Does anyone know of a sprinkler that meets the allowance for up 18 inches below 
a ceiling? I have an architect that's quoting that section, but I've never seen 
that unicorn...

8.7.4.1.1.2
Horizontal sidewall sprinklers shall be permitted to be located in a zone 6 in. 
to 12 in. (150 mm to 300 mm) or 12 in. to 18 in. (300 mm to 450 mm) below 
noncombustible and limited-combustible ceilings where listed for such use.


Taylor Schumacher
Security Fire Sprinkler<http://www.j-berd.com/>
1 Industrial Blvd | Sauk Rapids, MN 56379
Office: 320.656.0847 | Direct: 320.640.7050