Steve,

It should be:
[cid:[email protected]]

Where:
Px= The residual pressure at a particular flow (Qx)
Ps= The static pressure during the flow test
Pr= The residual pressure during the flow test correlating with Qr
Qx= The flow amount correlating with residual pressure being solved for (Px)
Qr= The flow measured during the test correlating with Pr

Though please run the calc through a known water supply  calc just to make sure 
its correct before you use it on an un-known.

Hope this helps!

Thanks,
Eric Rieve, SET
Rieve Fire Protection


From: Steve Leyton <[email protected]>
Sent: Friday, November 10, 2023 1:26 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Flow test adjustment formula

Happy Friday everyone:

Once I’ve taken a flow test, I know the formula for adjusting the flow at a 
particular  residual pressure; it’s published in NFPA 291.   But I’ve lost my 
notes on the corollary formula for calculating the residual pressure at a 
particular flow – does anyone have that handy?   I made cheat sheets years ago 
but they’ve decomposed and become grains in the sands of time…

Steve L.