Almost right Christopher. NEC 705.12(2) allows the ratings of the
overcurrent devices supplying power to the bus bar to be 120% of the
busbar rating. For a 225-amp busbar that amounts to 270 amps. So a
200-amp main breaker and a 70-amp back fed breaker from the solar
system. Or a 225-amp main breaker and a 45-amp back fed breaker from
the solar system.
Christopher Freitas wrote:
Ahhh – I think I get it – you get the 20% of the 200 amps (so 40 amps) +
the extra 25 amps because the buss is only running at 200 amps?
I just saw you emailed me…
Christopher
Christopher Freitas
Director of Research and Development
OutBack Power Systems, Inc.
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>
Tel 360 435 6030
Cell 360 202 4239
19009 62^nd Ave NE
Arlington WA 98223 USA
www.outbackpower.com <http://www.outbackpower.com/>
------------------------------------------------------------------------
*From:* [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] *On Behalf Of *David
Brearley
*Sent:* Thursday, December 04, 2008 11:41 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Square D 225A load center
It has an option for a factory-installed 200A main breaker.
On 12/4/08 12:31 PM, "Christopher Freitas" <[EMAIL PROTECTED]>
wrote:
How does the 225 amp rating make it ideal for 60 amp breakers? 20% of
225 amps is 45 amps – and even with “rounding up” it only gets you to 50
amps.
Christopher
Christopher Freitas
Director of Research and Development
OutBack Power Systems, Inc.
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>
Tel 360 435 6030
Cell 360 202 4239
19009 62nd Ave NE
Arlington WA 98223 USA
www.outbackpower.com <http://www.outbackpower.com/>
------------------------------------------------------------------------
*From:* [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED]
<mailto:[EMAIL PROTECTED]> *On Behalf Of
*Andrew Truitt
*Sent:* Thursday, December 04, 2008 8:33 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Square D 225A load center
Greetings all! I heard that Square D makes a load center with a 225A
buss bar and a 200A main breaker - ideal for installing 60A of solar
interconnection breakers. Does anyone have a part number (or any other
info) on this item?
Thanks!
Andrew Truitt
Standard Solar
MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be
protected by attorney-client or other privilege. If you believe that it has
been sent to you in error, please do not read it. If you are not the intended
recipient,you are hereby notified that any retention, dissemination,
distribution, or copying of this communication is strictly prohibited. Please
reply to the sender that you have received the message in error, then delete
it. Thank you.
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org