Size it as a break tank.  Take the volume needed for your duration minus the 
volume available from the supply.  The difference would be your minimum tank 
volume.

Thomas R. Worley
  Estimator/Design Manager
  Fire Foe Corp.
  999 Trumbull Ave.
  Girard, OH 44420
  P: 330-759-9834 x112
  F: 330-759-8949
  E: [email protected]<mailto:[email protected]>
[cid:[email protected]]<http://www.firefoe.com/>

From: Brian Harris <[email protected]>
Sent: Monday, July 1, 2024 7:53 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

Travis-
Yes, & yes. My question was since the system was designed and installed the 
water supply now is about 3/4 of what it was. We are looking to supplement the 
city supply with a water tank since the fire truck shuts down before we can get 
the 1000gpm. The city supply is running out of water. I was curious as to the 
sizing of a supplemental tank. I see if it's only supplied by a tank, it needs 
a 30-minute duration. Since the city is capable of supplying "most" of the 
demand I looking for the best way would be to properly size a tank.

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Travis Mack <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 7:45 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

I doubt that school is tall enough to  be a high rise. Manual is allowed per 
NFPA 14. Do you know what a manual standpipe is? If so, contact the AHJ to find 
out what they require you use as a supply value.  A manual standpipe has its 
supply as the FDC. So calculate as the FDC as your supply with the values the 
ahj provides. It's likely going to be something like 150 psi at 1000 gpm.


Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad

________________________________
From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 4:38:05 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe


Yasser



Thank you,



Brian Harris, CET

BVS Systems Inc.



From: Yasser Amer Ahmed <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 6:44 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe



Hi Brian,



As per NFPA-14, 5.2 (2024 Ed.) 5.2 Minimum Supply for Class I, Class D, and 
Class III Systems. The minimum water supply shall be capable of providing the 
system de1nand established by Chapter 10 for at least 30 minutes.



All Gratitude,



Yasser Amer Ahmed

Fire Protection & Plumbing Specialist

Registered Fire Protection Consultant

MBA, LEED AP BD+C(tm), CPD, CFPS, MIFireE, PMSFPE



[cid:[email protected]]



Smart Village, Cairo-Alexandria Desert Road

Street 26, Building 10

P.O. Box: 129, Giza 12577, Egypt

Tel: +202 3531 8000

Fax: +202 3537 1223

dar.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__dar.com_&d=DwMFAg&c=0YGvTs3tT-VMy8_v51yLDw&r=BPv183lhQEq9N7uN6BtSUYy-qO1aQth8MfS3CXy9v8o&m=AwHdiOGHCF__Z72zfS9hXpv57AcrHPsoC4nxS7tvlkY&s=RZxKhKFy24ZwTQD2ONzIVG3oH1WAdGB-GK2L6HoX0Fs&e=>



[cid:[email protected]]<https://urldefense.proofpoint.com/v2/url?u=http-3A__dar.com_&d=DwMFAg&c=0YGvTs3tT-VMy8_v51yLDw&r=BPv183lhQEq9N7uN6BtSUYy-qO1aQth8MfS3CXy9v8o&m=AwHdiOGHCF__Z72zfS9hXpv57AcrHPsoC4nxS7tvlkY&s=RZxKhKFy24ZwTQD2ONzIVG3oH1WAdGB-GK2L6HoX0Fs&e=>

Please consider the environment before printing this document







From: Travis Mack <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 1:34 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe



! External Email, Use Caution !



Is it a high rise or mid rise? If mid rise, calc it to the FDC and be done. If 
a high rise and automatic standpipe, check NFPA 14. The duration is 30 minutes. 
 So that is how you would size a tank.



Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mepcad.com%2f&c=E,1,-4N2RZKUba_tdy65g6bmxh0QKzZyB4IFxh7FewvPS08dfMil9SJ7e-nULD3iv8Tco6tXDK1EfeIYVTl6v8gt_jeh3nwQJShLejhSBFPVdWqVOxQnapv-TMIHA6g,&typo=1>
 | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad



________________________________

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 3:31:59 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Water Tank for Standpipe



We have a project where the water supply has degraded a good bit since 
installation was completed. Sprinkler system and pump test all pass but the 
standpipe test runs out of water. Only thing I can think of to help would be a 
water tank but how would you even size one since the "duration" of a standpipe 
test is open ended? Any other thoughts?



Thank you,



Brian Harris, CET

BVS Systems Inc.

bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,DxViP7dSzV-R2rx5fGIyoL1vsDK_tTbfrJamJJsCEkhMVaCVUXX3uMknt5ksggBpEfXELKFUusTuDEcjOcvs4e1Xf-ZA6si2AAvUiof7pgyIcg,,&typo=1>

Phone: 704.896.9989

Fax: 704.896.1935





________________________________



Confidentiality & Disclaimer Note: This e-mail (including any attachments) 
contain protected and confidential information intended for the sole use of the 
individual or organization addressee. If you are not the addressee or an 
authorized agent acting on their behalf, or if you have received this message 
by error, please notify the sender immediately be returning the message. It 
must not be copied, distributed or used in any other way but should be 
immediately deleted from your system.

While Dar and the Dar Group strive to maintain high standards of communication, 
reliability, authenticity and integrity, neither shall be liable for the 
improper or incomplete transmission of the information contained in this 
communication nor for any delay in its receipt or damage to your system. 
Neither Dar nor the Dar Group guarantees that the integrity of this 
communication has been maintained or that this communication is free of 
viruses, interceptions or interference.

Confidentiality & Disclaimer Note: This e-mail (including any attachments) 
contain protected and confidential information intended for the sole use of the 
individual or organization addressee. If you are not the addressee or an 
authorized agent acting on their behalf, or if you have received this message 
by error, please notify the sender immediately be returning the message. It 
must not be copied, distributed or used in any other way but should be 
immediately deleted from your system. While Dar and the Dar Group strive to 
maintain high standards of communication, reliability, authenticity and 
integrity, neither shall be liable for the improper or incomplete transmission 
of the information contained in this communication nor for any delay in its 
receipt or damage to your system. Neither Dar nor the Dar Group guarantees that 
the integrity of this communication has been maintained or that this 
communication is free of viruses, interceptions or interference.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to