The only way to do a capacity test is with a load bank over the rated discharge 
period of the batteries, it they have a 6 hour rate, use that one. The 20 hour 
rate takes too long! Voltage is a moving target and pretty much useless unless 
the battery has been sitting with no charge or discharge for 12 hours or so, 
and all that tells you is the state of charge nothing about the capacity of the 
battery.

 

If you are going to buy a load bank the old resistor load banks are the best 
choices, the newer electronic units are too sensitive to damage and the failure 
rate is quite high according to my suppliers. They have gone back to the 
resistor banks in most cases. The load banks can test up to a 48 volt bank at 
one time, so you don’t need to test each cell for 6 hours, you can spend 6 
hours and test them all at once! But your still going to spend 6 hours to do a 
correct test

 

My first experience with gels was bad enough to make me swear off them and that 
was 18 years ago. I am sure they have I improved but most of my work is off 
grid and flooded work best in that use.

 

Later,

Bob Ellison

 

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of North Texas 
Renewable Energy Inc
Sent: Monday, October 04, 2010 9:36 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery capacity testers

 

 

Todd

I've heard the same arguement, as well as its inverse. The battery choice was 
the decision of the system owner. I know they are more sensitive to 
charge/discharge abuse but I see the full charge rate last week at 52.xx V, 
just like day 1and I trust the Trimetric and the Sunny Islands. We're taking 
down the entire system to upgrade & install a 400A transfer switch so the 
batteries will have time to stabilize for the VOC check & cleaning. 

I guess a more accurate question would be is it good enough to properly check 
cell VOC and not bother with the discharge capacity check? A compromise could 
be cap check 12V blocks of cells instead of all 24 separately. Or is the 
capacity checker a waste of money.

Jim

 

 

 

 ----Original Message-----
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org]on Behalf Of 
toddc...@finestplanet.com
Sent: Monday, October 04, 2010 2:23 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Battery capacity testers

I know many on this list disagree, but this sounds SO typical for sealed 
batteries. It is why I never use em... never! If they are 5 years old, you are 
probably at the limit of their life. Replace em with flooded lead calciums and 
your customers (and you) will be happy for 20+ years.

my .o2

Todd



On Sunday, October 3, 2010 9:28pm, "North Texas Renewable Energy Inc" 
<nt...@1scom.net> said:

I have a customer with a set of 24 Concord PVX-6480s that have twice failed 
during grid outages during the night. No large loads are on the critical load 
panel and, since it's at night when they drop to 50% dod, I'm not sure what's 
up with them. I plan on cleaning and retightning all the cable connections 
first to eliminate that possibility then checking VOC of each cell. 

Eventually we'll install a 25 kW genset but my first task is to find out the 
state of the batterys. The system turns five next spring so I don't think they 
are near an early death. The BOS is 2 Sunny Island 4248s with upgraded chipsets 
and the charger is set to spec though that may need to be bumped up. The only 
culprit I suspect is the high summer temperatures in this unconditioned 
equipment room. 

Finally it may be time to invest in a capacity tester. What brand is popular 
among those Wrenches with lots of experience in diagnosing a batterys health? 
The Concord DC5000 only comes in 12 & 24 V models and these are 2V cells. 

Thanks as always

 

Jim Duncan

North Texas Renewable Energy

486 W.N. Woody Road

Azle Texas 76020

NABCEP Certified Solar PV

Installer No.31310-57

TECL 27398

nt...@1scom.net 

817.917.0527

www.ntrei.com <http://www.ntrei.com/> 

 




Sent from Finest Planet WebMail.

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to