Todd, the concealed spaces referenced in NFPA 13 are all regarding the 
construction of the building being protected.  The tables you describe would be 
defined as furniture and would not fit into the area of concealed spaces.  Just 
an AHJ point of view, but I believe supported strongly by the standard.

From: Fpdcdesign <[email protected]>
Sent: Monday, May 13, 2024 7:32 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Cannabis growing


⚠ CAUTION: External Email
Travis, The definition of EH2 and section 19.3.3.1.5 both deal with protection 
where there are unprotected spaces adjacent or within. The big difference is 
the word “extensive� in the EH2 definition. From what I have seen below grow 
tables it is a very wet environment with most of the combustibles being water 
and non-water filled PVC pipe. I’m not sure that would rise to extensive. The 
other argument if below the tables can be considered  a “concealed space�. 
Since there is no NFPA definition, we need to go to a dictionary definition. My 
dictionary say the definition of conceal is “to hide from view�. Nothing that 
talks about physical separation. I think this would meet that criteria.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)



On May 13, 2024 at 10:07 AM, <Travis Mack<mailto:[email protected]>> wrote:
The 3000 sq ft is specifically for unprotected concealed combustible spaces. So 
I don’t see how that could be used as you don’t have that from what you 
describe.


Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<https://urldefense.com/v3/__http:/www.mepcad.com/__;!!Lat9tvSZzw!hYW1c0quXj-tgkI7jtJeIADFs0UzZRCaNt6Klyp5YmmokALS2Z70wQ4QHeW7Vch8LNY7L4j3sJDp9A2MvacwyuUD$>
 | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad<https://urldefense.com/v3/__https:/calendly.com/t_mack_mepcad__;!!Lat9tvSZzw!hYW1c0quXj-tgkI7jtJeIADFs0UzZRCaNt6Klyp5YmmokALS2Z70wQ4QHeW7Vch8LNY7L4j3sJDp9A2MvTXkCk-_$>

________________________________
From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Monday, May 13, 2024 7:05:28 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Cannabis growing

Travis, What I have run into out here is that the grow tables are not fixed in 
place. Consequently, they become “furniture� and protection is not installed 
underneath. (I am trying to get that information). If they are not fixed, does 
the 3000 sqft area increase apply or do we go to EH2?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)



On May 13, 2024 at 9:25 AM, <Travis Mack<mailto:[email protected]>> wrote:

What unprotected concealed combustible spaces are you referencing?  The 3000 sq 
ft is for that.  Typically with grow houses, we have put sprinklers under the 
racks of tables, if I am understanding correctly what you are describing.



These houses are definitely a unique protection scheme and it seems the ways of 
the growers changing things to maximize product growth is ever changing and 
does need a constant review.



I have seen some where the tables slid along a racking system.  It was similar 
in concept to movable rack storage.  Since we couldn’t put sprinklers below the 
table areas, the AHJ said to protect as a heavily shielded fire and do the 
overhead system as EH2.  I’m not sure if that is the best method, but it did 
get it through in that particular jurisdiction.





Travis Mack, SET

M.E.P.CAD | Instructor / Support

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<https://urldefense.com/v3/__http:/www.mepcad.com/__;!!Lat9tvSZzw!hYW1c0quXj-tgkI7jtJeIADFs0UzZRCaNt6Klyp5YmmokALS2Z70wQ4QHeW7Vch8LNY7L4j3sJDp9A2MvacwyuUD$>
 | m: 480.547.9348| Whatspp: +14805479348

Email: [email protected]<mailto:[email protected]>



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Monday, May 13, 2024 4:49 AM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Cannabis growing



I know that NFPA 420 is coming but I believe has not been issued yet. I have 
been asked to look at a new growing facility. NFPA 13 calls out agriculture 
facilities os OH2, which make sense for this occupancy. My question comes from 
the tables. The tables are portable so sprinklers are required underneath. 
However, does the 3000 sqft demand area for unprotected spaces come into play? 
I would like to do something that is at least close to what 420 will be 
recommending.



Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080<tel:860-535-2080> (ofc)

860-554-7054<tel:860-554-7054>  (fax)

860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Lat9tvSZzw!hYW1c0quXj-tgkI7jtJeIADFs0UzZRCaNt6Klyp5YmmokALS2Z70wQ4QHeW7Vch8LNY7L4j3sJDp9A2MveMDC9ID$>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Lat9tvSZzw!hYW1c0quXj-tgkI7jtJeIADFs0UzZRCaNt6Klyp5YmmokALS2Z70wQ4QHeW7Vch8LNY7L4j3sJDp9A2MveMDC9ID$>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to