Tump - You are right about the large number of times that has been asked, and I 
wish I had a happy answer.

However, with all the work on Sunny Boy Storage and Sunny Central Storage (and 
even a Tripower storage), resources to develop and test a split phase Sunny 
Island are not available.  There is active work on updating the communications 
to support SMA’s Ethernet based communications.  Still, this may be months out.

With the Smartformer being discontinued, the MidNite MNX-240 is the recommended 
part to create 240 split phase from one Sunny Island.

Best regards –
Mike


SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: 
www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: 
https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/facebook.jpg]<http://www.facebook.com/pages/SMA-America/140290312717395>
 [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/twitter.jpg] 
<http://twitter.com/SMA_America>  
[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/wordpress.jpg] 
<http://www.smainverted.com/>  [Linkedin Logo] 
<http://www.linkedin.com/company/364675>  
[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/youtube.jpg] 
<http://www.youtube.com/playlist?list=PL840A5336CAC32332>  [SMAAFORUM_ICON] 
<http://smaadvance.com/signup/>
[cid:image008.jpg@01D43B9E.70803930]


This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Tump
Sent: Thursday, September 20, 2018 4:01 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Low voltage DC v. higher voltage DC

I bet Mike could retire from the industry if he had a nickel for every time he 
was asked for/about that. I’ve asked Santa for years…… still waiting. T
On Sep 20, 2018, at 5:21 PM, Chris Schaefer 
<ch...@solarandwindfx.com<mailto:ch...@solarandwindfx.com>> wrote:

Hey Michael from SMA, any chance we can finally get an 240vac SI here in the 
states?

Christopher

On Tue, Sep 18, 2018 at 12:11 PM, Harry Mahon 
<michael.ma...@sma-america.com<mailto:michael.ma...@sma-america.com>> wrote:
Marco –

I will need to ask for information about the BYD availability.  Once those 
units have all required listings/certifications and are available in US, they 
should be ready to use with SBS.  The CANBUS comms to the BMS has already been 
vetted, and they are on the SMA Approved battery list already.  But I will get 
confirmation on the immediate usability.

Best regards –
Mike




SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: 
www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: 
https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


<image001.jpg><http://www.facebook.com/pages/SMA-America/140290312717395> 
<image002.jpg><http://twitter.com/SMA_America> 
<image003.jpg><http://www.smainverted.com/> 
<image004.jpg><http://www.linkedin.com/company/364675> 
<image005.jpg><http://www.youtube.com/playlist?list=PL840A5336CAC32332> 
<image006.png><http://smaadvance.com/signup/>
<image007.jpg>


This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

From: RE-wrenches 
<re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Marco Mangelsdorf
Sent: Monday, September 17, 2018 10:20 PM

To: RE-wrenches 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] Low voltage DC v. higher voltage DC


Mahalo Mike.

Can you tell us please when the SS will actually be able to integrate the BYD 
battery platform in the north American market?

marco

On Monday, September 17, 2018, Harry Mahon 
<michael.ma...@sma-america.com<mailto:michael.ma...@sma-america.com>> wrote:
Marco and all – yes that is the correct spec sheet for the BYD batteries that 
will work with Sunny Boy Storage.

SMA strongly would recommend the Sunny Island for off-grid in general and 
certainly whole home backup.  See the attached from Home Power April/May 2011; 
quad stack of SIs acting as UPS for the home – just charging batteries when 
grid is present, powering home with batteries/PV when grid is gone.  A dual 
split phase cluster is almost 24,000 W continuous (!) capability and can handle 
crazy power factor loads with no issues.  Built in generator functions and two 
relay positions per Sunny Island allow for lots of redundancy and fail-safe 
load shedding to be built in.

The Sunny Boy Storage (SBS) is designed to be a grid-tied inverter to allow 
higher self consumption of local PV power.  Even with the ABU to allow off grid 
operation (grid forming on its AC outputs rather than just on the dedicated 
120VAC Secure Power Supply outlet), there can be a several second delay in the 
switch from grid power to microgrid as the ABU must signal the Sunny Boy 
Storage that it has disconnected from the grid and that it is safe for the SBS 
to form a grid on its output terminals.  Also be aware that there is no 
master-slave configuration ability with the SBS – they will always assume they 
are acting independently on their energy meter input information.

Best regards –
Mike

SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: 
www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: 
https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


<image001.jpg><http://www.facebook.com/pages/SMA-America/140290312717395><image002.jpg><http://twitter.com/SMA_America>
 <image003.jpg><http://www.smainverted.com/> 
<image004.jpg><http://www.linkedin.com/company/364675> 
<image005.jpg><http://www.youtube.com/playlist?list=PL840A5336CAC32332> 
<image006.png><http://smaadvance.com/signup/>
<image007.jpg>


This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

From: RE-wrenches 
<re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Marco Mangelsdorf
Sent: Saturday, September 15, 2018 10:08 PM
To: 'RE-wrenches' 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Subject: Re: [RE-wrenches] Low voltage DC v. higher voltage DC

Sabaidee from Vientiane, Lao PDR.

Attached is the spec sheet on the BYD battery in question.

I’ve confirmed with SMA directly that there’s no capability for the Sunny 
Storage design (S.S., ABU and battery) to use a generator input.  My apologies 
for mis-stating earlier that it could accommodate a generator.

As far as grid-tie with batteries, the Holy Grail as far as I’m concerned is 
being able to provide whole house back-up and not have to do the old fashioned 
and pain in the arse critical load sub-panel.  The more choices that we’re 
provided, the more better.  So I’m pleased that companies like SMA, Ensync, 
SolarEdge and others are bringing new equipment and designs to market to allow 
for whole house back-up.

marco

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of jay
Sent: Saturday, September 15, 2018 5:00 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Low voltage DC v. higher voltage DC

HI Harry,

The battery is charged from the AC side correct?
And is the charging algorithm inside the ABU.

If so why couldn’t you use a generator to charge the battery?

jay

peltz power



On Sep 13, 2018, at 7:10 AM, Harry Mahon 
<michael.ma...@sma-america.com<mailto:michael.ma...@sma-america.com>> wrote:

Marco –

The Sunny Boy Storage “Advanced Backup Unit” accessory or ABU will be discussed 
at SPI in a couple weeks – first units are being stocked now at our warehouses 
in US.  The ABU will allow the SBS to be a grid former in case of utility 
outage, however there are no plans to have any generator inputs/controls to 
allow for battery charging from generat
And yes, BYD BBox HV 5.12/7.68/10.24 devices will be supported when available 
in US (will be this year I understand)

Mike

-----


The SMA Sunny Storage looks promising.



It will be able to work with the LGC RESU10 HV battery and, sooner rather

than later I hope, BYD package as well.



And it will allow for a backup generator tie in.



Ta-dah!



marco



On Thursday, September 13, 2018, Bruce Erickson <bruce at 
mendocinosolar.com<http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>>

wrote:



> Hi Marco,

>

> I partially agree with you. I recently bid Outback, StorEdge, and Pika

> options for a GTBB customer, partly to understand pricing for myself, and

> found OB to be so much more expensive. The customer really wanted a system

> that would be to be able to charge the batteries off a generator in an

> outage, understandably. But the extra thousands in cost for OB ended up

> being prohibitive. Add-on rapid shutdown is a killer. So he’s opting for a

> nice modern high voltage DC system, with optimizers and built-in RSD, but

> when there’s an extended outage, he’ll have to hope the sun comes out right

> after the storm to recharge the batteries, or he’ll end up in the dark

> again, until the grid comes back. Maybe there’s a high voltage inverter

> that allows generator charging, or a third-party battery charger, that I’m

> not aware of. Otherwise high voltage systems are very limited for backup,

> at least in winter storm scenarios.

>

> *Bruce Erickson*

> Mendocino Solar Service

> PO Box 1252

> Mendocino, CA 95460

> 707-937-1701

> 707-937-1741 fax

> bruce at 
> mendocinosolar.com<http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org>

>

> *Connecting Mendocino County to Solar Since* *1994*

>

>

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>


_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org/>




--
Chris Schaefer’s
[http://www.solarandwindfx.com/wp-content/uploads/2015/01/Solar-Wind-FX-Logo.png]<http://www.solarandwindfx.com/>
Tel/Fax 585-229-2083 or Cell 585-748-1870
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com<http://www.solarandwindfx.com/> ~ E-mail: 
ch...@solarandwindfx.com<mailto:ch...@solarandwindfx.com>
[http://solarandwindfx.com/wp-content/uploads/2015/01/certs.jpg]
Thomas Jefferson, the author of our great Constitution, once said, "democracy" 
will cease to exist when you take away from those who are willing to work and 
give to those who would not."
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>

t...@swnl.net<blocked::mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>
               
www.SWNL.net<blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
                Solarwinds Northernlights
       Serving Mid Coast Maine & Northern California
                         207-832-7574   Cl. 610-517-8401
                              Blair "TUMP" May
               ********  MAINE'S CHARTER ********
                      NABCEP    "Certified PV Installer"

              ********  MAINE'S CHARTER ********
                  Trace Xantrex "Certified" Dealer / Installer"



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to