Sent: Tuesday, January 17, 2012 3:51 PM
To: RE
I would think that locating a CO detector on the ceiling of the room with
the battery bank would be enough to do it. You just would not know if it was
the battery bank or CO from another source. Your (or their) nose can do that
part of the job!
Bob Ellison
From: re-wrenches-boun
s, it says something.
I see no reason that the customers would suddenly change their maintenance
habits after years of doing it right!
This also happened with a replacement set that I had.
I have to blame the batteries,
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wre
Try Deluth Trading, they have rated "cheater" safety sun glasses if you need
a boost. For those unfamiliar they are glasses like readers for those of us
whose eyes are not what they were 20 - 30 years ago. They even have a "fat
head" version!
http://www.duluthtrading.com/search/searchresults/sites
top. The
factory insisted on returning the entire cases to the factory to replace the
cell instead of sending a couple cells and having me replace them.
This is the closest that I have seen a bank to catching fine in 20+ years of
doing this type of stuff….
Bob Ellison
From: re
r pressure tank to keep the pump from
frequently cycling and all seems to go well.
We are lucky in this area that we don't generally have to go real deep to
get water.
The SW series are still rebuild able, last fall we had to have 2 redone.
Later,
Bob Ellison
From: re-wrenches-b
I have used tool bags from Sears for years, graduating to bigger each time.
At the present time I have switched to the one with the rubber bottom, it's
big and will not soak up moisture when it gets set in a puddle or whatever.
Bob
-Original Message-
From: re-wrenches-boun...@lists.re-wre
Are you still selling the short towers? I guess that's answered..
That hurts small wind as much as the bozo installers.
Just my .02 worth,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ross Taylor
Sent: F
y of the original Edison Cells still
out there.
Later,
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Tom Duffy
Sent: Sunday, May 06, 2012 7:54 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Nick
t the MPPT controllers that
exist now.
Later,
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Exeltech
Sent: Monday, May 07, 2012 11:19 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Nickel
I have a supplier looking for a "Wrench" in the Hammonton, NJ. area for a
grid connect system.
If someone on the list is in that area please reply off list and I will pass
the info on to him.
Thanks,
Bob Ellison
___
List sponsored by
It might matter if they are high capacity batteries, some run a stronger
electrolyte to get more out of the batteries, this results in a lower cycle
life. Ie: 350 cycle life v/s 400 cycles. I have seen factory cells that are
fully charged at 1.315 - 1.325
To give them an EQ charge they have to
out there, it's just
not accurate and done by the anti wind folks.
Hope this helps,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Sent: Thursday, June 21, 2012 6:18 PM
To: RE-wrenches
Subject: [RE-wre
Go to www.hialeahmeter.com they have all the diagrams on the web site.
Good day,
Bob Ellison
http://www.google.com/url?sa=t&rct=j&q=hialeigh%20meter&source=web&cd=1&ved=
0CGkQFjAA&url=http%3A%2F%2Fwww.hialeahmeter.com%2F&ei=J3zoT521C4fy0gHVxa3XCQ
&usg=AF
just got done with a 2250 mile drive in
2 days and my mind is mush.
I can list more but the mind is just not up to it, between the miles and 106
degree temps I'm toast!
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists
.
Jeff
Jeff Wongstrom
NABCEP Certified
406.291.3416
Check out the new website:
www.thirstylakesolar.com
On Jul 1, 2012, at 3:29 PM, bob ellison wrote:
I will put on my flame suit and just say that Trojan seem to outlive the
batteries listed below.
With all things t
Been there on 2 occasions, the pumps may seem like small loads but there are
usually many of them that (at least in this area) add up to a heck of a load
for anything but a huge off grid system.
Don't worry the problems that result will all be the power systems and/or
the system installers fault.
that you do not need to
charge it occasionally.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink
Sent: Saturday, July 07, 2012 2:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Magnum Energy Remote Control
I haven't done it but why can't you use a standard lighting photocell to
turn on the inverter? There really is no current involved so the load
shouldn't be a problem.
I am assuming that you just want to turn on a light?
Just a thought,
Bob Ellison
From: re-wrenches-b
Try going to a starter and alternator shop, if you can get a guy with a
sense of humor he may be able to match up something close. Then hope it
doesn't leak after you sink it again.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lis
How do I contact "Flight Systems" I have a customer with a blown board from
a Hardy he would like to get rebuilt.
Thanks,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Mason
Sent: Thursday, Augus
inverter to get
gen power.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Mason
Sent: Saturday, August 18, 2012 7:26 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Heart Interface Inverter
For what it's
Look at the video on Midnite Solar's site, You will never use Deltas again.
Anyone want a deal on a bunch of LA302's?
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Will White
Sent: Monday, August 20,
I wire them thru bus bars now, but in the past before I did that I used to move
them around occasionally.
Later,
Bob
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
d...@foxfire-energy.com
Sent: Friday, August 31, 2012 6:5
Are you correcting for the changes in SG with the temperature increase?
I used to be able to get hydrometers with a built in thermometer and chart
but no longer have one. It died as most do, with a crash and shattering
sound.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
If you cut them during the day, under sunlight conditions it can do bad things
to the wire cutters.
Been there before,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of john
Sent: Tuesday, September 18, 2012 1:43
Watch the Chinese ones, lots of problems there.
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Aaron
Mandelkorn
Sent: Tuesday, September 25, 2012 4:52 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Ni-Fe batteries
as smoothly as possible, after 20+ years experimenting is
getting tiring.
Have a great day,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry
Crutcher, Starlight Solar Power Systems
Sent: Wednesday, September
an L-16 6 volt
Good day,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink
Sent: Monday, October 08, 2012 3:29 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trojan 2 volt L-16s
Tom, big cells are
I have had inverters ruined by drywall dust, it literally filled them within
a couple years as the owner worked on his house. Next thing I am getting a
call that it would not work..
I doubt that sawdust would be any different.
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re
positive plates. Those will weigh 90 - 100# for each cell.
Can send you more info if you want.
Got to run,
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Parrish,
Peter
Sent: Tuesday, November
ed to the opposite side of the battery bank might
help, unless you have them wired to buss bars or switch to 4.0 cables.
Just some random thoughts.
Merry Christmas everyone,
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lis
Not going to be doing it in Northern New York either!
The pump is broke and we will not get any sunshine until it is replaced!
We ARE that far back in the woods,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
Windseeker 500 rebladed
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeremy
Rodriguez- All Solar Inc.
Sent: Saturday, February 23, 2013 6:41 PM
Cc: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Fw: Anyone recognize th
They are still available in several configurations (hook up styles)
The DC 175/250 had a hold down strap instead of bolting to a panel.
Back to searching email.
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On
done that.
Later,
Bob Ellison
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of John Berdner
Sent: Wednesday, February 27, 2013 2:06 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC circuit breakers in parallel
Larry:
The
ise a good bulk charge to get by till the sun comes back would work
well.
If it has a taper charge from the factory t would take almost forever to
charge a large battery bank.
I do like the output, but probably will hate the price.
Later,
Bob Ellison
-Original Message-
From: re-wre
I can second the Morningstar SureSine, it just works! To bad it is not
available in 24 volts. I keep hoping.
Bob Ellison
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink
Sent: Wednesday, March 13
nding five labels laying on the bottom isn't pleasant!
Later,
Bob Ellison
Bob Ellison
On Jul 17, 2013, at 2:17 PM, David Brearley
wrote:
> I recently sat in on a free HellermannTyton webinar that included quite a bit
> of content related to solar labels:
>
> http://w
Would it be possible to make one if we had a sample to know the wire order?
Bob
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff
Clearwater, Village Power Design
Sent: Monday, March 30, 2009 6:05 PM
To
100 matches