TYCO TY3302

Thank you,

Derrek Crigler
Fire Sprinkler Design Manager

7130 Convoy CT, San Diego, CA 92111
o: 858-277-3473 | HillerFire.com

[Logo  Description automatically generated with low confidence]

From: Taylor Schumacher <[email protected]>
Sent: Tuesday, May 23, 2023 11:05 AM
To: '[email protected]' 
<[email protected]>
Subject: [Sprinklerforum] Sidewalls for 18 Inches Down

Does anyone know of a sprinkler that meets the allowance for up 18 inches below 
a ceiling? I have an architect that's quoting that section, but I've never seen 
that unicorn...

8.7.4.1.1.2
Horizontal sidewall sprinklers shall be permitted to be located in a zone 6 in. 
to 12 in. (150 mm to 300 mm) or 12 in. to 18 in. (300 mm to 450 mm) below 
noncombustible and limited-combustible ceilings where listed for such use.


Taylor Schumacher
Security Fire Sprinkler<http://www.j-berd.com/>
1 Industrial Blvd | Sauk Rapids, MN 56379
Office: 320.656.0847 | Direct: 320.640.7050

_________________________________________________________