Denver has been accepting OH2 for grow facilities for a long time. It doesn't matter if the tables are portable or not.

Kerry L

Kerry L. Madigan, PE

Principal, Sr. Fire Protection Engineer

**

*/VERITAS/*///Fire Engineering, Inc.///

12364 W. Alameda Pkwy, Suite 135

Lakewood, CO 80228

303-985-3300 ext 202

303-985-5594 fax

720-253-3549 cell

On 5/13/2024 5:48 AM, Fpdcdesign wrote:
I know that NFPA 420 is coming but I believe has not been issued yet. I have been asked to look at a new growing facility. NFPA 13 calls out agriculture facilities os OH2, which make sense for this occupancy. My question comes from the tables. The tables are portable so sprinklers are required underneath. However, does the 3000 sqft demand area for unprotected spaces come into play? I would like to do something that is at least close to what 420 will be recommending.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT