Here is a quote from an information sheet I made for owners quoting from
the 2014 edition of 25. I've not been playing since around 2019 so I have
not updated it since that 2014 edition. I don't know what edition you're
using or if the wording has changed since 2014, I would think that if you
include your jurisdictio9n's most current version of this and a list of
units you were not allowed access to as an addendum to your reports you
should be OK. But I'm no lawyer nor play one on TV so check with a real one
regarding your window of liability.

This is from NFPA 25, 2014 Edition: "*Chapter 4 General Requirements, **4.1
Responsibility of the Property Owner or Designated Representative, **4.1.1
Responsibility for Inspection, Testing, Maintenance, and Impairment. *The
property owner or designated representative shall be responsible for
properly maintaining a water- based fire protection system."

*4.1.3* *Accessibility*. The property owner or designated representative
shall provide ready accessibility to components of water-based fire
protection systems that require inspection, testing, and maintenance.

*A.4.1.3 *The components are not required to be open or exposed. Doors,
removable panels, or valve pits can be permitted to satisfy the need for
accessibility. Such equipment should not be obstructed by features such as
walls, ducts, columns, direct burial, or stock storage.

On Wed, Aug 14, 2024 at 7:53 AM <[email protected]> wrote:

> I do not think so. I think there is/was commentary about using a ladder
> and or binoculars if needed.
>
>
>
> Furthermore, I would not put my name on a tag for any sprinklers I could
> not see.
>
>
>
> R/
>
> Matt
>
>
>
> *Matthew J. Willis, CWBSP, C.E.T.*
>
> *Ferguson Fire Design, LLC*
>
> D: (602) 337-0721 <http://(602)%20337-0721> C: (307) 236-8249
> <http://(307)%20236-8249>
>
> [email protected]
>
>
>
> *From:* [email protected] <[email protected]>
> *Sent:* Wednesday, August 14, 2024 8:41 AM
> *To:* [email protected]
> *Subject:* [Sprinklerforum] Storage Unit Inspections
>
>
>
> *Caution:  This email originated from outside of the organization.  DO NOT
> click links or open attachments unless you recognize and trust the sender. *
> ------------------------------
>
> We have a chain of storage units that would like for us to conduct annual
> sprinkler inspections. The do not have access to the units that are being
> rented, but there is a gap above each door for air flow. Would we be
> stepping outside the realm of NFPA 25 if we utilized a ladder to see into
> each unit to perform the inspections?
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to