Ed,
There could be residual oils in the pipe or other chemicals that would cause 
the deterioration of the CPVC piping. Just a thought.
Chris

[cid:[email protected]]



From: Ed Kramer <[email protected]>
Sent: Tuesday, May 13, 2025 5:30 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] CPVC and pipe scheduled systems

Oh knowledgeable ones:  Is there anything in NFPA 13 that prohibits the use of 
CPVC pipe/fittings in the remodel of an old pipe schedule system?  The intent 
is to maintain the pipe schedule and not provide calculations.  I'm not aware 
of anything, but I don't want this to bite me later.

Thanks,
Ed K

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]

[cid:[email protected]]



Ed Kramer
Design Manager | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
M:   785.766.4894
A:   1383 W. North Street  Salina, KS  67401



_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to