Undoing the N-G bond at the E panel may not do it either.  Are you sure neutral isn't also bonded in the main distribution panel?  It usually is bonded at the generator, so you definitely have to unbond there.  I'd say 60 to 70% of off grid systems are not bonded correctly that I've seen.  Just what Kirk said: it should only be bonded N-G at one and only one spot.  Check sub panels too.  My record was seven N-G bonds on one site.  It caused the shower to be energized; the customer thought that was normal....(don't touch the shower head!?!).....That site even had a N-G bond in the well pump wiring!  Took 3 days of unF***ing that wiring to finally get it.

It ain't safe, until it's right.  The GFCI is doing its job, and so is the Magnum.  Now the electrician has to do his job.  Unless you wired the whole house, you're On to fix it.  Especially off grid, I see an amazing bunch of DIY garbage.  Find out who did the original wiring.  Probably not a pro.

Ray Walters
Remote Solar

On 12/16/2022 11:35 AM, Kirk Herander via RE-wrenches wrote:
You may have neutral and ground connected at more than 1 location, meaning at the genset and in house panel, which means the ground is carrying current back to the generator in parallel with the neutral.

I remember with some Honda portables we had to float the neutral at the genset or the inverter would trip the generator's GFI when trying to charge the batteries.

On Fri, Dec 16, 2022 at 1:16 PM Dave Angelini Offgrid Solar via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

    The easy answer is try another genset ! You have to be more
    specific, did it ever work? Is it new? etc. Good Luck !

    *Dave Angelini Offgrid Solar "we go where powerlines don't"
    http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net
    text 209 813 0060*


    On 2022-12-16 10:04 am, Chris Daum via RE-wrenches wrote:

    Hi folks:

    We have a new Magnum MS4024 mounted on an E-Panel using a MidNite
    Classic 150 and Whiz-Bang JR with power coming from an array of
    Trina TSM365-De06X-05(II) (three strings of three) with the
    ME-RC50 and a HUP SolarOne 6-85-14/24 battery.
    When we attempt to use the PFC (Power Factored Charger), the Gen
    Set’s GFCI outlets trip.  Thus far we have verified the
    connections are secure, assured that the gen set is grounded,
    disconnected the jumper within the E-Panel between the ground
    buss and neutral, checked AC voltages, removed the MNSPD’s from
    the buss(s)…  Stumped now on what an appropriate next step should
    be.  How do we get the PFC to function properly?  What are we
    missing?

    Best,

    Chris Daum
    Oasis Montana Inc.
    406-777-4309 or 4321
    406-777-4309 fax
    www.oasismontana.com <http://www.oasismontana.com>








    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org



--

*Kirk Herander / **kirkh@vermont.solar*

*Owner|Principal, VT Solar, LLC*

*/Celebrating our 31^st  Anniversary 1991-2022!!/*

*www.vermont.solar* <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>

dba Vermont Solar Engineering

802.863.1202


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to