Re: [RE-wrenches] battery venting; Corrosion

2012-01-05 Thread Kent Osterberg
John, Could you clarify units? "0.418 Liters/AH" is that per charge cycle? per hour? per minute? per cell? Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 1/5/2012 4:18 PM, John DeBo

Re: [RE-wrenches] battery venting

2012-01-06 Thread Kent Osterberg
Wrenches, While looking for information regarding standards about battery room ventilation I ran into this link, which has some good information and is certainly worth everyone's attention. http://www.belvoir.army.mil/safety/inc/battery-explosion.asp Kent Osterberg Blue Mountain Solar

Re: [RE-wrenches] Request for Gennie Recommendation

2012-01-09 Thread Kent Osterberg
ones are air cooled. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 1/9/2012 7:59 PM, Allan Sindelar wrote: Wrenches: We have cautiously agreed to take on a substantial upgrade and rehabilitation of a poorly designed 48V off-grid system. Our upgrade

Re: [RE-wrenches] battery venting; Corrosion

2012-01-16 Thread Kent Osterberg
rtly because it is intended to to cover all batteries and it is intentionally conservative. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 1/6/2012 5:53 PM, John DeBoever wrote: Wrenches, Thank you for your patience (as I was busy all day). I apprec

Re: [RE-wrenches] 24 vs. 48

2012-01-17 Thread Kent Osterberg
100-amp 24-volt charge puts about 25 amps (if you are careful with the wiring and the batteries aren't sulfated) into each string of batteries. A 50-amp 48-volt charger would accomplish the same thing. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On

Re: [RE-wrenches] 24 vs. 48

2012-01-17 Thread Kent Osterberg
the charge rate (C/X) that the batteries see is the same either way. Considering that lots of parallel strings of batteries is trouble waiting to happen and that a 48-volt system is more efficient, except for the smallest systems 48-volts is usually the way to go. Kent Osterberg Blue Mountain Solar

Re: [RE-wrenches] 24 vs. 48

2012-01-17 Thread Kent Osterberg
the charge rate (C/X) that the batteries see is the same either way. Considering that lots of parallel strings of batteries is trouble waiting to happen and that a 48-volt system is more efficient, except for the smallest systems 48-volts is usually the way to go. Kent Osterberg Blue Mountain Solar

Re: [RE-wrenches] 24 vs. 48

2012-01-17 Thread Kent Osterberg
-volt cells removed. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 1/17/2012 11:19 AM, Mark Frye wrote: Interesting. I can choose an OB VFX3524 w/ 85 ADC or an OB VFX3648 w/ 45 ADC of charging capacity. And assuming that I need C/10 during bulk charging

Re: [RE-wrenches] meter pan?

2012-01-24 Thread Kent Osterberg
the requirements. If the customer owns the production meter, then the utility company should have no say about it. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 1/24/2012 6:52 AM, mac Lewis wrote: Here in Xcel territory in Colorado, we are required to cold-sequence

Re: [RE-wrenches] How Is The M215 Doing?

2012-01-31 Thread Kent Osterberg
Mark, I haven't installed enough to speak to any reliability issues with the M215. But one thing I can say is that I like the new cabling system. The wire hangers make for a quick and clean looking cable installation. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t

Re: [RE-wrenches] wrenches] Battery Off Gassing and CO Detectors

2012-02-03 Thread Kent Osterberg
ow if these devices alarm before there is an explosive concentration of hydrogen? Sounds like recommending them for that purpose is risky. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 2/3/2012 8:23 AM, john wrote: Rich, I have found that having the CO detector anyw

Re: [RE-wrenches] Fwd: AC Coupled

2012-02-18 Thread Kent Osterberg
Larry, It sounds like the customer can power all loads with the generator and the non-critical load may even be the motivation for starting the generator? How about a relay that opens the SunnyBoy output or the Sunny Island input when the generator runs? Kent Osterberg Blue Mountain Solar

Re: [RE-wrenches] low head/low cost solar pump

2012-02-24 Thread Kent Osterberg
Mac, It probably doesn't pass the low cost hurdle, but this sounds like the perfect situation for a Dankoff Suncentric pump. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 2/24/2012 7:49 AM, mac Lewis wrote: Hi wrenches, I am looking for a relat

Re: [RE-wrenches] Adding acid to a battery

2012-02-24 Thread Kent Osterberg
necessary to equalize the battery until there is enough room for the replacement acid. Fortunately, it doesn't have to be done in one step. Since there was acid between the inner and outer case originally, I'd inspect carefully to make sure it is not filled with acid again. Kent Ost

Re: [RE-wrenches] Starting fires for fun with string wiring

2012-03-11 Thread Kent Osterberg
boB, Most local codes, have granted a delay on implementing arc fault protection. Also, the code only requires series faults to be cleared. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 3/11/2012 8:28 PM, b...@midnitesolar.com wrote: On 3/11/2012 7

Re: [RE-wrenches] Cracked Glass...Warranty?

2012-03-13 Thread Kent Osterberg
le to fracture from any minor stress. The glass will usually have larger fragments in that area and finer fragments farther away. A shorted diode should be warranty issue. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 3/13/2012 12:21 PM, benn kilburn wrote: Wrenches, I rec

Re: [RE-wrenches] Listed Battery Enclosure?

2012-03-22 Thread Kent Osterberg
I agree, Brian; especially when the battery system is large. It's important to design the room so it can be in compliance with NEC 480.9. (A) Ventilation, (B) Guarding live parts. The locked door qualifies, and (C) Working space. Kent Osterberg Blue Mountain Solar

Re: [RE-wrenches] Listed Battery Enclosure?

2012-03-22 Thread Kent Osterberg
Considering that wood trays are mentioned in NEC 480.8(B), it would be unreasonable to exclude wood. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 3/22/2012 5:24 PM, allso...@scswifi.net wrote: He stated "We cannot have any combustible materials&

[RE-wrenches] Evergreen Spruce 190 modules

2012-03-23 Thread Kent Osterberg
e off list. -- Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.c

[RE-wrenches] unusual module

2012-03-24 Thread Kent Osterberg
yone familiar with a low-voltage high-current Solarex module. -- Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http

Re: [RE-wrenches] unusual module

2012-03-24 Thread Kent Osterberg
Nathan, There are no jumpers, each j-box has a single terminal. It has 4" square multi-crystalline cells, a 2" bronze colored frame, and measures 17.5" x 42"; just a little smaller than a MSX-60. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com O

Re: [RE-wrenches] Unusual Module

2012-03-24 Thread Kent Osterberg
Allan, Your right about the modules from Carrizo being made by Arco. And weren't they mono-crystalline? Three of these modules in series would be 30 cells and not enough voltage for charging a 12-volt battery. But I think that's the biggest similarity to a Quad-Lam. Kent Oste

Re: [RE-wrenches] Off-grid ground mount: Can it be done cheaper

2012-03-24 Thread Kent Osterberg
tion plans. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 3/24/2012 10:29 AM, William Miller wrote: Daryl: Thanks for the photos and description of the mounts you are installing. We have installed many of the DPW ground mount systems in similar configurati

Re: [RE-wrenches] Off-grid ground mount: Can it be done cheaper

2012-03-24 Thread Kent Osterberg
Many inland areas in California, Oregon, and Washington are 85 mph zones. I think that's the lowest requirement anywhere in the U.S. I can't imagine designing for 185 mph winds. Doesn't that just blow the glass out of the modules? Kent Osterberg Blue Moun

Re: [RE-wrenches] small wind generators

2012-04-03 Thread Kent Osterberg
It is interesting that when you download the manual for the Sunforce 400, you get a 2002 vintage SWWP Air-X manual. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 4/3/2012 5:24 PM, Dan Fink wrote: Esteemed Wrenches; I've been watching this thread closely, an

Re: [RE-wrenches] Array spacing for optimum performance

2012-04-16 Thread Kent Osterberg
s than the latitude. This solution produces much less energy the maximum possible. And, of course, ignoring the value of the land or roof space isn't practical either. Ultimately, you have to look at what limits apply to the problem and work from there. Kent Osterberg Blue Moun

Re: [RE-wrenches] GFP and multiple charge controllers

2012-04-17 Thread Kent Osterberg
than on the charge controller output anyway. Midnite's instructions show the GFP on the charge controller input, but their 80-amp GFP is a single. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 4/17/2012 11:08 AM, Nathan Stumpff wrote: Wrenches, In a job coming up

Re: [RE-wrenches] GFP and multiple charge controllers

2012-04-18 Thread Kent Osterberg
r the charge controller. Except the the label and instructions the GFP and the GFDI are identical. In case you don't remember, the PSDC came with a schematic showing all possible options attached to the back of the front panel. When it comes time to troubleshoot sometime in the future,

Re: [RE-wrenches] GFP and multiple charge controllers

2012-04-18 Thread Kent Osterberg
lly a preventable circumstance: the GFP simply needs to open both PV+ and PV-. The manufacturers need to step up and correct this. The NEC needs to be changed to require it. This won't reduce the risks at the PV array, but it is certainly worth it to design components that don't but hom

Re: [RE-wrenches] GFP and multiple charge controllers

2012-04-18 Thread Kent Osterberg
ation of 110.3(B). I find the present situation very disturbing. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 4/18/2012 8:28 PM, Philip wrote: Hi Kent, I wanted to add a little more re positive grounding. OutBack's communication structure, like

Re: [RE-wrenches] Any experience with off-grid oxygen concentrators?

2012-04-21 Thread Kent Osterberg
I've got off-grid customers where both the husband and wife use oxygen at night. Because of energy supply limitations they use a liquid O2 system. But that may not be practical for a weekend use cabin. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 4/21/2012 12:

Re: [RE-wrenches] PV direct pump under 30V and conduit in building

2012-05-03 Thread Kent Osterberg
local codes specifying otherwise, MC cable should be allowed. Even that is overkill for a small 12-volt module. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 5/3/2012 9:34 AM, Jason Szumlanski wrote: I'd like some help with code references for an inspector th

Re: [RE-wrenches] Battery changing on SW inverter

2012-05-15 Thread Kent Osterberg
re not appropriate. Keep a copy of how you left the the system programmed in case there are ever any questions or need to reprogram it again later. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 5/15/2012 1:44 PM, Glenn Burt wrote: Hello wrenches, I am quoting a job t

Re: [RE-wrenches] PV into a resistor: please advise

2012-05-19 Thread Kent Osterberg
er is designed to boost the current when the voltage (and resistance) are less than optimum, so I think it would improve the power transfer. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 5/19/2012 12:35 PM, Mick Abraham wrote: Hi, Wrenchies~ Kindly educate me regardi

Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread Kent Osterberg
Steve, It would be appropriate for the GFDI to have 80-amp rated contacts that do not have an over-current trip mechanism. IMHO, the fact that they can trip on over-current and unnecessarily interrupt the dc system bond is a serious design flaw. Kent Osterberg Blue Mountain Solar, Inc

[RE-wrenches] Integrated GFDI (branch from Finding Ground Faults)

2012-05-23 Thread Kent Osterberg
It is safe to return to the list now. The rant is over. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 5/23/2012 12:18 PM, Steve Higgins wrote: From what I understand, future controllers from Outback Power will incorporate the Ground Fault detection into the co

Re: [RE-wrenches] Corrective EQ question

2012-06-01 Thread Kent Osterberg
plates. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 6/1/2012 1:28 PM, Allan Sindelar wrote: Wrenches, A long-time off grid client has a 48V Outback VFX system, with 1,680 watts of PV and two strings (16 batteries total) of Deka L16s, installed last October

Re: [RE-wrenches] Magnum Energy Remote Control

2012-06-28 Thread Kent Osterberg
ng as the ME-RC remote is connected)." So, if the default settings aren't adequate, your customer's will need a remote. They need it to equalize the batteries anyway. And since every battery system should have a battery monitor, there may as well be a remote for the purpose of using th

Re: [RE-wrenches] combiners and the 120% rule

2012-07-01 Thread Kent Osterberg
ckfed with micro-inverters. A few small loads on this panel just lowers the current on the bus bars. The risk that the 120% rule is supposed to address is the possibility of overloading the bus bars. In the case of the ac combiner that could happen if someone were to add some very large loads to

[RE-wrenches] Smart grid grid-connected compatibility

2012-07-05 Thread Kent Osterberg
ompatibility problems for various technologies. -- Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrench

Re: [RE-wrenches] Needed: Outback setpoints that won't ruin AGM's

2012-07-07 Thread Kent Osterberg
otherwise it'll be terminating the charge too soon. Realistically, you may as well disable the end amps feature. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 7/7/2012 2:53 PM, Mick Abraham wrote: Greetings, All~ My client's string of SunXtender two volt A

[RE-wrenches] Smart grid grid-connected compatibility

2012-07-08 Thread Kent Osterberg
l just have to live with the lost production time. Until Enphase comes up with a fix, I won't install any more Enphase inverters. -- Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 ___ List sponsored by

Re: [RE-wrenches] Smart grid grid-connected compatibility

2012-07-08 Thread Kent Osterberg
sending data. Never-the-less, it's actually easy to make a reliable frequency measurement by shifting the measurement threshold off zero far enough that the TWACS signal doesn't interfere. The Enpase folks should be able to do that with a firmware change. Kent Osterberg Blue Mountain

Re: [RE-wrenches] Smart grid grid-connected compatibility

2012-07-09 Thread Kent Osterberg
in the utility meter so it's going to both the customer and the substation. Also, the TWACS signal can be adjusted if necessary to generate a bigger signal. I guess that would be their first step in handling a site with a large capacitive load. Kent Osterberg Blue Mountain Solar, Inc. www.b

Re: [RE-wrenches] Smart grid grid-connected compatibility

2012-07-09 Thread Kent Osterberg
ssing, for about 8 or 10 seconds, while data are sent. I managed to capture the event with a scope and the waveform distortion is probably well less than 2% and much less than the distortion inverters are to allowed cause. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 54

[RE-wrenches] Mitsubishi MF170 needed

2012-07-14 Thread Kent Osterberg
Fellow wrenches, If anyone happens to have a Mitsubishi MF170 that is available, please contact me off list. I need one to add to a customer's small system. -- Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568

Re: [RE-wrenches] Outback with grid charging

2012-08-24 Thread Kent Osterberg
mable, the same meter can be used to record net energy - behave like most disk-type meters; ignore energy in one direction - behave like a detented meter; or record both incoming energy and outgoing energy separately - a two register meter. Kent Osterberg Blue Mountain Solar, Inc. www.bluemounta

Re: [RE-wrenches] Outback with grid charging

2012-08-24 Thread Kent Osterberg
Jesse, Sometimes the best thing you can do for a customer is document, in writing, what's wrong. And walk away if they aren't willing to fix it. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 8/24/2012 6:36 PM, Jesse Dahl wrote: Im with you on the wisdom o

Re: [RE-wrenches] Extensive Lightning Damage to Modules

2012-09-07 Thread Kent Osterberg
wire loop. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 9/7/2012 7:40 AM, Jeff Irish wrote: A customer of ours has recently suffered lightning damage to 31 out of 160 top of pole mounted modules. This is the first time in 10 years that I've se

Re: [RE-wrenches] Extensive Lightning Damage to Modules

2012-09-07 Thread Kent Osterberg
induced voltages. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 9/7/2012 11:14 AM, Jeff Irish wrote: Kent, Surge protection is at the inverters, 200 feet away, on both the AC and DC sides. Nothing at the array; never thought we'd need it

Re: [RE-wrenches] Disconnect BOTH positive and negative conductors from array?!?

2012-09-14 Thread Kent Osterberg
See 690.13. There must be a means to disconnect all conductors of a PV system. If it is a normally grounded array you are not allowed to put a switch in the grounded conductor, except for circumstances added in the 2011 code. Kent Osterberg Blue Mountain

Re: [RE-wrenches] Disconnect BOTH positive and negative conductors from array?!?

2012-09-14 Thread Kent Osterberg
ray, which will probably become more common as equipment is designed to operate that way, both conductors are supposed to be switched in the disconnect. In that case there shouldn't be any white wire going to the PV array. Kent Osterberg Blue

Re: [RE-wrenches] Fronius State 104

2012-10-08 Thread Kent Osterberg
data. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 10/8/2012 9:34 AM, Jeff Wongstrom wrote: Hello wrenches, We have a Fronius IG3000 that chronically and frequently cycles into and out of a state 104(grid freq

Re: [RE-wrenches] Fronius State 104

2012-10-09 Thread Kent Osterberg
blems with the time sync signal, I'd guess that the installation must be close to the substation where the signal originates. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 10/9/2012 9:20 AM, Jeff Wongstrom wrote: Kent, I just talked with Mike in the m

Re: [RE-wrenches] center fed main panel and 120% rule

2012-10-15 Thread Kent Osterberg
And what about the SQ D QO or HOM 6-12L100 or 8-16L100 panels that can be fed with main lugs that are on opposite ends (left for L1 and right for L2)? Seems like you shouldn't apply the 120% rule to these either. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 1

[RE-wrenches] AstroPower 120

2012-10-30 Thread Kent Osterberg
Does anyone happen to have one or two AstroPower AP1206 120-watt modules that they can part with? If you do, please contact me off list. Thanks. -- Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com ___ List sponsored by Home Power

Re: [RE-wrenches] Enphase and Romex

2012-11-01 Thread Kent Osterberg
d. Don't expect everyone to accept this practice. You might need a j-box in the attic to change wire type to NMC cable or THWN wire. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 11/1/2012 5:07 AM, Chris Mason wrote: I remember from a project we were doing that requi

[RE-wrenches] 3R box on the roof with snow?

2012-11-01 Thread Kent Osterberg
osure-types.pdf <http://www.nema.org/Products/Documents/nema-enclosure-types.pdf> From NEMA's definitions there is little difference between a type 4 box and 3R box. But the seal on a type 4 box prevents the entry of blowing snow while a 3R box doesn't. -- Kent Osterberg Blu

Re: [RE-wrenches] EMT in attic

2012-11-03 Thread Kent Osterberg
There is no need for an exception. Even in the 2008 NEC, 690.31(E) is clearly about the dc wiring. The proposed informational note adds nothing except to explain that ac isn't dc. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 11/3/2012 11:09 AM, Dan Fink

Re: [RE-wrenches] EMT in attic

2012-11-08 Thread Kent Osterberg
Article 100 has a definition for service. It doesn't seem like a PV system or a battery based inverter for off-grid fit the definition. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 11/8/2012 8:22 PM, Nick Vida wrote: Hi Wrenches, Thanks for you comments. Fun fo

Re: [RE-wrenches] Best practices for conduit penetration on roof

2012-11-25 Thread Kent Osterberg
My understanding has been that the Soladeck has only been listed for DC wiring. Perhaps they have a manufacturer rep on RE-wrenches that can clarify. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 11/25/2012 6:20 AM, Dave Palumbo wrote: Rich, We have been using

Re: [RE-wrenches] off-grid permitting problem

2012-12-12 Thread Kent Osterberg
rated to provide 63 amps continuously. Most 200-amp service panels don't really have 200 amps available except for short durations. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 12/12/2012 4:43 AM, Jason Szumlanski wrote: See 690.10, 690.1, and 690.3

Re: [RE-wrenches] Radian design limitation - am I missing something?

2012-12-16 Thread Kent Osterberg
r MPPT tracking, over the Midnite Classic or Morningstar TriStar MPPT charge controllers. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 12/16/2012 10:51 AM, Kirpal Khalsa wrote: Allan...indeed this is a limitationand yes i agree with you that a higher voltage charge c

Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread Kent Osterberg
If you are using the 2011 NEC, 705.12(D)(2) has an exception to the 120% rule for inverters with energy storage to allow for operation of loads. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 12/30/2012 4:27 PM, Jeremy Rodriguez- All Solar Inc. wrote

Re: [RE-wrenches] power monitor hardware

2013-01-16 Thread Kent Osterberg
transmits data via 433 MHz radio instead of power line carrier. Noisy inverters don't seem to bother it. Efergy meters are ETL listed, and are considerably cheaper than TED. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On 1/16/2013 2:07 PM, Kirk He

Re: [RE-wrenches] Enphase "AC Frequency out of Range"

2013-02-07 Thread Kent Osterberg
grees before the zero crossing. Supposedly, they increase the firing angle to get a stronger signal from sites that are hard to reach. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 2/7/2013 2:13 PM, Nick Soleil wrote:

Re: [RE-wrenches] Accessibility of Equipment on Roof was Are PV Systems Mechanical Equipment?

2013-02-08 Thread Kent Osterberg
roof should be permitted. There should also be an accessible disconnect elsewhere (at the panel feeding the combiner for instance.) That (may) makes the breakers in the ac combiner supplementary and thus they wouldn't have to be accessible. Kent Osterberg Blue Mountain Solar

Re: [RE-wrenches] Alarm start stop alarm

2013-02-08 Thread Kent Osterberg
I've got a customer that has outside lights that are only on when the generator runs. Also has a siren/strobe light alarm that comes on when the batteries are below the 2-minute threshold for the generator start. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 54

Re: [RE-wrenches] DC generators

2013-03-05 Thread Kent Osterberg
rging batteries in renewable energy systems. Considering the market for these, the normal unit is probably set up to provide a float charge voltage. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 3/5/2013 7:17 AM, jay peltz wrote: HI All, I know many of you like

Re: [RE-wrenches] Relay for excess PV/ AC coupling

2013-03-06 Thread Kent Osterberg
wall wart power supply would operate it. About $150 at Mouser.com <http://www.mouser.com/Search/Refine.aspx?Keyword=G9EB> You shouldn't have to switch at 600 volts. It should work just as well to short the lowest voltage pair of modules. Kent Osterberg Blue Mountain Solar, Inc. w

Re: [RE-wrenches] Relay for excess PV/ AC coupling

2013-03-06 Thread Kent Osterberg
ommon wall wart power supply would operate it. About $150 at Mouser.com <http://www.mouser.com/Search/Refine.aspx?Keyword=G9EB> You shouldn't have to switch at 600 volts. It should work just as well to short the lowest voltage pair of modules. Kent Osterberg Blue Mountain Solar, Inc. w

Re: [RE-wrenches] Relay for excess PV/ AC coupling

2013-03-06 Thread Kent Osterberg
How about this unit from Tyco that is rated 100 amps at 900 volts: http://www.te.com/catalog/pn/en/9-1618389-8?RQPN=LEV100A5ANG and only $110 at Mouser <http://www.mouser.com/ProductDetail/TE-Connectivity/LEV100A5ANG/?qs=%2fha2pyFadug1f8yBSHppXCbQVN7JiNYp4qGSI0ewLzHnRcQBcz6gcA%3d%3d>.

Re: [RE-wrenches] solar ramp

2013-03-16 Thread Kent Osterberg
y that would be different for a utility scale system where clouds could reduce the output of an entire plant in a few short amount of time. The article may have been in /Solar Today/, /Solar Industry/ or /Sun & Wind Energy/, unfortunately I can't find it now so maybe it was somepla

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-06 Thread Kent Osterberg
le strings of batteries. 2011 NEC 240.21(H) allows overcurrent protection to be installed as close as practical to battery terminals - even in classified locations. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 4/6/2013 7:29 AM, Phil Undercuffler wrote: Ray, 690 d

Re: [RE-wrenches] Enphase "AC Frequency Out Of Range"

2013-04-15 Thread Kent Osterberg
Dave, The problem occurs when the kWh meter sends data. I would expect any neighbors' meters on the same transformer to cause trouble. And probably neighbors that are not on the same transformer too. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com t: 541-568-4882 On

Re: [RE-wrenches] Micro-inverters for 3-phase 220/127 in Mexico

2013-04-15 Thread Kent Osterberg
Enphase lists the standard operating range for the 208-volt 3-phase configuration as 183 to 229 volts. Seems like 220-volt 3-phase might work with a little caution about wiring losses. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 4/15/2013 4:28 PM, Larry Crutcher

Re: [RE-wrenches] Modules approved for horizontal mounting

2013-04-20 Thread Kent Osterberg
The problem they'll have with a completely flat module is that rain won't wash the dust off. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 4/20/2013 10:09 PM, Benn Kilburn - DayStar Renewable Energy wrote: Carl, I realized mis-read/answered your question. I

Re: [RE-wrenches] TR Inverter Problems

2013-04-30 Thread Kent Osterberg
onths ago, I was asked to participate in a survey regarding Xantrex products and service. My responses must have got someone's attention because I got a follow-up call about the survey. There never has been a follow-up to correct this customer's problem inverter. Kent Osterberg Blue

[RE-wrenches] AC coupled ProSine

2013-05-13 Thread Kent Osterberg
Has any put together an ac-coupled system using the Xantrex ProSine inverter? I've got a customer that wants to try this and I don't even know if it is possible to do with the ProSine. I'd rather not be the first to give it a try. -- Kent Osterberg Blue Moun

Re: [RE-wrenches] AC coupled ProSine

2013-05-13 Thread Kent Osterberg
Thank you, David. I knew someone monitoring this list would know if it would work. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 5/13/2013 4:06 PM, David Katz wrote: Hi Kent, It will blow up. The Prosine is not bi-directional. You can only use an H-Bridge type

Re: [RE-wrenches] SE or SW

2013-05-15 Thread Kent Osterberg
nergy production with the 135° azimuth, the optimum tilt angle is about 60° and that gives 12% more energy in December than the 35° tilt would (without considering how much better the steep tilt does at shedding snow). The SE roof with the steeper pitch is certainly the better choice. Kent Oste

[RE-wrenches] Enphase M190 failures

2013-05-17 Thread Kent Osterberg
d to fail before the site met Enphase's criteria for replacement? I'd like to get an idea of how long I'll be in this mess. -- Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com ___ List sponsored by Home Power magazine

Re: [RE-wrenches] Combining Enphase M190 and M215 on same circuit

2013-05-19 Thread Kent Osterberg
fine. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 5/18/2013 3:26 PM, Jason Szumlanski wrote: Is there any reason I can't do this? I have an existing string of 3 M190's and want to add 7 M215's. I plan to tie into the same j-box, which has #10 going to a fusi

Re: [RE-wrenches] Enphase M190 failures

2013-05-20 Thread Kent Osterberg
Thanks for your input, Carl. That data looks pretty grim. This is a serious black eye for our industry. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 5/20/2013 12:36 PM, Carl Adams wrote: Ken, We installed our first Enphase units in Dec 2009, and our *last* Enphase

Re: [RE-wrenches] FM80

2013-05-28 Thread Kent Osterberg
Jesse, The controller is supposed to limit the output current to 80 amps. But the 80-amp GFDI breakers will trip anyway. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 5/28/2013 9:01 PM, Jesse Dahl wrote: When I was looking at the Outback Flexone setup today during

Re: [RE-wrenches] Gray code area

2008-07-27 Thread Kent Osterberg
utility on the bus bars? Or do you have one point of interconnection at the line side of the 200-amp breaker? I think it is really the second and I think that is what the electrical contractor was thinking. You may need to label the panel to make it clear that it isn't for loads. Ken

[RE-wrenches] System bond through DC GFP

2008-07-27 Thread Kent Osterberg
Generally a system bonding conductor must be as large as the GEC, 8 AWG minimum. Inverter manufacturer's often have a smaller conductor make the system bond through the inverter's GFP. For factory assembled and listed products, the small conductor is obviously accepted by a testing/listing la

Re: [RE-wrenches] utility EDS signage

2008-11-19 Thread Kent Osterberg
likely to send an emergency responder on a wild goose chase. Kent Osterberg Blue Mountain Solar Phil Schneider wrote: Wrenches, Our utilities require an external AC disconnect between the inverter and the point of interconnection, located next to the meter. In the past, we have marked this switc

Re: [RE-wrenches] DC Rating of Disconnects

2008-11-21 Thread Kent Osterberg
Peter, Many general duty safety switches, such as the Siemens GNF321R, are rated for 250 volts dc. They usually require the use of two switch poles. Kent Osterberg Blue Mountain Solar Peter Parrish wrote: Peter T. Parrish, Ph.D., President California Solar Engineering, Inc. 820

Re: [RE-wrenches] Square D 225A load center

2008-12-04 Thread Kent Osterberg
Almost right Christopher. NEC 705.12(2) allows the ratings of the overcurrent devices supplying power to the bus bar to be 120% of the busbar rating. For a 225-amp busbar that amounts to 270 amps. So a 200-amp main breaker and a 70-amp back fed breaker from the solar system. Or a 225-amp ma

Re: [RE-wrenches] SS zip ties

2008-12-10 Thread Kent Osterberg
Fastenal has stainless ties is various lengths http://www.fastenal.com/web/products/detail.ex?sku=0710242 For those that haven't used these before, beware that it is difficult to tighten them. Kent Osterberg Blue Mountain Solar ___ List spon

Re: [RE-wrenches] Mates Losing time & dates

2008-12-15 Thread Kent Osterberg
Mark, Any chance that the relay controlling the generator is in a FlexNet DC? I've had a least one customer's generator not shut down and was pretty sure that it was the latching relay in the FlexNet DC that was the culprit. Kent Osterberg Blue Mountain Solar Mark Dickson w

Re: [RE-wrenches] Wanted: poly battery boxes, many sizes

2009-01-29 Thread Kent Osterberg
Larry, I've found the Contico Pro Tuff Bin (Lowes part number 91573 - $65, or Grainger part number 1DZE8 - $70) to work well for holding four L-16 batteries. Kent Osterberg Blue Mountain Solar www.bluemountainsolar.com Starlight Solar, Yuma, AZ wrote: Greetings Wrenches, I need to f

Re: [RE-wrenches] Wanted: poly battery boxes, many sizes

2009-01-29 Thread Kent Osterberg
Larry, Here's another battery enclosure we've used: http://www.radiantsolartech.com/batteryboxes.html These items are also available from AEE Solar. Kent Osterberg Blue Mountain Solar www.bluemountainsolar.com Starlight Solar, Yuma, AZ wrote: Greetings Wrenches, I need to find a s

Re: [RE-wrenches] Charging with Outback

2009-03-03 Thread Kent Osterberg
. When you are only getting 3-amps into a 400-amphour battery, the solar system contribution is negligible anyway. None-the-less, poor performance is not expected from first rate gear. Kent Osterberg Blue Mountain Solar William Miller wrote: Friends: We have been noticing that when equa

Re: [RE-wrenches] Solar vent for flat roof

2009-04-08 Thread Kent Osterberg
other charging sources, a solar vent fan wouldn't be adequate. Kent Osterberg Blue Mountain Solar   Allan Sindelar wrote: We have twice used pairs of Zephyr Power Vents to successfully vent large banks, up to around 2200A/hr @48V. A 12V unit exits roof or wall with a 2" pvc stack;

Re: [RE-wrenches] Solar vent for flat roof

2009-04-08 Thread Kent Osterberg
ting for the battery room, we provided positive pressure to the room with the vent fan outside the room.  This avoided the issue of using a vent fan rated for explosive environments.  The ceiling vent is completely passive. Kent Osterberg Blue Mountain Solar Dana wrote: Kent –

Re: [RE-wrenches] Ampacity Ratings for Different Conductors

2020-08-11 Thread Kent Osterberg
temperature, maybe around -10%, should be included too. It looks like Cotek recommends a minimum cable size of 1/0, so out of fear of starving the inverter of enough voltage, I wouldn't use any smaller. Kent Osterberg Blue Mountain Solar On 8/11/2020 3:18 PM, peter...@pobox.com wrote: I have

Re: [RE-wrenches] Puzzle: Dryer does not work during FXR battery charging

2020-08-15 Thread Kent Osterberg
ency noise. Kent Osterberg Blue Mountain Solar On 8/15/2020 8:06 AM, Matt Sherald wrote: Hello All, My curiosity was piqued by a recent customer complaint. I'm hoping someone has bumped up against this issue before. The customer has a OB FXR2812 and a 3,000W Honda gen. Her gas clothes

Re: [RE-wrenches] Modifying a plumbing vent

2020-08-31 Thread Kent Osterberg
el. Pretty sure vent pipes under the array are not a good idea for many of us. Kent Osterberg Blue Mountain Solar 70177 Ponderosa Ln. Cove, OR 97824 www.bluemountainsolar.com On 8/31/2020 6:40 AM, Matt Partymiller wrote: Scot, What do you interpret the last part of that section to