In 13, the pipe schedule tables are specified for steel or copper only. 
27.5.3.4
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On May 13, 2025 at 5:30 PM,  <Ed Kramer (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
> Oh knowledgeable ones:    Is there anything in NFPA 13 that prohibits the use 
> of CPVC pipe/fittings in the remodel of an old pipe schedule system?    The 
> intent is to maintain the pipe schedule and not provide calculations.    I’m 
> not aware of anything, but I don’t want this to bite me later.
>
>   
>
>   
>
>   
>