Re: [RE-wrenches] Interstate UL-16 HC problem

2010-06-29 Thread R Ray Walters
IF those L 16s are much over 5 years old, they could be gone. L16s (of any brand) have less cycle life than a golf cart battery, just check the charts. They also don't fair very well long term in float charge. You can probably EQ them back to life as already mentioned, but then after 6 months to

Re: [RE-wrenches] Interstate UL-16 HC problem

2010-06-29 Thread R Ray Walters
7;t watered properly. L16s do have the advantage of holding more water, so I think that might be why folks like yourself beat the test results. R. Walters r...@solarray.com Solar Engineer On Jun 29, 2010, at 10:04 PM, Nick Soleil wrote: > Really Ray: > Almost all of the L-16s

Re: [RE-wrenches] Component Choices for MY RV - Apollo Solar?

2010-07-01 Thread R Ray Walters
See below: R. Walters r...@solarray.com Solar Engineer On Jul 1, 2010, at 7:09 AM, Jeff Clearwater wrote: > Dear Colleagues, > > Well this one's for me! Nice to do solar for oneself after installing for > others my whole life! > > I'm putting together an small RV system in my Sprinter Van th

Re: [RE-wrenches] Component Choices for MY RV - Apollo Solar?

2010-07-01 Thread R Ray Walters
ycling. R. Walters r...@solarray.com Solar Engineer On Jul 1, 2010, at 12:07 PM, Jeff Clearwater wrote: > HI Ray, > > Yes I meant to say Yellow Tops. They are overpriced - indeed! We've also > had limited success in EV projects. > > Do you have a supplier for B&

Re: [RE-wrenches] Trojan L16 2v vs 6v

2010-07-14 Thread R Ray Walters
Kent; Your table shows just what I found as well: too large a battery bank actually isn't as cost effective. Also, based on the Trojan chart, you can see that a regular L16 isn't even as good as golf cart battery, but that the 2 v version doubles the cycle life. (which makes sense, cycle life i

Re: [RE-wrenches] calculating DC voltage drop

2010-07-22 Thread R Ray Walters
I use actual operating current, without multipliers. I also use actual temperatures, not the worst case temperatures that many use. I created a spread sheet that uses the NEC adjustments for wire temperature, (see NEC chapter 9, table 8, FPN 2) It makes quite a difference! Volt drop and the accom

Re: [RE-wrenches] calculating DC voltage drop

2010-07-22 Thread R Ray Walters
st of your calculations will be confirmed with actual voltage drops measured on the proverbial "average" day. R. Walters r...@solarray.com Solar Engineer On Jul 22, 2010, at 2:12 PM, Michael Kelly wrote: > Hi All, > > I agree with Ray with the exception that I use Imp*1.25 i

Re: [RE-wrenches] line-side tap in subpanel

2010-07-22 Thread R Ray Walters
It would depend on which side of the OCD the 380 amp rated cable was on. IF the 400 A OCD is integral to the panel, then it doesn't matter what the cable size is on the other side of the OCD, it's protected by the OCD, and the current can't exceed that. If the OCD is remote and the subpanel does

Re: [RE-wrenches] calculating DC voltage drop

2010-07-22 Thread R Ray Walters
> "Responsible Technologies for Responsible People since 1988" > > From: re-wrenches-boun...@lists.re-wrenches.org > [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Michael Kelly > Sent: Thursday, July 22, 2010 2:13 PM > To: 'RE-wrenches' &

Re: [RE-wrenches] calculating DC voltage drop

2010-07-23 Thread R Ray Walters
I try to keep it in copper for DC, as I had always heard of trouble with Aluminum on DC. (True or Old Wrenches Tale?) We definitely go to Al on long AC runs, as its whats available, and the cost difference becomes remarkable. I've seen small cuts in Al, later corrode completely through the conduc

Re: [RE-wrenches] battery buss bars

2012-01-17 Thread R Ray Walters
Midnite has a new one: http://www.midnitesolar.com/productPhoto.php?product_ID=207&productCatName=Busbars&productCat_ID=17 Here's a new one I just found with Del City also: http://www.delcity.net/cartviewitem?item=80510DL&search=buss+bar or http://www.delcity.net/cartviewitem?item=80006DL&sear

Re: [RE-wrenches] 24 vs. 48

2012-01-17 Thread R Ray Walters
The only advantages of 24 v are that you can create smaller KWH battery banks, and that Bergey's XL.1 was only available in 24 v. Anytime the design allows, I jump to 48 v. R. Walters r...@solarray.com Solar Engineer On Jan 17, 2012, at 11:11 AM, Nathan Jones wrote: > > > Mark, > It would

Re: [RE-wrenches] battery buss bars

2012-01-17 Thread R Ray Walters
AM, Allan Sindelar wrote: > Ray, > We have a job under contract this summer with four Sunny Islands and a Radian > sharing the same battery bank. Even with the SIs protected by 125A DC > breakers, that's 850A of DC capacity that we have to buss together. > > The Midnite buss

Re: [RE-wrenches] reliable 12vdc to 5vdc converters for USB charging

2012-02-22 Thread R Ray Walters
http://www.goalzero.com/ has a nice battery/ power pack that has 12 v PV in, 12v and USB power out. I've been shopping for a solar charger to keep my "smart" phone going. R. Walters r...@solarray.com Solar Engineer On Feb 22, 2012, at 2:23 PM, Steve McCarney wrote: > Hi Jim > > Phocos ha

Re: [RE-wrenches] Off-grid ground mount

2012-03-25 Thread R Ray Walters
s, I quit using this method, but it might be just the ticket. Russ has done these before, too. Ray On Mar 25, 2012, at 9:21 AM, William Miller wrote: > Allan: > > We recommend the custom, top-of-pole roof-mount: > http://millersolar.com/MillerSolar/Portfolio/pole_mount/Custom_trac

Re: [RE-wrenches] Any experience with off-grid oxygen concentrators?

2012-04-21 Thread R Ray Walters
nce would cover it? Ray Walters On Apr 21, 2012, at 12:12 PM, Dan Fink wrote: > Esteemed Wrenches; > > One of our clients, 79 years old, has an off-grid cabin at 8200 ft altitude > that he built and has been using on weekends since 1982. Due to a heart > condition, his doctor

Re: [RE-wrenches] Nickel-Iron Batteries

2012-05-05 Thread R Ray Walters
It is a Colorado company, but they are importing them from China. I've met the owner. My understanding is the plates do not deteriorate, but the electrolyte needs to be replaced every 5 - 10 years, so technically you would never need another set, just KOH. Ray Walters On May 5, 2012,

Re: [RE-wrenches] outback power wrench support?

2012-06-20 Thread R Ray Walters
#x27;ve found, their customer service is truly lacking. It's why I tried to move to support other companies, like Midnite Solar when possible. Nobody (including me) is perfect, but how they handle problems speaks volumes about their integrity. Ray Walters On Jun 20, 2012, at 6:35 PM, Alla

Re: [RE-wrenches] L feet no flashing in shingle roof

2012-07-04 Thread R Ray Walters
g the venerable L foot has its place in our industry. I've seen some flashed installations that were code compliant, but looked horrible, and worse: leaked. Ray Walters On Jul 4, 2012, at 9:07 AM, David Brearley wrote: > Todd, > > The issue isn't whether your approach work

Re: [RE-wrenches] Outdoor woodstove/furnace and solar

2012-07-04 Thread R Ray Walters
I worked on one off grid system like this, it worked, but you have to have a big battery bank. Also, a really good generator is mandatory. Ray On Jul 4, 2012, at 5:59 PM, bob ellison wrote: > Been there on 2 occasions, the pumps may seem like small loads but there are > usually many o

Re: [RE-wrenches] Outdoor woodstove/furnace and solar

2012-07-05 Thread R Ray Walters
It definitely can work; the old house I'm in now has a 100 yr old radiator system (not steam) that has 2-1/2" main lines. No pumps. Every single pipe in the system has a slight fall all the way to the boiler in the basement. Ray On Jul 5, 2012, at 6:14 AM, wrote: > Seems I

Re: [RE-wrenches] Security / theft questions

2012-07-07 Thread R Ray Walters
4) higher voltages that are no longer 12 v DC compatible. Ray Walters NABCEP since 2004 On Jul 6, 2012, at 11:04 AM, Rebekah Hren wrote: > I'm researching an article on PV system security/theft, and I thought it > would be interesting to ask the wrenches list what y'all have be

Re: [RE-wrenches] Battery Experience

2012-07-14 Thread R Ray Walters
hs. I have a couple of higher end part time systems that the owner can monitor and contact us, if for instance the power goes out. This keeps it from leading to permanent damage. Ray Walters On Jul 14, 2012, at 8:58 AM, Jason Lerner wrote: > Hello John, > > Thank you for your help

Re: [RE-wrenches] Battery Experience

2012-07-14 Thread R Ray Walters
y was rated at 750 cycles, and was much cheaper per AH. Ray On Jul 14, 2012, at 1:58 PM, Jason Lerner wrote: > Hi Ray, > > With no inverter in the system and all the loads turned off do you think the > batteries are really cycling that much? Yes your scenario's sound familiar.

Re: [RE-wrenches] mounting hardware and U.L.

2012-07-19 Thread R Ray Walters
ity of equipment, so regardless of the seemingly omnipotent 110.2, an AHJ can't reasonably require equipment that doesn't exist. Ray On Jul 19, 2012, at 5:12 PM, Jay Peltz wrote: > Is unistrut UL? > > Kay > > Peltz power > > Sent from my iPhone > > On Jul

Re: [RE-wrenches] 12V loads

2012-08-09 Thread R Ray Walters
hat's worth a look, and their battery meter is also good for the 12 V crowd. Ray Walters On Aug 9, 2012, at 4:57 PM, Jesse Dahl wrote: > Thats what I was looking at. Cost wise, if you were to get crazy with > panelboards and stuff the price just skyrockets. > > Thanks eh

Re: [RE-wrenches] 12V loads

2012-08-10 Thread R Ray Walters
ly systems. Most of my DC only systems ended up adding at least a cheap inverter later, might as well do it right the first time. Ray Walters On Aug 10, 2012, at 8:35 AM, Dan Fink wrote: > On the cheap side, Square D QO. They are indeed rated to 48VDC, which means > you can use them w

Re: [RE-wrenches] 12V loads

2012-08-10 Thread R Ray Walters
a look at Midnite's Mini DC panel wired to Magnum's smallest inverter. You'd be surprised how cheap you can do a code compliant inverter based system, and how much money you can waste trying to do a code compliant DC only system. Ray Walters NABCEP certified since 2004 On Aug 10,

Re: [RE-wrenches] 12V loads

2012-08-10 Thread R Ray Walters
screw something up, they're not exactly going to vaporize the planet. They're much more likely to die in a car accident driving to your shop to get another fuse.. Ray Walters On Aug 10, 2012, at 6:37 PM, Jesse Dahl wrote: > The "code compliance" part has been my worry

Re: [RE-wrenches] 12V loads

2012-08-12 Thread R Ray Walters
On Aug 11, 2012, at 6:43 AM, Drake wrote: > Ray, > > If golf cart batteries can't surge over 2000 amps, then it would seem that > the fuse in line with the QO can be deleted in some cases. Is the 2000 A > surge for one 6 volt battery or 2 in series? Current stays th

Re: [RE-wrenches] Disconnets

2012-08-25 Thread R Ray Walters
ition. 600 VDC rated fuse holders for instance will completely arc across the open contacts at 900 vdc. This is one area where you don't have much safety factor, IMHO. Ray Walters On Aug 25, 2012, at 9:17 PM, Jesse Dahl wrote: > I've been using similar "solar" disconn

[RE-wrenches] Max Insolation

2012-08-29 Thread R Ray Walters
about 95 deg F. Any help on both the high insolation reading or Photowatt troubles would be great. Thanks in Advance, Ray Walters ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & setti

Re: [RE-wrenches] Ballasted Roof Racking Recommendations?

2012-08-31 Thread R Ray Walters
x27;s probably the best commercially available module in the world, definitely the most efficient. Last I checked it qualified as American made, though some of it is made in indonesia I believe. Ray Walters On Aug 31, 2012, at 1:36 PM, Bill Hoffer wrote: > Ryan > > I do not think that

Re: [RE-wrenches] Trojan 2 volt L-16s

2012-10-08 Thread R Ray Walters
At least the imbalance would only be one cell, not a whole string of cells. Ray On Oct 8, 2012, at 2:20 PM, William Miller wrote: > There may be another benefit: While there are really three strings in each > case, the connections are factory and maybe not prone to imbalance. This is

Re: [RE-wrenches] Was, Old School 12V Independent System? Now, controller tests

2012-10-11 Thread R Ray Walters
vious case, because no one will be there for several months at a time. I'd put a nice set of HUPs in to get the same or more amp hours. Efficiency will be much better, and they'll have a battery that will last 20 years. Ray Walters On Oct 11, 2012, at 1:45 PM, Mark Dickson wrote: > S

Re: [RE-wrenches] Power conditioner for Trace inverter

2023-09-08 Thread Ray via RE-wrenches
res, shorts?  Definitely needs to be in a metal enclosure. I think its either get a different washer or get a different inverter. At 22+ years, its slowly reaching the time to retire those old SWs. Ray Walters Remote Solar 303 505-8760 On 9/8/23 2:53 PM, Dave Angelini Offgrid Solar via RE-wre

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Ray Walters via RE-wrenches
em too.  You'll use them for all sorts of stuff; good to keep on the truck. Monk Wipes Heavy Duty Hand Cleaner | Large 9.6″ x 12 ... Ray Remote Solar On 4/15/2022 8:56 AM, Garrison via RE-wrenches wrote: Hi Mac, I second the isopropyl alcohol (diluted), a soft cloth, and razor blade i

Re: [RE-wrenches] Battery Monitor for Li

2022-09-02 Thread Ray Walters via RE-wrenches
Default efficiency on the TriMet was 94%, needs to be quite a bit higher for Li+.  I'd try 98%. 2nd point:  Customers have always obsessed about meter readings: they need to take a chill pill, and accept its not going to be better than +/- 10% accuracy.  Or get a Fortress battery with built in

Re: [RE-wrenches] Discover AES Wall Mount Considerations

2022-09-06 Thread Ray Walters via RE-wrenches
I agree with James here.  I will relate a "funny" story about a neighbor mounting a large Elk antler rack on his wall with lags. Worked fine, till one night they heard a big crash, and the antlers had pulled the wall stud right out of the wall into the living room. The 2x 4 came right out of  t

Re: [RE-wrenches] sol ark reliability question

2022-09-30 Thread Ray Walters via RE-wrenches
tance varied. Ray Walters On 9/30/2022 6:57 AM, Jay via RE-wrenches wrote: Hi all and thanks for the input. I guess he’s just been unlucky with the problems ( firmware upgrade switching to 50hz) and possibly just some random bad hardware. In regards to your thoughts of a install issue, he has

[RE-wrenches] Fortress Battery Problems

2022-11-16 Thread Ray Walters via RE-wrenches
I had properly paralleled the batteries. Has anyone else had a hard time with Fortress support?  Does anyone have a direct contact?  Customer is beyond pissed now, after almost 2 weeks hearing nothing, and having spent tens of thousands. Thanks;

Re: [RE-wrenches] Fortress Battery Problems

2022-11-16 Thread Ray Walters via RE-wrenches
  Using the aux out on the Classic to control a relay to turn on/off the inverters for LVD, since Outback programming (like Schneider) won't allow LVD settings above 48v. Ray On 11/16/2022 12:40 PM, Chris Sparadeo via RE-wrenches wrote: Hi Ray, I would suggest pushing the latest firm

Re: [RE-wrenches] Sol-Ark/Fortress charging issue

2022-11-16 Thread Ray Walters via RE-wrenches
Talk to Thomas Honey.  He is the Fortress rep, nice guy, and knowledgeable wrench.   He has stepped in on my issue. Ray On 11/16/2022 10:58 PM, Howie Michaelson via RE-wrenches wrote: Good Evening, I have a frustrating charging issue involving 2 Fortress eVault Maxs connected to a Sol-Ark

Re: [RE-wrenches] Sol-Ark/Fortress charging issue

2022-11-17 Thread Ray Walters via RE-wrenches
with built in color touch screen for monitoring, price much better. Simpliphi = no monitoring at all, have to parallel ridiculous qty of batteries to do a normal off grid home, but integration guides are the best. Ray Walters On 11/17/2022 1:16 PM, r...@solartechvt.com wrote: We’ve started t

Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Ray Walters via RE-wrenches
To add to Jeff's suggestion of targeting 95%, many Li+ batteries have a spike in voltage as they reach 100%.  We just don't have to worry anymore about sulfate damage from under charging. Ray Walters Remote Solar On 11/19/2022 7:14 AM, Jeff Clearwater via RE-wrenches wrote: Hi

Re: [RE-wrenches] Magnum MS4024 grief

2022-12-16 Thread Ray Walters via RE-wrenches
ecially off grid, I see an amazing bunch of DIY garbage.  Find out who did the original wiring.  Probably not a pro. Ray Walters Remote Solar On 12/16/2022 11:35 AM, Kirk Herander via RE-wrenches wrote: You may have neutral and ground connected at more than 1 location, meaning at the genset and in

[RE-wrenches] Fortress Battery Heater

2023-02-08 Thread Ray Walters via RE-wrenches
h the Solark's load controls. I've considered some DC options, but they don't make much sense, since the inverter has to be on to charge from PV anyway. The long term plan is for the client to finish the insulation, and sheet rock, and add a gas wall heater in there as needed.

[RE-wrenches] Solark-Fortress Com? (was Fortress Battery Heater)

2023-02-09 Thread Ray Walters via RE-wrenches
s 10 times more important than squeezing an extra 5% capacity out of the battery Notes in the online instructions such as "/Failure to properly upgrade the firmware may cause the battery to stop working!", / are not making we want to push ahead with closed loop either. Ray On 2/

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Ray Walters via RE-wrenches
://www.northerntool.com/shop/tools/product_200653609_200653609 Midnite makes small 30A and 60A T switches as well: https://www.midnitesolar.com/productPhoto.php?product_ID=416&productCat_ID=29&sortOrder=3&act=p Ray Walters On 3/2/2023 11:57 AM, Sindelar Solar via RE-wrenches wrote: Kris, It was SqD Q

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Ray Walters via RE-wrenches
p for anything greater than 60 amps for 2 poles, other than large DPDT switches which get pricey and hard to source especially for 200 amps? Howie On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches wrote: I probably still have one of the old QO boxes on the shelf, but I never

[RE-wrenches] 60v Inverter?

2023-03-02 Thread Ray Walters via RE-wrenches
ous motor that is in an Hammond organ, so that I can tune the organ down from A=440 Hz to A =432 Hz to match an even older piano.Yep, I'm living on the edge.. Ray Walters (Now Even More) Remote Solar ___ List sponsored by Redwo

Re: [RE-wrenches] PV and EMP

2023-03-09 Thread Ray Walters via RE-wrenches
I'm not an EMP expert by any means, but I've dealt with quite a few lightning damaged systems.  Having a good connection to a low impedance grounding system (steel cased well, Ufer ground) is crucial.  I also have had fantastic luck with Midnite's MNSPD line.  Delta, not so much. On 3/9/2023 1

Re: [RE-wrenches] Cell phone based relay control

2023-03-13 Thread Ray Walters via RE-wrenches
Michael; Can you share more about your sprinkler system and the power supply for it?  Over the years, at least two of my customers have lost their homes (and PV arrays) in wild fires. Ray Walters Remote Solar On 3/13/2023 2:34 PM, Michael Morningstar via RE-wrenches wrote: WebRelay. I use

[RE-wrenches] Fire Sprinklers (was Re: Cell phone based relay control)

2023-03-14 Thread Ray Walters via RE-wrenches
n you post a couple pics of your sprayer install? 2nd question:  what are the field results of these systems in actual fires? Thanks, Ray On 3/14/2023 10:03 AM, Todd Cory via RE-wrenches wrote: I can help with this as Michael built something similar to what I designed and installed in 2001:

Re: [RE-wrenches] Off Grid Battery Charging

2023-03-16 Thread Ray Walters via RE-wrenches
g into the system.  Maybe she could do what several folks have done: power a TV while you pedal.  Anyway, here is device that might do it:   https://www.econvergence.net/ Ray Walters Remote Solar On 3/16/2023 3:58 PM, Larry Brown via RE-wrenches wrote: Wrenches I have a client that we did a

Re: [RE-wrenches] Attaching Array To or Through Ply

2023-03-30 Thread Ray Walters via RE-wrenches
but then get that tool off the roof. Use an electric screw driver, socket wrench, or *drill with a clutch* set low to snug up the clamps, and then final torque with a torque wrench. Period. Ray Walters Remote Solar Former NABCEP 2004-2016 On 3/30/2023 4:34 PM, Jason Szumlanski via RE-wrenches w

Re: [RE-wrenches] Attaching Array To or Through Ply

2023-03-31 Thread Ray Walters via RE-wrenches
bit better with new found idea on each install. Thanks again for great ideas Wrenches, Ray On 3/31/2023 2:15 PM, Jason Szumlanski wrote: Hi Ray, I'm happy to have some confirmation from another major storm's impact. My father has a home in Dominica, which was hit by Maria with 165

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-03 Thread Ray Walters via RE-wrenches
ent choice, I've seen less than 5 years from sealed L16s like Trojan.  Full River is about the best in that field, and still only going to see 7 to 8 years.  It just doesn't pencil out compared to HUPs or Li+. Ray Walters Remote Solar On 4/3/2023 12:39 PM, William Miller via RE-wrenches

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-04 Thread Ray Walters via RE-wrenches
the CC to switch off the inverters.  IF the inverters are Outback, they have a remote switch, if its something else, you might have to actually switch off a relay on the AC output. Ray On 4/4/2023 2:45 PM, Daniel Young via RE-wrenches wrote: Thanks all for the advice. I figured it was not worth tryin

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-04 Thread Ray Walters via RE-wrenches
on't cheap out. Ray Walters Remote Solar On 4/4/2023 5:42 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote: Hurts my head !  Agree that you will have more trips to this house after the next one. This is most likely not going to get you 2 more years. All of the wiring is good, clean,

Re: [RE-wrenches] Truss finder

2023-04-17 Thread Ray Walters via RE-wrenches
If the temperature is right, my IR camera can see the rafters. Best to check early on a cold morning with the heat on in the building.  Otherwise I'm of the William "Hammer" system persuasion.  Never found anything better. On 4/17/2023 1:31 PM, Garrison via RE-wrenches wrote: Hi Kris, I star

Re: [RE-wrenches] Solar direct water pumping

2023-05-08 Thread Ray Walters via RE-wrenches
n the pipe.  That can be looked up (just like wire losses) for the size pipe and flow rate. Finally, you didn't mention how large a pond.  To fill the pond, it needs to overcome both evaporative losses, and leakage into the surrounding soil. Ray Walters Remote Solar On 5/8/2023 10:04 AM

Re: [RE-wrenches] Metering

2023-05-11 Thread Ray Walters via RE-wrenches
monthly electric bill, check the cumulative production on the PV system, and then do some subtraction.  Pretty simple for them, and you only get a call, if the inverter production is low or off. Ray Walters Remote Solar On 5/11/2023 2:20 PM, Larry Brown via RE-wrenches wrote: Does anyone have a

Re: [RE-wrenches] Tech Support Issues with Sensata

2023-05-31 Thread Ray Walters via RE-wrenches
f grid, and the only thing better than a Magnum for power quality is Exeltech in my experience. Ray Walters Remote Solar On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote: Hi all, I have a client with a Magnum MS 4024- PAE inverter. There are some serious issues with power out

Re: [RE-wrenches] Tech Support Issues with Sensata

2023-05-31 Thread Ray Walters via RE-wrenches
that variation.  That sounds more like a cooked control board.  I had lightning damage cause an inverter to put out 140 vac, while its onboard electronics read 120 vac. If it helps, I have a used MS 4024 PAE (very low hours) that I could send to you.   Contact me off list if you want. Ray Walte

Re: [RE-wrenches] Inverter output fluctuations

2023-07-03 Thread Ray Walters via RE-wrenches
ality of the driver circuits on the LED bulbs.  Only gets worse on a less than perfect AC waveform. Ray Walters Remote Solar On 7/3/2023 5:09 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote: I think I would try eliminating things. Turn off the AC coupling for a few days and get results.

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-13 Thread Ray Walters via RE-wrenches
odels. Absolutely makes no sense.  Schneider, Outback, even Magnum is too low...? Ray Walters On 7/11/2023 6:19 PM, Mac Lewis via RE-wrenches wrote: Hello Wrenches, I'm trying to solve an issue with an older Outback FX system.  It's a quad stack of Outback 3648 FX inverters and he

Re: [RE-wrenches] Damaged PV module cells

2023-07-16 Thread Ray Walters via RE-wrenches
Grape Solar was not a top brand BTW. Ray Walters On 7/16/2023 4:18 PM, Kent via RE-wrenches wrote: I think these modules are about 12 years old. I didn't have a voltmeter or ammeter with me this morning when this was discovered so I wasn't able to check the output. Kent Osterberg Blue

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-20 Thread Ray Walters via RE-wrenches
The aux off is only if the generator doesn't start.  You need to set the gen start voltage higher. Aux off is last ditch shut down, set for 44v for lead acid, or 47 to 49v, depending on the battery and inverter.   Hopefully DC coupled PV will raise the voltage enough to turn the inverters back

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-20 Thread Ray Walters via RE-wrenches
ay, so they can manually turn the inverters back on. Ray On 7/20/2023 5:15 PM, Jay wrote: Hi Ray This house won’t have an AGS, manual start only. And your comments exactly, having to wait until the next day when hopefully there is enough sun to charge the battery is iffy. Or they could do the

Re: [RE-wrenches] Wind machines

2023-08-17 Thread Ray Walters via RE-wrenches
be Kinetic art, which is what many folks find attractive, I think. Ray Walters On 8/17/2023 1:41 PM, Jay via RE-wrenches wrote: Im curious if anyone has actual measured data on a VAWT. It just seems like they are meat for the end of the worlders Jay _

Re: [RE-wrenches] Need a hand with Sunny Island/Sunny boy AC couple

2023-10-21 Thread Ray Walters via RE-wrenches
What is the array size vs the battery size?  Sounds like a big array on a small battery for the voltage to go that high that fast. Ray Remote Solar On 10/21/2023 5:46 PM, William Miller via RE-wrenches wrote: Friends: I’m kinda stuck on a project setting up a SI/SB AC coupled system off

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-09 Thread Ray Walters via RE-wrenches
quot; connector type. 10+ amps continuous, moist environment, 30F+  hotter than ambient temp, all are tough on connectors.  I predict more connector failures as module current ratings increase. Ray Walters Remote Solar On 11/9/2023 3:02 PM, Glenn Burt via RE-wrenches wrote: Good luck trying t

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-09 Thread Ray Walters via RE-wrenches
I'm trying to find a pic to post, but they were MC4 connectors, not the UTX. Ray On 11/9/2023 4:57 PM, Brian Mehalic wrote: Are they the Amohenol UTX connectors? SW had a recall on them, sounds like about the right timeframe. BREAKING: SolarWorld recalls PV modules with Amphenol conne

Re: [RE-wrenches] Lithium batteries

2024-02-07 Thread Ray Walters via RE-wrenches
ould have lasted a lifetime.  I hate being wrong.  I can only pray that more of these high price tag batteries don't start failing on my watch. I've been holding this rant back for a while, trying to give Simpliphi a chance to make this right. However, this week I heard their "

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Ray Walters via RE-wrenches
as to what transpires.  Right now, I'm shopping for SLA batteries to get this customer back in action. Reporting as always from the Bleeding Edge, Ray Walters Remote Solar On 2/8/2024 7:35 AM, Richard Nicol via RE-wrenches wrote: Hi Ray We had a complete failure of 6 Simpliphi batterie

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Ray Walters via RE-wrenches
Hi Richard; Off list, what was your outcome from Simpliphi?  Did they make any deal with you?  What did you put in as replacements? Thanks, Ray Walters Remote Solar On 2/8/2024 7:35 AM, Richard Nicol via RE-wrenches wrote: Hi Ray We had a complete failure of 6 Simpliphi batteries with the

Re: [RE-wrenches] XW EQ question

2024-02-12 Thread Ray Walters via RE-wrenches
What's funny, is the good old SWs from the Trace days had the same problem.   Never could get them to equalize.  Maybe that software carried over. Ray Walters Remote Solar On 2/12/2024 4:42 PM, jay via RE-wrenches wrote: Hi Kevin Thanks, I heard that exact thing from someone else. D

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Ray Walters via RE-wrenches
I second using the 48v to 12 v DC DC converter.  I've had success with that, and avoided the issues Jeremy mentioned. Ray Walters Remote Solar On 2/17/2024 9:35 AM, Bradley Bassett via RE-wrenches wrote: I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn&#

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Ray Walters via RE-wrenches
se, but definitely not there. Also, with all the mention of various UL listings, regulation needs to evolve to differentiate between LiFePO4 and other Li+ chemistries.  LiFePO4 is inherently much safer, but we're being forced to comply with all the same regulations as the less stable, more

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Ray Walters via RE-wrenches
lar assumption like "lead acid batteries aren't allowed", will get them to back down on the spot.  Getting solar trade organizations on your side to help with the process can add much needed weight. Ray Walters Remote Solar On 2/17/2024 2:26 PM, Dan Fink via RE-wrenches wrote: Jay -

Re: [RE-wrenches] Rugged Wind/Solar System For Radio

2024-02-21 Thread Ray Walters via RE-wrenches
Who carries the Superwind turbines?  We've been looking for a replacement for the old Bergey XL1 to offer clients. Thanks, Ray Walters Remote Solar On 2/21/2024 7:20 PM, John Blittersdorf via RE-wrenches wrote: As far as wind is concerned, I recommend SuperWind, made in Germany.  It is

Re: [RE-wrenches] Battery Electrolyte Level Measuring

2024-02-29 Thread Ray Walters via RE-wrenches
Bosch that's quite accurate; I tried it on some bottles with fluid in them, and it seemed to work well.  I'll try and remember to take out with me on the next job with FLA. Ray Walters Remote Solar On 2/29/2024 2:12 PM, William Miller via RE-wrenches wrote: Friends: Thanks to everyon

Re: [RE-wrenches] TPM Search

2024-03-08 Thread Ray Walters via RE-wrenches
I've had several modules pull off of bottom mount racking in high winds, but never top mount racking.  Newer modules have much thinner frames, but are much more surface area than the old days. So to answer Kent's question: Ray Walters Remote Solar On 3/8/2024 3:50 PM, Kent via R

Re: [RE-wrenches] TPM Search

2024-03-08 Thread Ray Walters via RE-wrenches
Here's another mount at the edge of failure, from the same system. Hardware is tight.  Like many, I had lots of love for good ol' fashion bottom mounting vs top mount, until this happened about 5 years ago. This is how we learn. On 3/8/2024 5:15 PM, Ray Walters via RE-wrenches wro

Re: [RE-wrenches] TPM Search

2024-03-10 Thread Ray Walters via RE-wrenches
cks with the top down mounting, and no losses.   I've been  suspicious of top down module racking; and I was quite satisfied with actual bolts and hardware to hold modules in place.  But its just not true anymore.    I added 3/4" angle stainless steel to reinforce the attachments on the t

Re: [RE-wrenches] Insurance for solar design and inspections

2024-03-11 Thread Ray Walters via RE-wrenches
hing that my company takes responsibility for, and I sleep well at night with my standard contractor's liability insurance. Remember, insurance agents primary goal is to sell more insurance.  Of course they want you to have an E&O policy, too. Ray Walters Remote Solar On 3/11/2024 7:4

Re: [RE-wrenches] Redundant gensets: Must I switch the neutral in the manual transfer switch?

2024-03-13 Thread Ray Walters via RE-wrenches
ingle separately derived system. Exception 1 specifically says a single N-G bond is allowed for multiple power sources. Ray Walters Remote Solar On 3/13/2024 3:19 PM, Mick Abraham via RE-wrenches wrote: Hi, Mechanix~ My off grid project gig has redundant 120y208 generators that need a 200a &quo

Re: [RE-wrenches] Minimum bus size, new requirements

2024-03-28 Thread Ray Walters via RE-wrenches
applications.   The rest of us in the other 49 states are Not required to comply with the 200 A requirement. Good Luck out there. Thank you, Ray Walters Remote Solar On 3/28/2024 12:33 PM, Lloyd Hoffstatter via RE-wrenches wrote: William, Here is the CA Energy Code with the upsized busbar

Re: [RE-wrenches] Plaques

2024-03-30 Thread Ray Walters via RE-wrenches
it in house to pencil out. I'm not sure if it ever would, considering that you still have to pay yourself or someone else to operate the engraver, and the blank plaques probably cost a bit too. Ray Walters Remote Solar On 3/30/2024 12:56 PM, Lou Russo via RE-wrenches wrote: Aloha Wrenche

Re: [RE-wrenches] PV/Charge Controller Troubleshoot Help

2024-04-23 Thread Ray Walters via RE-wrenches
and then you and the customer can be bored for a decade.  It will make more power too, especially on cold, sunny days when you really need it. Ray Walters Remote Solar On 4/23/2024 12:47 PM, Todd Cory via RE-wrenches wrote: My old MX60 said " hot" when the fan had failed. Todd "M

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-25 Thread Ray Walters via RE-wrenches
ational for more than a few minutes.  The cheapo BMS lears its ugly head once again.  All we're doing lately is fixing stuff less than 5 years old. Ray Walters Remote Solar On 4/25/2024 9:52 AM, Michael Morningstar via RE-wrenches wrote: Here's a different take. Just food for thought an

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Ray Walters via RE-wrenches
can't get enough air.   You didn't mention gen set model, or whether the frequency was a solid 60 hz.  I've seen bad things happen when the frequency got out of spec too.  I'm guessing a bad voltage regulator on the gen set. Ray Walters Remote Solar On 4/25/2024 11:24 AM, Ke

Re: [RE-wrenches] PWM Controllers in parallel

2024-05-07 Thread Ray Walters via RE-wrenches
inspection of the old array wiring will reveal it needs rewiring anyway.  Folks always blamed lightning for cooked connectors, when the real culprit was over paralleling.  I've seen the connections get so hot (4th module in parallel) that the j box was melted. Ray Walters Remote Solar O

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-26 Thread Ray Walters via RE-wrenches
the well, where the pressure is over 100 psi, I'd be using something better. Good Luck, Ray Walters Remote Solar On 5/26/2024 10:12 AM, Bradley Bassett via RE-wrenches wrote: Yes, lots of possibilities for leaks. I will be exploring them today. Thanks for the tips for finding the location.

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-27 Thread Ray Walters via RE-wrenches
adapters.  I have no idea who made them, or where I got them from. The closest I can find now are for poly gas line, and they're over $100/ fitting at Grainger. Main product photo I use PEX and Shark bite fittings for any plumbing I'm doing now.  Never had a leak, super fast, and r

Re: [RE-wrenches] Simpliphi Phi 3.8 48V Case Color

2024-05-29 Thread Ray Walters via RE-wrenches
idea, because of the age difference. As with lead acid, you probably could get away with it, but I don't think they would charge and discharge evenly. IMHO, those are too expensive to play with. Ray Walters Remote Solar On 5/29/2024 5:14 AM, Jason Szumlanski via RE-wrenches wrote:

Re: [RE-wrenches] How many times can a rafter have a lag screw put in and out before it is no longer structurally sound? Some roofs getting their 3rd set of new shingles

2024-05-30 Thread Ray Walters via RE-wrenches
nd installation. Unfortunately I think much of this will be lost, since some of the companies that roofers subcontract with to do these remove and replace jobs are not always the top solar contractors. Ray Walters Remote Solar On 5/29/2024 10:17 PM, William Miller via RE-wrenches wrote: Sco

Re: [RE-wrenches] Neutral run to critical loads sub-panel

2024-08-01 Thread Ray Walters via RE-wrenches
nches of the MLP, then I Would extend all branch circuit conductors, but I'd consider using a large J box adjacent to the MLP to keep all the extension splices out of the way. Ray Walters Remote Solar On 8/1/2024 12:06 PM, Jason Szumlanski via RE-wrenches wrote: I think it depends on how

Re: [RE-wrenches] Neutral run to critical loads sub-panel

2024-08-01 Thread Ray Walters via RE-wrenches
are not electricians. Code citations, please. Thanks, Ray Walters Remote Solar On 8/1/2024 2:44 PM, Dana Orzel via RE-wrenches wrote: Wire nuts in a breaker panel are not allowed per my inspector per code.  Pull the Romex out of the breaker panel & spllce in a wire gutter to extend. I have

<    8   9   10   11   12   13   14   >