Denver has been accepting OH2 for grow facilities for a long time. It
doesn't matter if the tables are portable or not.
Kerry L
Kerry L. Madigan, PE
Principal, Sr. Fire Protection Engineer
**
*/VERITAS/*///Fire Engineering, Inc.///
12364 W. Alameda Pkwy, Suite 135
Lakewood, CO 80228
303-985-3300 ext 202
303-985-5594 fax
720-253-3549 cell
On 5/13/2024 5:48 AM, Fpdcdesign wrote:
I know that NFPA 420 is coming but I believe has not been issued yet.
I have been asked to look at a new growing facility. NFPA 13 calls out
agriculture facilities os OH2, which make sense for this occupancy. My
question comes from the tables. The tables are portable so sprinklers
are required underneath. However, does the 3000 sqft demand area for
unprotected spaces come into play? I would like to do something that
is at least close to what 420 will be recommending.
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 <tel:860-535-2080> (ofc)
860-554-7054 <tel:860-554-7054> (fax)
860-608-4559 <tel:860-608-4559> (cell)