28.2.4.10.3 states “flow from a sprinkler shall be calculated using the nominal 
K-factor except that the manufacturer’s adjusted K-factors shall be utilized 
for dry-type sprinklers.”

You are supposed to use what is on the data sheet for that particular sprinkler 
and length. For example, here is one from a Tyco data sheet:

[cid:[email protected]]

Let me know if this comes through.

Kyle Montgomery
 [cid:[email protected]]
Pre-Construction Manager
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>






From: Mike Stewart <[email protected]>
Sent: Wednesday, March 26, 2025 12:47 PM
To: [email protected]
Cc: [email protected]
Subject: [External][Sprinklerforum] Re: Dry Sprinkler K-Factor

Since the connection point has a large opening and the “K Factor” has to do 
with the smaller opening size of the fire sprinkler itself then the “K Factor” 
should be added at the fire sprinkler head itself.

Mike Stewart
(843) 490-8366


On Mar 26, 2025, at 12:44 PM, Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:

The K factor has to do with discharge, so it should be applied at the 
sprinkler, unless noted otherwise by the manufacturer. If they are to be taken 
at the POC, then the K factor would be modified per length of sprinkler in the 
literature. Kind of like how Autosprink does it.

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559



On Mar 26, 2025 at 12:20 PM, <Travis Mack<mailto:[email protected]>> wrote:
Is the k-factor for a dry sprinkler to be applied at the sprinkler, or at the 
point of connection to the piping network?  I understand things like the 
Victaulic Dry Flex sprinkler have the k-factor at the POC.  What about all 
other dry sprinklers?  POC or sprinkler orifice?





Travis Mack, SET

M.E.P.CAD | Instructor / Support

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | 303-923-8215

Email: [email protected]<mailto:[email protected]>



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Academy of Fire Sprinkler Technology | Director, Engineering Technology

101 S Main Street, Suite 001, Decatur, IL 62523

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to