Excellent point. Thank you Todd & Kyle. So now on to the bonus round: On a pipe schedule system, can section 10.2.5.2.3.1 (2019) be applied to allow a sprinkler to be up to 9’ from a single wall? Ed
From: Fpdcdesign <[email protected]> Sent: Wednesday, May 14, 2025 6:50 AM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [Sprinklerforum] Re: CPVC and pipe scheduled systems In 13, the pipe schedule tables are specified for steel or copper only. 27.5.3.4 Todd Williams Fire Protection Design/Consulting Stonington, CT 860-608-4559 On May 13, 2025 at 5:30 PM, <Ed Kramer<mailto:[email protected]>> wrote: Oh knowledgeable ones: Is there anything in NFPA 13 that prohibits the use of CPVC pipe/fittings in the remodel of an old pipe schedule system? The intent is to maintain the pipe schedule and not provide calculations. I’m not aware of anything, but I don’t want this to bite me later. Thanks, Ed K [https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1] [cid:[email protected]] Ed Kramer Design Manager | Bamford Fire Sprinkler Co., Inc. P: 785.825.7710 F: 785.825.0667 M: 785.766.4894 A: 1383 W. North Street Salina, KS 67401 _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]<mailto:[email protected]>