What unprotected concealed combustible spaces are you referencing?  The 3000 sq 
ft is for that.  Typically with grow houses, we have put sprinklers under the 
racks of tables, if I am understanding correctly what you are describing.

These houses are definitely a unique protection scheme and it seems the ways of 
the growers changing things to maximize product growth is ever changing and 
does need a constant review.

I have seen some where the tables slid along a racking system.  It was similar 
in concept to movable rack storage.  Since we couldn’t put sprinklers below the 
table areas, the AHJ said to protect as a heavily shielded fire and do the 
overhead system as EH2.  I’m not sure if that is the best method, but it did 
get it through in that particular jurisdiction.


Travis Mack, SET
M.E.P.CAD | Instructor / Support
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348
Email: [email protected]

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: Fpdcdesign <[email protected]>
Sent: Monday, May 13, 2024 4:49 AM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] Cannabis growing

I know that NFPA 420 is coming but I believe has not been issued yet. I have 
been asked to look at a new growing facility. NFPA 13 calls out agriculture 
facilities os OH2, which make sense for this occupancy. My question comes from 
the tables. The tables are portable so sprinklers are required underneath. 
However, does the 3000 sqft demand area for unprotected spaces come into play? 
I would like to do something that is at least close to what 420 will be 
recommending.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to