Since the connection point has a large opening and the “K Factor” has to do with the smaller opening size of the fire sprinkler itself then the “K Factor” should be added at the fire sprinkler head itself. 

Mike Stewart
(843) 490-8366

On Mar 26, 2025, at 12:44 PM, Fpdcdesign <[email protected]> wrote:


The K factor has to do with discharge, so it should be applied at the sprinkler, unless noted otherwise by the manufacturer. If they are to be taken at the POC, then the K factor would be modified per length of sprinkler in the literature. Kind of like how Autosprink does it. 

Todd Williams 
Fire Protection Design/Consulting
Stonington, CT
860-608-4559


On Mar 26, 2025 at 12:20 PM, <Travis Mack> wrote:

Is the k-factor for a dry sprinkler to be applied at the sprinkler, or at the point of connection to the piping network?  I understand things like the Victaulic Dry Flex sprinkler have the k-factor at the POC.  What about all other dry sprinklers?  POC or sprinkler orifice?


 

Travis Mack, SET

M.E.P.CAD | Instructor / Support

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com | 303-923-8215

Email: [email protected]

 

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

 

Academy of Fire Sprinkler Technology | Director, Engineering Technology

101 S Main Street, Suite 001, Decatur, IL 62523


_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to