Thanks Jamie.

I just got it from Kevin Hall – I should have called tech support in the first 
place…

SL

From: Jamie Seidl <[email protected]>
Sent: Friday, November 10, 2023 11:05 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Flow test adjustment formula

If I remember correctly, you can convert your outlet (Flow and pressure) to a K 
factor K=Q/√P  then just solve for P with your flow number (Q/K)₂.

Jamie Seidl

On Fri, Nov 10, 2023 at 1:28 PM Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
Happy Friday everyone:

Once I’ve taken a flow test, I know the formula for adjusting the flow at a 
particular  residual pressure; it’s published in NFPA 291.   But I’ve lost my 
notes on the corollary formula for calculating the residual pressure at a 
particular flow – does anyone have that handy?   I made cheat sheets years ago 
but they’ve decomposed and become grains in the sands of time…

Steve L.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to