What Cliff said.

Among the issues I have to suggest you ask is "why" the city supply has diminished.  And, as always, I agree with Cliff, it's likely not the responsibility of the building owner (school district?) to sort out the "why" issues.

hope this helps,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235

Phone: (760) 745-6181
Visit the website

 

On 7/1/2024 10:03 AM, [email protected] wrote:

Hi Brian,

 

I may be completely off base on this  but, if the city supply can’t supply 1000 gpm to the site and it could at some point in time, it sounds like they have an issue with their underground piping.  They need to start looking for a partially closed isolation valve in their system.  It’s either that or an obstruction in their line.  Either way, I don’t think it’s the building owner’s responsibility to solve the City’s issue.

 

Cliff Whitfield, SET

President

 

Fire Design, Inc.

940 Summerbrooke Dr

Tallahassee, FL 32312

Ph: 828-284-4772

Description: New FDI Logo-4.jpg

 

From: Brian Harris <[email protected]>
Sent: Monday, July 1, 2024 10:57 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

 

Mostly volume, slight pressure.

 

Thank you,

 

Brian Harris, CET

BVS Systems Inc.

 

From: Fpdcdesign <[email protected]>
Sent: Monday, July 1, 2024 9:55 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

 

Volume or pressure?

 

Todd Williams 

Fire Protection Design/Consulting

Stonington, CT

860-608-4559



On Jul 1, 2024 at 9:25 AM, <Brian Harris> wrote:

Todd-

Yes, it’s a manual wet standpipe. Problem is the city supply has dropped a fair amount and now the standpipe test won’t pass.

 

Thank you,

 

Brian Harris, CET

BVS Systems Inc.

 

From: Fpdcdesign <[email protected]>
Sent: Monday, July 1, 2024 9:21 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

 

Isn’t this a 4 story building? Below the high rise threshold, I assume. Can it be a manual wet standpipe? 

 

Todd Williams 

Fire Protection Design/Consulting

Stonington, CT

860-608-4559




On Jul 1, 2024 at 9:09 AM, <Paul Kimble> wrote:

Has anyone done a valued engineering survey of the city water supply and compared the original water test provided to the current. Is the city supply a gravity fed system or a system utilizing pumps? There may have been a pump down when you performed your last test or there maybe valves within the city supply that are partially open causing your loss.  

 

Paul D. Kimble

VP Operations

A.S. Barlin Associates, Inc.

[email protected]

(973) 696-6601 Office

(973) 632-8341 Cell

 

From: Eric Rieve <[email protected]>
Sent: Monday, July 1, 2024 8:27 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

 

Brian,

 

I have the feeling that messing around with something complicated like a break-tank and having to rearrange your fire pump wouldn’t be worth it compared to simply installing a 30-minute duration dry hydrant on the property. It would be a lot larger tank but would guarantee you have a dedicated water supply volume just for standpipes.

 

If your city water supply has already lost 25% of it’s capacity, trying to design a work-around based on the new number is just setting the property up for having to go through the entire exercise again when the supply gets even worse. Taking the standpipe demand out altogether also benefits the sprinkler system’s design longevity since you’ll have significantly reduced the demand going forward.

 

Just my two cents.

 

Hope this helps,

Eric Rieve, SET
Rieve Fire Protection

 

From: Brian Harris <[email protected]>
Sent: Monday, July 1, 2024 7:53 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

 

Travis-

Yes, & yes. My question was since the system was designed and installed the water supply now is about 3/4 of what it was. We are looking to supplement the city supply with a water tank since the fire truck shuts down before we can get the 1000gpm. The city supply is running out of water. I was curious as to the sizing of a supplemental tank. I see if it’s only supplied by a tank, it needs a 30-minute duration. Since the city is capable of supplying “most” of the demand I looking for the best way would be to properly size a tank.

 

Thank you,

 

Brian Harris, CET

BVS Systems Inc.

 

From: Travis Mack <[email protected]>
Sent: Monday, July 1, 2024 7:45 AM
To: Discussion list on issues relating to automatic fire sprinklers <
[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

 

I doubt that school is tall enough to  be a high rise. Manual is allowed per NFPA 14. Do you know what a manual standpipe is? If so, contact the AHJ to find out what they require you use as a supply value.  A manual standpipe has its supply as the FDC. So calculate as the FDC as your supply with the values the ahj provides. It’s likely going to be something like 150 psi at 1000 gpm. 

 

Travis Mack, SET

M.E.P.CAD | 

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com | m: 480.547.9348

 

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

 

Book appointment time in my calendar

https://calendly.com/t_mack_mepcad

 


From: Brian Harris <[email protected]>
Sent: Monday, July 1, 2024 4:38:05 AM
To: Discussion list on issues relating to automatic fire sprinklers <
[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

 

Yasser

 

Thank you,

 

Brian Harris, CET

BVS Systems Inc.

 

From: Yasser Amer Ahmed <[email protected]>
Sent: Monday, July 1, 2024 6:44 AM
To: Discussion list on issues relating to automatic fire sprinklers <
[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

 

Hi Brian,

 

As per NFPA-14, 5.2 (2024 Ed.) 5.2 Minimum Supply for Class I, Class D, and Class III Systems. The minimum water supply shall be capable of providing the system de1nand established by Chapter 10 for at least 30 minutes.

 

All Gratitude,

 

Yasser Amer Ahmed

Fire Protection & Plumbing Specialist

Registered Fire Protection Consultant

MBA, LEED AP BD+C™, CPD, CFPS, MIFireE, PMSFPE

 

 

Smart Village, Cairo-Alexandria Desert Road

Street 26, Building 10

P.O. Box: 129, Giza 12577, Egypt

Tel: +202 3531 8000

Fax: +202 3537 1223

dar.com

 

Please consider the environment before printing this document

 

 

 

From: Travis Mack <[email protected]>
Sent: Monday, July 1, 2024 1:34 PM
To: Discussion list on issues relating to automatic fire sprinklers <
[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

 

! External Email, Use Caution !

 

Is it a high rise or mid rise? If mid rise, calc it to the FDC and be done. If a high rise and automatic standpipe, check NFPA 14. The duration is 30 minutes.  So that is how you would size a tank. 

 

Travis Mack, SET

M.E.P.CAD | 

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com | m: 480.547.9348

 

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

 

Book appointment time in my calendar

https://calendly.com/t_mack_mepcad

 


From: Brian Harris <[email protected]>
Sent: Monday, July 1, 2024 3:31:59 AM
To:
[email protected] <[email protected]>
Subject: [Sprinklerforum] Water Tank for Standpipe

 

We have a project where the water supply has degraded a good bit since installation was completed. Sprinkler system and pump test all pass but the standpipe test runs out of water. Only thing I can think of to help would be a water tank but how would you even size one since the “duration” of a standpipe test is open ended? Any other thoughts?

 

Thank you,

 

Brian Harris, CET

BVS Systems Inc.

bvssystemsinc.com

Phone: 704.896.9989

Fax: 704.896.1935

 

 





Confidentiality & Disclaimer Note: This e-mail (including any attachments) contain protected and confidential information intended for the sole use of the individual or organization addressee. If you are not the addressee or an authorized agent acting on their behalf, or if you have received this message by error, please notify the sender immediately be returning the message. It must not be copied, distributed or used in any other way but should be immediately deleted from your system.

While Dar and the Dar Group strive to maintain high standards of communication, reliability, authenticity and integrity, neither shall be liable for the improper or incomplete transmission of the information contained in this communication nor for any delay in its receipt or damage to your system. Neither Dar nor the Dar Group guarantees that the integrity of this communication has been maintained or that this communication is free of viruses, interceptions or interference.

Confidentiality & Disclaimer Note: This e-mail (including any attachments) contain protected and confidential information intended for the sole use of the individual or organization addressee. If you are not the addressee or an authorized agent acting on their behalf, or if you have received this message by error, please notify the sender immediately be returning the message. It must not be copied, distributed or used in any other way but should be immediately deleted from your system. While Dar and the Dar Group strive to maintain high standards of communication, reliability, authenticity and integrity, neither shall be liable for the improper or incomplete transmission of the information contained in this communication nor for any delay in its receipt or damage to your system. Neither Dar nor the Dar Group guarantees that the integrity of this communication has been maintained or that this communication is free of viruses, interceptions or interference.

_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]

_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]


Virus-free.www.avast.com

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to