[RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
Greetings Esteemed Wrenches: I've just heard back from our inspector here in Colorado, and we are still being required to disconnect the batteries under 690.12. No where in 690.12 are batteries mentioned, nor in the appropriate 690.71 section that deals with batteries. The entire reasoning b

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
ge systems (Article 706) will have their own requirements in time--that is guaranteed. Bill. -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters Sent: Tuesday, March 15, 2016 9:02 AM To: RE-wrenches Subject: [RE-wrenches] Rapid

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
ists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Ray Walters Sent: Tuesday, March 15, 2016 9:02 AM To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>> Subject: [RE-wrenches] Rapid Shutdown Greetings Esteemed Wrenches:

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
nal Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Ray Walters Sent: Tuesday, March 15, 2016 9:02 AM To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>> Subje

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
trip breaker as part of their ebox that works with the birdhouse I've used one in the past Is it not ul listed That's all from me Pat Patrick A. Shortell Licensed Master Electrician Certified Solar Installer 71 Oregon Street Long Beach N.Y. 11561 Www.thesolarstorehouse.com <http://ww

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
-that is guaranteed. Bill. -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Ray Walters Sent: Tuesday, March 15, 2016 9:02 AM T

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Ray Walters
cian Solar Design Engineer 303 505-8760 On 3/15/2016 8:04 PM, b...@midnitesolar.com wrote: On 3/15/2016 5:23 PM, Ray Walters wrote: Hi Brad; I think that remotely tripping the inverter might work with Outback, but definitely not with Magnum. (I checked with them today) Also, if the battery cable

Re: [RE-wrenches] DC to DC converters

2016-03-28 Thread Ray Walters
What about building a 30 vdc system (5 x 6v batteries in series) and adjust the settings on a Midnite Classic to work with that? How tight does the 30 vdc output need to be? On inverters, I've had trouble with the Suresine, basically not working with GFCI outlets. I keep trying different mod

Re: [RE-wrenches] Specific AC Coupling question

2016-04-04 Thread Ray Walters
Also worth looking at Magnum's new AC diversion load system. It does the frequency shifting but also 4 kw dump load that can be set up to any AC electric load. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 4/4

Re: [RE-wrenches] small inverters

2016-04-20 Thread Ray Walters
Hi Wayne; Which GFCI outlets do you use? We've had trouble with random tripping with the Morningstar. I switched outlet models, thought I fixed it, but its tripping again. Morningstar's list of approved GFCIs is outdated. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Lic

Re: [RE-wrenches] Does a Netral COunt as a CCC

2016-04-21 Thread Ray Walters
Also look at the notes to the tables in Chapter 9. For conduit fill, all wires are counted. 310.15 covers ampacity derating for more than 3 current carrying conductors in the raceway. The key is "current carrying conductors". The neutral definitely carries current. You don't have to count g

Re: [RE-wrenches] Battery charging problems

2016-04-21 Thread Ray Walters
That doesn't make sense, the inverter's charger determines the max charge rate and the max draw from the generator. The 8.5 kW Kohler should have no problem running the 4.4 kW Magnum. What is the altitude? Is it wired for 240 vac ? If the generator is running at 120 vac, then you are only r

Re: [RE-wrenches] Does a Neutral Count as a CCC

2016-04-24 Thread Ray Walters
However, in this case, Peter's installing lots of 120 vac branch circuits, so all of those neutrals will be carrying full current (unless they are shared neutral circuits). Mike Holt's exception would apply to 240vac circuits if they had a neutral. Further, Holt's exception would not be appli

Re: [RE-wrenches] Off-grid generator update?

2016-04-28 Thread Ray Walters
FYI, generally we haven't had cold start issues with propane units, as long as the pipe is sized properly ( as mentioned in another recent post) and the starter battery is kept fully charged. This is based on about 20 years experience in the Rockies with temps below 0, but not 40 below. We don

Re: [RE-wrenches] Off-grid generator update?

2016-04-28 Thread Ray Walters
ttery charging needs to be added foroff grid Jerry Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone Original message ---- From: Ray Walters Date:04/28/2016 7:28 AM (GMT-10:00) To: RE-wrenches Subject: Re: [RE-wrenches] Off-grid generator update? FYI, generally w

Re: [RE-wrenches] Outback programing question

2016-04-29 Thread Ray Walters
What's wrong with the chargers being on? Just set the charge settings (absorb 56 v, and absorb time 5 minutes) fairly low. It will lightly charge for a few minutes, and then go to float. Just because your customer imagines this to be a problem, doesn't mean it actually is. Its not going to hur

Re: [RE-wrenches] Outback programing question

2016-04-29 Thread Ray Walters
n’t want and I agree to have an additional cycle on the batteries when they don’t need it. I’m working with OB to find out why this is happening. Thanks jay peltz power On Apr 29, 2016, at 11:07 AM, Ray Walters wrote: What's wrong with the chargers being on? Just set the charge se

[RE-wrenches] Backup System Blues

2016-06-15 Thread Ray Walters
Hi All; I'm in the process of finishing a grid tie with battery backup system, and besides the many pitfalls of this type of work, I destroyed a Tripp lite surge suppressor when I turned on the system. The system has a pair of the new Outback VFXR 3524 inverters wired in 120/240 series config.

Re: [RE-wrenches] Enphase Support Non-Responsive

2016-08-05 Thread Ray Walters
Could you tell us about the metal conduit vs. Romex installation differences between the Enphase and SolarEdge? Thanks, R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 8/5/2016 11:54 AM, penobscotso...@midmaine.c

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-09 Thread Ray Walters
I think the issue has always been locating the right parts, not the installation. Everyone carries the Cobra X flex, but not the ferrules. We usually crimp lugs on and use breakers with stud terminals, so the need for ferrules is minimal. I have always wondered about the terminal bussbars from

Re: [RE-wrenches] Pass through/transition box for Enphase

2016-08-11 Thread Ray Walters
So this may be a dumb question, but I'm assuming wire nuts are not suitable for Fine strand wire? I agree that most installs are not code compliant in this regard. Its really tough to find parts or even good info on this. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licens

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread Ray Walters
My guess is that in your case the GTPV will just help alleviate the volt drop situation. I wouldn't start adding transformers, etc until you are having a problem. Put in the contract that this extra cost may be necessary for proper function, but I would keep it as a backup. Based on the numb

Re: [RE-wrenches] Battery issue

2016-08-24 Thread Ray Walters
Trojan L 16s have a known issue with premature cell failures. The T105s seem to still be fine, but I won't sell the L16 anymore. SG readings don't even matter when you have an obvious cell failure. Its like doing blood work on a corpse. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Ins

Re: [RE-wrenches] Tracker controller service?

2016-08-31 Thread Ray Walters
My old trick for Wattsun trackers was just to turn them into fixed racks. Usually the tilt actuator could be hot wired with a 12 v battery to get summer and winter tilt. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-87

Re: [RE-wrenches] Test procedure for Concorde batteries

2016-09-01 Thread Ray Walters
Hi Gary; I think it would be a waste of time to load test a sealed battery that is 9 years old. Even at only 20% discharge, that battery only has 2800 cycles. At 80% discharge, its 550 cycles. The daily system cycle is probably roughly a 10% cycle, coupled with the frequent deep cycles. We

Re: [RE-wrenches] Wire nuts

2016-09-06 Thread Ray Walters
1) I've used the Euro connectors you show for decades with good results. Not necessarily legal here, but I like them 2) Before bad mouthing the wire nuts, I've found installer error to almost always be the problem. In the installation pictured, the wire nuts are not outdoor rated, and the

Re: [RE-wrenches] Splices in service panel

2016-09-08 Thread Ray Walters
Hi Mac; I'm not sure I understand how you would extend the wires without splicing. BTW you only need to extend the hots, not the neutrals or grounds. *NEC 312.8* sets a cross sectional area limit of 75% for the splices and wires inside an OCPD Enclosure. I just found these inline splices to us

Re: [RE-wrenches] Splices in service panel

2016-09-08 Thread Ray Walters
Hi Chris; Its the same as a switch leg for a light. The neutral stays at the light, only the hot is run down to the switch and back. Also, with some critical load panel set ups available (ie Generac), there is no provision to even run the neutrals to the new CLP. This is cleaner and involves m

Re: [RE-wrenches] Fluke 337

2016-09-13 Thread Ray Walters
HI Drake; My old Fluke clamp on died last year, and some good Wrench here turned me on to the Seaward solar power clamp. It does everything the Fluke did, and offers some amazing power analysis too. It can do real time power readings that even account for power factor. It can break out THD

Re: [RE-wrenches] Issue with DR1512 and oven

2016-09-19 Thread Ray Walters
Sounds like ovens have gotten more complicated over the years. As soon as I read "control board" and modified sine wave, I cringe. The good old DR inverters worked great, I even ran my own shop on one for several years back in the 90s. I for the most part quit selling them though, as even tho

Re: [RE-wrenches] Deep well submersible pump query

2016-10-05 Thread Ray Walters
Constant pressure pumps are a much better set up. The Grundfos SQE is a great example. Your well driller is right on target. However, expecting 10 gpm from a 600 ft deep well off grid is overkill. I would compromise on that flow rate. 5 gpm will be plenty of water in most cases, outside of w

Re: [RE-wrenches] PV Recombiner

2016-10-10 Thread Ray Walters
This thread actually brings up issues I've struggled with for years too. QOs are really not good for over 50 v. The panel mount QOUs are really expensive and special order. I believe they're only good to 125 vdc, so that not much help with higher voltage arrays. There are much better breakers

Re: [RE-wrenches] GSLC work-arounds

2016-10-11 Thread Ray Walters
Nice work William, thanks for posting all this info. That issue with mounting the Mate 3 is just ridiculous, I totally agree they need to make an adapter to interface with regular boxes. They can sell it separately. In the 90s it was understood we had to fab our own solutions, but at this p

[RE-wrenches] TIny House Pump

2016-10-28 Thread Ray Walters
Greetings Esteemed Wrenches: We have a tiny house project, and need to supply the pressure pump. My go to pump has been the Grundfos MQ series of constant pressure pumps. They have no start up surge, and don't require an external pressure switch or pressure tank. For small part time cabins,

Re: [RE-wrenches] TIny House Pump

2016-10-28 Thread Ray Walters
ll need a small pressure tank. jay peltz power On Oct 28, 2016, at 1:13 PM, Ray Walters wrote: Greetings Esteemed Wrenches: We have a tiny house project, and need to supply the pressure pump. My go to pump has been the Grundfos MQ series of constant pressure pumps. They have no start up s

Re: [RE-wrenches] 690.8

2016-11-10 Thread Ray Walters
The exception under 690.8(B)(1) definitely applies. All of Midnite' breakers and boxes are rated for 100% continuous operation. I believe, this does not apply to their touch safe fuse assemblies, however. Also FYI, you should be able to use the 90 deg C rating for complying with 110.14 (C)

Re: [RE-wrenches] Outback Programming Ghost

2016-11-10 Thread Ray Walters
It almost sounds like someone got in there and tried to reprogram stuff themselves. Have you installed the proper anti-Gremlin devices? R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 11/10/2016 12:34 PM, William

Re: [RE-wrenches] Outback Programming Ghost

2016-11-11 Thread Ray Walters
Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 11/10/2016 9:26 PM, William Miller wrote: Ray: I have no reason to believe anyone has been meddling. No one knows the password. It does look like some serious glitch. William On Nov 10, 2

Re: [RE-wrenches] Firmware, Firmware, Firmaware was Outback Programming Ghost

2016-11-12 Thread Ray Walters
ller *Sent:* Thursday, November 10, 2016 11:26 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Outback Programming Ghost Ray: I have no reason to believe anyone has been meddling. No one knows the password. It does look like some serious glitch. William On Nov 10, 2016, at 6:25 PM, Ray Walte

Re: [RE-wrenches] Ring Connectors

2016-11-14 Thread Ray Walters
Here's the lug you would use for the inverter and batteries https://www.delcity.net/store/Straight-Tinned-Copper-Lugs/p_810763.h_796015.t_1 It doesn't say here, but on the bag I got, it specifically is listed for fine strand cables too. I have 3 crimpers that I use: one like Allan's for the lar

Re: [RE-wrenches] Milwaukee M18 one key tools

2016-11-29 Thread Ray Walters
I believe that the reason they don't list actual torque values for drill settings is that they can vary quite a bit depending on the SOC of the battery, temperature, drill age, etc. If its a critical torque application, I would not depend on the drill settings, but instead do a final tightening

Re: [RE-wrenches] Milwaukee M18 one key tools

2016-11-29 Thread Ray Walters
I own the M18, and the power varies noticeably with discharge, and also with higher amp hour packs. My drill screams with a 5 AH pack! I agree its less of a drop with discharge than with lead acid or NiiCad, but its still enough to make torque settings inaccurate. R.Ray Walters CTO, Solarray

Re: [RE-wrenches] Milwaukee M18 one key tools

2016-11-30 Thread Ray Walters
stem I did, a third party was hired to audit the PV work. It was on the checklist to spot check torques. I have been spot-checking torque ever since. *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray Walters *Sent:* Tuesday, November 29, 2016 1:14 P

Re: [RE-wrenches] Retrofit variable speed drive to old well pump?

2016-12-11 Thread Ray Walters
Hey Dan; If this just problem just started, I'm with Drake, you could have a premature cell failure. I also agree with Allan, 2 wire pumps are certainly problematic on inverters. Many well service folks don't even install them because they don't last near as long as 3 wire pumps, so your cu

Re: [RE-wrenches] AC/DC in Same Trench?

2016-12-28 Thread Ray Walters
Also, you didn't specify, but AC and DC are specifically allowed in the same raceway per 300.3(C)(1). Only If the DC circuits are PV source or output circuits, then 690.31(B) prevails, which says they can't share a raceway. But again, as Chris mentions, this restriction does not apply to dire

Re: [RE-wrenches] Conext SW 4024 with bad firmware

2016-12-29 Thread Ray Walters
I've seen similar weirdness with many systems of various brands. The issue seems to be having the generator shutting down while still under load, with as you noted, the frequency and voltage dropping, and the inverter not transferring quick enough. Basically I suggest to my customers having si

[RE-wrenches] Solar World Wind Damage

2017-01-10 Thread Ray Walters
Greetings All; I just had the dreaded call from one of my higher profile commercial clients: a remote radio repeater station had modules ripped off the frame by high winds. Two SW285s were damaged. The wind was strong enough to rip right through the aluminum side rails. We had used the prop

Re: [RE-wrenches] Solar World Wind Damage

2017-01-10 Thread Ray Walters
Hi Daryl; I wonder if the DP&W rack is allowing some bending or torqueing of the module frame, that over time with thin aluminum causes metal fatigue, cracking, and finally total failure. Funny both of our isolated failures involved the same rack. Also, I did more sluething and these modu

Re: [RE-wrenches] Solar World Wind Damage

2017-01-10 Thread Ray Walters
ugs the ground is best. That is a lay opinion, however. William Lic 773985 millersolar.com 805-438-5600 -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters Sent: Tuesday, January 10, 2017 2:31 PM To: RE-wrenches Subject: [RE-wrenches

Re: [RE-wrenches] Solar World Wind Damage

2017-01-11 Thread Ray Walters
hat is a lay opinion, however. William Lic 773985 millersolar.com 805-438-5600 -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters Sent: Tuesday, January 10, 2017 2:31 PM To: RE-wrenches Subject: [RE-wrenches] Solar World Wind

Re: [RE-wrenches] Solar World Wind Damage

2017-01-12 Thread Ray Walters
ismontana.com <http://www.oasismontana.com> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray Walters *Sent:* Thursday, January 12, 2017 2:16 PM *To:* RE-wrenches *Cc:* Sefchick,

Re: [RE-wrenches] Solar World Wind Damage

2017-01-12 Thread Ray Walters
lto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray Walters *Sent:* Thursday, January 12, 2017 5:22 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Solar World Wind Damage Chris & Dana; Our site is a mountain in Wyoming and does have some focusing effects, so maybe 170 mph is po

Re: [RE-wrenches] Hidden corrosion caused catastrophic battery system failure

2017-01-21 Thread Ray Walters
HI Dave; Based on the evidence, I might suspect a short in the inverter, or the inverter was feeding a heavy load when the melt down occurred. I can't see how a short at the battery would cause an inverter failure, unless the melted lead caused the polarity to be reversed, or created a positi

Re: [RE-wrenches] Hidden corrosion caused catastrophic battery system failure

2017-01-21 Thread Ray Walters
When I'm evaluating an old system, one thing I do is really yank on all the battery connections. If it turns, tighten it down, and in several cases, the cable just pulls loose from the connector. They are time consuming to do right. Cable has to be stripped long enough, the crimper needs to

Re: [RE-wrenches] New Washer - Old Inverter

2017-02-08 Thread Ray Walters
117 vac is perfect output. If the washing machine is having issues, it would be with the stepped waveform, not the voltage. The old Trace had a pretty choppy "pure sine wave". I had washers not run on the Trace SWs, and we were able to put a capacitor on the inverter output that fixed the pr

Re: [RE-wrenches] Outback 2024 FX

2011-12-16 Thread Ray Walters
Let Ebay decide. I sold an old SW4024 on there recently. I got $1500 for it, so I'd guess the Outback might be worth $1100? Ray On 12/16/2011 3:38 PM, Drake wrote: A friend has a very early Outback 2024 FX that he is thinking about selling. It sat in the original box until last year. When

[RE-wrenches] Outback Breaker Problem

2011-12-16 Thread Ray Walters
apter that would let me use that type of breaker on the Flexware box? Ray Walters ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wr

Re: [RE-wrenches] Outback Breaker Problem

2011-12-17 Thread Ray Walters
e only way I work on them with larger wire is with the breaker mounted in the mounting plate and the mounting plate screwed in, then I bring the wire pre bent/unstressed to the post. Jay Peltz Power Sent from my iPad On Dec 16, 2011, at 9:14 PM, Ray Walters wrote: Hi Folks; Anybody else

Re: [RE-wrenches] Landing into a sub-panel without a main service panel, just a main switch

2011-12-22 Thread Ray Walters
n the load side and be code compliant. Ray Walters On 12/22/2011 11:34 AM, Pekka Laine wrote: All, We have been contracted to install a 10kW-ac system into a 45-year old house that has no main service breaker panel, only a 200A fused main switch (Zinsco). There are five 125 A rated

Re: [RE-wrenches] Landing into a sub-panel without a main service panel, just a main switch

2011-12-22 Thread Ray Walters
be 10,965W because the gross power rating as defined by FPL would be 9,971W. Jason Szumlanski Fafco Solar -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org> [mailto:re-wrenches-boun...@lists.re-wrenches.org <mai

[RE-wrenches] Fwd: Re: Landing into a sub-panel without a main service panel, just a main switch

2011-12-23 Thread Ray Walters
Original Message Subject: Re: [RE-wrenches] Landing into a sub-panel without a main service panel, just a main switch Date: Fri, 23 Dec 2011 09:41:24 -0700 From: Ray Walters To: JRQ HI Jeffrey; Electricity certainly can flow in both directions on a conductor

Re: [RE-wrenches] Fwd: Re: Landing into a sub-panel without a main service panel, just a main switch

2011-12-23 Thread Ray Walters
a statistical difference, I'm willing to concede the point. Jeffrey Quackenbush -------- *From:* Ray Walters *To:* RE-wrenches *Sent:* Friday, December 23, 2011 10:29 PM *Subject:* [RE-wrenches] Fwd: Re: Landing i

Re: [RE-wrenches] Outback Breaker Problem and looking towards 2012

2011-12-27 Thread Ray Walters
d in a week delay, and another unpaid 2 hour round trip to fix. (Outback or Carling care to cover my costs?) My 2012 resolution: Quit losing money fixing other companies' problems Ray Walters NABCEP Certified Installer BS Mechanical Engineering First In

Re: [RE-wrenches] Outback Breaker Problem and looking towards 2012

2011-12-27 Thread Ray Walters
That's great; As a company, I'm willing to pay more for the breakers with the better posts, because it will be much cheaper in the end. Ray We have just requested that Carling start providing real studs on all of our C series breakers (MNEDCXX). boB Midnite Solar On 12/27/2011 5:26 P

Re: [RE-wrenches] battery venting

2011-12-31 Thread Ray Walters
I, 2nd Allan's recommendation, or better, use sealed batteries, since its battery backup, and so small. People are bad about battery maintenance on anything but off grid. You definitely can't afford to have hydrogen sulfide going up through the building. Ray Walters On 12/31/20

Re: [RE-wrenches] Pole Mount PVC

2012-01-03 Thread Ray Walters
We've only had to use Schedule 80 out of the concrete, but never otherwise had a problem. Is his concern the structure of the concrete? It's ballast, not a pier that takes a compressive load. We've never had a problem in 2 decades. Ray On 1/3/2012 11:48 AM, Jeff Yago wrote: Drake, This

Re: [RE-wrenches] battery venting

2012-01-03 Thread Ray Walters
H2 is actually very difficult to contain, and can migrate through most materials. A super sealed, very small space, with a lot of charging source, its possible to reach combustion, but IMHO, you'd have to really try to create a system to do that. I've had a cell burn off its H2 once, so yes yo

Re: [RE-wrenches] Pole Mount PVC

2012-01-03 Thread Ray Walters
I've only done it that way when some Bozo forgot to install the conduit in the concrete. Definitely not the preferred method. Ray On 1/3/2012 3:19 PM, Drake wrote: At 01:48 PM 1/3/2012, you wrote: This is a very common way to install this conduit, so I really would like to know how this in

Re: [RE-wrenches] DC to AC derate

2012-01-05 Thread Ray Walters
I have a related question to this. Does setting up a pair of Outback GVFXs with the balancing transformer and allowing one inverter to go to sleep at lower AC output improve efficiency? It seems we would be reducing electronic loads, but adding transformer losses. Any comments? I have a rece

[RE-wrenches] Carling C Series Breakers (was Outback Breaker problem)

2012-01-06 Thread Ray Walters
re, I would pay a bit more for a breaker that didn't snap off in the field, as its way cheaper than a return trip on an off grid project. Its always nice to feel like we wrenches in the field are being listened to. We're really trying to make this better and safer for everyone involved

Re: [RE-wrenches] Request for Gennie Recommendation

2012-01-14 Thread Ray Walters
I have only limited experience with the GIllette, but I was impressed with the specs on that 15 Kw unit, it was a water cooled 4 cyl running at 1800 rpm, just what your customer needs, but probably way more than they want to spend. Can you add more PV to reduce the generator run time? Ray On

Re: [RE-wrenches] Shedding ice

2012-01-16 Thread Ray Walters
Hi Mark; Robin Gudgel at Midnite was talking about a setting on the Classic that could do that. I'm not sure how far they went with the concept, but it definitely is beyond mere theory. I'd check with them, and see where they were at with that. Ray Walters On 1/16/2012 11:0

Re: [RE-wrenches] battery venting; Corrosion

2012-01-16 Thread Ray Walters
I've found the Zephyr Power vents to be a little undersized in larger batteries with arrays over 1000 watts. Still get that smell in the room outside of the battery box, though its not explosive. That was with the 12 v model. I wouldn't mind seeing someone make a similar vent plumbed to larg

Re: [RE-wrenches] Paralleling Multiple Inverter

2012-01-22 Thread Ray Walters
l slots are filled with PV breakers, you're off the hook, at least according to Mike Holt, and my self for the little that matters ;-) Now you have to convince the AHJ, so you might want to show them Mike's book on the subject. Ray Walters On 1/22/2012 2:13 PM, Rich Nicol wrote: My take o

Re: [RE-wrenches] Grounding Separately Derived AC System

2012-01-23 Thread Ray Walters
That's always been my interpretation as well, reinforced at seminars with John Wiles and Bill Brooks. Ray Walters On 1/23/2012 6:13 PM, Dave Palumbo wrote: Regarding NEC Article 250.30 Informational Note #1 // // My interpretation is that a standard net-metered PV system is therefor

Re: [RE-wrenches] Grounding Separately Derived AC System

2012-01-24 Thread Ray Walters
the definition of separately derived system. In the end, I don't believe it matters whether we consider the DC side to be separately derived or not, as 250.30 only applies to AC, and 690 is now fairly clear about bonding and grounding requirements regardless. Ray Walters On 1/24/2012

Re: [RE-wrenches] Apparent power

2012-02-05 Thread Ray Walters
sell some battery amp-hrs at $1/ kwh every once in a while. Ray Walters On 2/4/2012 7:05 PM, b...@midnitesolar.com wrote: Sounds like a voltage source (and sinking) inverter to me. These types can cause current distortion which the UL1741 / IEEE 1547 specs try to prevent. Apparent must

Re: [RE-wrenches] Apparent power

2012-02-06 Thread Ray Walters
Hi Chris; Marco Manglesdorf (on this list) is the man to talk to about that. He is based in the Hawaiian islands; I only had the good fortune to work for him for a few projects. Ray Walters On 2/6/2012 5:30 PM, Comet Systems wrote: Ray, The idea that the utility in an island is seeing an

[RE-wrenches] Tax Credit for New Construction?

2012-02-07 Thread Ray Walters
Hi All; I just had a customer ask if he could take the federal solar credit for his PV system on his newly built off grid home. I always thought you could, but the wording on the IRS form sounded a bit like you couldn't take it for new construction. What's the group's opinio

Re: [RE-wrenches] 110Vac LED resistance to weak grids in developing world

2012-02-09 Thread Ray Walters
Personally I love my latest LED lights. They have gotten substantially better just in the past year. We have some 8 watt units in our kitchen that illuminate just like a 35 watt halogen, beautiful color rendition, not that blue they used to have. I especially like my new 1000 lumen spotlight t

Re: [RE-wrenches] Interstate L-16 vs Trojan L-16REB

2012-02-14 Thread Ray Walters
No, both golf cart batteries and industrial cells get more cycle life per $. Ray On 2/14/2012 1:18 PM, William Miller wrote: Colleagues: Do any of you have experience with Interstate L-16 batteries? Are they a good value? Thanks in advance, William Miller __

Re: [RE-wrenches] Design Question re Battery Bank Sizing

2012-02-15 Thread Ray Walters
Hi Allan; B&B battery, which I've used for years for sealed battery applications has excellent charts on discharge rate vs time; just what you need for your design. I've also found them to have stable voltage under very heavy loads (electric vehicles) right up until they're fully discharged.

Re: [RE-wrenches] Interstate L-16 vs Trojan L-16REB

2012-02-16 Thread Ray Walters
without over paralleling or breaking the off grid spinster budget. Ray Walters On 2/16/2012 6:39 AM, John DeBoever wrote: Wrenches, Drake, Trojan Premium lineL16RE-A, L16RE-B and L16RE-2V are optimized for renewable energy applications. They offer 1,600 cycles @ 50% DOD @ 77F. For details

Re: [RE-wrenches] Marine battery bank switch

2012-10-11 Thread Ray Walters
e old bank to a neighbor, or use it on a separate system. Ray Walters On 10/11/2012 5:51 PM, SunHarvest wrote: Thanks Allan,   I always value your insight. There is a TriMetric on this system but I'm look

Re: [RE-wrenches] Two NEC questions

2012-10-13 Thread Ray Walters
say the attic, it will interrupt the electricity at its source, not at the load. Ray Walters On 10/13/2012 9:12 AM, Rebecca Lundberg wrote: Dear fellow wrenches, Does anyone have suggestions for the 'best' way to keep up with product availability for meeting 690.11 on DC AFCI? I

Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-15 Thread Ray Walters
I've run a 3 HP well pump off a pair of Outbacks, but make sure you have plenty of battery behind it. We had shut downs from low voltage, when the batteries were at 50% charge from the starting surge. My experience with Magnum has been good, and they have even more surge current than the Outbac

Re: [RE-wrenches] 500A bussing

2012-10-15 Thread Ray Walters
de of the shunt. Ray Walters On 10/15/2012 9:21 AM, jay peltz wrote: Hi Mac Check out midnight they have exactly what you need Jay Peltz power Sent from my iPad On Oct 15, 2012, at 5:24 AM, mac Lewis <mailto:maclew...@gmail.com>> wrote: Hi Wrenches, I am looking for a >500A DC

Re: [RE-wrenches] Enphase and Romex

2012-10-26 Thread Ray Walters
an other wiring. Ray Walters On 10/26/2012 12:02 PM, benn kilburn wrote: Glenn/Jason, So you wouldn't use romex to feed an exterior outlet on an outside wall, or to any outside lights??? ___ List sponsored by Home Power magazine List

Re: [RE-wrenches] Wattsun Tracker Foundations

2012-10-26 Thread Ray Walters
Did you get soil tests done? That seems really deep. We have strong clay soils in New Mexico and Colorado, and I've always gone 4 ft in, and 6 ft out. Never an issue, with wind gusts that have blown debris and broken modules. No footing trouble though. I could see in a loose, sandy soil

Re: [RE-wrenches] Enphase and Romex

2012-10-26 Thread Ray Walters
So if the Romex is loaded with THHN/THWN (damp/wet rated), and no where does the outer covering of the Romex itself get exposed to the wet location, that should be sufficient? Ray Walters On 10/26/2012 7:45 PM, Glenn Burt wrote: 300.9 Raceways in Wet Locations Above Grade. Where raceways

Re: [RE-wrenches] Two sealed battery questions, please

2012-11-12 Thread Ray Walters
eelings if they don't last very long. A solid load capacity test would tell you a lot more about them. Ray Walters On 11/12/2012 3:55 PM, Allan Sindelar wrote: Wrenches: First question: for a large grid-tied with battery backup system (9.8 kW array, two SB5000s, dual Sunny Islands), we h

Re: [RE-wrenches] Roof flashings on L-feet in high snow load conditions

2012-11-13 Thread Ray Walters
HI Todd; That's very interesting. What roof pitch does that happen? I'm guessing that at a step enough tilt, the frame damage is alleviated? Also on your tall pole mounts what pole design do you use? I've tried telescoping type, and guy wires on tall poles. Ray On 11/13/2012 12:08 PM, tod

Re: [RE-wrenches] Roof flashings on L-feet in high snow load conditions

2012-11-13 Thread Ray Walters
vember 13, 2012 11:12am, "Ray Walters" said: HI Todd; That's very interesting. What roof pitch does that happen? I'm guessing that at a step enough tilt, the frame damage is alleviated? Also on your tall pole mounts what pole design do you use? I've tried telescoping

Re: [RE-wrenches] Protecting/Cleaning un-connected MC Connectors

2012-11-24 Thread Ray Walters
I would think good old CRC contact cleaner, as the connectors have a grease coating that collects dust if left unconnected. Follow up by regreasing with silicon gel as Glenn suggested. I've been playing around with using unterminated connectors to temporarily seal up the dangling connectors. Th

Re: [RE-wrenches] Fix the Fluorescents: What about LED tubes for late 2012?

2012-12-05 Thread Ray Walters
hand held LED flash light that is as bright as my car headlights (1100 lumens) and I still haven't charged its Li+ battery in 6 months. LEDs are the future amigos. Ray Walters On 12/5/2012 8:33 PM, William Dorsett wrote: In the early days, LED's were rated by the candela and so

Re: [RE-wrenches] Two Load Questions

2012-12-10 Thread Ray Walters
in winter scenario will probably cut the run time down by 80%. I've done that same trick, and the customers loved it, but they moved it in in the summer as it ran too much in the summer in 85 deg weather. Ray Walters On 12/10/2012 9:12 PM, Allan Sindelar wrote: Wrenches, We still t

Re: [RE-wrenches] DC, or not DC, Dat is Da question (Two Load Questions)

2012-12-11 Thread Ray Walters
#x27;s built in low voltage disco keeps the batteries from getting ruined if the charge system is down, but loads stay on. I lived for years with a DC fridge, and my family has no desire to go back. Ray Walters 12/11/2012 12:54 PM, Jason Lerner wrote: Hello Larry, I still install DC fridge/

Re: [RE-wrenches] Small PV system/experiment for kids

2012-12-12 Thread Ray Walters
Array direct is definitely better as Stephen points out, and I've built units that run a fan other visibly moving device. Definitely don't want to roof mount the module, as others pointed out, you want the kids to be able to experiment with angles and shading. Throwing in some analog meters f

Re: [RE-wrenches] DC, or not DC, Dat is Da question (Two Load Questions)

2012-12-12 Thread Ray Walters
re. My overall foot print is less than building a new "efficient" home out in the vanishing wilderness. I've tried it all, and that's just where I landed for now. I'm currently working on an off grid PV charging system for a customer's Chevy Volt, though, so I&#x

Re: [RE-wrenches] Single axis tracker

2012-12-15 Thread Ray Walters
company that has been doing tracking right for decades. Ray Walters On 12/15/2012 10:59 AM, Bill Turberville wrote: Does anyone have suggestions for a 50KW single axis tracker system. This is going on top of a berm that does not run east-west

<    1   2   3   4   5   6   7   8   9   10   >