Volume or pressure?
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On Jul 1, 2024 at 9:25 AM,  <Brian Harris (mailto:[email protected])> 
>  wrote:
>   
>   
>           
>   
>
> Todd-
>
>   
>
> Yes, it’s a manual wet standpipe. Problem is the city supply has dropped a 
> fair amount and now the standpipe test won’t pass.
>
>   
>
>   
>
>   
>   
>
>  Thank you,
>
>   
>
>     
>
>   
>
>  Brian Harris, CET
>
>   
>
>  BVS Systems Inc.
>
>   
>   
>
>   
>
>   
>   
>   
>
> From:   Fpdcdesign  <[email protected]>
>   Sent:  Monday, July 1, 2024 9:21 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected]>
>   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
>
>   
>   
>   
>
>   
>
>   
>   
>
> Isn’t this a 4 story building? Below the high rise threshold, I assume. Can 
> it be a manual wet standpipe?   
>
>   
>   
>
>   
>
>   
>   
>   
>   
>
> Todd Williams   
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-608-4559
>
>   
>   
>   
>   
>   
>   
>   
>
>
>   
>   
>
>
>   
> >   
> >   
> >
> > On Jul 1, 2024 at 9:09 AM,  <Paul Kimble (mailto:[email protected])>  
> > wrote:
> >
> >   
> >   
> >   
> >
> > Has anyone done a valued engineering survey of the city water supply and 
> > compared the original water test provided to the current. Is the city 
> > supply a gravity fed system or a system utilizing pumps? There may have 
> > been a pump down when you performed your last test or there maybe valves 
> > within the city supply that are partially open causing your loss.    
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> > Paul D. Kimble
> >
> >   
> >
> > VP Operations
> >
> >   
> >
> > A.S. Barlin Associates, Inc.
> >
> >   
> >
> >  [email protected] (mailto:[email protected])
> >
> >   
> >
> > (973) 696-6601 Office
> >
> >   
> >
> > (973) 632-8341 Cell
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > From:   Eric Rieve  <[email protected] (mailto:[email protected])>
> >   Sent:  Monday, July 1, 2024 8:27 AM
> >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >
> > Brian,
> >
> >   
> >
> >   
> >
> >   
> >
> > I have the feeling that messing around with something complicated like a 
> > break-tank and having to rearrange your fire pump wouldn’t be worth it 
> > compared to simply installing a 30-minute duration dry hydrant on the 
> > property. It would be a lot larger tank but would guarantee you have a 
> > dedicated water supply volume just for standpipes.
> >
> >   
> >
> >   
> >
> >   
> >
> > If your city water supply has already lost 25% of it’s capacity, trying to 
> > design a work-around based on the new number is just setting the property 
> > up for having to go through the entire exercise again when the supply gets 
> > even worse. Taking the standpipe demand out altogether also benefits the 
> > sprinkler system’s design longevity since you’ll have significantly reduced 
> > the demand going forward.
> >
> >   
> >
> >   
> >
> >   
> >
> > Just my two cents.
> >
> >   
> >
> >   
> >
> >   
> >
> > Hope this helps,
> >
> >   
> >
> > Eric Rieve, SET
> >  Rieve Fire Protection
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > From:   Brian Harris  <[email protected] 
> > (mailto:[email protected])>
> >   Sent:  Monday, July 1, 2024 7:53 AM
> >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >
> > Travis-
> >
> >   
> >
> > Yes,  &  yes. My question was since the system was designed and installed 
> > the water supply now is about 3/4 of what it was. We are looking to 
> > supplement the city supply with a water tank since the fire truck shuts 
> > down before we can get the 1000gpm. The city supply is running out of 
> > water. I was curious as to the sizing of a supplemental tank. I see if it’s 
> > only supplied by a tank, it needs a 30-minute duration. Since the city is 
> > capable of supplying “most” of the demand I looking for the best way would 
> > be to properly size a tank.
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> >  Thank you,
> >
> >   
> >
> >     
> >
> >   
> >
> >  Brian Harris, CET
> >
> >   
> >
> >  BVS Systems Inc.
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > From:   Travis Mack  <[email protected] (mailto:[email protected])>
> >   Sent:  Monday, July 1, 2024 7:45 AM
> >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > I doubt that school is tall enough to    be a high rise. Manual is allowed 
> > per NFPA 14. Do you know what a manual standpipe is? If so, contact the AHJ 
> > to find out what they require you use as a supply value.    A manual 
> > standpipe has its supply as the FDC. So calculate as the FDC as your supply 
> > with the values the ahj provides. It’s likely going to be something like 
> > 150 psi at 1000 gpm.   
> >
> >   
> >   
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > Travis Mack, SET
> >
> >   
> >
> > M.E.P.CAD   |   
> >
> >   
> >
> > 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
> >
> >   
> >
> > www.mepcad.com (http://www.mepcad.com/)   |   m:   480.547.9348
> >
> >   
> >
> >   
> >
> >   
> >
> > AutoSPRINK    |    AutoSPRINK FAB    |    AutoSPRINK RVT    |    AlarmCAD
> >
> >   
> >
> >   
> >
> >   
> >
> > Book appointment time in my calendar
> >
> >   
> >
> > https://calendly.com/t_mack_mepcad
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >  From:    Brian Harris  <[email protected] 
> > (mailto:[email protected])>
> >   Sent:  Monday, July 1, 2024 4:38:05 AM
> >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >  Yasser
> >
> >   
> >
> >     
> >
> >   
> >
> >  Thank you,
> >
> >   
> >
> >     
> >
> >   
> >
> >  Brian Harris, CET
> >
> >   
> >
> >  BVS Systems Inc.
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > From:   Yasser Amer Ahmed  <[email protected] 
> > (mailto:[email protected])>
> >   Sent:  Monday, July 1, 2024 6:44 AM
> >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >
> > Hi Brian,
> >
> >   
> >
> >   
> >
> >   
> >
> > As per NFPA-14, 5.2 (2024 Ed.) 5.2 Minimum Supply for Class I, Class D, and 
> > Class III Systems. The minimum water supply shall be capable of providing 
> > the system de1nand established by Chapter 10 for at least 30 minutes.
> >
> >   
> >
> >   
> >
> >   
> >
> > All Gratitude,
> >
> >   
> >
> >   
> >
> >   
> >
> > Yasser Amer Ahmed
> >
> >   
> >
> > Fire Protection  &  Plumbing Specialist
> >
> >   
> >
> > Registered Fire Protection Consultant
> >
> >   
> >
> > MBA,  LEED AP BD+C™, CPD, CFPS, MIFireE, PMSFPE
> >
> >   
> >
> >   
> >
> >   
> >
> >
> >
> >   
> >
> >   
> >
> >   
> >
> > Smart Village, Cairo-Alexandria Desert Road
> >
> >   
> >
> > Street 26, Building 10
> >
> >   
> >
> > P.O. Box: 129, Giza 12577, Egypt
> >
> >   
> >
> > Tel: +202 3531 8000
> >
> >   
> >
> > Fax: +202 3537 1223
> >
> >   
> >
> >   dar.com 
> > (https://urldefense.proofpoint.com/v2/url?u=http-3A__dar.com_&d=DwMFAg&c=0YGvTs3tT-VMy8_v51yLDw&r=BPv183lhQEq9N7uN6BtSUYy-qO1aQth8MfS3CXy9v8o&m=AwHdiOGHCF__Z72zfS9hXpv57AcrHPsoC4nxS7tvlkY&s=RZxKhKFy24ZwTQD2ONzIVG3oH1WAdGB-GK2L6HoX0Fs&e=)
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> > (https://urldefense.proofpoint.com/v2/url?u=http-3A__dar.com_&d=DwMFAg&c=0YGvTs3tT-VMy8_v51yLDw&r=BPv183lhQEq9N7uN6BtSUYy-qO1aQth8MfS3CXy9v8o&m=AwHdiOGHCF__Z72zfS9hXpv57AcrHPsoC4nxS7tvlkY&s=RZxKhKFy24ZwTQD2ONzIVG3oH1WAdGB-GK2L6HoX0Fs&e=)
> >
> >   
> >
> > Please consider the environment before printing this document
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > From:   Travis Mack  <[email protected] (mailto:[email protected])>
> >   Sent:  Monday, July 1, 2024 1:34 PM
> >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >
> >  ! External Email, Use Caution !
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >
> > Is it a high rise or mid rise? If mid rise, calc it to the FDC and be done. 
> > If a high rise and automatic standpipe, check NFPA 14. The duration is 30 
> > minutes.    So that is how you would size a tank.   
> >
> >   
> >   
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > Travis Mack, SET
> >
> >   
> >
> > M.E.P.CAD   |   
> >
> >   
> >
> > 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
> >
> >   
> >
> >  www.mepcad.com 
> > (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mepcad.com%2f&c=E,1,-4N2RZKUba_tdy65g6bmxh0QKzZyB4IFxh7FewvPS08dfMil9SJ7e-nULD3iv8Tco6tXDK1EfeIYVTl6v8gt_jeh3nwQJShLejhSBFPVdWqVOxQnapv-TMIHA6g,&typo=1)
> >    |   m:   480.547.9348
> >
> >   
> >
> >   
> >
> >   
> >
> > AutoSPRINK    |    AutoSPRINK FAB    |    AutoSPRINK RVT    |    AlarmCAD
> >
> >   
> >
> >   
> >
> >   
> >
> > Book appointment time in my calendar
> >
> >   
> >
> > https://calendly.com/t_mack_mepcad
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >  From:    Brian Harris  <[email protected] 
> > (mailto:[email protected])>
> >   Sent:  Monday, July 1, 2024 3:31:59 AM
> >   To:   [email protected] 
> > (mailto:[email protected])     
> > <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  [Sprinklerforum] Water Tank for Standpipe
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >   
> >
> > We have a project where the water supply has degraded a good bit since 
> > installation was completed. Sprinkler system and pump test all pass but the 
> > standpipe test runs out of water. Only thing I can think of to help would 
> > be a water tank but how would you even size one since the “duration” of a 
> > standpipe test is open ended? Any other thoughts?
> >
> >   
> >
> >   
> >
> >   
> >
> > Thank you,
> >
> >   
> >
> >   
> >
> >   
> >
> > Brian Harris, CET
> >
> >   
> >
> > BVS Systems Inc.
> >
> >   
> >
> >   bvssystemsinc.com 
> > (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,DxViP7dSzV-R2rx5fGIyoL1vsDK_tTbfrJamJJsCEkhMVaCVUXX3uMknt5ksggBpEfXELKFUusTuDEcjOcvs4e1Xf-ZA6si2AAvUiof7pgyIcg,,&typo=1)
> >
> >   
> >
> > Phone: 704.896.9989
> >
> >   
> >
> > Fax: 704.896.1935
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> >   
> >   
> >   
> >  Confidentiality  &  Disclaimer Note: This e-mail (including any 
> > attachments) contain protected and confidential information intended for 
> > the sole use of the individual or organization addressee. If you are not 
> > the addressee or an authorized agent acting on their behalf, or if you have 
> > received this message by error, please notify the sender immediately be 
> > returning the message. It must not be copied, distributed or used in any 
> > other way but should be immediately deleted from your system.
> >   
> >  While Dar and the Dar Group strive to maintain high standards of 
> > communication, reliability, authenticity and integrity, neither shall be 
> > liable for the improper or incomplete transmission of the information 
> > contained in this communication nor for any delay in its receipt or damage 
> > to your system. Neither Dar nor the Dar Group guarantees that the integrity 
> > of this communication has been maintained or that this communication is 
> > free of viruses, interceptions or interference.
> >   
> > Confidentiality  &  Disclaimer Note: This e-mail (including any 
> > attachments) contain protected and confidential information intended for 
> > the sole use of the individual or organization addressee. If you are not 
> > the addressee or an authorized agent acting on their behalf, or if you have 
> > received this message by error, please notify the sender immediately be 
> > returning the message. It must not be copied, distributed or used in any 
> > other way but should be immediately deleted from your system. While Dar and 
> > the Dar Group strive to maintain high standards of communication, 
> > reliability, authenticity and integrity, neither shall be liable for the 
> > improper or incomplete transmission of the information contained in this 
> > communication nor for any delay in its receipt or damage to your system. 
> > Neither Dar nor the Dar Group guarantees that the integrity of this 
> > communication has been maintained or that this communication is free of 
> > viruses, interceptions or interference.
> >
> >   
> >   
> >   
> >
> >  _________________________________________________________ SprinklerForum 
> > mailing list:   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])
> >
> >   
> >   
>   
>   
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to