The array of tables are about 1000 sqft each
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On May 13, 2024 at 10:42 AM,  <Spencer Tomlinson 
> (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
> I’m in the 2019 edition, but sections 9.5.5.3.1.5 and 9.5.5.3.2 may help 
> provide guidance.    They do not up the hazard level due to an obstruction in 
> place, I like the idea of taking into effect a shielded fire, especially with 
> the size of some of these grow ops these days, but there are certain 
> provisions that would suggest otherwise….
>
>   
>
>   
>
>   
>   
>
>  Spencer Tomlinson, PE
>
>   
>
>  Owner, Fire Protection Engineer
>
>   
>
>     
>
>   
>
>
>
>   
>
>       Cell: 620-955-7293
>
>   
>   
>
>   
>
>   
>   
>   
>
> From:  Fpdcdesign  <[email protected]>
>   Sent:  Monday, May 13, 2024 9:32 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected]>
>   Subject:  [Sprinklerforum] Re: Cannabis growing
>
>   
>   
>   
>
>   
>
>   
>   
>
> Travis, The definition of EH2 and section 19.3.3.1.5 both deal with 
> protection where there are unprotected spaces adjacent or within. The big 
> difference is the word “extensive” in the EH2 definition. From what I have 
> seen below grow tables it is a very wet environment with most of the 
> combustibles being water and non-water filled PVC pipe. I’m not sure that 
> would rise to extensive. The other argument if below the tables can be 
> considered    a “concealed space”. Since there is no NFPA definition, we need 
> to go to a dictionary definition. My dictionary say the definition of conceal 
> is “to hide from view”. Nothing that talks about physical separation. I think 
> this would meet that criteria.      
>
>   
>   
>
>   
>
>   
>   
>   
>
> Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>   
>   
>   
>
> 860-554-7054 (tel:860-554-7054)     (fax)
>
>   
>   
>   
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>   
>   
>   
>   
>   
>   
>
>
>   
>   
>
>
>   
> >   
> >   
> >
> > On May 13, 2024 at 10:07 AM,  <Travis Mack (mailto:[email protected])>  
> > wrote:
> >
> >   
> >   
> >   
> >   
> >   
> >
> > The 3000 sq ft is specifically for unprotected concealed combustible 
> > spaces. So I don’t see how that could be used as you don’t have that from 
> > what you describe.   
> >
> >   
> >   
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > Travis Mack, SET
> >
> >   
> >
> > M.E.P.CAD   |   
> >
> >   
> >
> > 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
> >
> >   
> >
> >  www.mepcad.com 
> > (https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mepcad.com_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=SMKi3MpB_L04QTNOI8wsXTbQAi8Ov0kr5kJ9QWv4K58&m=Rt2Ku0kdmBZShB-fHbPlOHh8rfl-aQkPP6VbfAr-e7kT2fRmXYAjbMGp_kV4Nqy3&s=UpVuXPq25y_S_GAXByMhUQqOZrb0zMeyhfjGV8qVydo&e=)
> >    |   m:   480.547.9348
> >
> >   
> >
> >   
> >
> >   
> >
> > AutoSPRINK    |    AutoSPRINK FAB    |    AutoSPRINK RVT    |    AlarmCAD
> >
> >   
> >
> >   
> >
> >   
> >
> > Book appointment time in my calendar
> >
> >   
> >
> >   https://calendly.com/t_mack_mepcad 
> > (https://urldefense.proofpoint.com/v2/url?u=https-3A__calendly.com_t-5Fmack-5Fmepcad&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=SMKi3MpB_L04QTNOI8wsXTbQAi8Ov0kr5kJ9QWv4K58&m=Rt2Ku0kdmBZShB-fHbPlOHh8rfl-aQkPP6VbfAr-e7kT2fRmXYAjbMGp_kV4Nqy3&s=Mqd76qng9bxij52cNbe4j_54BKlqyfyCL638vCVKos8&e=)
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >
> > From:   Fpdcdesign  <[email protected] (mailto:[email protected])>
> >   Sent:  Monday, May 13, 2024 7:05:28 AM
> >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  [Sprinklerforum] Re: Cannabis growing
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >   
> >
> > Travis, What I have run into out here is that the grow tables are not fixed 
> > in place. Consequently, they become “furniture” and protection is not 
> > installed underneath. (I am trying to get that information). If they are 
> > not fixed, does the 3000 sqft area increase apply or do we go to EH2?   
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > Todd G Williams, PE
> >
> >   
> >   
> >
> > Fire Protection Design/Consulting
> >
> >   
> >   
> >   
> >
> > Stonington, CT
> >
> >   
> >   
> >   
> >
> > 860-535-2080 (tel:860-535-2080)  (ofc)
> >
> >   
> >   
> >   
> >
> > 860-554-7054 (tel:860-554-7054)     (fax)
> >
> >   
> >   
> >   
> >
> > 860-608-4559 (tel:860-608-4559)  (cell)
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >
> >   
> >   
> >
> >
> >   
> > >   
> > >   
> > >
> > > On May 13, 2024 at 9:25 AM,  <Travis Mack (mailto:[email protected])>  
> > > wrote:
> > >
> > >   
> > >   
> > >   
> > >   
> > >
> > > What unprotected concealed combustible spaces are you referencing?    The 
> > > 3000 sq ft is for that.    Typically with grow houses, we have put 
> > > sprinklers under the racks of tables, if I am understanding correctly 
> > > what you are describing.   
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >
> > > These houses are definitely a unique protection scheme and it seems the 
> > > ways of the growers changing things to maximize product growth is ever 
> > > changing and does need a constant review.
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >
> > > I have seen some where the tables slid along a racking system.    It was 
> > > similar in concept to movable rack storage.    Since we couldn’t put 
> > > sprinklers below the table areas, the AHJ said to protect as a heavily 
> > > shielded fire and do the overhead system as EH2.    I’m not sure if that 
> > > is the best method, but it did get it through in that particular 
> > > jurisdiction.
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >
> > > Travis Mack, SET
> > >
> > >   
> > >
> > > M.E.P.CAD| Instructor / Support
> > >
> > >   
> > >
> > > 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
> > >
> > >   
> > >
> > >  www.mepcad.com 
> > > (https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mepcad.com_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=SMKi3MpB_L04QTNOI8wsXTbQAi8Ov0kr5kJ9QWv4K58&m=Rt2Ku0kdmBZShB-fHbPlOHh8rfl-aQkPP6VbfAr-e7kT2fRmXYAjbMGp_kV4Nqy3&s=UpVuXPq25y_S_GAXByMhUQqOZrb0zMeyhfjGV8qVydo&e=)
> > >    |  m: 480.547.9348|  Whatspp: +14805479348
> > >
> > >   
> > >
> > > Email:  [email protected] (mailto:[email protected])
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >
> > > AutoSPRINK    |    AutoSPRINK FAB    |    AutoSPRINK RVT    |    AlarmCAD
> > >
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >
> > > From:   Fpdcdesign  <[email protected] (mailto:[email protected])>
> > >   Sent:  Monday, May 13, 2024 4:49 AM
> > >   To:  Sprinklerforum  <[email protected] 
> > > (mailto:[email protected])>
> > >   Subject:  [Sprinklerforum] Cannabis growing
> > >
> > >   
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >
> > > I know that NFPA 420 is coming but I believe has not been issued yet. I 
> > > have been asked to look at a new growing facility. NFPA 13 calls out 
> > > agriculture facilities os OH2, which make sense for this occupancy. My 
> > > question comes from the tables. The tables are portable so sprinklers are 
> > > required underneath. However, does the 3000 sqft demand area for 
> > > unprotected spaces come into play? I would like to do something that is 
> > > at least close to what 420 will be recommending.   
> > >
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >
> > > Todd G Williams, PE
> > >
> > >   
> > >   
> > >
> > > Fire Protection Design/Consulting
> > >
> > >   
> > >   
> > >   
> > >
> > > Stonington, CT
> > >
> > >   
> > >   
> > >   
> > >
> > > 860-535-2080 (tel:860-535-2080)  (ofc)
> > >
> > >   
> > >   
> > >   
> > >
> > > 860-554-7054 (tel:860-554-7054)     (fax)
> > >
> > >   
> > >   
> > >   
> > >
> > > 860-608-4559 (tel:860-608-4559)  (cell)
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > >  _________________________________________________________ SprinklerForum 
> > > mailing list:   
> > > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > >   To unsubscribe send an email to  
> > > [email protected] 
> > > (mailto:[email protected])
> > >
> > >   
> > >   
> >   
> >   
> >   
> >   
> >
> >  _________________________________________________________ SprinklerForum 
> > mailing list:   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])
> >
> >   
> >   
>   
>   
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to