So Ron, this sounds like they have to remove sheet rock ceilings and ductwork 
before the inspector show up.   
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On Aug 14, 2024 at 2:51 PM,  <Ron Greenman (mailto:[email protected])>  
> wrote:
>   
>   
>   
>   
> Here is a quote from an information sheet I made for owners quoting from the 
> 2014 edition of 25. I've not been playing since around 2019 so I have not 
> updated it since that 2014 edition. I don't know what edition you're using or 
> if the wording has changed since 2014, I would think that if you include   
> your jurisdictio9n's most current version of this and a list of units you 
> were not allowed access to as an addendum to your reports you should be OK. 
> But I'm no lawyer nor play one on TV so check with a real one regarding your 
> window of liability.
>   
>
>   
> This is from NFPA 25, 2014 Edition: "Chapter 4 General Requirements,   4.1 
> Responsibility of the Property Owner or Designated Representative,   4.1.1 
> Responsibility for Inspection, Testing, Maintenance, and Impairment.   The 
> property owner or designated representative shall be responsible for properly 
> maintaining a water- based fire protection system."
>   
>
>   
> 4.1.3   Accessibility. The property owner or designated representative shall 
> provide ready accessibility to components of water-based fire protection 
> systems that require inspection, testing, and maintenance.
>   
>
>   
>
>   
>
>   A.4.1.3   The components are not required to be open or exposed. Doors, 
> removable panels, or valve pits can be permitted to satisfy the need for 
> accessibility. Such equipment should not be obstructed by features such as 
> walls, ducts, columns, direct burial, or stock storage.
>
>   
>   
>   
>   
> On Wed, Aug 14, 2024 at 7:53 AM  <[email protected] 
> (mailto:[email protected])>  wrote:
>   
> >   
> >   
> >   
> >   
> >
> > I do not think so. I think there is/was commentary about using a ladder and 
> > or binoculars if needed.
> >
> >   
> >
> >   
> >
> >   
> >
> > Furthermore, I would not put my name on a tag for any sprinklers I could 
> > not see.
> >
> >   
> >
> >   
> >
> >   
> >
> > R/
> >
> >   
> >
> > Matt
> >
> >   
> >
> >   
> >
> >   
> >
> >    Matthew J. Willis, CWBSP, C.E.T.
> >
> >   
> >
> >    Ferguson Fire Design, LLC
> >
> >   
> >
> > D:   (602) 337-0721 (http://(602)%20337-0721)   C:   (307) 236-8249 
> > (http://(307)%20236-8249)
> >
> >   
> >
> > [email protected] (mailto:[email protected])
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> > From:   [email protected] (mailto:[email protected])   
> > <[email protected] (mailto:[email protected])>
> >   Sent:  Wednesday, August 14, 2024 8:41 AM
> >   To:   [email protected] 
> > (mailto:[email protected])
> >   Subject:  [Sprinklerforum] Storage Unit Inspections
> >
> >   
> >   
> >
> >   
> >
> >   
> >
> >    Caution:    This email originated from outside of the organization.    
> > DO NOT click links or open attachments unless you recognize and trust the 
> > sender.   
> >
> >   
> >   
> >   
> >
> > We have a chain of storage units that would like for us to conduct annual 
> > sprinkler inspections. The do not have access to the units that are being 
> > rented, but there is a gap above each door for air flow. Would we be 
> > stepping outside the realm of NFPA 25 if we utilized a ladder to see into 
> > each unit to perform the inspections?
> >
> >   
> >   
> >   
> >  _________________________________________________________
> >  SprinklerForum mailing list:
> >   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])      
> > _________________________________________________________ SprinklerForum 
> > mailing list: 
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> > To unsubscribe send an email to 
> > [email protected]            
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to