Generally a system bonding conductor must be as large as the GEC, 8 AWG minimum. Inverter manufacturer's often have a smaller conductor make the system bond through the inverter's GFP. For factory assembled and listed products, the small conductor is obviously accepted by a testing/listing lab. The MidNite and Outback GFPs are often field installed and they come pre-wired with 14 AWG. Obviously this is large enough if the GFP trips at 1/2-amp or 1-amp. Seems to me that the Code section that requires a DC GFP should address the system bonding conductor size.