I believe it's at the connection for all types of sprinklers.  Tyco I think is 
the only one that specifies a variable K based on length anymore, I assume the 
others use a slightly oversized head and adjust the restriction of the tube 
inside to keep the K constant for all lengths.  Reliable has a good section 
view of theirs where you can see it wicks down inside the tube to the head.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Estimator * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625
email [email protected]<mailto:[email protected]>
24/7<outlook-data-detector://2/> SERVICE LINE 888.217.7055<tel:888.217.7055>
[cid:[email protected]]

From: Travis Mack <[email protected]>
Sent: Wednesday, March 26, 2025 12:20 PM
To: '[email protected]' 
<[email protected]>
Subject: [Sprinklerforum] Dry Sprinkler K-Factor

Is the k-factor for a dry sprinkler to be applied at the sprinkler, or at the 
point of connection to the piping network? I understand things like the 
Victaulic Dry Flex sprinkler have the k-factor at the POC. What about all other 
dry sprinklers?
ZjQcmQRYFpfptBannerStart
This Message Is From an External Sender
This message originated outside your organization.
ZjQcmQRYFpfptBannerEnd
Is the k-factor for a dry sprinkler to be applied at the sprinkler, or at the 
point of connection to the piping network?  I understand things like the 
Victaulic Dry Flex sprinkler have the k-factor at the POC.  What about all 
other dry sprinklers?  POC or sprinkler orifice?





Travis Mack, SET

M.E.P.CAD | Instructor / Support

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<https://urldefense.com/v3/__http:/www.mepcad.com/__;!!FaxH778!a3vEqPdH6NUzuW69R__rw0WGU9AXwgmxbMNdo8uqF2DCwC0Cw3ONry0rrZwISSwXLwdpd7Sk8ulhdUI$>
 | 303-923-8215

Email: [email protected]<mailto:[email protected]>



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Academy of Fire Sprinkler Technology | Director, Engineering Technology

101 S Main Street, Suite 001, Decatur, IL 62523

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to