Would the same apply to platforms in churches if they are doing any sort of 
production?
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On Jul 22, 2024 at 1:11 PM,  <Steve Leyton 
> (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
> Here in California…
>
>   
>
>   
>
>   
>
> K-12 schools are under the jurisdictional authority of the Division of the 
> State Architect (DSA) and my firm does a LOT of educational occupancy 
> projects.      We wrestled with the stage/platform thing too until about 10 
> years ago, when DSA decided that stages and platforms are equivalent if they 
> have a curtain.      High schools tend to have dedicated athletic gyms and 
> performing arts centers with legitimate stages, but at elementary and middle 
> schools usually have an multi-purpose room    with platform on one side.      
> A platform is decidedly NOT a stage as the ceiling of the MPR runs 
> continuously throughout the room and there’s no fly space above.     
>
>   
>
>   
>
>   
>
> What the agency found over the course of a year of field investigation is 
> that if there’s a curtain, schools have a tendency to store stuff on the 
> platform, so they decided to classify these spaces as ordinary hazard.      
> It seemed a little far-fetched to me at first but A) Why would we object to a 
> definitive ruling that makes sprinkler protection more robust and, B) Based 
> on the experiences that I and staff have had doing survey’s at ES and MS 
> campuses, we have found that their conclusion was correct and the fire loads 
> of “platforms” can often be equal to what’s found on and even above stages in 
> practice.      I think the OP was about a gym and this particular branch in 
> the occupancy hazard classification decision tree doesn’t really exist in 
> such a building, but if we’re talking about splitting hairs in any of these 
> occupancies, I don’t think it’s overkill to call it OH and move on.
>
>   
>
>   
>
>   
>
> Steve L.
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>
> From:   Tony Silva  <[email protected]>
>   Sent:  Sunday, July 21, 2024 10:39 PM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected]>
>   Subject:  [Sprinklerforum] Re: Gym Hazard Classification
>
>   
>   
>
>   
>
>   
>   
>   
>
> There was a school that had a Gymnasium with a platform at one end. It was 
> basically a platform, a couple of feet high, no curtains, no extra lighting 
> but the Architect named it "stage" on the drawings. A fire started on the 
> roof at the "stage" end of the Gymnasium and the entire school burned down. 
> NFPA compiled a report as it was a major fire. In the NFPA report they 
> claimed that the sprinkler system failed as the "stage" end of the Gymnasium 
> should have been designed to Ordinary Hazard.
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> Tony
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> On Fri, Jul 19, 2024 at 5:51 PM Steve Leyton  <[email protected] 
> (mailto:[email protected])>  wrote:
>
>   
>   
> >   
> >   
> >   
> >   
> >
> > Is it just a “gym” or a multi-purpose building that will also be available 
> > for “community” uses?        Gym mats are one thing, rummage sales, craft 
> > fairs, job and college recruiting expos, church and other assemblies, those 
> > are different things.      I agree that an athletic/sports facility such as 
> > a high-school or college gym is light hazard in the main room, but the 
> > school or college district or municipality that will own and operate this 
> > building should provide you with an articulate owner’s certificate before 
> > it gets nailed down.
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> > Steve L.
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> >   From:   Adam Levine, P.E. [mailto:[email protected]]
> >   Sent:  Friday, July 19, 2024 12:58 PM
> >   To:   [email protected] 
> > (mailto:[email protected])
> >   Subject:  [Sprinklerforum] Gym Hazard Classification
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >
> > I’ve always designed gyms as light hazard, although I’ve heard over the 
> > years that some designers increase the hazard because of the plastic mats 
> > (even if they are not stored over 5’). Assuming this is a standard gym (no 
> > foam rock walls or anything complicated), how would most of you classify a 
> > gym?
> >
> >   
> >
> >   
> >
> >   
> >
> > Thanks!  🙌
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >    ADAM   LEVINE,   P.E.​​​​
> >
> >   
> >   
> >   
> >   
> >   
> >
> >  PRESIDENT
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >    ​phone:   
> >
> >   
> >   
> >   
> >
> >  718.533.6800   ext   137 (tel:718.533.6800%20ext%20137)
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >    email:
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >  [email protected] (mailto:[email protected])
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >  |
> >
> >   
> >   
> >   
> >   
> >   
> >
> >  |
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >    direct:   ​
> >
> >   
> >   
> >   
> >
> >  917.818.4211
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >    fax:   
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >  917.810.2677
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >   (https://capitolfire.com/)
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >   (https://www.facebook.com/CapitolFireSprinkler)
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >   (https://twitter.com/CapitolFire)
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >   (https://www.youtube.com/user/CapitolFireSprinkler/feed)
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >
> >
> >  _________________________________________________________
> >  SprinklerForum mailing list:
> >   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])
> >
> >   
> >   
>   
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     