I do not think so. I think there is/was commentary about using a ladder and or binoculars if needed.
Furthermore, I would not put my name on a tag for any sprinklers I could not see. R/ Matt Matthew J. Willis, CWBSP, C.E.T. Ferguson Fire Design, LLC D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249> [email protected]<mailto:[email protected]> From: [email protected] <[email protected]> Sent: Wednesday, August 14, 2024 8:41 AM To: [email protected] Subject: [Sprinklerforum] Storage Unit Inspections Caution: This email originated from outside of the organization. DO NOT click links or open attachments unless you recognize and trust the sender. ________________________________ We have a chain of storage units that would like for us to conduct annual sprinkler inspections. The do not have access to the units that are being rented, but there is a gap above each door for air flow. Would we be stepping outside the realm of NFPA 25 if we utilized a ladder to see into each unit to perform the inspections?