Travis-
It's a 4-story multi-use/school, manual wet standpipe. Not 100% sure I'm 
following "calc it to the FDC"?

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Travis Mack <[email protected]>
Sent: Monday, July 1, 2024 6:34 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

Is it a high rise or mid rise? If mid rise, calc it to the FDC and be done. If 
a high rise and automatic standpipe, check NFPA 14. The duration is 30 minutes. 
 So that is how you would size a tank.


Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad

________________________________
From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 3:31:59 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Water Tank for Standpipe


We have a project where the water supply has degraded a good bit since 
installation was completed. Sprinkler system and pump test all pass but the 
standpipe test runs out of water. Only thing I can think of to help would be a 
water tank but how would you even size one since the "duration" of a standpipe 
test is open ended? Any other thoughts?



Thank you,



Brian Harris, CET

BVS Systems Inc.

bvssystemsinc.com<http://bvssystemsinc.com/>

Phone: 704.896.9989

Fax: 704.896.1935