I don't see anywhere that it is specifically prohibited. But the pipe schedule tables only address steel pipe and copper pipe. So there is nothing to point to in the code that says how many sprinklers can be fed from a particular size of CPVC pipe.
-Kyle M Aero From: Ed Kramer <[email protected]> Sent: Tuesday, May 13, 2025 2:30 PM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [External][Sprinklerforum] CPVC and pipe scheduled systems Oh knowledgeable ones: Is there anything in NFPA 13 that prohibits the use of CPVC pipe/fittings in the remodel of an old pipe schedule system? The intent is to maintain the pipe schedule and not provide calculations. I'm not aware of anything, but I don't want this to bite me later. Thanks, Ed K [https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1] [cid:[email protected]] Ed Kramer Design Manager | Bamford Fire Sprinkler Co., Inc. P: 785.825.7710 F: 785.825.0667 M: 785.766.4894 A: 1383 W. North Street Salina, KS 67401
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]