K factor is simply a ratio of pressure and GPM discharged and can be assigned 
to an orifice, or an orifice and piping etc.  Dry barrel sprinklers are not a 
simple piece of empty schedule 40 pipe or whatever, you don’t adjust for the 
barrel length unless the manufacturer tells you to, because you can’t unless 
they provided the friction loss characteristics of the barrel, which they don’t.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Estimator • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625
email [email protected]<mailto:[email protected]>
24/7<outlook-data-detector://2/> SERVICE LINE 888.217.7055<tel:888.217.7055>
[cid:[email protected]]

From: Mike Stewart <[email protected]>
Sent: Wednesday, March 26, 2025 3:47 PM
To: [email protected]
Cc: [email protected]
Subject: [Sprinklerforum] Re: Dry Sprinkler K-Factor

Since the connection point has a large opening and the “K Factor” has to do 
with the smaller opening size of the fire sprinkler itself then the “K Factor” 
should be added at the fire sprinkler head itself. Mike Stewart (843) 490-8366 
On Mar
ZjQcmQRYFpfptBannerStart
This Message Is From an Untrusted Sender
You have not previously corresponded with this sender.
ZjQcmQRYFpfptBannerEnd
Since the connection point has a large opening and the “K Factor” has to do 
with the smaller opening size of the fire sprinkler itself then the “K Factor” 
should be added at the fire sprinkler head itself.

Mike Stewart
(843) 490-8366


On Mar 26, 2025, at 12:44 PM, Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:

The K factor has to do with discharge, so it should be applied at the 
sprinkler, unless noted otherwise by the manufacturer. If they are to be taken 
at the POC, then the K factor would be modified per length of sprinkler in the 
literature. Kind of like how Autosprink does it.

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559



On Mar 26, 2025 at 12:20 PM, <Travis Mack<mailto:[email protected]>> wrote:
Is the k-factor for a dry sprinkler to be applied at the sprinkler, or at the 
point of connection to the piping network?  I understand things like the 
Victaulic Dry Flex sprinkler have the k-factor at the POC.  What about all 
other dry sprinklers?  POC or sprinkler orifice?





Travis Mack, SET

M.E.P.CAD | Instructor / Support

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<https://urldefense.com/v3/__http:/www.mepcad.com/__;!!FaxH778!aAr-BkS_1pr4Jp9Gp4ZtcIhC2_FapjVhkuMCZdanJM6V-DHq1nmjZZUgGYgYo70L_RD_dD7ehLjrYcwNzBikSa46_l4$>
 | 303-923-8215

Email: [email protected]<mailto:[email protected]>



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Academy of Fire Sprinkler Technology | Director, Engineering Technology

101 S Main Street, Suite 001, Decatur, IL 62523

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!FaxH778!aAr-BkS_1pr4Jp9Gp4ZtcIhC2_FapjVhkuMCZdanJM6V-DHq1nmjZZUgGYgYo70L_RD_dD7ehLjrYcwNzBikMMXNN9A$>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!FaxH778!aAr-BkS_1pr4Jp9Gp4ZtcIhC2_FapjVhkuMCZdanJM6V-DHq1nmjZZUgGYgYo70L_RD_dD7ehLjrYcwNzBikMMXNN9A$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to