Dude:

I have actually threatened to terminate our contract with cause in a couple of 
situations.  Had to tell the clients that we are bound to follow the provisions 
of the adopted codes and standards in our state, and the NFPA 13 standard 
mandates that they provide  us with the information that we need to put forth a 
responsive design.  My experience with public agencies is that they are very 
willing to partner once we explain what we need and why we need it.



Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



-------- Original message --------
From: Fpdcdesign <[email protected]>
Date: 7/19/24 6:49 PM (GMT-08:00)
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Gym Hazard Classification

“Articulate owner’s certificate”? LMFAO

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559


On Jul 19, 2024 at 7:52 PM, <Steve Leyton<mailto:[email protected]>> 
wrote:

Is it just a “gym” or a multi-purpose building that will also be available for 
“community” uses?    Gym mats are one thing, rummage sales, craft fairs, job 
and college recruiting expos, church and other assemblies, those are different 
things.   Iagree that an athletic/sports facility such as a high-school or 
college gym is light hazard in the main room, but the school or college 
district or municipality that will own and operate this building should provide 
you with an articulate owner’s certificate before it gets nailed down.

Steve L.


From: Adam Levine, P.E. [mailto:[email protected]]
Sent: Friday, July 19, 2024 12:58 PM
To: [email protected]
Subject: [Sprinklerforum] Gym Hazard Classification

I’ve always designed gyms as light hazard, although I’ve heard over the years 
that some designers increase the hazard because of the plastic mats (even if 
they are not stored over 5’). Assuming this is a standard gym (no foam rock 
walls or anything complicated), how would most of you classify a gym?

Thanks! 🙌
ADAM LEVINE, P.E.​​​​
PRESIDENT
​phone:
718.533.6800 ext 137<tel:718.533.6800%20ext%20137>
email:
[email protected]<mailto:[email protected]>
|
|
direct: ​
917.818.4211
fax:
917.810.2677
[cid:[email protected]]<https://capitolfire.com/>
[Facebook]<https://www.facebook.com/CapitolFireSprinkler>
[Twitter]<https://twitter.com/CapitolFire>
[cid:[email protected]]<https://www.youtube.com/user/CapitolFireSprinkler/feed>

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to