Hi William,
We have a half dozen plus off grid systems using SolArk inverters and
TIGO optimizers. They work well and the TIGO's, from my experience,
have been really reliable. The necessary 12 volt signal can come
directly from the relay in the SolArk inverter.
Best,
Daryl DeJoy
NABCEP Certifi
Hi Nick,
We have about 16 SolArk's installed and have a single 12 kW that has
that "bus imbalance" error every once in a while. It seems to be a
specific appliance (electric mixer) that it does it with, and only
occasionally. I spoke with SolArk about it and they have a small "plug
in" that does
I would reiterate you take a look at Fortress Evaults. We have many, and
in multiple numbers, installed with SolArk and they are an elegant
solution.
Daryl
> Hi Jason,
>
> Simpliphi AccESS taps out at a maximum of 22.8 kWh per unit. I really
> appreciate the integrated bussing system on the Acc
We have been using them regularly with Fortress Power EVaults (18.5 kW)
with very good results. Fortress is working on the communications between
the two, already have their Flex5Kw battery working with it. Easy to
install, dependable and the 400 lb EVault is on wheels. Just back from
installing a
We've had great luck using the Tigo (and SMA) optimizers with SolArk to
conform to NEC2017 and CEC2018.
> There is a huge distinction in a hybrid inverter that integrates MPPT
> charge control. Eliminating all of the extraneous hardware and circuit
> protection associated with charge controllers
Hey Bill,
They're still small enough that, at least so far, there is no hold music!
And we combine ac outputs with an "ac combiner panel" simply a single
phase or three phase panel, with each inverter feeding a breaker in that
panel and ensuring that we use either a main breaker that can be back
What do you see, Dave? We have 6 12 kW and two 8 kW installed so far in
the Bahamas and two here in Maine, all with Fortress batteries, and I
cannot be more pleased. I do wish they had a remote monitor panel for
easier at home monitoring and I guess I would rather they had their own
monitoring syst
http://www.magneticshoes.com/home
> we switched to "clear" soda as the cola's and colored variety were
> sometimes leaving trace evidence behind on (un coated) galv roofing.. it
> is still critical you anchor up so the crew has something to hold onto..
> Be safe out there humans!! đź‘Ť
>
> Joe Nels
I second Jay's suggestion to look at the SolArk. The 8kW has no battery
disconnect, but the 12 kW has one, if you're using non-lithium based
batteries.
Daryl
Penobscot Solar Design
> HI Dave,
>
> The reason I’ve not used it, is that is has no surge.
>
> You might also look at the Sol Ark
>
> J
Fortress EVaults have their own lcd screen with Soc, but Dave is right,
it's not as accurate on RE Optics. We do get a battery reading without any
add-ons, they are just usually off up to 10% from each other.
>
>
> Hi David,
>
> They all work but none of them can get Soc and a few other
> things ou
Hi Dave,
We've been using Fortress Power EVaults (18.5 kw per) with good results
with Radian 8048's
Daryl
> Hello Wrenches,
> I am working with some people that want to use a 20 kw-hour to 30 kw-hour
> 48 volt lithium-ion battery with an Outback Radian and Outback FM charge
> controllers.
> They
We have been using Fortress 18.5 kWh, 48 volt battery banks with SolArk
inverters. Six and six work well for a 100 kW system. With SolArk (and
really, all batteries) it is highly recommended to use busbars to parallel
all battery connections. This also makes it easy to double the battery
size.
Dar
Hi Kent,
We have two 8 kW and four 12 kW installed in the Bahamas. We installed
one in a bedroom closet about two months ago and the client is still
happy. There are some relays and occasional hum but to my ears, they
are less noisy than the XW+ and certainly no more than the Radian. The
initial
The easiest way is using TS4-A-F (TIGO) optimizers.
> How is rapid shutdown achieved with Sol-Ark?
>
> On Sun, Feb 2, 2020 at 1:45 PM wrote:
>
>> I'm with you Joe,
>>We have a half dozen installed in the Bahamas, off grid and multiple
>> hybrid uses, and they are my go-to from now on. The 12
I'm with you Joe,
We have a half dozen installed in the Bahamas, off grid and multiple
hybrid uses, and they are my go-to from now on. The 12 kW I
particularly like and they are coming out with a more "universal"
communications dongle for the slightly confusing current online
monitoring choices.
One of my pet peeves with SolarEdge (I have a few) is that we are now
forced to buy the StorEdge inverters with GSM service, an extra $400 or so
added to the price of the inverter. The carrier is T-Mobile, which does
not work in 95% of Maine. It does not seem to work with other carriers
where we in
Hi all,
I have been registered as an installer for Schneider tech support for
quite a while. I no longer have a way to contact them. The number I
received refers me to internet support. Any help out there. I have a
bad out of the box off grid Conext SW 2524.
Thanks for any help,
Daryl
Hi Howie,
Have you looked at Fortress Power batteries? We're about to install
some and they look like a very decent battery. Google will get you the
basic info to start.
Daryl
Penobscot Solar Design
> Hi Folks,
> About to spec my first Lithium battery backup job. The client is not a
> hea
I would like to add my experience with Tesla so far.
We applied to be an installer in Maine more than a year ago. Beside
getting an initial email stating that they received our application, we
have not heard a word since. I have one client with a SolarEdge 7600
StorEdge who put a deposit down in Ma
Hi Dana,
We have been using Grundfos SQ-O 1/2 hp, 5 GPM (or they have a 10 GPM
model) soft start pumps for years, with great outcomes. We have sold 60
or so over the years with no returns.
Daryl
> Hey all you solar wise guys,
>
>
>
> I am looking for a recommendation based on your experi
Hi Jay,
My advice is walk away unless they want to meet your terms. You will
save yourself a tremendous amount of trouble/waiting/lost sleep/lost
money. I do 50% of my business internationally, mostly in the
Caribbean. If they do not accept my very reasonable terms (prepay for
all materials, 50%
FYI Howie,
Schneider engineers are actively working on a communication solutions
between the Schneider Xanbus and Midnite controllers. I've been talking
to an engineer working on it who says it should be ready very soon. It
will also work with the combox for remote monitoring.
Daryl
> Hi All,
I just spent a couple of months over the past year in Western PR,
investigating possibly buying a home.living/working/doing business
there. I was unimpressed with the solar companies I talked with. The
biggest company, with offices across PR, had racking which I would
never use in Maine, never m
Funny, Tom, I was just looking at these as well and wondering if they
would work with SolarEdge StorEdge solutions. The Tesla Powerwall 2, which
several of my clients have deposits down on, seems to be only ghosts,
although with an excellent PR firm behind themI'm looking for
alternatives.The L
That is true. The problem is selling a product and saying you will provide
installer compensation, then withdrawing it when you feel like it is a
very short term "fix". They have alienated many installers who have been
installing and selling their product for many years and you'd think that
if they
I believe that I found out for certain. I spoke to two different people at
Enphase and was "assured" that I would not be compensated as of June 1,
2017 for any M-190 replacements. I told them I would be purchasing
SolarEdge, not Enphase, from now on until they felt that, as I do, they
were breaking
Hi all,
For those who have installed M-190's, Enphase has now discontinued as
of June 1st any installer compensation for replacing failed
microinverters with that designation. We have a system we installed in
2011 that I found out today, after replacing the three failed M-190's,
that I was on my
Sorry, 200 amp main breaker in a 400 amp rated panel.
> Hi Daryl,
>
> From your description, yes, if you are attaching to lugs connected to
> busses and then to the 400A main breaker, with no other overcurrent device
> between, you would have to size the wire for the 400A rating.
>
> Brian Teitel
I re-read and see that I need to clarify my earlier question. The 400 amp,
120/208 panel has a main breaker that will be used for the utility input,
coming in on 3/0 copper. The four 60 amp breakers will be used because
the four 10 kW inverters maximum ac output is 48 amps each (x 1.25 =60
amps oc
Esteemed wrenches,
We're working often in the Bahamas and now that net metering is
approved there, the inspectors are far behind in their comprehension.
That said, we are currently required to combine the utility with the PV
in a main load center before going to the generator transfer switch. I
These guys sell all sizes:
https://www.buyrailings.com/product/hanger-bolt-316-stainless-steel-m8-x-2-each-/5368?gdffi=a1d228a0145c40b2b64b7bf62559eafa&gdfms=A2FA3E88DA104CFB950485A2F169884A&keyword=&gclid=CNmksPTrs9QCFQpMDQod7S0LYA
Daryl
> Dear Wrenches,
> Can anyone direct me to a source for
Esteemed wrenches,
Would anyone have a suggestion for an 8-10 kW 3 phase 208/120 battery
based inverter that might be ac coupled with a Solaredge grid tied
system already in place? None of the usual suspects (OutBack,
Schneider, Magnum,SMA, etc.) will work without considerable expense.
Has an
I have used three strings of these for three seasons now and they keep on
tickin'...decent company and decently made lights with a lot of variety:
https://www.environmentallights.com/led-christmas-lights/led-solar-string-lights.html
Daryl
> I would also like something that is built for the lon
I'm not sure if Daniel Two Eagles is still working with Apollo, but his
number is (603)654-4333. Maybe he can help if these other suggestions
don't.
Daryl
> I believed I used the below number about a year ago:
>
> 203-790-6400 <%28203%29%20790-6400>
>
>
> I've also used:
>
>
> techsupp...@apollo
I'll rephrase this and possibly someone has a suggestion. In the Bahamas
(they use CEC 2015), they are currently not allowing any load side taps in
gentran switches. They suggest including a large, expensive load center
with backfed breakers to combine the utility and pv ac output before
connecting
Is anyone out there familiar enough with CEC 2015 to answer a question for
me about load side taps in a generator transfer switch? To the best of
your knowledge, is using load side taps allowed when connecting PV to the
utility side of an ATS?
Thanks,
Daryl DeJoy
NABCEP Certified PV
Penobscot Sola
They aren't out of business. The downside, for me, is that the standard
racking we use (SnapN Rack) comes in 122" and 162" lengths. I think of
these as three module and four module lengths. With Solaria, they're not.
The modules are too wide (41.6") for the "standard" configuration. There
is a nort
William,
The only place we use splicing is in the transition box, where we
transition from USE/RHW or PV wire to THWN in conduit. We almost always
have this transition in smaller systems without need of a combiner box.
I suspect it is the same for others. In larger systems there is no need
for s
Chris,
I had this happen once about six years ago. We do torque to specs, but
anything is possible. We have been using Burndy products for the past
five years and have zero problems with them. They are actually just a
little bit less in cost than Polaris.
Daryl DeJoy
NABCEP Certified PV
Penobsc
Hello wrenches,
I have a serious inquiry from a man in Saluda, SC. Is anyone on here
close to this area of western South Carolina and want a live one?
Please contact me off list.
Thanks,
Daryl
___
List sponsored by Redwood Alliance
List Address: RE-
Jeff Randall
RC FAB Corporation
2615 Princeton Dr NE
Albuquerque, NM 87107
505-503-6459
Cell: 505-288-5552
> He changed the name to RC Fab about a year ago, but when I last talked
> with him they were changing the name again. Check RC Fab in Albuquerque,
> NM
>
>
>
>> I can't find
He changed the name to RC Fab about a year ago, but when I last talked
with him they were changing the name again. Check RC Fab in Albuquerque,
NM
> I can't find the link to Jeff randles new rack company?
>
> Can someone help me out
>
> Thx
> Jay
> Peltz power.
>
> Sent from my iPhone
>
>> On Ja
Hi Ray,
I don't have much advice, but I can tell you that we have a couple of
ground mounted arrays at a local college (along the ocean) on the same
DPW high wind rated racks. The college chose to buy Chinese modules
from a competitor instead of my recommendation and one of the modules,
after ab
FYI, everyone, as someone who looked to Jeff Randall for many, many years
for high quality racking and custom battery boxes, I am happy to see he
has reincarnated his old business, and named it Solar Rackworks.
Here's a link to his new site. I am not an employee nor related in any
way, just a happy
There is at least one company (nameless at this point, but not SMA) that
has been providing replacements for swapping out faulty arc fault
detectors in their inverters. Could it be possible you have a bad
detector?
Daryl
> Hi All,
>
> Maybe someone will have some ideas for why a couple inverter
We supply them to all our clients in the Bahamas and they do help cut down
on watering to various degrees. In hot climates with a lot of sun every
little bit helps.
Call Roy at RAE Storage Battery to see if he can get you some. (860)828-6007
Daryl
> Top o' the morning!
> Has anyone used the Ro
This is what I would use, Corey.
http://www.elecdirect.com/lug-compression-connectors/insulated-power-connectors/insulated-powerbar-4-14sol-single-sided-entry-3-conductors-clear?gclid=CIaN4KHKyM8CFURbhgodTlwGxA
Daryl
> We're looking for a way to transition from #6 PV wire to #8/#10 PV wire
>
Check out Iron Edison batteries. They are pricey but well worth it for
anyone in it for the long run. Specs below. I'll sell you them but you can
likely buy directly from them if you set up an account.
http://ironedison.com/nickel-iron-ni-fe-battery
> I have a client that is interested in this
Hi all,
I have some possibilities of reasonable size commercial jobs where the
buildings have "corrugated" type roofs with purlins run underneath
which are worst case 16 gauge steel. On steel roofs I typically use #14
Marutex stainless screws but in this case the job is in the Caribbean
and ther
Very simply, is this not contrary to the NEC? I did not think we could run
wires of differing voltages in the same conduit. This is your CYA to the
client.
Daryl
> Well, I don’t think anyone on this list is a network specialist, which
> is what I would consider an expert…. But…
>
>
>
> R
We pay half the price for SolarEdge optimizers that we pay for Enphase
micros. On a system of any decent size the cost is minimally different, at
least in our experience. Customer service is important to me, as well as
companies doing what they say they will do. Over four months for
reimbursement i
It is a very simple install. With SolarEdge there is no trunk cable, which
definitely cuts down on wire management, especially using SnapNRack
mounting. Everything is MC4, so PV wire to a transition box, to the
inverter input(s) make it pretty simple. We almost always mount our
inverters outside, e
Since I am having such a tough time even getting a call back, never mind
reimbursments, we have started very happily using SolarEdge with very good
results so far. Communications, no problem, occasional tech support is
timely, we are seeing less than a 1% failure on optimizers. Ease and
safety of i
Just to renew this line of conversation, I have been waiting for several
call backs form Enphase, with no results, for the past three weeks. I also
have warranty claims that go back four months+ that have not been
fulfilled. I will not sell any more Enphase, at all, until they resolve
these communi
We use this:
https://www.bigrocksupply.com/store/p/5943-EternaBond-DoubleStick-2-in-x-50-ft.aspx?feed=Froogle&gclid=CIP7jrKEl80CFVclgQod0pkJvA
> ​Yeah, the three suppliers in my area all give me the same nonsense -
> it's
> not in their catalog and they have to order a full pallet to get it
Ignore, Dave. I get this crap at least weekly, if not more
Daryl
> Wrenches,
>
>
>
> People named Dave Firth and Hugh Tian have been trying to get me to
> respond
> to emails that say I sent a company, Power Blessed a PO. Which I did not,
> I've never heard of them before this.
>
>
>
> I ha
Hi Dana,
We have done them, but our method only works when the interior is
unfinished, for (I guess it depends on the customer) aesthetic reasons.
I had aluminum "plates", 8"x8" and 1/8" thick made up by a local
fabricator. We also fabricated flashing for the topside using 12"
aluminum. We used
Have to add to this thread that I called them this morning with a minor
issue and they picked up from hold within one minute.
Daryl
> The manuals could be a lot better too. Usually I need a few pages
> from a long manual, and don't benefit from reading pages and pages of
> warnings and basic stu
I talked to David Hamilton (head of technical support) about this almost
six months ago. I'm not sure why, but things have not changed as of yet.
Hopefully soon.
> I just got off the phone w/ Sandra Herrera, making her aware of this
> thread. Sandra said she is aware of our frustrations and is wo
I too have been frustrated with Outback tech support. I have sat on hold
for as long as 40 minutes before anyone picked up. I have suggested they
have a "dealers only" line and as any good customer support person would,
they empathized with me..One tech actually told me the majority of
thei
As with Tump, we have been using the KS series for over 20 years with
little issue. My own particular caveat is that we have now started to use
Crown as well and are finding them as rugged, easier to move (metal cases
with handles), with built in water miser caps, and a better warranty, and
with gr
LG even has a 305 Neon. Very nice modules.
Daryl
> LG Neon? Available through several distributors.
>
> Jeff
>
> -Original Message-
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of jay
> Sent: Thursday, September 17, 2015 8:03 PM
> To: RE-wrenches
>
I'm with Jason. Even though for years we installed without flashing, we
now use it on every job. It is code and besides, why take the chance? We
use Snap N Rack flashing very successfully in Maine, where snow, ice, rain
and large heat/cold expansion/contractions make flashing a great
insurance. On
What do you typically get out of a 300 watt panel for production when you
are grid tied? I know in theory (STC) it is a 300 watt module but we
rarely if ever (except in very cold weather)see near that for an output. I
use (as a general, 77 degrees F) design parameter, 77% for overall power
producti
Hey Jason,
The M-250's work well with LG 300 watt (60 cell) modules.
Daryl
> Hi Jason,
>
> The Enphase C250 Microinverters for three-phase commercial applications
> does work with 72 cell modules.
>
> On Sun, Feb 8, 2015 at 12:58 PM, Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wro
We have 0 M-215 failures out of about 300 installed. Pretty good failure
rate, if I do say so myself
> M215 failures? I've seen only 1 or 2 out of thousands. The M215 was a
> remarkable improvement over the M190. Are you having a different
> experience?
>
> Jason Szumlanski
>
> On Fri, Feb 6,
I'm with Ray on this, Allan. 27 years of using Burndy and Greenlee
crimpers with tinned copper lugs on battery and inverter cables without a
failure says a lot. Like Ray, we do set it a little "tighter" than the
scale indicates.
Daryl
> If there actually is a small hydraulic pump connected betwe
Hi all,
I know this is a real shot in the dark, but is there a possibility
someone out there has an SW4024 for sale. I have an off grid client
whose has a major issue. Because they are off grid, they do not want to
send the inverter off to be fixed and have to run their generator for a
couple of
Does anyone have a number for Schneider's solar tech support? It seems
impossible to reach people there with a direct question, without having to
send an email and wait by a phonesomething it is hard to do and make
money at the same time.
Thanks,
Daryl DeJoy
NABCEP Certified PV installer
Penob
Hello fellow wrenches,
I have an "opportunity" to inherit a poorly installed system which the
client has had problems with for years OR simply replace his original,
but no longer functioning Beacon Power M5 inverter. I would greatly
prefer to do the latter, but Beacon has been out of business fo
Jay,
A couple of things.
There is a source for the Surrette/Rolls as 2 volt cells in a single
poly enclosure as opposed to the double, four volt cells. Contact me
off list.
We have been using these cells for more than 13 years in the Caribbean
with great results. We do use ventilated batter
No problem at all Mac. We've done it for years with Grundfos pumps with
great success (no service calls). The torque arrestors are a good thing,
even with the no surge models.
Daryl
> Hello wrenches,
>
> Is there any problem to putting a small diameter pump in a larger well
> casing? Specifical
Mac,
My only recommendation is that if they are off grid or concerned about
consumption not to use one. We have many off grid systems installed in
Maine (very cold weather) that have generators with block heaters
which have been disabled. They start and run just fine without the
heater.
Daryl
Hi Ray,
This works very well with the SI's. We have an off grid, dual SI system
in the Bahamas which uses 5 Classics and 20 kW of PV, along with a 60
kW generator. It's been in for about 6 months and the client is very
pleased. Midnite makes a nice pre-wired panel (8' x4'), heavy, but in
off off
Mac, for this type of large system we typically use Surrette/Rolls
2YS31.They are 2430 ah. When we get into battery banks this large we
typically only run two cells deep (front to back) for ease of maintenance.
I hope your customer has some free time on their hands for maintenance.
Remember, Surret
Hi William,
I wonder as well. About two months ago we installed a 20 kW off grid
system using two SI6048's with Midnite Solar's BOS and while it made
for an extremely heavy (two piece) powerpanel, it has performed very
wel and seems that Midnite has done the homework for us in providing
excellen
I recently installed a system using a Classic that required current
limiting. Like the OutBack, the limit setting can be a few amps off. I was
told that to be safe, for a 60 amp max, to set the controller current
limiting to 55 or 56 amps. It has been working great and has hit 59 amps
several times
Hi Allan,
Is it possible to use 1/2" carflex connectors and nm carflex from panel
to panel? You could then use THWN anywhere you wanted. This is what we
used to do with all our systems back in the day
Daryl
>
>
>
>
>
>
> Wrenches,
> I do a fair amount of work on an
Ron,
We also install a lot of top of pole mounts and use conduit similar to
what Kirpal describes. We typically will trench and install the conduit
before we pour the concrete foundations (at least to the elbow at the
pole) as it allows for conduit to sweep up the pole instead of having
to come
Hi all,
Does anyone have a source of just the center conductor (small metal
inserts) for MC4 connectorsI seem to have accumulated a lot of
female - plastic without the associated crimpable center conductor
Daryl
___
List sponsored by Home Pow
Honestly, William, in these type of cases I usually walk away from the job
if the customer isn't willing to reduce where possible. There is no such
thing as a completely fool proof off grid PV system. Like a good lawyer,
the best way to have a stellar record is to know which cases to
takejust o
I second Tump's experience!
Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design
> I install large battery banks ALL the time. We DO NOT use any battery that
> is incased in a metal enclosure.
> REAL pain to move, cells DO go bad & when they do its a real pain to bring
> the engine h
We have had at least a half dozen off grid folks with "camps" in Maine
where they stay for a couple of months every year be completely honest
with their tax person and receive the 30% federal tax incentive. Their tax
people were comfortable with the wording vs. the use of the building with
the inst
Hi Kirk,
The Ecogens we have out there (3) have been working great, without
needing service. We do leave the switch set to "manual" which I don't
believe has a phantom load. It so, it is very minimal as we haven't had
customers complaining of lack of power. I continue to recommend them
for small
Wrenches,
I have a potential customer in Dominica who has asked for a quote. He
has already spec'd out a system with an internet company. They have
recommended a Victron 10 kw inverter, 5590 watts of PV and a 48 volt,
835 ah Victron battery bank. Does anyone have any experience with this
equipme
Wrenches,
I have a potential customer in Dominica who has asked for a quote. He
has already spec'd out a system with an internet company. They have
recommended a Victron 10 kw inverter, 5590 watts of PV and a 48 volt,
835 ah Victron battery bank. Does anyone have any experience with this
equipme
Hi Allan,
While not a separate gas unit, Premiere makes a nice stainless steel
and black propane gas stove/oven. It's sort of a step up from the
Lehmans Catalogue old school stuff but still not what you're looking
for. I have used one at home for the last four years with good
experience
Da
It is my favorite. My crew said they would mutiny if I changed back to
others we have used. Wire management is simplified due to a large channel,
spacing of L feet can be up to 6 feet on a 12 pitch roof. We have tried
many manufacturers and this is all we have been using for the last three
years.
Living on the coast of Maine, the majority of our M-215 installs
(approximately 200) are along the immediate coast, say, within a couple
thousand feet of salt water. We have had zero failures of this inverter
(M-215) since it came out. We had one non-coastal issue with AC Out Of
Frequency events th
Would anyone be willing to share secrets about installing on Western Red
Cedar shingle roofing shingles? We're looking at our first ever job on a 7
year old roof. Any and all suggestions welcome.
Thanks,
Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design
___
Dave,
In multiple conversations about this with both the utility and Enphase
there was concern about high inductive loads, possibly from the paper
mill in the town, that turned out not to be the case. The fix Enphase
developed worked, but I thought it would be worth mentioning.
Daryl
> Dave,
>
We use as clips specifically designed to hold Enphase trunk cable to SnapN
Rack rails. We buy them from ARE.
DARYL
> Heyco Sunbundler!
>
> Typos courtesy of my iPhone.
>
> On Apr 11, 2013, at 8:52 PM, Aaron Mandelkorn wrote:
>
>> Just wondering what people like to use for supporting the trunk c
Bill,
We've tried it with both Mate and Mate 3 and it has not worked. It
seems like only one of the ports on the hub, whether 4 or 10, will
work.
Hopefully something that can happen in the future, though, as it could be
very handy on certain situations.
Daryl
> Wrenches,
>
> I ne
And I would second, third and fourth Alan, Ray and William's
recommendations.Stainless steel flat washers on both sides of the terminal
with a split washer and vaseline coating have kept almost all of our
battery banks trouble free over the last twenty five years. We provide
each customer a laminat
Hi Drake,
We used to have problems with the Outback gen-start s/w, but it seems,
at least over the last year, that Outback has gotten the software
corrected. No complaints from customers over the last year (winter) say
so. Time will tell, but I'm feeling more comfortable with them.
Daryl
> He
Hi all,
I am not sure Michael will let this one pass, but with all the problems
we seem to have at times, I thought it was worth mentioning...
We are currently working out of the country, in the Caribbean, in a
very isolated, off grid location. Our distributor (this name will
beheld for the "
Enphase engineers have contacted my client and will do a preliminary test
of the Enphase fix sometime next week to see if it is effective. They will
be using a Hioki PQA during the testing. I applaud Enphase for staying on
this and even if this first fix needs some tweaking, I am confident they
wi
Thanks for the succinct explanation Nick. I look forward to the fix. Like
you, I believe this is happening with other inverters, but lacking the
level of monitoring available with Enphase, people just aren't aware it is
happening.
Daryl
> Hi wrenches,
>
> The frequency out of range issue is bei
Will do. Enphase had originally projected the beginning of February for
the release of the fix. It is now projected for the end of March. I am
hoping it will be a done deal before this next "season" starts here in
Maine. It might be good incentive to try Power One, Exeltech or other
inverters. In a
Dave,
It doesn't happen often, and the longest I've seen him stay "down" is
about a half hour, but it seems to get progressively worse as time goes
on for some reason (initially only the five minutes, but longer down
times lately). This particular customer is difficult and picky, to
boot. I hope
1 - 100 of 241 matches