I do not think so. I think there is/was commentary about using a ladder and or 
binoculars if needed.

Furthermore, I would not put my name on a tag for any sprinklers I could not 
see.

R/
Matt

Matthew J. Willis, CWBSP, C.E.T.
Ferguson Fire Design, LLC
D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249>
[email protected]<mailto:[email protected]>

From: [email protected] <[email protected]>
Sent: Wednesday, August 14, 2024 8:41 AM
To: [email protected]
Subject: [Sprinklerforum] Storage Unit Inspections

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
We have a chain of storage units that would like for us to conduct annual 
sprinkler inspections. The do not have access to the units that are being 
rented, but there is a gap above each door for air flow. Would we be stepping 
outside the realm of NFPA 25 if we utilized a ladder to see into each unit to 
perform the inspections?
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to